In message <002401d0eca7$2cb83e30$8628ba90$@cs.com>, dated Fri, 11 Sep 2015, Pete Perkins <0061f3f32d0c-dmarc-requ...@ieee.org> writes: You are going where no man has gone before - to repeat a familiar saying. Let's hope it's not a five-year mission, though. It could easily be. -- OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk When I turn my back on the sun, it's to look for a rainbow John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] requirement for spacings
Bostjan et al, The original ideas that led to insulation coordination were conceived in the early days of electricity when it was clear that failures in the system should be forced into the smaller, cheaper components and not the larger expensive components. Best not to have to replace the generator due to a failure. The long term experience in all of this was captured in IEC 60664 - Insulation Coordination - requirements and was based upon the experience with the extensive power grid in place worldwide. Now a goodly portion of this power grid is being replaced with local sources - such as the windmill or solar panel sources being installed. There are now many more players (such as the ones that you are dealing with) in this business. Not many of them have the same level of experience as the traditional suppliers and, as such, aren't watching all of the same issues in getting into this market. The safety standards for products have been built upon the traditional network practices and should be acceptable in this new electro-space but difficult to apply, as you have found. There will be a lot of pushing and shoving to get the correct set of requirements smoothly running here. From your description the extreme voltage is not an external transient but an expected startup condition of the generator. If it cannot be kept from the dc/dc smps you are designing then you must consider accommodating it. Or, alternatively, since the difference is relatively small between the max tolerance and the occasional peak, you may consider ignoring it and put up with the difficulty it may cause occasionally. None of this provides direct standards guidance but should give you a place to start discussions with the customer and the test house folks. You are going where no man has gone before - to repeat a familiar saying. :>) br, Pete Peter E Perkins, PE Principal Product Safety Engineer PO Box 23427 Tigard, ORe 97281-3427 503/452-1201 fone/fax p.perk...@ieee.org _ _ _ _ _ Hello Rich, I understand your point. Unit is DC/DC converter supplied from generator or windmill. There is a 3 phase rectifier in front of the unit. Wind mild has rated phase voltage 230V tolerances of -15%/+30% (e.g. 195,5-299V). For short period (at start) output voltage can achieve 343V~ (up to 1 min). When you rectify this values you get rated voltage 563Vdc and with considered ac tolerances 480-730Vdc. If you check IEC 60950-1 standard, it says you need to consider for dc mains tolerances of -15%/+20% unless otherwise specified by the manufacturer. For clearances and creepage distances you only need to consider rated voltage (not tolerances) of the product (only 560VDC will be marked on the unit). In this particular case manufacturer specified a bit higher tolerances. There is nothing mention about value of tolerances. I know many products have rated voltage 220-240V and operational voltage range 180-276V. For clearances and creepage distances only 240V was considered. Therefore I am a bit confused what should we consider for determination of working voltage. Is it rated voltage (marked on the unit) or we need to consider also tolerances or even short-term voltage? Best regards, Bostjan -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Thursday, September 10, 2015 12:28 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] requirement for spacings > I can't understand how a 'rated voltage' can be 560 V > +30%/-15%. It must > mean something other than what is normally understood as 'rated > voltage' > in safety standards. In the IEC, rated voltage is a value assigned by the manufacturer. For years, standards committees have attempted to specify one or more formats for the voltage rating. Each standard is different, and sometimes each edition is different. The problem is when a manufacturer uses a single, nominal value. We know that line voltages vary, so standards committees choose, say, +6%, -10%. We have commonly seen wide-ranging power supplies rated 90-250 volts. But, we cannot fault a manufacturer for rating his wide-ranging product as 150 volts, +166%, -60%. With your i-Phone, you can easily calculate whether the equipment will operate on your power line! In this case, the manufacturer has rated his product to operate from 470 to 728 volts. What is wrong? Best regards, Rich - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (i
