Re: Intrinsic safety for factory communication?

1999-09-03 Thread Peter Merguerian

Joe,

There  truly are standards for factory automation for the US and 
Europe (although I have to dig into my files to tell you the 
standards). For ITE, industrial control, robotic or any other 
equipment for use in hazardous locations, the equipment must 
either be intinsically safe or protected such as by purging or 
locating within explosion-proof enclosures. You can refer to the US 
National Electrical Code (NFPA 70) and the European regulations 
to get an idea of what is a hazardous location (Classes and 
Zones). Depending on the Classes and/or Zones, various protection 
schemes are allowed.

To cut the story short, factory automation equipment does not 
necessarily have to be intrinsically safe and/or explosion-proof. 
This depends on the factory environment in which it is placed.

Have a good day.

 
 Hello All:
 
 I am hoping that some of you can help me gain an understanding of the 
 requirements for intrinsic safety for communication wiring that is used in 
 a manufacturing environment.
 
 My background is in telecom and ITE, not factory automation.  However, I have 
 been asked to assist a client with developing some communication technology 
 that will be used for sensors and controls on a factory floor.  
 
 My client tells me that for communication wiring that is used in a factory, 
 there are requirements for intrinsic safety of the wiring.  Among other 
 things, there is reportedly a test where connections are made and broken in 
 an atmosphere that contains explosive gases.  Since any sparks generated from 
 the make/break of the connections could ignite the gases, it is reportedly 
 necessary to design the communication scheme in such a way that no sparks are 
 generated.
 
 When I asked where these requirements are documented, I was told that there 
 is no written standard for intrinsic safety.  Rather, the system must be 
 submitted to an independent agency for review, and this agency will evaluate 
 the system according to their own (internal) criteria.
 
 Now, coming from a background in ITE, I find this hard to believe.  In the 
 ITE world, we have documented standards for safety such as UL 1950 in the USA 
 and EN 60950 in Europe.  I find it hard to imagine that there are no 
 comparable standards for factory automation.
 
 Can any of you clarify this issue for me?  Where does the concept of 
 intrinsic safety come from, and how is compliance determined?  I am 
 interested in addressing this issue for both North America and Europe.  Any 
 assistance you could provide would be greatly appreciated.
 
 
 Joe Randolph
 Telecom Design Consultant
 Randolph Telecom, Inc.
 781-721-2840
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 
 


PETER S. MERGUERIAN
MANAGING DIRECTOR
PRODUCT TESTING DIVISION
I.T.L. (PRODUCT TESTING) LTD.
HACHAROSHET 26, P.O.B. 211
OR YEHUDA 60251, ISRAEL

TEL: 972-3-5339022
FAX: 972-3-5339019
E-MAIL: pe...@itl.co.il
Visit our Website: http://www.itl.co.il

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Intrinsic safety for factory communication?

1999-09-03 Thread cnewton



In addition to the very good info already offered,  you might consider
purchasing an excellent text from the National Fire Protection Association
at  http://www.nfpa.org/

The text is Electrical Installations in Hazardous Locations and is intended
for the beginner and the practitioner.  I purchased my copy about 10 years ago,
but I visited their catalog site and it appears that the current revision is
1998.
This text was tremendous help to me way back when I started my haz loc
learning curve.  The book will describe the spark ignition test you refer to.
My revision also touched upon international compliance and the EU Zone
ratings.

Your best contacts for information are likely to be Factory Mutual for North
America (781-255-4822, Bill Lawrence) and BASEEFA for the EU
(United Kingdom, Ron Sinclair, 44-1298-28-203).

Carl Newton
Xycom Automation





From: j...@aol.com on 09/02/99 04:59 PM GMT

Please respond to j...@aol.com

To:   emc-p...@majordomo.ieee.org
cc:(bcc: Carl Newton/XYCOM)

Subject:  Intrinsic safety for factory communication?





Hello All:

I am hoping that some of you can help me gain an understanding of the
requirements for intrinsic safety for communication wiring that is used in
a manufacturing environment.

