[Emc-users] Noise Problems with Pico Systems USC and Gecko 203V Stepper Drives

2020-08-27 Thread Matthew Herd
I spent some time the week before last investigating the noise issue that I’ve 
been having on my Bridgeport BOSS mill.  The system architecture involves a 
single phase 240V input, which powers a VFD for the 2HP spindle motor, a 120V 
step down transformer to power some devices on the machine (spray mister, 
accessory lights, cabinet ventilation fans), and a 72V/24V/12V DC power supply 
to power the USC board and the three Gecko 203V stepper drivers.  First, I 
disconnected every device from the DC power supply by disconnecting the 
positive terminal and disconnected one of the 240V AC wires to the VFD.  I 
measured the noise from the ground bolt to the ground pin of the 12V output of 
the power supply.  Noise was nominal, perhaps 20-40mV peak to peak at 50ms/div 
(as I recall).  Reconnecting the VFD gave approximately 600mV of noise peak to 
peak.  This seemed rather surprising given the fact that I’m essentially 
measuring the same wire across about 18".

I installed a Rasmi VFD filter and I re-wired the grounds.  Instead of 2 
grounds which were connected via the machine, I ran all grounds back to the 
ground bolt in the power cabinet.  Previously, the 72V ground to the drives was 
only wired directly from the power supply to the drives.  It was isolated from 
the other power and logic grounds, but is now common.  The only ground that was 
not run to the power cabinet ground was the stepper’s step and direction signal 
ground.  This ground is connected at the USC board to a ground which is common 
with the 12V power input ground that powers the USC board (and is therefore run 
back to the main ground bolt).  Upon powering up everything I discovered that 
the spindle index encoder noise had increased from around 1.4V peak to peak to 
more like 7V peak to peak.  I’m shocked that a ground wiring change could 
impact this measurement so dramatically.  The VFD only noise is now measuring 
approximately 400mV p-p at the power supply 12V ground, which I believe is 
acceptable.  However, I’m sure I could find higher spikes if I reduced the time 
scale based on my previous test results.  I got some conflicting results when 
trying to isolate the cause, so I rechecked my measurements today.  Rechecking 
my measurements at the 12V output ground on the power supply, I found:

VFD only:
~300mV

USC only:
~40mV

USC and 24V devices (mostly SSRs for pneumatic valves):
~40-50mV

USC, 24V devices, and Geckos with NO 72V input (i.e. only step & direction 
inputs)
~40-50mV

USC, 24V devices, and Geckos with 72V input (i.e. ready to move motors)
~1-1.2V

Now I tested the 72V wire at the gecko’s power input and found noise of 
approximately 5V.

Then I removed the wire at one of the two 72V supply outputs (it has dual 72V 
outputs) and measured at the + terminal with two other geckos powered from the 
other 72V output.  Noise was minimal (though difficult to measure as my scope 
wouldn’t let me scale to see the ripple as clearly — at most it’s probably 
1-2V).  This leads me to the conclusion that either the supply somehow 
struggles under load or the Geckos are introducing inordinate noise.  I’m 
doubtful the supply is the culprit because the noise appears to be a much 
higher frequency than would be expected from a simple rectified power supply 
with filtering capacitors.  The geckos are in the control cabinet with the USC. 
 Would it help to move them closer?

Thanks,
Matt

___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Noise Problems with Pico Systems USC and Gecko 203V Stepper Drives

2020-08-31 Thread Matthew Herd
Thanks all for the advice.  I now have plenty to try.  I may just replace them 
for something else though.