Re: [PSES] requirement for spacings
In message , dated Thu, 10 Sep 2015, =?iso-8859-2?Q?Bo=B9tjan_Glavi=E8?= writes: Therefore I am a bit confused what should we consider for determination of working voltage. Is it rated voltage (marked on the unit) or we need to consider also tolerances or even short-term voltage? Rated voltage range should not be indicated as percentages, but as '470 V - 728 V' in accordance with IEC/EN 61293. Then it's easier to see that the working voltage for determination of clearance and creepage is at least 728 V, but may be higher, depending on how over-voltages, if they occur, are treated in the relevant safety standard. -- OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk When I turn my back on the sun, it's to look for a rainbow John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] requirement for spacings
In message <002901d0eb4e$c4f177c0$4ed46740$@ieee.org>, dated Wed, 9 Sep 2015, Richard Nute writes: In the IEC, rated voltage is a value assigned by the manufacturer. Agreed; I introduced that simplified definition. For years, standards committees have attempted to specify one or more formats for the voltage rating. Each standard is different, and sometimes each edition is different. Supply voltage rating is a special case, since indeed it may be multi-valued, but few other 'rated values' are multi-valued. IEC 61293 (also EN 61293) (formerly a TC16 document, now TC3) specifies how supply voltage data shall be indicated. This was taken over from an original incentive of TC84. The problem is when a manufacturer uses a single, nominal value. We know that line voltages vary, so standards committees choose, say, +6%, -10%. I'm not sure that's relevant to how the manufacturer *indicates* the rated supply voltage. We have commonly seen wide-ranging power supplies rated 90-250 volts. But, we cannot fault a manufacturer for rating his wide-ranging product as 150 volts, +166%, -60%. Not in accordance with IEC 61293. In any case, we do not know that the 560 V is a supply voltage. With your i-Phone, you can easily calculate whether the equipment will operate on your power line! In this case, the manufacturer has rated his product to operate from 470 to 728 volts. What is wrong? According to IEC 61293, that is indicated by '470 V - 728 V'. -- OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk When I turn my back on the sun, it's to look for a rainbow John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] requirement for spacings
Hello Rich, I understand your point. Unit is DC/DC converter supplied from generator or windmill. There is a 3 phase rectifier in front of the unit. Wind mild has rated phase voltage 230V tolerances of -15%/+30% (e.g. 195,5-299V). For short period (at start) output voltage can achieve 343V~ (up to 1 min). When you rectify this values you get rated voltage 563Vdc and with considered ac tolerances 480-730Vdc. If you check IEC 60950-1 standard, it says you need to consider for dc mains tolerances of -15%/+20% unless otherwise specified by the manufacturer. For clearances and creepage distances you only need to consider rated voltage (not tolerances) of the product (only 560VDC will be marked on the unit). In this particular case manufacturer specified a bit higher tolerances. There is nothing mention about value of tolerances. I know many products have rated voltage 220-240V and operational voltage range 180-276V. For clearances and creepage distances only 240V was considered. Therefore I am a bit confused what should we consider for determination of working voltage. Is it rated voltage (marked on the unit) or we need to consider also tolerances or even short-term voltage? Best regards, Bostjan -Original Message- From: Richard Nute [mailto:ri...@ieee.org] Sent: Thursday, September 10, 2015 12:28 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] requirement for spacings > I can't understand how a 'rated voltage' can be 560 V > +30%/-15%. It must > mean something other than what is normally understood as 'rated > voltage' > in safety standards. In the IEC, rated voltage is a value assigned by the manufacturer. For years, standards committees have attempted to specify one or more formats for the voltage rating. Each standard is different, and sometimes each edition is different. The problem is when a manufacturer uses a single, nominal value. We know that line voltages vary, so standards committees choose, say, +6%, -10%. We have commonly seen wide-ranging power supplies rated 90-250 volts. But, we cannot fault a manufacturer for rating his wide-ranging product as 150 volts, +166%, -60%. With your i-Phone, you can easily calculate whether the equipment will operate on your power line! In this case, the manufacturer has rated his product to operate from 470 to 728 volts. What is wrong? Best regards, Rich - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald: - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] requirement for spacings
> I can't understand how a 'rated voltage' can be 560 V > +30%/-15%. It must > mean something other than what is normally > understood as 'rated voltage' > in safety standards. In the IEC, rated voltage is a value assigned by the manufacturer. For years, standards committees have attempted to specify one or more formats for the voltage rating. Each standard is different, and sometimes each edition is different. The problem is when a manufacturer uses a single, nominal value. We know that line voltages vary, so standards committees choose, say, +6%, -10%. We have commonly seen wide-ranging power supplies rated 90-250 volts. But, we cannot fault a manufacturer for rating his wide-ranging product as 150 volts, +166%, -60%. With your i-Phone, you can easily calculate whether the equipment will operate on your power line! In this case, the manufacturer has rated his product to operate from 470 to 728 volts. What is wrong? Best regards, Rich - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] requirement for spacings
In message , dated Wed, 9 Sep 2015, =?iso-8859-2?Q?Bo=B9tjan_Glavi=E8?= writes: Manufacturer specified rated voltage of his product as 560VDC +30%/-15% but input voltage can temporarily reach 840VDC (max 1 min). I can't understand how a 'rated voltage' can be 560 V +30%/-15%. It must mean something other than what is normally understood as 'rated voltage' in safety standards. -- OOO - Own Opinions Only. With best wishes. See www.jmwa.demon.co.uk When I turn my back on the sun, it's to look for a rainbow John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
Re: [PSES] requirement for spacings
bmail rev 3.13 smptlib 2.7.10 UL508 points to UL840 as alternate for spacing at terminals and internal crp/clr. UL508 wants you to be min OV cat III for use of UL840. Also UL840 addresses 'recurring peak voltages' for PCB spacings. Brian From: McDiarmid, Ralph [mailto:ralph.mcdiar...@schneider-electric.com] Sent: Wednesday, September 09, 2015 10:20 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] requirement for spacings Clause 5.2.3 in EN50178 (Decisive Voltage) should help clarify. It writes about "occurs continuously" and "worst operating condition". I don't think UL508 will be much help, unless it allows use of UL840 (insulation coordination) as an alternate approach to spacings. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering From: Boštjan Glavič To: EMC-PSTC@LISTSERV.IEEE.ORG, Date: 09/09/2015 09:47 AM Subject: Re: [PSES] requirement for spacings Dear Scot, Douglas, Thank you. Unit is investigated to UL 508, IEC 62477-1 and EN 50178. I have experiences with IEC 60950-1 which requires to determine required distances based on rated voltage - tolerances not considered. 840 VDC might appear on the input during start up of the generator. However I need to agree with you that 30% tolerances seem to be very high and not consider that might be wrong. Best regards, Bostjan On 9. sep. 2015, at 17.41, Douglas Powell mailto:doug...@gmail.com>> wrote: Bostjan, As Scott mentioned, it is very important to know which end standard is being applied to this product. In addition there are many other factors such as environmental conditions, application, location, etc. If this is truly DC powered, it is entirely possible your spacings will be for secondary circuits and somewhat reduced. Nevertheless wiring, connections, fuses and the like will have to be rated and certified/listed for that voltage. If you can provide a little more information about the application and end use, we may be able to provide better assistance. All the best, Doug From: Scott Aldous Sent: Wednesday, September 9, 2015 9:15 AM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Reply To: Scott Aldous Subject: Re: [PSES] requirement for spacings Hi Bostjan, It's difficult to give detailed guidance without knowing what end standards are being applied, but the general guidance in IEC 60664-1 should be helpful. In general, +30% tolerance on input voltage is outside the assumptions of most (if not all) safety