Ian Mason wrote:



On 6 Mar 2006, at 15:06, [EMAIL PROTECTED] wrote:



On Mon, Mar 06, 2006 at 09:49:39AM -0500, Steven M. Bellovin wrote:



On Mon, 06 Mar 2006 21:17:17 +1100
Matthew Sullivan [EMAIL PROTECTED] wrote:


(In the
UK where I served my apprenticeship, we were required to provide  earth
bonding to the copper plumbing system, additional bonding at every
exposed fitting - this caused a few issues when plumbers first  
starting

using PVC pipes)...



The US National Electrical Code (which has no national force of law;
it's a model code voluntarily adopted by many jurisdictions) now bars
grounding to pipes except within (as I recall) six feet of where the
pipe enters the building, for precisely that reason.



The use in modern times of teflon tape at joints in copper
piping makes them unuseable for earth grounds even near the entry
point to the building. A long (e.g. 2-3 meters) copper stake must be
driven for a proper earth ground, or else a large copper mesh mat if
the ground is rocky -- unless you are certain that the copper piping
that you want to use extends a significant distance underground and
unbroken.



The purpose here is not to use the piping *as* a ground, but to  ensure 
that the piping *is* at ground potential. Otherwise, if an  electrical 
failure causes the pipe to reach a dangerous potential  then so does the 
water in it, then so do the hands you're washing in  that water. Thus if 
there's an electrical discontinuity in the piping  it is even more 
important to earth bond any conductive piping/taps  etc. that are on the 
non-earth side of that discontinuity. The same  applies too to gas 
piping except here the principal risk is static,  sparks and the 
subsequent explosion.






I think it is also important to note that NEC 250.52(B) prohibits gas 
piping as a grounding electrode(1990 or so). The gas pipe ceased as a 
grounding electrode due to the dielectric fitting at the meter. The gas 
company did not want a bond around the meter because it defeated the 
isolation fitting.


The presence of gas is not relevant, IIRC.

In the old days, it was a big no no (at least according to the hourly 
wage fellows who actually do the work) to hook the gas line as ground 
other than any incidental grounding which ocurs in a gas furnace as an 
example.


Good place for resources is http://www.mikeholt.com in the forums. 
Decent community of knowledgeable folk there.


Good luck, and no do not use your body/fingers/arms/etc to connect 
various pieces of equipment to see if a voltage exists:-) That's best 
left to close friends who stand near electric fences.


I had problems in the mid 1990's in an older home where the galvanized 
water supply pipe was the primary ground. Over time, corrosion of the 
pipe reduced conductivity, and lightening storms toasted a few expensive 
items (e.g. ISDN gear, sun workstation, etc) before finally driving a 
few grounding bars into the soil in the basement.


Cheers,
andy


Re: Presumed RF Interference

2006-03-07 Thread Ian Mason



On 6 Mar 2006, at 15:06, [EMAIL PROTECTED] wrote:



On Mon, Mar 06, 2006 at 09:49:39AM -0500, Steven M. Bellovin wrote:


On Mon, 06 Mar 2006 21:17:17 +1100
Matthew Sullivan [EMAIL PROTECTED] wrote:


(In the
UK where I served my apprenticeship, we were required to provide  
earth

bonding to the copper plumbing system, additional bonding at every
exposed fitting - this caused a few issues when plumbers first  
starting

using PVC pipes)...


The US National Electrical Code (which has no national force of law;
it's a model code voluntarily adopted by many jurisdictions) now bars
grounding to pipes except within (as I recall) six feet of where the
pipe enters the building, for precisely that reason.


The use in modern times of teflon tape at joints in copper
piping makes them unuseable for earth grounds even near the entry
point to the building. A long (e.g. 2-3 meters) copper stake must be
driven for a proper earth ground, or else a large copper mesh mat if
the ground is rocky -- unless you are certain that the copper piping
that you want to use extends a significant distance underground and
unbroken.



The purpose here is not to use the piping *as* a ground, but to  
ensure that the piping *is* at ground potential. Otherwise, if an  
electrical failure causes the pipe to reach a dangerous potential  
then so does the water in it, then so do the hands you're washing in  
that water. Thus if there's an electrical discontinuity in the piping  
it is even more important to earth bond any conductive piping/taps  
etc. that are on the non-earth side of that discontinuity. The same  
applies too to gas piping except here the principal risk is static,  
sparks and the subsequent explosion.






Re: Presumed RF Interference

2006-03-06 Thread Michael . Dillon

 RF problem or not, how would you track down this problem? 

To start with I would install some cheap equipment that
is more likely to fail so that you can INCREASE your
failure rate and get some more data. Maybe consumer grade
DSL switch/routers or something like that. Also, talk to
radio experts (ham radio) about how to measure the field
strength. It is entirely possible that there is some kind
of accidental waveguide that channels RF into your facility
under the right conditions. Grounding could also be a problem
if somebody is pumping lots of volts into the ground nearby.

By the way, your timetable sounds like a factory source.
Something is done on every shift change, and then maintenance
does it once more during the night shift.

--Michael Dillon



Re: Presumed RF Interference

2006-03-06 Thread Matthew Sullivan


Jon,

Peter Dambier wrote:


Cut the ground wire in your power cords but ground the equipment directly
to a metal frame.


As a time-served electrician... *DO NOT DO THIS* - it will kill 
someone.


However

You could try separate earth bonding of each components (ie connecting 
all the chassis together via a provided grounding terminal using nice 
thick copper wire), however if there is a significant earth fault even 
that could be dangerous (think fire) - so get a qualified electrician to 
do it - if there is a ground fault it will use the chassis and the 
bonded earths as it's route to ground.


