Re: UPS question

2010-08-14 Thread Ian Smith
In freebsd-questions Digest, Vol 323, Issue 9, Message: 3
On Wed, 11 Aug 2010 15:18:01 -0500 Ryan Coleman ryan.cole...@cwis.biz wrote:
  On Aug 11, 2010, at 3:06 PM, David Brodbeck wrote:
  
   On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:
   He thinks that at 500W needed it would give me about 12 minutes on a
   1400VA. My consideration is, then, give the server 2 minutes on battery.
   If full power has not been returned, shut down the server but leave the
   modem (w/ wireless) and switch running with power for up to 6 hours.
   
   A bit of advice: If this is an unattended system, give some thought to how
   you will boot the server back up if the outage is longer than two minutes
   but shorter than six hours.  Most UPS installations have *some* kind of
   race condition issue if power comes back after the servers have begun a
   shutdown, but in your case it's an unusually long window.
  
  Meaning that my 2-minute window is unusually long? If the UPS can 
  support the system for 12 minutes, I say give it 20% of the life of 
  the support because our power outages here are usually spikes that 
  kill my current web server (but amazingly *not* my file server). In 
  fact, one of those power fluxes occurred last night. I love storms 
  for the light shows, but hate them for the toll they take on my 
  servers.

Indeed.  Ryan, I'm coming in late but I've read the whole thread, after
many people have added useful insights.

However I must question your initial power estimate for this server; in 
your first post you said (cutting a bit):

  I am looking at a 1400VA / 980W UPS to run a single server with a 
  usually not on monitor, a DSL modem and a simple switch. The server 
  should generate about 330W in power consumption, the monitor another
  50-100, the modem about 10 and the switch about another 10 watts.
 
  So:
  UPS: 1400VA
 
  Server: 400W (liberal estimate)
  Modem: 10W
  Switch: 10W
  Monitor: 75W
 
  Total: 495W

First, forget the monitor.  You said it's usually off anyway, as you'd 
expect on a server.  Plug it into the mains directly as needed, not on 
the UPS.  Or at least use DPMS to suspend it after a minute or so idle.

Secondly, get a power meter and actually measure your server running.  
Unless it's a real monster, it will likely draw less than 200W in normal 
use, possibly much less if using powerd to moderate CPU speed by load.

So I suspect you may get something like 5 times the full-load rated time 
out of your 1400VA UPS, maybe 20-25 minutes or so.  5 minutes should be 
a comfortable runtime, to shut it down with 70-80% capacity remaining.

Thirdly, I'll second using another UPS (eg 300VA units are cheap) for 
powering other than your server.  That way you can use features of your 
software (eg NUT) to properly signal the UPS to shutdown (irrevocably) 
just after your server shuts down, to get proper resumption when power 
returns.  Should you get multiple successive on-battery then on-mains 
events, good UPSs will delay restarting until there's enough capacity to 
run another cycle, which time may be tunable for your requirements.

  Additionally I spent $34 on a video card today that reduces my power 
  consumption by 150Watts, resulting in a $13 per month savings in my 
  powerbill - in MN we have a fixed-rate utility fee structure per 
  season (winter power costs less than summer, I believe, for whatever 
  reason) and a $10 mail-in rebate on the card means I will be turning 
  a net profit in 2 months! -- Ryan

Sorry, I don't get why you'd run a video card using in excess of 150W on 
any server?  Or is that for your hot gaming box? :)

cheers, Ian
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-14 Thread Ryan Coleman
Just going to reply to this one bit for now: The computer used to be a gaming 
computer, converted this past fall into a file server when I lacked time to 
play any games in a year.

 Additionally I spent $34 on a video card today that reduces my power 
 consumption by 150Watts, resulting in a $13 per month savings in my 
 powerbill - in MN we have a fixed-rate utility fee structure per 
 season (winter power costs less than summer, I believe, for whatever 
 reason) and a $10 mail-in rebate on the card means I will be turning 
 a net profit in 2 months! -- Ryan
 
 Sorry, I don't get why you'd run a video card using in excess of 150W on 
 any server?  Or is that for your hot gaming box? :)
 
 cheers, Ian
 ___
 freebsd-questions@freebsd.org mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-13 Thread David Brodbeck
On Thu, August 12, 2010 8:14 pm, Al Plant wrote:
 #3. Thats why setting the bios not to self boot would work. (Stopping
 the bios from turning the server on after an outage.) Someone would have
 to check the power status manually before throwing the switch manually
 to make it come up after power has been restored.  Also turning servers
 and some desktops off and on is many cases a bad idea.