standards. An electrical rating of 560Vdc +30%/-15% doesn't seem to be appropriate and should be expressed as a range instead. The range here is from 476 - 728 Vdc! For example, 600V rated wire would seem to be an acceptable choice for external wiring for the input of a device marked with a 560V input rating, but in this case the input voltage may be able to be significantly higher than 600V for extended periods. A marked rating of 560Vdc would be misleading. If your end standard allows the clearances to be determined based on assumed transient levels, then the nominal input voltage (or voltages) becomes less important for clearances as long as you are able to make an accurate assumption about the transients. The 840Vdc level potentially could be taken as a temporary overvoltage for the purposes of calculation of clearance, again depending on the end product standard. At least one end product standard that I know of, IEC 62109-1, takes both transient overvoltages and temporary overvoltages into account for calculation of clearances. For creepage, at a minimum, I think you would want to base creepage distance requirements on the 728Vdc high end of the input voltage (560Vdc + 30%). Whether or not you should use the 840Vdc level instead may depend on the specifics of the case, such as how frequently this can happen, what controls are in place to ensure that this is reliably the case, etc. Again, the requirements of the end product standard need to be taken into account and will certainly influence your decision. On Wed, Sep 9, 2015 at 4:03 AM, Boštjan Glavič mailto:bostjan.gla...@siq.si>> wrote: Dear Experts, Manufacturer specified rated voltage of his product as 560VDC +30%/-15% but input voltage can temporarily reach 840VDC (max 1 min). Do we need to consider 840VDC for determination of required distances? Usually standard requires to consider rated voltage only what is in this case 560VDC (marked on the label). Thank you for your support. Best regards, Bostjan Boštjan Glavič Laboratory of Electronic Engineering Head of Laboratory SIQ Ljubljana, Tržaška cesta 2 SI-1000 Ljubljana, Slovenia T: + 386 (0)1 47 78 265 F: + 386 (0)1 47 78
Re: [PSES] requirement for spacings
Clause 5.2.3 in EN50178 (Decisive Voltage) should help clarify. It writes about "occurs continuously" and "worst operating condition". I don't think UL508 will be much help, unless it allows use of UL840 (insulation coordination) as an alternate approach to spacings. ___ Ralph McDiarmid | Schneider Electric | Solar Business | CANADA | Regulatory Compliance Engineering From: Boštjan Glavič To: EMC-PSTC@LISTSERV.IEEE.ORG, Date: 09/09/2015 09:47 AM Subject: Re: [PSES] requirement for spacings Dear Scot, Douglas, Thank you. Unit is investigated to UL 508, IEC 62477-1 and EN 50178. I have experiences with IEC 60950-1 which requires to determine required distances based on rated voltage - tolerances not considered. 840 VDC might appear on the input during start up of the generator. However I need to agree with you that 30% tolerances seem to be very high and not consider that might be wrong. Best regards, Bostjan On 9. sep. 2015, at 17.41, Douglas Powell mailto:doug...@gmail.com>> wrote: Bostjan, As Scott mentioned, it is very important to know which end standard is being applied to this product. In addition there are many other factors such as environmental conditions, application, location, etc. If this is truly DC powered, it is entirely possible your spacings will be for secondary circuits and somewhat reduced. Nevertheless wiring, connections, fuses and the like will have to be rated and certified/listed for that voltage. If you can provide a little more information about the application and end use, we may be able to provide better assistance. All the best, Doug From: Scott Aldous Sent: Wednesday, September 9, 2015 9:15 AM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Reply To: Scott Aldous Subject: Re: [PSES] requirement for spacings Hi Bostjan, It's difficult to give detailed guidance without knowing what end standards are being applied, but the general guidance in IEC 60664-1 should be helpful. In general, +30% tolerance on input voltage is outside the assumptions of most (if not all) safety standards. An electrical rating of 560Vdc +30%/-15% doesn't seem to be appropriate and should be expressed as a range instead. The range here is from 476 - 728 Vdc! For example, 600V rated wire would seem to be an acceptable choice for external wiring for the input of a device marked with a 560V input rating, but in this case the input voltage may be able to be significantly higher