> On Aug 27, 2020, at 11:30 PM, Chris Albertson  
> wrote:
> 
> I have to admit most of my noise-hunting experience is with vacuum
> tube-based amplifiers.   But the exact same techniques apply.  The first
> step is to always apply the best-practice construction technique.  Then if
> that does not quiet things down you cut the system in half and see which
> half still has the noise problem and then cut that part in half and so on.
> 
> Using this we can make tube amps today that are better than anything
> people could buy back in the tube era.  All the advice about physical
> separation, twisting all the wires and shields and star grounds really does
> work.  But it is a lot of work to do as you have to think about every inch
> of every wire.
> 
> Hey, it could be worse, be glad you were not the one who had to work out
> the wiring for something like the photo below.  Seriously they make up
> these rules about 10X cable diameter spacing and such so stuff almost works
> the first time even really hard cases like below.   Same with my
> Amplifiers.  I apply every technique I know and they now work the first
> time.  Before it would take days to debug.
> 
> [image: poza-China-roboti-1280x620.jpg]
> 
> On Thu, Aug 27, 2020 at 6:25 PM Matthew Herd  wrote:
> 
>> Hi Chris,
>> 
>> The frequency of the noise as measured on the ground appears to be a
>> ringing signal repeating at roughly 600kHz.  I guess my previous
>> measurement of 80kHz was wrong.  I’m not sure why it would be different.
>> I’m not 100% sure that it’s a consistent 600kHz, and might actually be
>> several signals overlaid.  The noise events appear to ring, as they decay
>> from a larger sinusoidal spike, with about 6 sinusoidal pulses in total
>> until they taper off.
>> 
>> The wires are generally bundled, so that may be a factor.
>> 
>> The housings on the motors, drivers, and supplies are grounded to the
>> machine.  Only the encoders and motor to drive cables are shielded, and
>> they’re shielded on only one end.  The remaining wires are simply primary
>> cable and are not grounded.  Only some of the signal wires are twisted
>> pairs.
>> 
>> Thanks!
>> Matt
>> 
>> 
>>> On Aug 27, 2020, at 1:24 PM, Chris Albertson 
>> wrote:
>>> 
>>> Can you measure the frequency of the noise?  If this is a digital scope
>> it
>>> might be able to show a spectra.  Lacking that you can eyeball-estimate
>> the
>>> period or width of any spikes.
>>> 
>>> The other bit of information we don't have is how the wiring is laid out.
>>> Best practice would be to use tightly twisted pairs where the current in
>>> each of the two members of the pair is equal and also to never bundle
>> power
>>> and signal wires.  The field around a twisted pair is close to zero
>>> after about 10 cable-diameters so if a twisted power cable is 3mm thick,
>>> keep other wires 30mm away.
>>> 
>>> Are all the housing on the motors, drivers, and supplies grounded.  This
>>> would be to a protective ground  Also are the wires shielded and grounded
>>> on one and only one end?
>>> 
>>> If the noise is determined to be a relative high frequency then ferrite
>>> cores on the wires help but they no nothing for 120 Hz.
>>> 
>>> 
>>> 
>>> On Thu, Aug 27, 2020 at 10:00 AM Matthew Herd 
>> wrote:
>>> 
 I spent some time the week before last investigating the noise issue
>> that
 I’ve been having on my Bridgeport BOSS mill.  The system architecture
 involves a single phase 240V input, which powers a VFD for the 2HP
>> spindle
 motor, a 120V step down transformer to power some devices on the machine
 (spray mister, accessory lights, cabinet ventilation fans), and a
 72V/24V/12V DC power supply to power the USC board and the three Gecko
>> 203V
 stepper drivers.  First, I disconnected every device from the DC power
 supply by disconnecting the positive terminal and disconnected one of
>> the
 240V AC wires to the VFD.  I measured the noise from the ground bolt to
>> the
 ground pin of the 12V output of the power supply.  Noise was nominal,
 perhaps 20-40mV peak to peak at 50ms/div (as I recall).  Reconnecting
>> the
 VFD gave approximately 600mV of noise peak to peak.  This seemed rather
 surprising given the fact that I’m essentially measuring the same wire
 across about 18".
 
 I installed a Rasmi VFD filter and I re-wired the grounds.  Instead of 2
 grounds which were connected via the machine, I ran all grounds back to
>> the
 ground bolt in the power cabinet.  Previously, the 72V ground to the
>> drives
 was only wired directly from the power supply to the drives.  It was
 isolated from the other power and logic grounds, but is now common.  The
 only ground that was not run to the power cabinet ground was the
>> stepper’s
 step and direction signal ground.  This ground is connected at the USC
 board to

Re: [Emc-users] Noise Problems with Pico Systems USC and Gecko 203V Stepper Drives

2020-08-27 Thread Chris Albertson
Can you measure the frequency of the noise?  If this is a digital scope it
might be able to show a spectra.  Lacking that you can eyeball-estimate the
period or width of any spikes.

The other bit of information we don't have is how the wiring is laid out.
Best practice would be to use tightly twisted pairs where the current in
each of the two members of the pair is equal and also to never bundle power
and signal wires.  The field around a twisted pair is close to zero
after about 10 cable-diameters so if a twisted power cable is 3mm thick,
keep other wires 30mm away.

Are all the housing on the motors, drivers, and supplies grounded.  This
would be to a protective ground  Also are the wires shielded and grounded
on one and only one end?

If the noise is determined to be a relative high frequency then ferrite
cores on the wires help but they no nothing for 120 Hz.



