Re: CP30 to CP60 upgrade
We have two FT pair of CP60s installed in our operating units and in both cases the Fieldbus has caused us numerous headaches until we figured out the correct installation. In fact we are still having some problems. We thought the coax ethernet cabling would be easy, but we discovered otherwise. We have seen a lot of problems similar to yours. The coax ethernet installation is very different from the previous Fieldbus cabling. Basis our experience, the way the terminators were installed or connection problems, is our best guess as to the source of your problem.Here is what some of what we have learned the hard way: 1. Don't branch (split) the coax ethernet signal with tees. Wire in a serial path - go in one leg of a FBI10E and then out the other (every FBI10E has 2 cables). Put a terminator only at the end of the serially wired leg. There should be only a total of 2 terminators on each coax Fieldbus (A/B) segment - one is probably at the CP end and the other is probably at the field (FBM) end. 2. If you are using coax to fiber media converters, the BNC connection at each of the media converters has to be terminated. In our case using the Black Box media converters provided by Foxboro, we had to put a tee with a terminator. 3. We have a CP60FT installation that connects via coax to about 17 old style FBMs using 3 pair of FBI10Es (3 different Field8 enclosures). These have not been a problem after we got the terminators and Fieldbus cabling installed correctly. 4. We have another CP60FT installation that connects to about 26 old style FBMs (in an IE32) using a pair of FBI10Es and four 200 series I/O using a pair of FCMs. A fiber optic segment (using 2 coax to fiber media converters each) is used in the middle of each of the Fieldbus A B cabling. This installation has been a very big headache. Now that we are cabled serially and have terminators installed in the correct places, we are still experiencing intermittent Fieldbus B problems (usually only with the 200 series I/O which is at the end of the leg). We punted on the problem and called in Foxboro yesterday to look at it, the only thing noticeably wrong with the installation is that we need a newer rev of Fieldbus terminators that go on the 200 series I/O back plate. I am not sure if the new terminators will solve our problem, but I hope so. One of the early problems with this installation was that we had problems with some of the FBMs in the IE32 enclosure and it was before we installed the 200 series I/O segment. The FBMs in the enclosure were originally split between 2 pair of FBI10Es and they were cabled serially. To solve the problem, I removed 1 pair of FBI10Es and used local extension cables to connect the Fieldbus in the upper portion of the cabinet to the lower portion of the cabinet. Once we added the 200 series I/O then we had a new set of problems. 5. Is your Fieldbus properly terminated within your I/O rack/enclosure. If it is not properly terminated, you are more apt to have a problem with the new Fieldbus than you previously did with the older slower one. 6. A bad coax terminator or tee could cause the problem. I have heard of a few problems with the FBI10E heads - I guess the cables might get strained. 7. Depending on your available slots, the number of FBMs involved, and the number of different remote Fieldbus connections involved, I have found that you can keep the old Fieldbus intact on the back end and only convert the front end (CP end) by using both a Fieldbus Isolator and a FBI10E. For instance, you can take a I/O rack and put an FBI10E in slot 1 and a FBI in slot 2. Wire the FBI10E to your CP60 and wire your FBI to the old style FBMs with the old style Fieldbus cabling. Even if Foxboro supported this arrangement, they would probably tell you not to have communications for more than 21 FBMs going through a single FBI. I hope there is something in this list that can help you. Campbell John C [EMAIL PROTECTED] To: Foxboro Casandra (E-mail) Sent by: [EMAIL PROTECTED] [EMAIL PROTECTED]cc: oject.org Subject: CP30 to CP60 upgrade
RE: CP30 to CP60 upgrade
Yes they were all updated. This doesn't seem to be the problem, but we'll keep checking. Thanks for your assistance. John I know all FBM's require EEPROM update for version 6.2.1. But you have done that I guess... Ron Deen Campbell John C wrote: We are currently upgrading one of our sites from a CP30FT to a CP60FT and are experiencing some difficulties. The actual upgrade went relatively smoothly but after the AW was placed back on line with the new CP60's we started to receive numerous fieldbus failure alarms (PIOBUS A/B) that would randomly come in and out. Sometimes we would have no alarms for about 1/2 hour and then continuous alarms for the next 20 minutes. There was no pattern as to when the alarms would occur. Occasionally when the alarms occurred we would lose communication to the fieldbus altogether (blue flu on the operator screen). Until we do some more detail investigations (with Fox Mass.) we have gone back to the old CP30 system. Has anyone else experienced similar problems and what did you do to get around it. Some back ground information: The switchover is being performed at the same time as a revision upgrade from 6.1 to 6.2.1 on a AW/WP51B system. All fieldbus modules are of the traditional rack mounted type (no din rail mounted modules). Much appreciation for any assistance. John Campbell Dofasco [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED]
Re: CP30 to CP60 upgrade
I noticed you have CP60FT. The filedbus cabling can be confusing and you may have both fieldbusses connected to eachother. Take care of termination and as mentioned here: do not branch. Termination will not be correct. Only two must be installed per fieldbus. Ron Campbell John C wrote: Yes they were all updated. This doesn't seem to be the problem, but we'll keep checking. Thanks for your assistance. John I know all FBM's require EEPROM update for version 6.2.1. But you have done that I guess... Ron Deen Campbell John C wrote: We are currently upgrading one of our sites from a CP30FT to a CP60FT and are experiencing some difficulties. The actual upgrade went relatively smoothly but after the AW was placed back on line with the new CP60's we started to receive numerous fieldbus failure alarms (PIOBUS A/B) that would randomly come in and out. Sometimes we would have no alarms for about 1/2 hour and then continuous alarms for the next 20 minutes. There was no pattern as to when the alarms would occur. Occasionally when the alarms occurred we would lose communication to the fieldbus altogether (blue flu on the operator screen). Until we do some more detail investigations (with Fox Mass.) we have gone back to the old CP30 system. Has anyone else experienced similar problems and what did you do to get around it. Some back ground information: The switchover is being performed at the same time as a revision upgrade from 6.1 to 6.2.1 on a AW/WP51B system. All fieldbus modules are of the traditional rack mounted type (no din rail mounted modules). Much appreciation for any assistance. John Campbell Dofasco [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED]
RE: CP30 to CP60 upgrade
We use single CP60's and got the same problem (we are using 200 series I/O) the problem went away when we went to 24 FBM's. When we had 23 FBM's the fault was as you explained regardless of FBM location. The errors predominantly reported to an individual location and usually to a FBM204 (output fbm) We have 4 identical process streams and the symptom was the same on all 4 I sent off CAR#1001152 and the reply stated the errors are not a problem and the fix would be in 6.3 The errors are a problem as they make the system button flash While I am mentioning FBM204's I have found 50% are not up to calibration specification -Original Message- From: Campbell John C [mailto:[EMAIL PROTECTED]] Sent: Friday, May 04, 2001 12:44 AM To: Foxboro Casandra (E-mail) Subject: CP30 to CP60 upgrade We are currently upgrading one of our sites from a CP30FT to a CP60FT and are experiencing some difficulties. The actual upgrade went relatively smoothly but after the AW was placed back on line with the new CP60's we started to receive numerous fieldbus failure alarms (PIOBUS A/B) that would randomly come in and out. Sometimes we would have no alarms for about 1/2 hour and then continuous alarms for the next 20 minutes. There was no pattern as to when the alarms would occur. Occasionally when the alarms occurred we would lose communication to the fieldbus altogether (blue flu on the operator screen). Until we do some more detail investigations (with Fox Mass.) we have gone back to the old CP30 system. Has anyone else experienced similar problems and what did you do to get around it. Some back ground information: The switchover is being performed at the same time as a revision upgrade from 6.1 to 6.2.1 on a AW/WP51B system. All fieldbus modules are of the traditional rack mounted type (no din rail mounted modules). Much appreciation for any assistance. John Campbell Dofasco [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED] --- This list is neither sponsored nor endorsed by the Foxboro Company. All postings from this list are the work of list subscribers and no warranty is made or implied as to the accuracy of any information disseminated through this medium. By subscribing to this list you agree to hold the list sponsor(s) blameless for any and all mishaps which might occur due to your application of information received from this mailing list. To be removed from this list, send mail to [EMAIL PROTECTED] with unsubscribe foxboro in the Subject. Or, send any mail to [EMAIL PROTECTED]