than 600V for extended periods. A marked rating of 560Vdc would be misleading. If your end standard allows the clearances to be determined based on assumed transient levels, then the nominal input voltage (or voltages) becomes less important for clearances as long as you are able to make an accurate assumption about the transients. The 840Vdc level potentially could be taken as a temporary overvoltage for the purposes of calculation of clearance, again depending on the end product standard. At least one end product standard that I know of, IEC 62109-1, takes both transient overvoltages and temporary overvoltages into account for calculation of clearances. For creepage, at a minimum, I think you would want to base creepage distance requirements on the 728Vdc high end of the input voltage (560Vdc + 30%). Whether or not you should use the 840Vdc level instead may depend on the specifics of the case, such as how frequently this can happen, what controls are in place to ensure that this is reliably the case, etc. Again, the requirements of the end product standard need to be taken into account and will certainly influence your decision. On Wed, Sep 9, 2015 at 4:03 AM, Boštjan Glavič mailto:bostjan.gla...@siq.si>> wrote: Dear Experts, Manufacturer specified rated voltage of his product as 560VDC +30%/-15% but input voltage can temporarily reach 840VDC (max 1 min). Do we need to consider 840VDC for determination of required distances? Usually standard requires to consider rated voltage only what is in this case 560VDC (marked on the label). Thank you for your support. Best regards, Bostjan Boštjan Glavič Laboratory of Electronic Engineering Head of Laboratory SIQ Ljubljana, Tržaška cesta 2 SI-1000 Ljubljana, Slovenia T: + 386 (0)1 47 78 265 F: + 386 (0)1 47 78 444 E-Mail: bostjan.gla...@siq.si<mailto:bostjan.gla...@siq.si> - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used
Re: [PSES] requirement for spacings
Dear Scot, Douglas, Thank you. Unit is investigated to UL 508, IEC 62477-1 and EN 50178. I have experiences with IEC 60950-1 which requires to determine required distances based on rated voltage - tolerances not considered. 840 VDC might appear on the input during start up of the generator. However I need to agree with you that 30% tolerances seem to be very high and not consider that might be wrong. Best regards, Bostjan On 9. sep. 2015, at 17.41, Douglas Powell mailto:doug...@gmail.com>> wrote: Bostjan, As Scott mentioned, it is very important to know which end standard is being applied to this product. In addition there are many other factors such as environmental conditions, application, location, etc. If this is truly DC powered, it is entirely possible your spacings will be for secondary circuits and somewhat reduced. Nevertheless wiring, connections, fuses and the like will have to be rated and certified/listed for that voltage. If you can provide a little more information about the application and end use, we may be able to provide better assistance. All the best, Doug From: Scott Aldous Sent: Wednesday, September 9, 2015 9:15 AM To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG> Reply To: Scott Aldous Subject: Re: [PSES] requirement for spacings Hi Bostjan, It's difficult to give detailed guidance without knowing what end standards are being applied, but the general guidance in IEC 60664-1 should be helpful. In general, +30% tolerance on input voltage is outside the assumptions of most (if not all) safety standards. An electrical rating of 560Vdc +30%/-15% doesn't seem to be appropriate and should be expressed as a range instead. The range here is from 476 - 728 Vdc! For example, 600V rated wire would seem to be an acceptable choice for external wiring for the input of a device marked with a 560V input rating, but in this case the input voltage may be able to be significantly higher than 600V for extended periods. A marked rating of 560Vdc would be misleading. If your end standard allows the clearances to be determined based on assumed transient levels, then the nominal input voltage (or voltages) becomes less important for clearances as long as you are able to make an accurate assumption about the transients. The 840Vdc level potentially could be taken as a temporary overvoltage for the purposes of calculation of clearance, again depending on the end product standard. At least one end product standard that I know of, IEC 62109-1, takes both transient overvoltages and temporary overvoltages into account for calculation of clearances. For creepage, at a minimum, I think you would want to base creepage distance requirements on the 728Vdc high end of the input voltage (560Vdc + 30%). Whether or not you should use the 840Vdc level instead may depend on the specifics of the case, such as how frequently this can happen, what controls are in place to ensure that this is reliably the case, etc. Again, the requirements of the end product standard need to be taken into account and will certainly influence your decision. On Wed, Sep 9, 2015 at 4:03 AM, Boštjan Glavič mailto:bostjan.gla...