Yeah, that's why I prefaced my original misgivings by asking if this was
an unattended system.  If someone will be around to push the button,
there's no need to worry about bringing the system back up automatically. 
But if someone's going to have to drive 50 miles on a weekend to do it,
automatic start-up is a good idea. ;)

Where I work we have most of our systems set to *not* power back up after
an outage.  This is deliberate; I can't guarantee that the air
conditioners will come back on when power is restored, so I need to
manually verify that they're working before all that heat-generating
equipment is powered back on.


___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread David Brodbeck
On Wed, August 11, 2010 1:18 pm, Ryan Coleman wrote:
 On Aug 11, 2010, at 3:06 PM, David Brodbeck wrote:

 On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:
 He thinks that at 500W needed it would give me about 12 minutes on a
 1400VA. My consideration is, then, give the server 2 minutes on
 battery.
 If full power has not been returned, shut down the server but leave the
 modem (w/ wireless) and switch running with power for up to 6 hours.

 A bit of advice: If this is an unattended system, give some thought to
 how
 you will boot the server back up if the outage is longer than two
 minutes
 but shorter than six hours.  Most UPS installations have *some* kind of
 race condition issue if power comes back after the servers have begun a
 shutdown, but in your case it's an unusually long window.

 Meaning that my 2-minute window is unusually long? If the UPS can support
 the system for 12 minutes, I say give it 20% of the life of the support
 because our power outages here are usually spikes that kill my current web
 server (but amazingly *not* my file server). In fact, one of those power
 fluxes occurred last night. I love storms for the light shows, but hate
 them for the toll they take on my servers.

Nope, 2 minutes is fine, maybe even short depending on how long your
system takes to shut down.  What I'm asking about is this scenario:

1. Power goes out.
2. Server shuts itself down after 2 minutes.
3. Power comes back on before the UPS batteries are exhausted.

The server never sees a power cycle, so it doesn't boot itself back up
until someone physically goes and pushes the button.


___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread Ryan Coleman

On Aug 11, 2010, at 6:01 PM, David Brodbeck wrote:

 On Wed, August 11, 2010 1:18 pm, Ryan Coleman wrote:
 On Aug 11, 2010, at 3:06 PM, David Brodbeck wrote:
 
 On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:
 He thinks that at 500W needed it would give me about 12 minutes on a
 1400VA. My consideration is, then, give the server 2 minutes on
 battery.
 If full power has not been returned, shut down the server but leave the
 modem (w/ wireless) and switch running with power for up to 6 hours.
 
 A bit of advice: If this is an unattended system, give some thought to
 how
 you will boot the server back up if the outage is longer than two
 minutes
 but shorter than six hours.  Most UPS installations have *some* kind of
 race condition issue if power comes back after the servers have begun a
 shutdown, but in your case it's an unusually long window.
 
 Meaning that my 2-minute window is unusually long? If the UPS can support
 the system for 12 minutes, I say give it 20% of the life of the support
 because our power outages here are usually spikes that kill my current web
 server (but amazingly *not* my file server). In fact, one of those power
 fluxes occurred last night. I love storms for the light shows, but hate
 them for the toll they take on my servers.
 
 Nope, 2 minutes is fine, maybe even short depending on how long your
 system takes to shut down.  What I'm asking about is this scenario:
 
 1. Power goes out.
 2. Server shuts itself down after 2 minutes.
 3. Power comes back on before the UPS batteries are exhausted.
 
 The server never sees a power cycle, so it doesn't boot itself back up
 until someone physically goes and pushes the button.

Good points. I just want to make sure it has a safe shutdown (the usual reason 
for a UPS) but it will be set with a BIOS turn on time if it is not on. This is 
for a mirrored archive that updates overnight. If it is in the middle of the 
process it will kill and shut off.

Most power outages in my area are 1) during the hottest days of the summer - 
like today and 2) last less than 60 seconds. It's biggest draw is to give it a 
steady stream of power.

--
Ryan___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread Michael Powell
Oliver Fromme wrote:

 Ryan Coleman ryan.cole...@cwis.biz wrote:
   He thinks that at 500W needed it would give me about 12 minutes on
   a 1400VA.
 
 That W and VA numbers of the UPS are pretty much irrelevant,
 because they tell nothing about the capacity of the battery.
 Those numbers only give an upper limit on the power that
 the UPS can handle (i.e. you cannot connect devices totalling
 800 W to a 500 W UPS, for example).
 
 In order to be able to estimate how long the UPS can power
 wattage, you need to know the capacity of the battery.
 The capacity is usually given in Ah units (Ampere hours).
 
 For example, a battery with 10 Ah capacity can deliver
 10 Ampere for 1 hour, or 20 Ampere for 30 minutes, or
 30 Ampere for 20 Minutes ...  and so on.
 At a typical battery voltage of 12 V, 30 A would be 360 W.
 
 So, theoretically a 10 Ah battery would be able to hold
 devices that use 360 W for about 20 Minutes.  In practice
 it will be less because no UPS has 100% efficiency.
 