On Thu, Aug 27, 2020 at 10:00 AM Matthew Herd  wrote:

> I spent some time the week before last investigating the noise issue that
> I’ve been having on my Bridgeport BOSS mill.  The system architecture
> involves a single phase 240V input, which powers a VFD for the 2HP spindle
> motor, a 120V step down transformer to power some devices on the machine
> (spray mister, accessory lights, cabinet ventilation fans), and a
> 72V/24V/12V DC power supply to power the USC board and the three Gecko 203V
> stepper drivers.  First, I disconnected every device from the DC power
> supply by disconnecting the positive terminal and disconnected one of the
> 240V AC wires to the VFD.  I measured the noise from the ground bolt to the
> ground pin of the 12V output of the power supply.  Noise was nominal,
> perhaps 20-40mV peak to peak at 50ms/div (as I recall).  Reconnecting the
> VFD gave approximately 600mV of noise peak to peak.  This seemed rather
> surprising given the fact that I’m essentially measuring the same wire
> across about 18".
>
> I installed a Rasmi VFD filter and I re-wired the grounds.  Instead of 2
> grounds which were connected via the machine, I ran all grounds back to the
> ground bolt in the power cabinet.  Previously, the 72V ground to the drives
> was only wired directly from the power supply to the drives.  It was
> isolated from the other power and logic grounds, but is now common.  The
> only ground that was not run to the power cabinet ground was the stepper’s
> step and direction signal ground.  This ground is connected at the USC
> board to a ground which is common with the 12V power input ground that
> powers the USC board (and is therefore run back to the main ground bolt).
> Upon powering up everything I discovered that the spindle index encoder
> noise had increased from around 1.4V peak to peak to more like 7V peak to
> peak.  I’m shocked that a ground wiring change could impact this
> measurement so dramatically.  The VFD only noise is now measuring
> approximately 400mV p-p at the power supply 12V ground, which I believe is
> acceptable.  However, I’m sure I could find higher spikes if I reduced the
> time scale based on my previous test results.  I got some conflicting
> results when trying to isolate the cause, so I rechecked my measurements
> today.  Rechecking my measurements at the 12V output ground on the power
> supply, I found:
>
> VFD only:
> ~300mV
>
> USC only:
> ~40mV
>
> USC and 24V devices (mostly SSRs for pneumatic valves):
> ~40-50mV
>
> USC, 24V devices, and Geckos with NO 72V input (i.e. only step & direction
> inputs)
> ~40-50mV
>
> USC, 24V devices, and Geckos with 72V input (i.e. ready to move motors)
> ~1-1.2V
>
> Now I tested the 72V wire at the gecko’s power input and found noise of
> approximately 5V.
>
> Then I removed the wire at one of the two 72V supply outputs (it has dual
> 72V outputs) and measured at the + terminal with two other geckos powered
> from the other 72V output.  Noise was minimal (though difficult to measure
> as my scope wouldn’t let me scale to see the ripple as clearly — at most
> it’s probably 1-2V).  This leads me to the conclusion that either the
> supply somehow struggles under load or the Geckos are introducing
> inordinate noise.  I’m doubtful the supply is the culprit because the noise
> appears to be a much higher frequency than would be expected from a simple
> rectified power supply with filtering capacitors.  The geckos are in the
> control cabinet with the USC.  Would it help to move them closer?
>
> Thanks,
> Matt
>
> ___
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users
>


-- 

Chris Albertson
Redondo Beach, California

___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Noise Problems with Pico Systems USC and Gecko 203V Stepper Drives

2020-08-27 Thread Matthew Herd
Hi Chris,

The frequency of the noise as measured on the ground appears to be a ringing 
signal repeating at roughly 600kHz.  I guess my previous measurement of 80kHz 
was wrong.  I’m not sure why it would be different.  I’m not 100% sure that 
it’s a consistent 600kHz, and might actually be several signals overlaid.  The 
noise events appear to ring, as they decay from a larger sinusoidal spike, with 
about 6 sinusoidal pulses in total until they taper off.

The wires are generally bundled, so that may be a factor.  

The housings on the motors, drivers, and supplies are grounded to the machine.  
Only the encoders and motor to drive cables are shielded, and they’re shielded 
on only one end.  The remaining wires are simply primary cable and are not 
grounded.  Only some of the signal wires are twisted pairs.