@siq.si>> wrote: Dear Experts, Manufacturer specified rated voltage of his product as 560VDC +30%/-15% but input voltage can temporarily reach 840VDC (max 1 min). Do we need to consider 840VDC for determination of required distances? Usually standard requires to consider rated voltage only what is in this case 560VDC (marked on the label). Thank you for your support. Best regards, Bostjan Boštjan Glavič Laboratory of Electronic Engineering Head of Laboratory SIQ Ljubljana, Tržaška cesta 2 SI-1000 Ljubljana, Slovenia T: + 386 (0)1 47 78 265 F: + 386 (0)1 47 78 444 E-Mail: bostjan.gla...@siq.si<mailto:bostjan.gla...@siq.si> - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas mailto:sdoug...@ieee.org>> Mike Cantwell mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher: mailto:j.bac...@ieee.org>> David Heald: mailto:dhe...@gmail.com>> -- Scott Aldous Compliance Engineer Google 650-253-1994 scottald...@google.com<mailto:scottald...@google.com> - ---
Re: [PSES] requirement for spacings
Bostjan,As Scott mentioned, it is very important to know which end standard is being applied to this product. In addition there are many other factors such as environmental conditions, application, location, etc.If this is truly DC powered, it is entirely possible your spacings will be for secondary circuits and somewhat reduced. Nevertheless wiring, connections, fuses and the like will have to be rated and certified/listed for that voltage. If you can provide a little more information about the application and end use, we may be able to provide better assistance. All the best, DougFrom: Scott AldousSent: Wednesday, September 9, 2015 9:15 AMTo: EMC-PSTC@LISTSERV.IEEE.ORGReply To: Scott AldousSubject: Re: [PSES] requirement for spacingsHi Bostjan,It's difficult to give detailed guidance without knowing what end standards are being applied, but the general guidance in IEC 60664-1 should be helpful.In general, +30% tolerance on input voltage is outside the assumptions of most (if not all) safety standards. An electrical rating of 560Vdc +30%/-15% doesn't seem to be appropriate and should be expressed as a range instead. The range here is from 476 - 728 Vdc! For example, 600V rated wire would seem to be an acceptable choice for external wiring for the input of a device marked with a 560V input rating, but in this case the input voltage may be able to be significantly higher than 600V for extended periods. A marked rating of 560Vdc would be misleading.If your end standard allows the clearances to be determined based on assumed transient levels, then the nominal input voltage (or voltages) becomes less important for clearances as long as you are able to make an accurate assumption about the transients. The 840Vdc level potentially could be taken as a temporary overvoltage for the purposes of calculation of clearance, again depending on the end product standard. At least one end product standard that I know of, IEC 62109-1, takes both transient overvoltages and temporary overvoltages into account for calculation of clearances.For creepage, at a minimum, I think you would want to base creepage distance requirements on the 728Vdc high end of the input voltage (560Vdc + 30%). Whether or not you should use the 840Vdc level instead may depend on the specifics of the case, such as how frequently this can happen, what controls are in place to ensure that this is reliably the case, etc. Again, the requirements of the end product standard need to be taken into account and will certainly influence your decision.On Wed, Sep 9, 2015 at 4:03 AM, Boštjan Glavičwrote:Dear Experts, Manufacturer specified rated voltage of his product as 560VDC +30%/-15% but input voltage can temporarily reach 840VDC (max 1 min). Do we need to consider 840VDC for determination of required distances? Usually standard requires to consider rated voltage only what is in this case 560VDC (marked on the label). Thank you for your support. Best regards, Bostjan Boštjan Glavič Laboratory of Electronic Engineering Head of Laboratory SIQ Ljubljana, Tržaška cesta 2 SI-1000 Ljubljana, Slovenia T: + 386 (0)1 47 78 265 F: + 386 (0)1 47 78 444 E-Mail: bostjan.gla...@siq.si - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald: -- Scott AldousCompliance EngineerGoogle650-253-1994scottald...@google.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to t