 Best regards
Oliver
 

Another often overlooked detail is how long the battery will last. These 
amp-hour figures are all for new batteries, and the number of 
discharge/charge cycles has some effect over time as well. Generally 
speaking when a UPS just sits there and does very little the batteries are 
like new for the first two years. Somewhere into year 3 they begin to nose 
over the derating curve. So at year 3.75 they will have signifigantly less 
full power runtime than when new. The quality of manufacture for the 
batteries controls this, for example with lead-acid how much metal goes into 
the plates.

I admit to being bitten a time or two: There is a certain tendency to put 
the UPS in the rack and walk away and forget all about it. I've learned the 
hard way to keep records so I can replace weak batteries in a timely 
fashion. Or this happens: But that server should have been able to stay up 
20 minutes instead of crashing at 7 minutes... 

-Mike


___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread Al Plant

David Brodbeck wrote:

On Wed, August 11, 2010 1:18 pm, Ryan Coleman wrote:

On Aug 11, 2010, at 3:06 PM, David Brodbeck wrote:


On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:

He thinks that at 500W needed it would give me about 12 minutes on a
1400VA. My consideration is, then, give the server 2 minutes on
battery.
If full power has not been returned, shut down the server but leave the
modem (w/ wireless) and switch running with power for up to 6 hours.

A bit of advice: If this is an unattended system, give some thought to
how
you will boot the server back up if the outage is longer than two
minutes
but shorter than six hours.  Most UPS installations have *some* kind of
race condition issue if power comes back after the servers have begun a
shutdown, but in your case it's an unusually long window.

Meaning that my 2-minute window is unusually long? If the UPS can support
the system for 12 minutes, I say give it 20% of the life of the support
because our power outages here are usually spikes that kill my current web
server (but amazingly *not* my file server). In fact, one of those power
fluxes occurred last night. I love storms for the light shows, but hate
them for the toll they take on my servers.


Nope, 2 minutes is fine, maybe even short depending on how long your
system takes to shut down.  What I'm asking about is this scenario:

1. Power goes out.
2. Server shuts itself down after 2 minutes.
3. Power comes back on before the UPS batteries are exhausted.

The server never sees a power cycle, so it doesn't boot itself back up
until someone physically goes and pushes the button.


##


I have had these power dips and surges here in Hawaii. I have installed 
 UPS power from two stationary batters that will run the servers for 12 
hours. We have experienced extensive outages in the past and this was 
our only solution. Surges are almost impossible to stop. I have them 
jump cross a surge protector. I have recently  had several UPS Desktop 
backups fail from a surge and then a drop below 70 v. This caused the 
UPS to have the charging diodes blow. It was cheaper to replace the UPS 
's than to repair them.


#3. The motherboard bios can be set to stop a server from self booting 
from a power outage.



~Al Plant - Honolulu, Hawaii -  Phone:  808-284-2740
  + http://hawaiidakine.com + http://freebsdinfo.org +
  + http://aloha50.net   - Supporting - FreeBSD  7.2 - 8.0 - 9* +
   email: n...@hdk5.net 
All that's really worth doing is what we do for others.- Lewis Carrol

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread Ryan Coleman

On Aug 12, 2010, at 12:52 PM, Al Plant wrote:

 David Brodbeck wrote:
 On Wed, August 11, 2010 1:18 pm, Ryan Coleman wrote:
 On Aug 11, 2010, at 3:06 PM, David Brodbeck wrote:
 
 On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:
 He thinks that at 500W needed it would give me about 12 minutes on a
 1400VA. My consideration is, then, give the server 2 minutes on
 battery.
 If full power has not been returned, shut down the server but leave the
 modem (w/ wireless) and switch running with power for up to 6 hours.
 A bit of advice: If this is an unattended system, give some thought to
 how
 you will boot the server back up if the outage is longer than two
 minutes
 but shorter than six hours.  Most UPS installations have *some* kind of
 race condition issue if power comes back after the servers have begun a
 shutdown, but in your case it's an unusually long window.
 Meaning that my 2-minute window is unusually long? If the UPS can support
 the system for 12 minutes, I say give it 20% of the life of the support
 because our power outages here are usually spikes that kill my current web
 server (but amazingly *not* my file server). In fact, one of those power
 fluxes occurred last night. I love storms for the light shows, but hate
 them for the toll they take on my servers.
 Nope, 2 minutes is fine, maybe even short depending on how long your
 system takes to shut down.  What I'm asking about is this scenario:
 1. Power goes out.
 2. Server shuts itself down after 2 minutes.
 3. Power comes back on before the UPS batteries are exhausted.
 The server never sees a power cycle, so it doesn't boot itself back up
 until someone physically goes and pushes the button.
 ##
 
 I have had these power dips and surges here in Hawaii. I have installed  UPS 
 power from two stationary batters that will run the servers for 12 hours. We 
 have experienced extensive outages in the past and this was our only 
 solution. Surges are almost impossible to stop. I have them jump cross a 
 surge protector. I have recently  had several UPS Desktop backups fail from a 
 surge and then a drop below 70 v. This caused the UPS to have the charging 
 diodes blow. It was cheaper to replace the UPS 's than to repair them.
 
 #3. The motherboard bios can be set to stop a server from self booting from a 
 power outage.
 


Yes. The downside comes from when the BIOS is told to turn on the server at, 
say, 10pm and the power is still out... it starts the process and runs out of 
battery mid-way through the boot before it gets the chance to load the UPS 
controller.

--
Ryan___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread David Brodbeck


On Aug 12, 2010, at 12:40 PM, Ryan Coleman wrote:
Yes. The downside comes from when the BIOS is told to turn on the  
server at, say, 10pm and the power is still out... it starts the  
process and runs out of battery mid-way through the boot before it  
gets the chance to load the UPS controller.


You may want to think about using two UPS units -- a large one for  
your server, and a smaller one for your network stack.  This way you  
can use UPS monitoring software (like NUT or PowerChute) to have the  
server command its UPS to switch off when it's fully shut down.  Then  
when power comes back the server UPS will switch back on and the  
server will boot back up, assuming you've set the BIOS to boot up on  
power recovery.  Some UPS units have the ability to set a power  
recovery delay to ensure the battery has some charge before the server  
starts up, too.


___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread Ryan Coleman

On Aug 12, 2010, at 2:49 PM, David Brodbeck wrote:

 
 On Aug 12, 2010, at 12:40 PM, Ryan Coleman wrote:
 Yes. The downside comes from when the BIOS is told to turn on the server at, 
 say, 10pm and the power is still out... it starts the process and runs out 
 of battery mid-way through the boot before it gets the chance to load the 
 UPS controller.
 
 You may want to think about using two UPS units -- a large one for your 
 server, and a smaller one for your network stack.  This way you can use UPS 
 monitoring software (like NUT or PowerChute) to have the server command its 
 UPS to switch off when it's fully shut down.  Then when power comes back the 
 server UPS will switch back on and the server will boot back up, assuming 
 you've set the BIOS to boot up on power recovery.  Some UPS units have the 
 ability to set a power recovery delay to ensure the battery has some charge 
 before the server starts up, too.

Great idea, I'll definitely keep that in mind.

--
Ryan___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-12 Thread Al Plant

Ryan Coleman wrote:

On Aug 12, 2010, at 12:52 PM, Al Plant wrote:


David Brodbeck wrote:

On Wed, August 11, 2010 1:18 pm, Ryan Coleman wrote:

On Aug 11, 2010, at 3:06 PM, David Brodbeck wrote:


On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:

He thinks that at 500W needed it would give me about 12 minutes on a
1400VA. My consideration is, then, give the server 2 minutes on
battery.
If full power has not been returned, shut down the server but leave the
modem (w/ wireless) and switch running with power for up to 6 hours.

A bit of advice: If this is an unattended system, give some thought to
how
you will boot the server back up if the outage is longer than two
minutes
but shorter than six hours.  Most UPS installations have *some* kind of
race condition issue if power comes back after the servers have begun a
shutdown, but in your case it's an unusually long window.

Meaning that my 2-minute window is unusually long? If the UPS can support
the system for 12 minutes, I say give it 20% of the life of the support
because our power outages here are usually spikes that kill my current web
server (but amazingly *not* my file server). In fact, one of those power
fluxes occurred last night. I love storms for the light shows, but hate
them for the toll they take on my servers.

Nope, 2 minutes is fine, maybe even short depending on how long your
system takes to shut down.  What I'm asking about is this scenario:
1. Power goes out.
2. Server shuts itself down after 2 minutes.
3. Power comes back on before the UPS batteries are exhausted.
The server never sees a power cycle, so it doesn't boot itself back up
until someone physically goes and pushes the button.
##

I have had these power dips and surges here in Hawaii. I have installed  UPS 
power from two stationary batters that will run the servers for 12 hours. We 
have experienced extensive outages in the past and this was our only solution. 
Surges are almost impossible to stop. I have them jump cross a surge protector. 
I have recently  had several UPS Desktop backups fail from a surge and then a 
drop below 70 v. This caused the UPS to have the charging diodes blow. It was 
cheaper to replace the UPS 's than to repair them.

#3. The motherboard bios can be set to stop a server from self booting from a 
power outage.




Yes. The downside comes from when the BIOS is told to turn on the server at, 
say, 10pm and the power is still out... it starts the process and runs out of 
battery mid-way through the boot before it gets the chance to load the UPS 
controller.





#3. Thats why setting the bios not to self boot would work. (Stopping the 
bios from turning the server on after an outage.) Someone would have to check the power 
status manually before throwing the switch manually to make it come up after power has 
been restored.  Also turning servers and some desktops off and on is many cases a bad 
idea.


Example:

I was called out today to look at a desktop that was turned off while 
the user went away for a month. It did not survive the turn on. 
Corrosion took its toll on the mobo and fans. The humidity was the 
cause. No humidity in the case when the unit is on and fans (3 of them) 
are working.


Hope you can solve your problem.



--

~Al Plant - Honolulu, Hawaii -  Phone:  808-284-2740
  + http://hawaiidakine.com + http://freebsdinfo.org +
  + http://aloha50.net   - Supporting - FreeBSD  7.2 - 8.0 - 9* +
   email: n...@hdk5.net 
All that's really worth doing is what we do for others.- Lewis Carrol

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


UPS question

2010-08-11 Thread Ryan Coleman
I know that APC's website states this load on this unit results in this runtime.

However I do not trust these figures, typically, when coming from smaller 
manufacturers than APC.

I am looking at a 1400VA / 980W UPS to run a single server with a usually not 
on monitor, a DSL modem and a simple switch. The server should generate about 
330W in power consumption, the monitor another 50-100, the modem about 10 and 
the switch about another 10 watts.

So:
UPS: 1400VA

Server: 400W (liberal estimate)
Modem: 10W
Switch: 10W
Monitor: 75W

Total: 495W

According to a calculator if I enter all that information:
http://www.csgnetwork.com/upssizecalc.html
It says that it will use 693VA.

Enter that into http://www.csgnetwork.com/batterylifecalc.html
It requires Amps... 495W  / 120 voltage = 4.125 amps... doesn't seem right 
but...
192 hours... that's not right, right?

--
Ryan___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-11 Thread Chuck Swiger
Hi, Ryan--

On Aug 11, 2010, at 8:51 AM, Ryan Coleman wrote:
 Total: 495W
 
 According to a calculator if I enter all that information:
 http://www.csgnetwork.com/upssizecalc.html
 It says that it will use 693VA.

That sounds reasonable.  The better PSUs have 80 Plus certification for 
efficiency, and that's better than the typical wall warts used for modems and 
switches and the like commonly manage.  (The efficiency they're assuming is a 
bit over 70%; using 80% would be around 600VA.)

 Enter that into http://www.csgnetwork.com/batterylifecalc.html
 It requires Amps... 495W  / 120 voltage = 4.125 amps... doesn't seem right 
 but...
 192 hours... that's not right, right?

Assume for discussion their number was right.  In order to get 495W of output 
load, the UPS needs to provide 693 volt-amps of juice to your equipment.  After 
the inverter and 10:1 stepup transformer used to convert 12VDC or whatever the 
UPS batteries are charged to up to 120VAC, the current needed would be 5.77 
amps.  However, the 12VDC battery source itself would be getting a draw of 57 
amps (ideally; again, the inverter+transformer themselves might only rate about 
90% efficiency for very good quality UPS, so would be drawing more like 60 or 
65 amps).

A standard APC/Tripplite/whatever 700VA UPS tend so have a lead-acid battery 
reasonably similar to a car battery, and typically will have around 100 
amp-hours of charge; they'd probably give you 90 minutes of backup time.  But 
you can look up the detailed specs of specific models and work from their 
amp-hour (or watt-hour) ratings-- actually, I think I'm guestimating more from 
what a 1200VA unit might provide, and a 700VA model is probably going to 
provide more like 40-60 minutes of power...

Regards,
-- 
-Chuck

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-11 Thread Ryan Coleman
Thanks, Chuck.

I talked with a former colleague that has a lot of experience in specing out 
UPS requirements (between battery-ready and generator-ready backups at the 
office they have up to 5 minutes of battery backup before the gas generator is 
needed with a 128-hour recharge time just to support their servers and wiring 
racks in the office).

He thinks that at 500W needed it would give me about 12 minutes on a 1400VA. My 
consideration is, then, give the server 2 minutes on battery. If full power has 
not been returned, shut down the server but leave the modem (w/ wireless) and 
switch running with power for up to 6 hours.

Now I need to build a server (looking at RAID5 8x2TB) for less than $1600 w/o a 
CPU if I can... a local custom builder quoted me $4000 today for a full system 
inc. CPU, RAM and DVD.

--
Ryan

On Aug 11, 2010, at 11:44 AM, Chuck Swiger wrote:

 Hi, Ryan--
 
 On Aug 11, 2010, at 8:51 AM, Ryan Coleman wrote:
 Total: 495W
 
 According to a calculator if I enter all that information:
 http://www.csgnetwork.com/upssizecalc.html
 It says that it will use 693VA.
 
 That sounds reasonable.  The better PSUs have 80 Plus certification for 
 efficiency, and that's better than the typical wall warts used for modems and 
 switches and the like commonly manage.  (The efficiency they're assuming is a 
 bit over 70%; using 80% would be around 600VA.)
 
 Enter that into http://www.csgnetwork.com/batterylifecalc.html
 It requires Amps... 495W  / 120 voltage = 4.125 amps... doesn't seem right 
 but...
 192 hours... that's not right, right?
 
 Assume for discussion their number was right.  In order to get 495W of output 
 load, the UPS needs to provide 693 volt-amps of juice to your equipment.  
 After the inverter and 10:1 stepup transformer used to convert 12VDC or 
 whatever the UPS batteries are charged to up to 120VAC, the current needed 
 would be 5.77 amps.  However, the 12VDC battery source itself would be 
 getting a draw of 57 amps (ideally; again, the inverter+transformer 
 themselves might only rate about 90% efficiency for very good quality UPS, so 
 would be drawing more like 60 or 65 amps).
 
 A standard APC/Tripplite/whatever 700VA UPS tend so have a lead-acid battery 
 reasonably similar to a car battery, and typically will have around 100 
 amp-hours of charge; they'd probably give you 90 minutes of backup time.  But 
 you can look up the detailed specs of specific models and work from their 
 amp-hour (or watt-hour) ratings-- actually, I think I'm guestimating more 
 from what a 1200VA unit might provide, and a 700VA model is probably going to 
 provide more like 40-60 minutes of power...
 
 Regards,
 -- 
 -Chuck
 
 ___
 freebsd-questions@freebsd.org mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org

___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-11 Thread David Brodbeck
On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:
 He thinks that at 500W needed it would give me about 12 minutes on a
 1400VA. My consideration is, then, give the server 2 minutes on battery.
 If full power has not been returned, shut down the server but leave the
 modem (w/ wireless) and switch running with power for up to 6 hours.

A bit of advice: If this is an unattended system, give some thought to how
you will boot the server back up if the outage is longer than two minutes
but shorter than six hours.  Most UPS installations have *some* kind of
race condition issue if power comes back after the servers have begun a
shutdown, but in your case it's an unusually long window.


___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-11 Thread Ryan Coleman
On Aug 11, 2010, at 3:06 PM, David Brodbeck wrote:

 On Wed, August 11, 2010 12:25 pm, Ryan Coleman wrote:
 He thinks that at 500W needed it would give me about 12 minutes on a
 1400VA. My consideration is, then, give the server 2 minutes on battery.
 If full power has not been returned, shut down the server but leave the
 modem (w/ wireless) and switch running with power for up to 6 hours.
 
 A bit of advice: If this is an unattended system, give some thought to how
 you will boot the server back up if the outage is longer than two minutes
 but shorter than six hours.  Most UPS installations have *some* kind of
 race condition issue if power comes back after the servers have begun a
 shutdown, but in your case it's an unusually long window.

Meaning that my 2-minute window is unusually long? If the UPS can support the 
system for 12 minutes, I say give it 20% of the life of the support because our 
power outages here are usually spikes that kill my current web server (but 
amazingly *not* my file server). In fact, one of those power fluxes occurred 
last night. I love storms for the light shows, but hate them for the toll they 
take on my servers.

Additionally I spent $34 on a video card today that reduces my power 
consumption by 150Watts, resulting in a $13 per month savings in my powerbill - 
in MN we have a fixed-rate utility fee structure per season (winter power costs 
less than summer, I believe, for whatever reason) and a $10 mail-in rebate on 
the card means I will be turning a net profit in 2 months!
--
Ryan___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


Re: UPS question

2010-08-11 Thread Oliver Fromme
Ryan Coleman ryan.cole...@cwis.biz wrote:
  He thinks that at 500W needed it would give me about 12 minutes on
  a 1400VA.

That W and VA numbers of the UPS are pretty much irrelevant,
because they tell nothing about the capacity of the battery.
Those numbers only give an upper limit on the power that
the UPS can handle (i.e. you cannot connect devices totalling
800 W to a 500 W UPS, for example).

In order to be able to estimate how long the UPS can power
wattage, you need to know the capacity of the battery.
The capacity is usually given in Ah units (Ampere hours).

For example, a battery with 10 Ah capacity can deliver
10 Ampere for 1 hour, or 20 Ampere for 30 minutes, or
30 Ampere for 20 Minutes ...  and so on.
At a typical battery voltage of 12 V, 30 A would be 360 W.

So, theoretically a 10 Ah battery would be able to hold
devices that use 360 W for about 20 Minutes.  In practice
it will be less because no UPS has 100% efficiency.

Best regards
   Oliver

-- 
Oliver Fromme, secnetix GmbH  Co. KG, Marktplatz 29, 85567 Grafing b. M.
Handelsregister: Registergericht Muenchen, HRA 74606,  Geschäftsfuehrung:
secnetix Verwaltungsgesellsch. mbH, Handelsregister: Registergericht Mün-
chen, HRB 125758,  Geschäftsführer: Maik Bachmann, Olaf Erb, Ralf Gebhart

FreeBSD-Dienstleistungen, -Produkte und mehr:  http://www.secnetix.de/bsd

Passwords are like underwear.  You don't share them,
you don't hang them on your monitor or under your keyboard,
you don't email them, or put them on a web site,
and you must change them very often.
___
freebsd-questions@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to freebsd-questions-unsubscr...@freebsd.org


APC UPS question

2004-10-21 Thread Matt Navarre
I'm in the market for a UPS that works with FreeBSD. Does anyone know if the 
APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and apcupsd? As far 
as I can tell apcupsd support for usb on FreeBSD is not reliable, but this 
one's serial and affordable but I'd like to know if it works before I buy.

Thanks.
-- 
We all enter this world in the same way: naked, screaming,
 and soaked in blood. But if you live your life right, that kind
 of thing doesn't have to stop there. -- Dana Gould
___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


RE: APC UPS question

2004-10-21 Thread Ted Mittelstaedt
I have a backups 280 and there is no serial port on it.  Are you
sure your looking at the right thing?  In any case a 280 is barely
enough to keep a PC powered much less a PC and monitor.  I use mine
for my DSL modem and DSL router.

There's lots of SmartUPS 450 UPSs on Ebay.  Find one that the seller
isn't claiming that he has 'refurbished' with new batteries.  Buy it
and when it arrives just buy new batteries from any electrical store
and give them your old ones.  (since it's going to be a given that
the batteries will be toasted no matter what the seller claims)

APS themselves also sells refurbs off their website.

Ted

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] Behalf Of Matt Navarre
 Sent: Wednesday, October 20, 2004 11:06 PM
 To: [EMAIL PROTECTED]
 Subject: APC UPS question


 I'm in the market for a UPS that works with FreeBSD. Does anyone
 know if the
 APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and
 apcupsd? As far
 as I can tell apcupsd support for usb on FreeBSD is not reliable,
 but this
 one's serial and affordable but I'd like to know if it works before I buy.

 Thanks.
 --
 We all enter this world in the same way: naked, screaming,
  and soaked in blood. But if you live your life right, that kind
  of thing doesn't have to stop there. -- Dana Gould
 ___
 [EMAIL PROTECTED] mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to
 [EMAIL PROTECTED]


___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: APC UPS question

2004-10-21 Thread Nikolas Britton
http://buy.apc.com/commerce/storefronts/factoryoutlet/default.asp
Ted Mittelstaedt wrote:
I have a backups 280 and there is no serial port on it.  Are you
sure your looking at the right thing?  In any case a 280 is barely
enough to keep a PC powered much less a PC and monitor.  I use mine
for my DSL modem and DSL router.
There's lots of SmartUPS 450 UPSs on Ebay.  Find one that the seller
isn't claiming that he has 'refurbished' with new batteries.  Buy it
and when it arrives just buy new batteries from any electrical store
and give them your old ones.  (since it's going to be a given that
the batteries will be toasted no matter what the seller claims)
APS themselves also sells refurbs off their website.
Ted
 

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Matt Navarre
Sent: Wednesday, October 20, 2004 11:06 PM
To: [EMAIL PROTECTED]
Subject: APC UPS question
I'm in the market for a UPS that works with FreeBSD. Does anyone
know if the
APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and
apcupsd? As far
as I can tell apcupsd support for usb on FreeBSD is not reliable,
but this
one's serial and affordable but I'd like to know if it works before I buy.
Thanks.
--
We all enter this world in the same way: naked, screaming,
and soaked in blood. But if you live your life right, that kind
of thing doesn't have to stop there. -- Dana Gould
___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to
[EMAIL PROTECTED]
   

___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]
 


___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


re: APC UPS question

2004-10-21 Thread John Koepke
I have purchased a few APC Ups's from a vendor on Ebay.  Wonderful to
work with.  a few weeks ago the UPS I purchased about 1 and a half
years ago had a electrical problem and the ups failed.  He sent me
another unit and it arrived in just a few days.  I Paid $179 for a APC
Smart 1400 RM UPS.  I currently have 3 servers attached to it with my
various other routers and it will run for about 20 or 30 minutes.
With only 1 server it will run for almost 90 minutes or so.   He sends
out NEW batteries with the unit's...

http://search.ebay.com/_W0QQgotopageZ1QQsassZupspowerQQsosortorderZ1QQsosortpropertyZ1

already i see he has a few Net UPS 650's for $79 or a Smart UPS 700 for $100




On Wed, 20 Oct 2004 23:05:32 -0700, Matt Navarre [EMAIL PROTECTED] wrote:
 I'm in the market for a UPS that works with FreeBSD. Does anyone know if the
 APC Back-UPS Pro 280VA Just Works with FreeBSD 4-STABLE and apcupsd? As far
 as I can tell apcupsd support for usb on FreeBSD is not reliable, but this
 one's serial and affordable but I'd like to know if it works before I buy.

 Thanks.
 --
 We all enter this world in the same way: naked, screaming,
  and soaked in blood. But if you live your life right, that kind
  of thing doesn't have to stop there. -- Dana Gould
 ___
 [EMAIL PROTECTED] mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to [EMAIL PROTECTED]

___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


RE: APC UPS question

2004-10-21 Thread Robert Huff

Ted Mittelstaedt writes:

  I have a backups 280 and there is no serial port on it.  Are you
  sure your looking at the right thing?

I believe they have the BackUPS _Pro_ 280, the larger brothers
(420 and 650) of which are sitting two feet behind me.  Both have
serial ports only.  (They are 5+ years old.)


Robert Huff



___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: APC UPS question

2004-10-21 Thread Matt Navarre
On Thursday 21 October 2004 07:35, Robert Huff wrote:
 Ted Mittelstaedt writes:
   I have a backups 280 and there is no serial port on it.  Are you
   sure your looking at the right thing?

  I believe they have the BackUPS _Pro_ 280, the larger brothers
 (420 and 650) of which are sitting two feet behind me.  Both have
 serial ports only.  (They are 5+ years old.)


  Robert Huff

Does the 650 work well with FreeBSD? I can get a refurb 650 from APC for the 
same price as I can find the 280.

-- 
We all enter this world in the same way: naked, screaming,
 and soaked in blood. But if you live your life right, that kind
 of thing doesn't have to stop there. -- Dana Gould
___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


RE: APC UPS question

2004-10-21 Thread Ted Mittelstaedt
they all use the same protocol, the difference is between the smart
ups and the backups. all smartups use one protocol all backups
use another.

The very newest ones with usb and such might have changed this, I
don't know.

incidentally with the smartups you can query the ups for the
amount of runtime left so you know how much life is left in the
battery, the ups self-tests this periodically and you can send
a command to it to do this.  Very useful.

Ted

 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] Behalf Of Matt Navarre
 Sent: Thursday, October 21, 2004 8:52 AM
 To: [EMAIL PROTECTED]
 Cc: Robert Huff
 Subject: Re: APC UPS question
 
 
 On Thursday 21 October 2004 07:35, Robert Huff wrote:
  Ted Mittelstaedt writes:
I have a backups 280 and there is no serial port on it.  Are you
sure your looking at the right thing?
 
   I believe they have the BackUPS _Pro_ 280, the larger brothers
  (420 and 650) of which are sitting two feet behind me.  Both have
  serial ports only.  (They are 5+ years old.)
 
 
   Robert Huff
 
 Does the 650 work well with FreeBSD? I can get a refurb 650 from 
 APC for the 
 same price as I can find the 280.
 
 -- 
 We all enter this world in the same way: naked, screaming,
  and soaked in blood. But if you live your life right, that kind
  of thing doesn't have to stop there. -- Dana Gould
 ___
 [EMAIL PROTECTED] mailing list
 http://lists.freebsd.org/mailman/listinfo/freebsd-questions
 To unsubscribe, send any mail to 
 [EMAIL PROTECTED]
 
___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


RE: APC UPS question

2004-10-21 Thread Robert Huff

Ted Mittelstaedt writes:

  incidentally with the smartups you can query the ups for the
  amount of runtime left so you know how much life is left in the
  battery, the ups self-tests this periodically and you can send
  a command to it to do this.  Very useful.

That's also true for the BackUPS Pro providing you get the
right cable (I used the -0095A) and the right software (PowerChute
Personal Edition (Windows) or apcupsd (FreeBSD)).


Robert Huff


___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]


Re: APC UPS question

2004-10-21 Thread Robert Huff

Matt Navarre writes:

I believe they have the BackUPS _Pro_ 280, the larger brothers
   (420 and 650) of which are sitting two feet behind me.  Both have
   serial ports only.  (They are 5+ years old.)

  Does the 650 work well with FreeBSD? I can get a refurb 650 from
  APC for the same price as I can find the 280.

It worked well for many years, then died within the 3 months.
It's sitting on my parts shelf in the hope I have an excuse to make
a trip to Rhode Island soon.
(I replaced the battery within the last year, and would like to
get the electronics refurbed.)


Robert Huff







___
[EMAIL PROTECTED] mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-questions
To unsubscribe, send any mail to [EMAIL PROTECTED]