Responses: What is Class 1, Div. 1 Group D?

1998-06-16 Thread BACHERJ
6057


Hello!

My name is Paul Kelly and I am in charge of UL's Hazardous Locations section 
here at our Northbrook, Illinois office.  Mike Windler forwarded your question 
to me regarding Class I, Division 1, Group D and I hope that the following 
proves helpful:

1. The marking string "Class I (Roman Numeral One), Division 1 (Arabic Numeral 
One), Group D" defines the characteristics of a "hazardous" (i.e. potentially 
explosive) area in accordance with the National Electrical Code (NEC).  See 
Articles 500 and 501 of 1996 NEC.

2. Class I indicates that the "hazard" is flammable gases, vapors or liquids.

3. Division 1 indicates that the "hazard" is likely to exist all of the time or 
some of the time.

4. Group D indicates that the ignition-related properties of the "hazard" are 
similar to propane.

5. Equipment installed in such areas must be protected by one of the following 
methods - explosionproof, intrinsic safety or purging/pressurization.

6. Explosionproof is a protection method that relies on the enclosure of an 
incendive arcing part to withstand the impact of an internal explosion and to 
prevent propagation of any flames from the inside to the outside of the 
enclosure.  The U.S. requirements for this protection method are contained in 
ANSI/UL1203, "Explosion-Proof and Dust-IgnitionProof Electrical Equipment for 
Use in Hazardous (Classified) Locations".

7. Intrinsic Safety is a protection method that does not rely on the enclosure, 
but instead relies on the "intrinsic design" of the circuitry to not be able to 
ignite the atmosphere under single or double fault conditions.  The U.S. 
requirements for this protection method are contained in ANSI/UL913, 
"Intrinsically Safe Apparatus and Associated Apparatus for Use in Class I, II, 
and III, Division 1, Hazardous (Classified) Locations".

8. Purging/Pressurization is a protection method that relies on the use of a 
"protective gas" to prevent entry of the hazardous atmosphere into the enclosure
of an incendive arcing part.  The U.S. requirements for this protection method 
are contained in ANSI/NFPA496, "Purged and Pressurized Enclosures for Electrical
Equipment".

Note: Please realize that these "definitions" in Items 6, 7 and 8 above 
are only intended to convey 
the basic concepts of each protection method.

9. Equipment utilizing any of the above protection methods can obtain a "rating"
of Class I, Division 1, Group D - but the certification evaluation would be 
distinctly different for each.

10. UL has an educational poster that details all of the above information - and
a good deal more.  If you would like complimentary copies of this poster, just 
let me know your address and how many you could use and I can have them mailed 
to you.

Let me know if I can provide any further assistance...

Paul T. Kelly
Associate Managing Engineer
Hazardous Locations
E-mail: kel...@ul.com


The question was :
__ Reply Separator _
Subject: What is Class 1, Div. 1 Group D?
Author:  bach...@ccmail.mmsday.com (BACHERJ) at Internet_Gateway
List-Post: emc-pstc@listserv.ieee.org
Date:6/9/ 0 8:14 AM


Yesterday we had a customer call asking if our products were Class 1, Div. 
1, Group D compliant.  Can anyone tell me where I can get information on 
what it is and what it takes to meet it?

Jim Bacher
Paxar-Monarch
bach...@monarch.com


Re: What is Class 1, Div. 1 Group D?

1998-06-10 Thread mike harris
Jim,

Try National Electrical Code Article 500 Hazardous (Classified) Locations

Class 1 is locations where "flammable gases or vapors are or may be in the
air in quantities sufficient to produce explosive or ignitible mixtures"

Class 1 Div 1 is as above due to  1) normal conditions, or 2) frequently
because of repair operations/leakage/etc, or 3) breakdown/faulty operation

Group D is atmospheres such as acetone, ammonia, benzene, butane,
cyclopropane, ethanol, gasoline, hexane, methanol, methane, natural gas,
naptha, propane, etc

If your product carries a rating label with the above Class 1 Div 1 Group D
rating and a NRTL mark, you can claim to meet this performance level. If
not, I suggest to contact UL in Northbrook IL at 847-272-8800 to discuss
evaluating your product.