My background is in telecom and ITE, not factory automation.  However, I have
been asked to assist a client with developing some communication technology
that will be used for sensors and controls on a factory floor.

My client tells me that for communication wiring that is used in a factory,
there are requirements for intrinsic safety of the wiring.  Among other
things, there is reportedly a test where connections are made and broken in
an atmosphere that contains explosive gases.  Since any sparks generated from
the make/break of the connections could ignite the gases, it is reportedly
necessary to design the communication scheme in such a way that no sparks are
generated.

When I asked where these requirements are documented, I was told that there
is no written standard for intrinsic safety.  Rather, the system must be
submitted to an independent agency for review, and this agency will evaluate
the system according to their own (internal) criteria.

Now, coming from a background in ITE, I find this hard to believe.  In the
ITE world, we have documented standards for safety such as UL 1950 in the USA
and EN 60950 in Europe.  I find it hard to imagine that there are no
comparable standards for factory automation.

Can any of you clarify this issue for me?  Where does the concept of
intrinsic safety come from, and how is compliance determined?  I am
interested in addressing this issue for both North America and Europe.  Any
assistance you could provide would be greatly appreciated.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2840

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).









-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Intrinsic safety for factory communication?

1999-09-02 Thread jmerrill

Intrinsically Safe apparatus.
USA Standards
Factory Mutual Research Corp
Standard 3610 Intrinsically Safe Apparatus for use in Class 1, 2, and 3,
Division 1 Hazardous (Classified) Locations.
Also for reference with this standard, 3600 Electrical Equipment for Use in
Hazardous (Classified) Locations General Requirements
Underwriters Laboratories
UL 913 Intrinsically Safe Apparatus

Canadian Standards
CAN/CSA C22.2 No. 157  Intrinsically Safe Apparatus

IEC 79 series Electrical apparatus for Explosive gas atmospheres.
EN50020
EN50039

 Factory Automation Equipment
UL 508, C or UL31010-1
CAN/CSA 22.2 No. 14, 142, or 1010-1
IEC 1131 Series Programmable logic control
IEC 1010-1 Industrial, Scientific and Measurement

Sincerely,


John Merrill
Product Safety Engineer
Schneider Automation Inc.





j...@aol.com on 09/02/99 12:59:54 PM

Please respond to j...@aol.com

To:   emc-p...@majordomo.ieee.org
cc:(bcc: John Merrill/Aut/Schneider)
Subject:  Intrinsic safety for factory communication?





Hello All:

I am hoping that some of you can help me gain an understanding of the
requirements for intrinsic safety for communication wiring that is used in
a manufacturing environment.

My background is in telecom and ITE, not factory automation.  However, I have
been asked to assist a client with developing some communication technology
that will be used for sensors and controls on a factory floor.

My client tells me that for communication wiring that is used in a factory,
there are requirements for intrinsic safety of the wiring.  Among other
things, there is reportedly a test where connections are made and broken in
an atmosphere that contains explosive gases.  Since any sparks generated from
the make/break of the connections could ignite the gases, it is reportedly
necessary to design the communication scheme in such a way that no sparks are
generated.

When I asked where these requirements are documented, I was told that there
is no written standard for intrinsic safety.  Rather, the system must be
submitted to an independent agency for review, and this agency will evaluate
the system according to their own (internal) criteria.

Now, coming from a background in ITE, I find this hard to believe.  In the
ITE world, we have documented standards for safety such as UL 1950 in the USA
and EN 60950 in Europe.  I find it hard to imagine that there are no
comparable standards for factory automation.

Can any of you clarify this issue for me?  Where does the concept of
intrinsic safety come from, and how is compliance determined?  I am
interested in addressing this issue for both North America and Europe.  Any
assistance you could provide would be greatly appreciated.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2840

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).









-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Re: Intrinsic safety for factory communication?

1999-09-02 Thread Art Michael

Hi Joe,

Start with UL 913.  Then go to CSA, UL or FM sites and search on the
topics, intrinsic safety hazardous locations hazloc.

Also, on the Safety Link, you will find a link to a 6-part tutorial on
this subject . Search on the term intrinsically safe or crouse-hinds 

www.safetylink.com

Regards, Art Michael
 * * * * * * * * * * * * * * * * * * * * * * 
*   International Product Safety Bookshop   *
*  Check out our current offerings! *
* http://www.safetylink.com/bookshop.html *   
*   *
* Another service of the Safety Link*
*  www.safetylink.com *
 * * * * * * * * * * * * * * * * * * * * * * 


---

On Thu, 2 Sep 1999 j...@aol.com wrote:

 
 Hello All:
 
 I am hoping that some of you can help me gain an understanding of the 
 requirements for intrinsic safety for communication wiring that is used in 
 a manufacturing environment.
 
 My background is in telecom and ITE, not factory automation.  However, I have 
 been asked to assist a client with developing some communication technology 
 that will be used for sensors and controls on a factory floor.  
 
 My client tells me that for communication wiring that is used in a factory, 
 there are requirements for intrinsic safety of the wiring.  Among other 
 things, there is reportedly a test where connections are made and broken in 
 an atmosphere that contains explosive gases.  Since any sparks generated from 
 the make/break of the connections could ignite the gases, it is reportedly 
 necessary to design the communication scheme in such a way that no sparks are 
 generated.
 
 When I asked where these requirements are documented, I was told that there 
 is no written standard for intrinsic safety.  Rather, the system must be 
 submitted to an independent agency for review, and this agency will evaluate 
 the system according to their own (internal) criteria.
 
 Now, coming from a background in ITE, I find this hard to believe.  In the 
 ITE world, we have documented standards for safety such as UL 1950 in the USA 
 and EN 60950 in Europe.  I find it hard to imagine that there are no 
 comparable standards for factory automation.
 
 Can any of you clarify this issue for me?  Where does the concept of 
 intrinsic safety come from, and how is compliance determined?  I am 
 interested in addressing this issue for both North America and Europe.  Any 
 assistance you could provide would be greatly appreciated.
 
 
 Joe Randolph
 Telecom Design Consultant
 Randolph Telecom, Inc.
 781-721-2840
 
 -
 This message is coming from the emc-pstc discussion list.
 To cancel your subscription, send mail to majord...@ieee.org
 with the single line: unsubscribe emc-pstc (without the
 quotes).  For help, send mail to ed.pr...@cubic.com,
 jim_bac...@monarch.com, ri...@sdd.hp.com, or
 roger.volgst...@compaq.com (the list administrators).
 
 
 




-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).



Intrinsic safety for factory communication?

1999-09-02 Thread JPR3

Hello All:

I am hoping that some of you can help me gain an understanding of the 
requirements for intrinsic safety for communication wiring that is used in 
a manufacturing environment.

My background is in telecom and ITE, not factory automation.  However, I have 
been asked to assist a client with developing some communication technology 
that will be used for sensors and controls on a factory floor.  

My client tells me that for communication wiring that is used in a factory, 
there are requirements for intrinsic safety of the wiring.  Among other 
things, there is reportedly a test where connections are made and broken in 
an atmosphere that contains explosive gases.  Since any sparks generated from 
the make/break of the connections could ignite the gases, it is reportedly 
necessary to design the communication scheme in such a way that no sparks are 
generated.

When I asked where these requirements are documented, I was told that there 
is no written standard for intrinsic safety.  Rather, the system must be 
submitted to an independent agency for review, and this agency will evaluate 
the system according to their own (internal) criteria.

Now, coming from a background in ITE, I find this hard to believe.  In the 
ITE world, we have documented standards for safety such as UL 1950 in the USA 
and EN 60950 in Europe.  I find it hard to imagine that there are no 
comparable standards for factory automation.

Can any of you clarify this issue for me?  Where does the concept of 
intrinsic safety come from, and how is compliance determined?  I am 
interested in addressing this issue for both North America and Europe.  Any 
assistance you could provide would be greatly appreciated.


Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2840

-
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: unsubscribe emc-pstc (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).