Re: Power Factor correction

2004-10-18 Thread owner-emc-p...@listserv.ieee.org
In article f7e9180f6f7f5840858d3db815e4f7ad05fb9...@cms21.t-yuden.com,
Brian O'Connell boconn...@t-yuden.com writes

Typically, I have always measured/calculated distortion PF using the
current waveform. What market segments tend to use/prefer the voltage
w/f ? Do you think that end-users of component power supplies prefer one
parametric over the other ?

I tried to keep the explanation brief, but obviously it was too brief.
In general, both the voltage and the current are distorted, and in-phase
components of the voltage and current harmonics add to the true power.
Equally, quadrature components add to the apparent power. If you just
assume that the voltage is sinusoidal when it isn't, you do not get the
right answers.


 If it only meets the Class A limits, it doesn't have much distortion
 power factor correction, if any. The displacement power factor depends
 on how heavily the power supply is loaded.

I would appreciate if you could offer more commentary/insight on this
statement. Perhaps this is not based on power supplies that use active
PFC, where output loading has minimal influence on measured PF within
the unit's ratings.

It isn't based on power supplies with active PFC. But such supplies
normally meet the Class D limits if under 600 W active input power, so I
inferred from the citing of Class A limits that your power supply didn't
have active PFC. If it does, the power factor is likely to be very high,
and not a matter of concern for your customer. But it would be unwise to
guess a figure.
--
Regards, John Woodgate, OOO - Own Opinions Only.
The good news is that nothing is compulsory.
The bad news is that everything is prohibited.
http://www.jmwa.demon.co.uk Also see http://www.isce.org.uk


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Ron Pickard:  emc-p...@hypercom.com
 Scott Douglas emcp...@ptcnh.net

For policy questions, send mail to:

 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



RE: Power Factor correction

2004-10-18 Thread owner-emc-p...@listserv.ieee.org


 -Original Message- 
 From: John Woodgate [ mailto:j...@jmwa.demon.co.uk] 
 Sent: Saturday, October 16, 2004 2:03 PM 
 To: emc-p...@ieee.org 
 Subject: Re: Power Factor correction 

 Then there is the 'distortion power factor', which is a measure of the 
 ratio of total r.m.s. voltage to its fundamental component and of the 
 total r.m.s current to its fundamental component. 

Typically, I have always measured/calculated distortion PF using the current
waveform. What market segments tend to use/prefer the voltage w/f ? Do you
think that end-users of component power supplies prefer one parametric over
the other ?

  
 If it only meets the Class A limits, it doesn't have much distortion 
 power factor correction, if any. The displacement power factor depends 
 on how heavily the power supply is loaded. 

I would appreciate if you could offer more commentary/insight on this
statement. Perhaps this is not based on power supplies that use active PFC,
where output loading has minimal influence on measured PF within the unit's
ratings.


 You aren't going to solve this without getting your hands on an actual 
 power supply. Believe me! 

All should heed this statment from a man older and wiser then me... 
Nothing beats empirical verification, under end-use conditions. 

luck, 
Brian 

 This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/listserv/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Ron Pickard: emc-p...@hypercom.com Scott Douglas emcp...@ptcnh.net 


For policy questions, send mail to: 


Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc




Re: Power Factor correction

2004-10-16 Thread owner-emc-p...@listserv.ieee.org
In article 9F347458EDACB64B8FF57DB67E6E0FAA0121E14D@cerebrum.spraycool.
com, Gary McInturff gmcintu...@spraycool.com writes

  We have a new project that is, for all practical purposes a custom
design for a client.
We purchase a supply that indicates compliance with EN61000-3-2
harmonics. Our customer wants a more quantitative number. Is it 90%
PFC, 95% etc.

You don't have '90% PFC' power factor correction), you have '90% PF'
(power factor). Next, power factor, defined as true power/apparent
power, is composite if the load is non-linear. There is a 'displacement
power factor', which, if the voltage wave form OR the current waveform
is substantially undistorted is simply the cosine of the phase angle
between the sinusoidal quantity and the fundamental component of the
non-sinusoidal quantity. If both voltage and current are non-sinusoidal,
then both the true power and the apparent power contain terms associated
with harmonic frequencies.

Then there is the 'distortion power factor', which is a measure of the
ratio of total r.m.s. voltage to its fundamental component and of the
total r.m.s current to its fundamental component.

I can't tell that from the spec sheet and quite frankly at this
point I can't lay my hands on a power supply yet and obviously we
haven't gone to test yet with this in our equipment so I don't
believe I have any way of determining this (not sur
   e that I could
tell from the conformance test anyway - can I?)

Yes, if you get the raw data (amplitude of every component of supply
voltage and input current, with their phase angles) and process it.

When I call the power supply manufacturer, I can't directly
address the design engineer and all they can tell me is that it
meets the requirements for Class A waveform.
Am I overlooking something here in the datasheet? Is there
anyway to infer what what the PFC % is?

If it only meets the Class A limits, it doesn't have much distortion
power factor correction, if any. The displacement power factor depends
on how heavily the power supply is loaded.

You aren't going to solve this without getting your hands on an actual
power supply. Believe me!
--
Regards, John Woodgate, OOO - Own Opinions Only.
The good news is that nothing is compulsory.
The bad news is that everything is prohibited.
http://www.jmwa.demon.co.uk Also see http://www.isce.org.uk


This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list.Website:  http://www.ieee-pses.org/

To post a message to the list, send your e-mail to emc-p...@ieee.org

Instructions:  http://listserv.ieee.org/listserv/request/user-guide.html

List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:

 Ron Pickard:  emc-p...@hypercom.com
 Scott Douglas emcp...@ptcnh.net

For policy questions, send mail to:

 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:

http://www.ieeecommunities.org/emc-pstc



RE: Power Factor correction

2004-10-12 Thread owner-emc-p...@listserv.ieee.org
To calc PF you would need to know the true power and apparent power at a
particular test configuration. 

PF for an unit with active (more expensive) PFC should vary very little over
the rated input range. PF for units with passive (less expensive) PFC will
probably vary several percent over the rated input and output ranges. PF for
unit with no PFC (cheap) vary significantly with changes in line quality, and
significantly over the rated input and output ranges. No free lunch...

It is important to measure PF with an instrument intended for the measurement.
There are many ways to measure PF using just scopes and/or meters, but unless
you have instruments with very high crest factors, that can make
phase-relative measurements, and can accurately integrate over many cycles,
your resultant number could be suspect.

Final caveat, I have tested component power supplies from various sources. And
I have noted a few atypical cases where a unit reliably maintained a
consistent and high PF, but was operating at the limits or failing (depending
on the Class) according to CISPRs and the 61000-3-2 conducted immunity test.

luck, 
Brian 


-Original Message- 
From: robert Macy [ mailto:m...@california.com] 
Sent: Monday, October 11, 2004 4:16 PM 
To: Gary McInturff; emc-p...@ieee.org 
Subject: Re: Power Factor correction 

Gary, 

Is it possible to calculate the pfc from the spec? 

   - Robert - 

On Mon, 11 Oct 2004 10:54:01 -0700 
 Gary McInturff gmcintu...@spraycool.com wrote: 
 Ladies and Gentlemen 
 I think I may be stuck between a rock and a hard 
 place. 
 We have a new project that is, for all practical 
 purposes a custom 
 design for a client. 
 We purchase a supply that indicates compliance with 
 EN61000-3-2 
 harmonics. Our customer wants a more quantitative number. 
 Is it 90% PFC, 95% 
 etc. 
 I can't tell that from the spec sheet and quite 
 frankly at this point I 
 can't lay my hands on a power supply yet and obviously we 
 haven't gone to 
 test yet with this in our equipment so I don't believe I 
 have any way of 
 determining this (not sure that I could tell from the 
 conformance test 
 anyway - can I?) 
 When I call the power supply manufacturer, I can't 
 directly address the 
 design engineer and all they can tell me is that it meets 
 the requirements 
 for Class A waveform. 
 Am I overlooking something here in the datasheet? Is 
 there anyway to 
 infer what what the PFC % is? 
 Gary 

 This message
is from the IEEE Product Safety Engineering Society emc-pstc discussion list.
Website: http://www.ieee-pses.org/ 

To post a message to the list, send your e-mail to emc-p...@ieee.org 


Instructions: http://listserv.ieee.org/listserv/request/user-guide.html 


List rules: http://www.ieee-pses.org/listrules.html 


For help, send mail to the list administrators: 


Ron Pickard: emc-p...@hypercom.com Scott Douglas emcp...@ptcnh.net 


For policy questions, send mail to: 


Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org 


All emc-pstc postings are archived and searchable on the web at: 


http://www.ieeecommunities.org/emc-pstc




Re: Power Factor Correction

2003-03-04 Thread John Woodgate

I read in !emc-pstc that Dave Spencer dspen...@dsl-only.net wrote (in
185530-22003324161424...@dsl-only.net) about 'Power Factor Correction'
on Tue, 4 Mar 2003:
I am looking for some input on your experience with PFC as it relates
to testing (EN61000-3-2 and EN55022).  Has anyone using an AC-AC
external transformer in the 15-20 Watt range experienced difficulty
passing, e.g. no PFC?

Well, you don't say what the transformer is feeding! Assuming it's a
bridge rectifier with a fat filter capacitor, the resistances of the
transformer windings are usually sufficient to make the rectifier
conduction angle exceed 65 degrees, which should be sufficient to meet
the Class D limits. BUT those limits doesn't apply below 75 W anyway!

One might guess that you haven't read the standard, and have thus been
worrying over a non-problem. OTOH, one might, of course, be wrong in an
entirely unexpected direction.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Power Factor Correction - Power supply unit

2002-01-31 Thread John Woodgate

I read in !emc-pstc that am...@westin-emission.no wrote (in LFENJLPMMJB
mhpeibnilieihccaa.am...@westin-emission.no) about 'Power Factor
Correction - Power supply unit', on Thu, 31 Jan 2002:

Hi all,

An AC/DC power supply (230AC in / 28VDC 3A out) shall power an ITE (fire
alarm panel). I assume that EN61000-3-2 will apply for the total system
(Power supply + ITE).

Yes.

I was told that the power supply must have Power Factor Correction in order
to pass the harmonic EN61000-3-2 test.

Not necessarily. The ***Class A*** limits apply, not the Class D. This
is possibly the most significant change introduced by the Millennium
Amendment (A14). Class D applies now to PCs, VDUs and TV sets, not to
all ITE.

I think it is unlikely that a 100 W power supply can violate the Class A
limits. If it isn't a switch-mode type (i.e. it has a mains transformer)
it may even meet the Class D limits, or could be modified at low cost to
do so.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero.
PLEASE do NOT copy news posts to me by E-MAIL!

---
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Michael Garretson:pstc_ad...@garretson.org
 Dave Healddavehe...@mediaone.net

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
No longer online until our new server is brought online and the old 
messages are imported into the new server.


Re: Power Factor Correction, Medical Equipment?

1996-05-31 Thread LITTLEWORF
Although you are correct - neither does the EMC Directive. BUT the EN for
harmonics IS in the OJ and it would seem to me to be applicable. Any one else
agree??


Re: Power factor Correction

1995-12-11 Thread QA


The power factor correction standard is IEC 1000-3-2 (aka
EN 61000-3-2).

This standard applies to ALL electrical and electronic products
exceeding 75 watts maximum rated power.

The EN standard applies to all countries of the European
Community (most of Western Europe).

EN 61000-3-2 falls under the EMC Directive.  

The EMC Directive is effective 01 January 1996.  Therefore,
EN 61000-3-2 is effective 01 January 1996.



EN 61000-3-2 replaces EN 60555-2 (aka IEC 555-2).

EN 60555-2 applies to home appliances.  

For products currently under EN 60555-2, the Date of Withdrawal 
(DOW) of EN 60555-2 is 01 January 1997.  Therefore, EN 61000-3-2
is effective for home appliances 01 January 1997. 



An interpretation is that because EN 60555-2 excludes all other
equipment, the DOW is also the effective date for all equipment
excluded from EN 60555-2.  Therefore, the effective date of 
EN 61000-3-2 for ALL equipment is 01 January 1997.

From discussions in this forum, it appears that some authorities
in some countries (e.g., the U.K.) are accepting this 
interpretation, while other authorities and other countries are 
silent.



The conservative approach (i.e., without risk) for non-home 
appliance products is that such products comply with EN 61000-3-2 
as of 01 January 1996.

The risky approach is to delay incorporation of power factor
correction until 01 January 1997.  

The risky approach relies on an interpretation, which varies 
among authorities and countries.  If an authority or country 
holds the conservative position, then the risk is that of being 
caught claiming compliance with the EMC Directive, yet not 
including EN 61000-3-2 in the Manufacturer's Declaration.  The 
risk is having products denied entry into the country, and recall 
for those products already within the country.



Clearly, the folks responsible for EN 61000-3-2 have created a
very difficult position for manufacturers, one without sufficient
notice for implementation, and one with confusing effective dates.

If you have followed the development of IEC 1000-3-2, you will
have seen the rather dictatorial style of the committee leaders
and lack of consideration for other viewpoints.  Furthermore, it
is clear that they have not provided leadership in providing
adequate public announcement that the standard becomes effective
with the EMC Directive.  We've had years to prepare for the EMC
Directive, but only about one year to prepare for EN 61000-3-2.


Best regards,