I used to work at Square D Co., which makes HazLoc electrical equipment,
and was responsible for building an in-house hydrogen-air testing facility,
plus testing with UL witnessing our tests for Listing.

My company helps manufacturers get UL and other agency certifications. If
we can help, feel free to contact me.

Mike Harris
Teccom Co.
tecco...@i-cafe.net
707-258-1360/fax 1361

--
> From: BACHERJ 
> To: emc-p...@majordomo.ieee.org
> Subject: What is Class 1, Div. 1 Group D?
> Date: Tuesday, June 09, 1998 5:14 AM
> 
> Yesterday we had a customer call asking if our products were Class 1,
Div. 
> 1, Group D compliant.  Can anyone tell me where I can get information on 
> what it is and what it takes to meet it?
> 
> Jim Bacher
> Paxar-Monarch
> bach...@monarch.com


RE: What is Class 1, Div. 1 Group D?

1998-06-09 Thread Kazimier Gawrzyjal
Jim,

I'm not positive but that sounds like classifications under a Hazardous
Locations safety standard (UL or CSA) ... I don't have any on hand to
verify.  

Kaz Gawrzyjal
Nortel
k...@nortel.com

> -Original Message-
> From: bach...@ccmail.mmsday.com [SMTP:bach...@ccmail.mmsday.com]
> Sent: Tuesday, June 09, 1998 6:14 AM
> To:   emc-p...@majordomo.ieee.org
> Subject:      What is Class 1, Div. 1 Group D?
> 
> Yesterday we had a customer call asking if our products were Class 1, Div.
> 
> 1, Group D compliant.  Can anyone tell me where I can get information on 
> what it is and what it takes to meet it?
> 
> Jim Bacher
> Paxar-Monarch
> bach...@monarch.com


FW: What is Class 1, Div. 1 Group D?

1998-06-09 Thread Schanker, Jack
Jim:

If you have to ask, chances are your products are not compliant, much
less approved.

A source for information is a safety approval agency such as UL, Factory
Mutual, or CSA. Call them or check their web sites for free information.

In short, Class I (roman numeral I) is an area where flammable gases,
vapors, or liquids may be present. Division 1 is "where ignitable
concentrations of flammable gases, vapors, or liquids can exist all of
the time or some of the time under normal operating conditions." Group D
tells you that the gas in question is propane.

To be compliant, a product must be designed, and tested by an approved
agency to demonstrate that sparks, or excessive operating temperatures
which could cause ignition of the gas, do not exist, and cannot exist
even with a fault.

Hope this helps. I suggest you tell the customer NO.

Jacob Z. Schanker, P.E.
Director of Agency Compliance
California Microwave
716 242 8454 (voice)
716 242 8427 (fax)
j.schan...@mdsroc.com
--->
>--
>From:  bach...@ccmail.mmsday.com[SMTP:bach...@ccmail.mmsday.com]
>Sent:  Tuesday, June 09, 1998 8:14 AM
>To:emc-p...@majordomo.ieee.org
>Subject:   What is Class 1, Div. 1 Group D?
>
>Yesterday we had a customer call asking if our products were Class 1,
>Div. 
>1, Group D compliant.  Can anyone tell me where I can get information
>on 
>what it is and what it takes to meet it?
>
>Jim Bacher
>Paxar-Monarch
>bach...@monarch.com
>


What is Class 1, Div. 1 Group D?

1998-06-09 Thread BACHERJ
Yesterday we had a customer call asking if our products were Class 1, Div. 
1, Group D compliant.  Can anyone tell me where I can get information on 
what it is and what it takes to meet it?

Jim Bacher
Paxar-Monarch
bach...@monarch.com