Re: [PSES] requirement for spacings
Hi Bostjan, It's difficult to give detailed guidance without knowing what end standards are being applied, but the general guidance in IEC 60664-1 should be helpful. In general, +30% tolerance on input voltage is outside the assumptions of most (if not all) safety standards. An electrical rating of 560Vdc +30%/-15% doesn't seem to be appropriate and should be expressed as a range instead. The range here is from 476 - 728 Vdc! For example, 600V rated wire would seem to be an acceptable choice for external wiring for the input of a device marked with a 560V input rating, but in this case the input voltage may be able to be significantly higher than 600V for extended periods. A marked rating of 560Vdc would be misleading. If your end standard allows the clearances to be determined based on assumed transient levels, then the nominal input voltage (or voltages) becomes less important for clearances as long as you are able to make an accurate assumption about the transients. The 840Vdc level potentially could be taken as a temporary overvoltage for the purposes of calculation of clearance, again depending on the end product standard. At least one end product standard that I know of, IEC 62109-1, takes both transient overvoltages and temporary overvoltages into account for calculation of clearances. For creepage, at a minimum, I think you would want to base creepage distance requirements on the 728Vdc high end of the input voltage (560Vdc + 30%). Whether or not you should use the 840Vdc level instead may depend on the specifics of the case, such as how frequently this can happen, what controls are in place to ensure that this is reliably the case, etc. Again, the requirements of the end product standard need to be taken into account and will certainly influence your decision. On Wed, Sep 9, 2015 at 4:03 AM, Boštjan Glavič wrote: > Dear Experts, > > Manufacturer specified rated voltage of his product as 560VDC +30%/-15% > but input voltage can temporarily reach 840VDC (max 1 min). > > Do we need to consider 840VDC for determination of required distances? > Usually standard requires to consider rated voltage only what is in this > case 560VDC (marked on the label). > > Thank you for your support. > Best regards, > Bostjan > > > > Boštjan Glavič > Laboratory of Electronic Engineering > Head of Laboratory > SIQ Ljubljana, Tržaška cesta 2 > SI-1000 Ljubljana, Slovenia > T: + 386 (0)1 47 78 265 > F: + 386 (0)1 47 78 444 > E-Mail: bostjan.gla...@siq.si > > > > - > > This message is from the IEEE Product Safety Engineering Society emc-pstc > discussion list. To post a message to the list, send your e-mail to < > emc-p...@ieee.org> > > All emc-pstc postings are archived and searchable on the web at: > http://www.ieee-pses.org/emc-pstc.html > > Attachments are not permitted but the IEEE PSES Online Communities site at > http://product-compliance.oc.ieee.org/ can be used for graphics (in > well-used formats), large files, etc. > > Website: http://www.ieee-pses.org/ > Instructions: http://www.ieee-pses.org/list.html (including how to > unsubscribe) > List rules: http://www.ieee-pses.org/listrules.html > > For help, send mail to the list administrators: > Scott Douglas > Mike Cantwell > > For policy questions, send mail to: > Jim Bacher: > David Heald: > -- Scott Aldous Compliance Engineer Google 650-253-1994 scottald...@google.com - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald:
[PSES] requirement for spacings
Dear Experts, Manufacturer specified rated voltage of his product as 560VDC +30%/-15% but input voltage can temporarily reach 840VDC (max 1 min). Do we need to consider 840VDC for determination of required distances? Usually standard requires to consider rated voltage only what is in this case 560VDC (marked on the label). Thank you for your support. Best regards, Bostjan Boštjan Glavič Laboratory of Electronic Engineering Head of Laboratory SIQ Ljubljana, Tržaška cesta 2 SI-1000 Ljubljana, Slovenia T: + 386 (0)1 47 78 265 F: + 386 (0)1 47 78 444 E-Mail: bostjan.gla...@siq.si - This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Attachments are not permitted but the IEEE PSES Online Communities site at http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used formats), large files, etc. Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas Mike Cantwell For policy questions, send mail to: Jim Bacher: David Heald: