Comparative Tracking Index

1998-02-19 Thread Rick Busche

IEC 950 defines CIT (comparative tracking index) in terms of
material groups for the determination of creapage distance. Specifically
groups I, II, IIIa and IIIb. are mentioned. In paragraph 2.9.3 (note 3)
the actual index (CTI) is referred to as <600 or <400. My questions are
as follows:

1. Is this CTI (as assigned by UL in the yellow book) actually a
voltage level?
2. The FR4 laminate we use has been rated at 205. As such the
maximum creapage distance is mandated. Is it common to find better
material? Is this 205 level typical of common FR4 materials?

Thanks

Rick Busche
Evans & Sutherland
rbus...@es.com


Re: Comparative Tracking Index

1998-02-20 Thread Robert Tims

Rick,
The Comparitive Tracking Index (CTI), ASTM D3638 and UL746A, is a test intended 
to show the susceptibility to surface tracking of solid electrical insulating   
materials when exposed under electrical stress, to a contaminant solution.This 
test applies to relatively low voltages under 600 volts.
The CTI test attempts to cause a permanent electrically conductive carbon path  
along the surface of a material using an aluminum chloride electrolyte applied  
at the rate of 1 drop every 30 seconds to the test specimen. The surface of the 
specimen is subjected to an AC voltage, s.c. current limited to one amp. The 
current flow must exceed 100 mA for at least a half second to register as an
established path. 
ANSWER TO 1) The CTI level (205 in your note) is the voltage level that 
 corresponds to 50 drops on the tracking-voltage curve that is plotted as a 
result of testing multiple 3.0mm  thick samples at various voltage levels, up 
to600 V. 
ANSWER to 2) UL has CTI index levels, while international standards call out
the actual voltage levels. Either way 200 volts is an probably an OK level for  
the material and what you will be using it for. I believe levels anywhere from 
100 to 250 volts are typically called out for that use. Just my humble opinion,
though. 
Any other questions, I have a bit of experience on this subject, please do not  
hesitate to e-mail me.
Regards,
Bob Tims
Standards and Compliance
rt...@emx.ericsson.se



RE: Comparative Tracking Index

1998-02-22 Thread Peter Tarver
But would you be surprised to know that UL doesn't retest a laminate's
CTI after processing?  They don't, unless specifically asked by the
board mfg., which I'd have to suggest is rare.  The CTI for finished
boards in UL's RCD is based on those for the base laminate and no
assumption should be made to the contrary.  If a board house claims
otherwise, ask them to provide the test data.

Regards,

Peter L. Tarver
Nortel
ptar...@nt.com

> --
> From: Harold Leipold[SMTP:harold_leip...@sec.siemens.com]
> Sent: Friday, February 20, 1998 6:04 AM
> 
> 
> Just to add my "2 cents" to this discussion. CTI etc. after
> manufactured
> into a finished PCB is actually more important than the CTI of the
> basic
> laminate itself. That is one reason why one should use PCB vendors who
> have
> their process UL recognized (and use the recognized logo on the
> finished
> product for identification).
> The PCB fabrication process, solder mask, etc. can affect both CTI and
> flammability greatly.
> 
> Comments are personal and do not necessarily reflect corporate
> opinion.
> 
> Harold Leipold
> Siemens EC
> Princeton, IN
> Tel  812-386-2161
> Fax 812-386-2616


RE: Comparative Tracking Index

1998-02-21 Thread POWELL, DOUG

Rick,

In past years I spent significant time researching this question.  I also 
found that most materials manufacturers do not understand CTI.  Even though 
the concept has been known for more than 50 years.

As far as standards go I put this table together simply to help correlate 
the International, European and UL standards:

VOLTAGE   UL 746IEC 112   VDE 303   

600 or greater 0II
400 - 599  1II   II
250 - 399  2IIIa IIIa
175 - 249  3IIIa IIIa
100 - 174  4IIIb III b
0 - 99 5n/a  n/a

(If the columns do not line up, use tabs to delimit)

If you have the UL yellow Recognized Component directory, you should be able 
to find the UL CTI info at the beginning of the plastics section.  It is on 
page 1893 in my 1994 version.

The 205 figure that you mention does not look like a CTI number, rather a 
thermal performance number.   FR-4 "typically" is greater than 180C in 
thermal performance and the flame rating is UL 94V-0.

CTI is a function of the organic content of the material,  material that is 
able to be carbonized.  For example anorganic materials such as glass and 
ceramics always have the highest possible CTI ratings and essentially do not 
track.  If you will note, when using FR-4 for PCB's most standards including 
IEC950 and EN 60950 make a special case and provide a separate spacing 
table.  The creepage numbers generally correlate directly to equivalent CTI 
of 600V.

If you are using the FR-4 for something other than PCB's you will need to 
get exact information from the laminate manufacturer.  Try to get past the 
sales people and you may still need to educate technical types as to what 
CTI is before you can get meaningful information.  Chances are most all FR-4 
laminates are CTI 600V, depending on glass content..

Doug Powell
Advanced Energy Industries, Inc.
Fort Collins, Colorado USA

 --
From: Rick Busche
To: emc-p...@ieee.org
Subject: Comparative Tracking Index
List-Post: emc-pstc@listserv.ieee.org
Date: Thursday, February 19, 1998 8:26PM



 IEC 950 defines CTI (comparative tracking index) in terms of
material groups for the determination of creapage distance. Specifically
groups I, II, IIIa and IIIb. are mentioned. In paragraph 2.9.3 (note 3)
the actual index (CTI) is referred to as <600 or <400. My questions are
as follows:

 1. Is this CTI (as assigned by UL in the yellow book) actually a
voltage level?
 2. The FR4 laminate we use has been rated at 205. As such the
maximum creapage distance is mandated. Is it common to find better
material? Is this 205 level typical of common FR4 materials?

 Thanks

 Rick Busche
 Evans & Sutherland
 rbus...@es.com




RE: Comparative Tracking Index

1998-02-20 Thread Sushil Gour
Rick, UL defines CTI as "the voltage which causes tracking after 50 drops of 
0.1 percent ammonium chloride solution have fallen on the material.  The 
results of testing the nominal 3mm thickness are considered representative of 
the material's performance in any thickness."
Thanks
SGour

-Original Message-
From:   Rick Busche [SMTP:rbus...@es.com]
Sent:   Thursday, February 19, 1998 12:23 PM
To: emc-p...@ieee.org
Subject:    Comparative Tracking Index


IEC 950 defines CIT (comparative tracking index) in terms of
material groups for the determination of creapage distance. Specifically
groups I, II, IIIa and IIIb. are mentioned. In paragraph 2.9.3 (note 3)
the actual index (CTI) is referred to as <600 or <400. My questions are
as follows:

1. Is this CTI (as assigned by UL in the yellow book) actually a
voltage level?
2. The FR4 laminate we use has been rated at 205. As such the
maximum creapage distance is mandated. Is it common to find better
material? Is this 205 level typical of common FR4 materials?

Thanks

Rick Busche
Evans & Sutherland
rbus...@es.com


Re: Comparative Tracking Index

1998-02-20 Thread Harold Leipold

Just to add my "2 cents" to this discussion. CTI etc. after manufactured
into a finished PCB is actually more important than the CTI of the basic
laminate itself. That is one reason why one should use PCB vendors who have
their process UL recognized (and use the recognized logo on the finished
product for identification).
The PCB fabrication process, solder mask, etc. can affect both CTI and
flammability greatly.

Comments are personal and do not necessarily reflect corporate opinion.

Harold Leipold
Siemens EC
Princeton, IN
Tel  812-386-2161
Fax 812-386-2616







ri...@sdd.hp.com on 02/19/98 02:48:17 PM

Please respond to ri...@sdd.hp.com

To:   rbus...@es.com
cc:   emc-p...@ieee.org (bcc: Harold Leipold/PRI/SEC/US)
Subject:  Re: Comparative Tracking Index






Hi Rick:


You ask about CTI for printed wiring boards, and typical
values.

According to the UL Yellow Book, CTI is indicated in volts.

In glancing through the UL Yellow Book, very few board
manufacturers have submitted their boards for CTI.

The few that have submitted, have CTIs in the range of
less than 100 up to about 250.  A very few manufacturers
can provide boards with CTI exceeding 600.


Best regards,
Rich


"Life is ours to be spent, not to be saved."
 -- D. H. Lawrence


-
 Richard Nute Quality Department
 Hewlett-Packard Company   Product Regulations Group
 San Diego Division (SDD)  Tel   :  619 655 3329
 16399 West Bernardo Drive FAX   :  619 655 4979
 San Diego, California 92127   e-mail:  ri...@sdd.hp.com
-













RE: Comparative Tracking Index

1998-02-20 Thread Mel Pedersen
Hello Rich:  it is a challenge to find a flame retardant material with a good 
CTI rating.  The flame retardant in use tend to lower CTI ratings.

- Mel

--
From:   Rick Busche[SMTP:rbus...@es.com]
Sent:   Thursday, February 19, 1998 12:23 PM
To: emc-p...@ieee.org
Subject:Comparative Tracking Index


IEC 950 defines CIT (comparative tracking index) in terms of
material groups for the determination of creapage distance. Specifically
groups I, II, IIIa and IIIb. are mentioned. In paragraph 2.9.3 (note 3)
the actual index (CTI) is referred to as <600 or <400. My questions are
as follows:

1. Is this CTI (as assigned by UL in the yellow book) actually a
voltage level?
2. The FR4 laminate we use has been rated at 205. As such the
maximum creapage distance is mandated. Is it common to find better
material? Is this 205 level typical of common FR4 materials?

Thanks

Rick Busche
Evans & Sutherland
rbus...@es.com



Re: Comparative Tracking Index

1998-02-19 Thread Rich Nute


Hi Rick:


You ask about CTI for printed wiring boards, and typical 
values.

According to the UL Yellow Book, CTI is indicated in volts.

In glancing through the UL Yellow Book, very few board
manufacturers have submitted their boards for CTI.

The few that have submitted, have CTIs in the range of
less than 100 up to about 250.  A very few manufacturers 
can provide boards with CTI exceeding 600.


Best regards,
Rich


"Life is ours to be spent, not to be saved."
 -- D. H. Lawrence


-
 Richard Nute Quality Department 
 Hewlett-Packard Company   Product Regulations Group 
 San Diego Division (SDD)  Tel   :  619 655 3329 
 16399 West Bernardo Drive FAX   :  619 655 4979 
 San Diego, California 92127   e-mail:  ri...@sdd.hp.com 
-







Re: Comparative Tracking Index

1998-02-19 Thread FRANK_DOMINGUEZ
 Rick,
 Table 22.1 and clause 22 of UL 746A talk about CTI.  The CTI is a 
 voltage.  
 UL 746C, clause 11 talks more about CTI.  Clause 11.2 states that the 
 comparative tracking voltage is an index and is not directly related 
 to the suitable operating voltage in actual service.  Clause 11.3 
 states that the CTI provides an indication of the relative track 
 resistance of the material at voltages up to 600V.
 Regards,
 Frank Dominguez


__ Reply Separator _
Subject: Comparative Tracking Index
Author:  Non-HP-rbusche (rbus...@es.com) at HP-Boise,mimegw150
List-Post: emc-pstc@listserv.ieee.org
Date:2/19/98 11:23 AM


 
IEC 950 defines CIT (comparative tracking index) in terms of
material groups for the determination of creapage distance. Specifically 
groups I, II, IIIa and IIIb. are mentioned. In paragraph 2.9.3 (note 3) 
the actual index (CTI) is referred to as <600 or <400. My questions are 
as follows:
 
1. Is this CTI (as assigned by UL in the yellow book) actually a
voltage level?
2. The FR4 laminate we use has been rated at 205. As such the
maximum creapage distance is mandated. Is it common to find better 
material? Is this 205 level typical of common FR4 materials?
 
Thanks
 
Rick Busche
Evans & Sutherland
rbus...@es.com


Comparative Tracking Index (CTI) question

1996-08-23 Thread Steve Costello
 Can anyone tell me if the UL CTI ratings/results are the same as the 
 IEC  112 CTI. Many EN and harmonized standards use CTI for determining 
 creepage requirements but is the  CTI number in the UL Recognized 
 Component Directory a valid number for this value?   
 
 Thanks,
 
 Steve Costello
 National Instruments
 steve.coste...@natinst.com


Re: Comparative Tracking Index (CTI) question

1996-08-27 Thread a-pex
In reply to Mr. Costello's CTI question, we asked similar questions directly 
to UL Santa Clara in July this year.  Our questions were concerning UL 1950 
(3rd ed.), Cl. 2.9.3 CTI requirements.


Q.  Does "IEC 112 Method A" described in UL 1950 (3rd) mean "Solution A"?

A.  Yes.


Q.  What are the differences between IEC 112 and ASTM D 3688-85?

A.  The main differences are the equipment used for conducting the tests and 
resistivity.  UL has conducted comparison testing between IEC 112 Solution A 
and UL 746A (ASTM D 3688-85) and the result was pretty much the same.  The IEC 
112 has recently been revised and we are currently evaluating the revision 
through comparison testing.


Q.  Does UL accept the CTI value of UL 746A to determine a material group?

A.  Yes, we accept CTI value according to UL 746A for determining a material 
group.


Q.  Can UL test CTI in accordance with IEC 112, method A?

A.  Yes (prior to the revisions).  Currently the test period is basically UL 
746A.  Currently, the test period is 4-5 weeks.  We would require 10 samples 
(size 4x4) for the test.  The RTP office is currently determining what testing 
would be necessary for the revised version of IEC 112, Method A.


Hope this info is of help.  We suggest that you confirm this directly with UL, 
as their requirements may be different in your specific situation.  Also, they 
may have more information about the revisions to the IEC 112, and whether or 
not it affects the testing comparison between UL 746A and IEC 112.

A-Pex International Co., Ltd.
a-...@tcp-ip.or.jp

>  Can anyone tell me if the UL CTI ratings/results are the same as the 
>  IEC  112 CTI. Many EN and harmonized standards use CTI for determining 
>  creepage requirements but is the  CTI number in the UL Recognized 
>  Component Directory a valid number for this value?   
>  
>  Thanks,
>  
>  Steve Costello
>  National Instruments
>  steve.coste...@natinst.com
> 



re: Comparative Tracking Index (CTI) question

1996-08-26 Thread Bob M. Miller

You asked if UL CTI ratings are equivalent to IEC 112 CTI ratings.

The simple answer is no.  The test methods are different, therefore, there is 
no correlation.  

This is not my area of expertese, if you need more detailed information 
contact John Augis at our Santa Clara office:

Phone:  408-985-2400 ext.32440
E-Mail: aug...@ul.com

Usual disclaimers.



_

Bob M. Miller 
Underwriters Laboratories Inc.  Voice : (408) 985-2400 x32382
1655 Scott Blvd.   Fax: (408) 296-3256
Santa Clara, CA 95050   E-mail: mill...@ul.com