Thanks!
Matt


> On Aug 27, 2020, at 1:24 PM, Chris Albertson  
> wrote:
> 
> Can you measure the frequency of the noise?  If this is a digital scope it
> might be able to show a spectra.  Lacking that you can eyeball-estimate the
> period or width of any spikes.
> 
> The other bit of information we don't have is how the wiring is laid out.
> Best practice would be to use tightly twisted pairs where the current in
> each of the two members of the pair is equal and also to never bundle power
> and signal wires.  The field around a twisted pair is close to zero
> after about 10 cable-diameters so if a twisted power cable is 3mm thick,
> keep other wires 30mm away.
> 
> Are all the housing on the motors, drivers, and supplies grounded.  This
> would be to a protective ground  Also are the wires shielded and grounded
> on one and only one end?
> 
> If the noise is determined to be a relative high frequency then ferrite
> cores on the wires help but they no nothing for 120 Hz.
> 
> 
> 
> On Thu, Aug 27, 2020 at 10:00 AM Matthew Herd  wrote:
> 
>> I spent some time the week before last investigating the noise issue that
>> I’ve been having on my Bridgeport BOSS mill.  The system architecture
>> involves a single phase 240V input, which powers a VFD for the 2HP spindle
>> motor, a 120V step down transformer to power some devices on the machine
>> (spray mister, accessory lights, cabinet ventilation fans), and a
>> 72V/24V/12V DC power supply to power the USC board and the three Gecko 203V
>> stepper drivers.  First, I disconnected every device from the DC power
>> supply by disconnecting the positive terminal and disconnected one of the
>> 240V AC wires to the VFD.  I measured the noise from the ground bolt to the
>> ground pin of the 12V output of the power supply.  Noise was nominal,
>> perhaps 20-40mV peak to peak at 50ms/div (as I recall).  Reconnecting the
>> VFD gave approximately 600mV of noise peak to peak.  This seemed rather
>> surprising given the fact that I’m essentially measuring the same wire
>> across about 18".
>> 
>> I installed a Rasmi VFD filter and I re-wired the grounds.  Instead of 2
>> grounds which were connected via the machine, I ran all grounds back to the
>> ground bolt in the power cabinet.  Previously, the 72V ground to the drives
>> was only wired directly from the power supply to the drives.  It was
>> isolated from the other power and logic grounds, but is now common.  The
>> only ground that was not run to the power cabinet ground was the stepper’s
>> step and direction signal ground.  This ground is connected at the USC
>> board to a ground which is common with the 12V power input ground that
>> powers the USC board (and is therefore run back to the main ground bolt).
>> Upon powering up everything I discovered that the spindle index encoder
>> noise had increased from around 1.4V peak to peak to more like 7V peak to
>> peak.  I’m shocked that a ground wiring change could impact this
>> measurement so dramatically.  The VFD only noise is now measuring
>> approximately 400mV p-p at the power supply 12V ground, which I believe is
>> acceptable.  However, I’m sure I could find higher spikes if I reduced the
>> time scale based on my previous test results.  I got some conflicting
>> results when trying to isolate the cause, so I rechecked my measurements
>> today.  Rechecking my measurements at the 12V output ground on the power
>> supply, I found:
>> 
>> VFD only:
>> ~300mV
>> 
>> USC only:
>> ~40mV
>> 
>> USC and 24V devices (mostly SSRs for pneumatic valves):
>> ~40-50mV
>> 
>> USC, 24V devices, and Geckos with NO 72V input (i.e. only step & direction
>> inputs)
>> ~40-50mV
>> 
>> USC, 24V devices, and Geckos with 72V input (i.e. ready to move motors)
>> ~1-1.2V
>> 
>> Now I tested the 72V wire at the gecko’s power input and found noise of
>> approximately 5V.
>> 
>> Then I removed the wire at one of the two 72V supply outputs (it has dual
>> 72V outputs) and measured at the + terminal with two other geckos powered
>> from the other 72V output.  Noise was minimal (though difficult to measure
>> as my scope wouldn’t let me scale to see the ripple as clearly — at most
>> it

Re: [Emc-users] Noise Problems with Pico Systems USC and Gecko 203V Stepper Drives

2020-08-27 Thread Jon Elson

On 08/27/2020 11:57 AM, Matthew Herd wrote:

This leads me to the conclusion that either the supply somehow struggles under 
load or the Geckos are introducing inordinate noise.
Geckos are known to be quite noisy.  They are sending 72 V 
square wave pulses at 20 KHz into the motor coils.  Possibly 
putting a bit of a filter on the motor wires (maybe a small 
choke of 100 uH or less on each wire) might help.  Also, 
they send strong pulses into their metal cabinet, you might 
try isolating the Gecko mounting plate from the machine 
housing.  Make VERY sure to route motor wires and power 
wires for the Gecko drives well away from all other wiring, 
and if possible have these wires cross at right angles to 
any other wiring.


Jon