Re: RF field strength units

2006-03-20 Thread emc-p...@ieee.org
Bill Flanigan asked:

>> I have purchased a field-strength meter which displays - over a range of
frequencies - field strength in units dBmV, dBuV or dBm.
It uses a whip antenna. Is there any way to convert any of these figures to
V/m (I am doing RF immunity testing and I need to ensure 10 V/m)? Or is
this <<

It may not be useful for _this_ purpose.

>From the description, it is an RF voltmeter with a whip. If accurately
calibrated, it could be quite helpful comparing "before and after" fields.
However, in order to tell what the field IS, you need the whip's antenna
factor (installed on the instrument) and it is more than possible the
manufacturer doesn't know that.

If you can connect an antenna whose factors are known, you need only sum
that with the reading you get.  0 dBmV is 1 millivolt.  1 volt is 1000 mV,
60 dBmV; 10 volts is 10,000 mV, 80 dBmV.  A biconical dipole might from 30
to 200 MHz have an antenna factor varying between 6dB  and 30dB (or
higher). In a field of 10 V/m, that antenna would deliver (not counting
feedline loss) anywhere between 316 mV and 5 volts. The corresponding
numbers in dBmV are 50 dBmV to 74 dBmV.  And if your instrument has a flat
response across the frequencies you want to measure, it'll work.

That was the last of the good news; using a bicon or other full-sized
antenna affects the field one is measuring. For checking radiated fields
for immunity testing, you need really small antennas (and instruments).
Since a 10V/m field demands no great sensitivity, commercial  sensors for
immunity work usually have 3-axis (polarization irrelevant) short,
resistive dipoles with detectors at the antenna feeding rectified DC to a
high impedance measuring circuit, and also, with some way to get the
readings out of the chamber without affecting the field with long wires;
fiber optic, usually. You pay for this; precision and suitability for the
job don't come cheap. 

Good luck!


Cortland
KA5S

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Scott Douglas   emcp...@ptcnh.net
 Mike Cantwell   mcantw...@ieee.org

For policy questions, send mail to:

 Jim Bacher: j.bac...@ieee.org
 David Heald:emc-p...@daveheald.com

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



RE: RF field strength units

2006-03-20 Thread emc-p...@ieee.org
Bill:
The "antenna factor" is a conversion factor that converts the field strength 
of an E-Field that the antenna sees to the voltage (Volts or micro-volts
present 
on the output terminals of the antenna into a specified load (Normally 50
ohms).  
 
The AF for an antenna will vary over frequency.  Therefore, the manufacturer 
should generally provide you with a graph showing frequency vs. AF, or a
suitable 
table. 
 
The other option is to have the antenna calibrated by a lab that performs that 
service such as Liberty Labs.  If you are going that route, be sure to specify 
how you are going to use the antenna.  (Immunity vs. radiated emissions 
measurements). 
 
 
John Shinn, P.E.
Manager, Laboratory Operations
Sanmina-SCI
 
 
 

  _  

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Bill Flanigan
Sent: Monday, March 20, 2006 11:17 AM
To: 'Emc-Pstc'
Subject: RF field strength units


Associates,
 
I have purchased a field-strength meter which displays - over a range of
frequencies - field strength in units dBmV, dBuV or dBm.
It uses a whip antenna. Is there any way to convert any of these figures to
V/m (I am doing RF immunity testing and I need to ensure 10 V/m)? Or is this
conversion dependent on knowing the antenna factors over the frequency ranges?
 
I am in the middle of unproductive communications with the manufacturer
(Korea) and the vendor (Arizona).
 
WmFlanigan

_
Scanned by Sanmina-SCI eShield 

-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc 


_
Scanned by Sanmina-SCI eShield 


-  This
message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Scott Douglas emcp...@ptcnh.net Mike Cantwell mcantw...@ieee.org 


For policy questions, send mail to: 


Jim Bacher: j.bac...@ieee.org David Heald: emc-p...@daveheald.com 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc