Hello Moshe:

It seems to me that your customer is too worried.  I am assuming that you have 
your board layout designed for BASIC INSULATION between points the 
Telecommunications Network connection and points b) and c) of clause 6.4.2.2 of 
IEC 950.  This is the requirement, and it will withstand a 1.0kV HY-POT.  You 
should have 1.6mm of creepage and clearance between the network traces and the 
SELV traces.  Points b) and c) should be SELV.  With 1.6mm, you should be fine, 
as the breakdown for air is on the order of 3.0kV/mm.

Assuming that you are talking about the ADSL line you refereed to earlier, 
another clause of IEC 950 may require a HY-POT test on the order of 1150V; 
Australia will require 1.5kV between the Network connection and points b) and 
c).  Your board should pass at 1.5kV also.  Norway and Sweden may require 
SUPPLEMENTARY INSULATION here rated for 250VDC between any circuit connected to 
Earth Ground and the Network, which is 2.5mm of spacing.  That would also 
require a 1.5kV HY-POT test.

If the above is not true, I will question my sanity.  I do not think that you 
have anything to worry about.  Make sure that your spacings are correct, and 
that you meet requirements for any components (transformers, capacitors, etc.) 
that might be bridging this barrier.  Then you should be fine.

Mel Pedersen                            Midcom, Inc.
Homologations Engineer             Phone:  (605) 882-8535
mpeder...@midcom-inc.com     Fax:  (605) 882-8633


----------
From:   mvald...@netvision.net.il[SMTP:mvald...@netvision.net.il]
Sent:   Thursday, August 06, 1998 2:10 AM
To:     emc-p...@ieee.org
Subject:        150VDC basic insulation versus 1000VAC test

Hello everyone,

My customer is having doubts about how a product designed for 150V pollution 
deg 2, CTI group 
3, shall withstand the 1000V test (950 clause 6.4.2.2)

It seems to me OK since the test is done for just one minute and very 
carefully. (And in a 
benign environment)

Am I right to feel at ease about this? Should I add more separation between 
conductors (or 
other means) to make sure the product passes?

regards,

Moshe
--------------------------------------------
Name: moshe valdman
E-mail: mvald...@netvision.net.il
Phone: 972-52-941200
Telefax: 972-3-5496369
List-Post: emc-pstc@listserv.ieee.org
Date: 6/8/98
Time: 0:10:05
You are most welcome to visit my homepage at:

http://www.geocities.com/CapeCanaveral/5233/
--------------------------------------------




---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.com
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
ri...@sdd.hp.com, or roger.volgst...@compaq.co (the list
administrators).

Reply via email to