Earth faults are often easily detectable by using a digital volt meter 
(Note: analog volt meters do not work for this unless there is a serious 
fault).  First check for induced and ungrounded 'floating' voltages (any 
AC or DC voltage above 0.05v should be investigated), then if the DVM is 
fused, check for any current (amps) between chassis.


If you have money to spend before investigation find out if the building 
has a grounding stake and if not add one...  A couple of meters of 
copper stake which  will be connected to either the armoring of the 
supply cable (TN-S) or to the incoming return cable and installation 
earth PME (TN-C-S) - likely based what someone else in this threat 
said.  In either type of grounding scheme the structure metal frame 
could (and should) be grounded (esp if exposed) which is likely to cause 
the phone RF signal drop.  A faulty bonding in the structure (esp as it 
is steal) can also provide for some interesting ground faults as it is 
not uncommon to provide localised grounding to building frames.  (In the 
UK where I served my apprenticeship, we were required to provide earth 
bonding to the copper plumbing system, additional bonding at every 
exposed fitting - this caused a few issues when plumbers first starting 
using PVC pipes)... All this said with the faults appearing with no 
external power and with just UPS supply, ground faults really do not 
'fit' the problem - however if a generator is used also, you are in an 
IT type installation (electrical term 'IT' not 'Information Technology' 
;-)) and will have to have a grounding stake on site.


Please note, I am trained from the UK - laws and regulations change from 
country to country - get a local qualified/licensed sparky to do the 
work or assist you.


Regards,

Mat




Re: Presumed RF Interference

2006-03-06 Thread Randy Bush

 Cut the ground wire in your power cords but ground the equipment
 directly to a metal frame.

i strongly recommend that you do this, especially in your 240vac
environment.  excellent solution to a lot of problems.

randy



Re: Presumed RF Interference

2006-03-06 Thread Peter Dambier


Randy Bush wrote:

Cut the ground wire in your power cords but ground the equipment
directly to a metal frame.



i strongly recommend that you do this, especially in your 240vac
environment.  excellent solution to a lot of problems.

randy



I agree, dont propose this to a wood logger :)

But yes, I did.

I have seen an installation where ground was floating somewhere
at 110 Volts AC. There was no way to tame it. We had to cut it.
Ofcourse we did it not on the wire but in the sockets and we got
a reasonable ground before we did.

Dont read in the books - and dont tell a lawer :)

The soil was extremly dry (not in europe) and the powerline was
extremly long...

Regards
Peter and Karin

--
Peter and Karin Dambier
The Public-Root Consortium
Graeffstrasse 14
D-64646 Heppenheim
+49(6252)671-788 (Telekom)
+49(179)108-3978 (O2 Genion)
+49(6252)750-308 (VoIP: sipgate.de)
mail: [EMAIL PROTECTED]
mail: [EMAIL PROTECTED]
http://iason.site.voila.fr/
https://sourceforge.net/projects/iason/



Re: Presumed RF Interference

2006-03-06 Thread Steven M. Bellovin

On Mon, 06 Mar 2006 21:17:17 +1100
Matthew Sullivan [EMAIL PROTECTED] wrote:

 (In the 
 UK where I served my apprenticeship, we were required to provide earth 
 bonding to the copper plumbing system, additional bonding at every 
 exposed fitting - this caused a few issues when plumbers first starting 
 using PVC pipes)... 

The US National Electrical Code (which has no national force of law;
it's a model code voluntarily adopted by many jurisdictions) now bars
grounding to pipes except within (as I recall) six feet of where the
pipe enters the building, for precisely that reason.


Re: Presumed RF Interference

2006-03-06 Thread ww

On Mon, Mar 06, 2006 at 09:49:39AM -0500, Steven M. Bellovin wrote:
 
 On Mon, 06 Mar 2006 21:17:17 +1100
 Matthew Sullivan [EMAIL PROTECTED] wrote:
 
  (In the 
  UK where I served my apprenticeship, we were required to provide earth 
  bonding to the copper plumbing system, additional bonding at every 
  exposed fitting - this caused a few issues when plumbers first starting 
  using PVC pipes)... 
 
 The US National Electrical Code (which has no national force of law;
 it's a model code voluntarily adopted by many jurisdictions) now bars
 grounding to pipes except within (as I recall) six feet of where the
 pipe enters the building, for precisely that reason.

The use in modern times of teflon tape at joints in copper
piping makes them unuseable for earth grounds even near the entry
point to the building. A long (e.g. 2-3 meters) copper stake must be 
driven for a proper earth ground, or else a large copper mesh mat if
the ground is rocky -- unless you are certain that the copper piping
that you want to use extends a significant distance underground and
unbroken.

-w


Re: Presumed RF Interference

2006-03-06 Thread Jay Hennigan


Randy Bush wrote:


Cut the ground wire in your power cords but ground the equipment
directly to a metal frame.


i strongly recommend that you do this, especially in your 240vac
environment.  excellent solution to a lot of problems.


Don't even joke about doing this, please.  If there is potential on the 
grounding conductor, then that problem needs to be corrected as it is a 
safety of life issue.  Even if you cut the conductor and safely ground 
the equipment in that one rack, you are ignoring the fact that you have 
very strong evidence of a serious wiring problem in the form of 
destroyed equipment.


Say you do what you suggest, ensure that your rack is well and solidly 
grounded.  And, you're aware that the building grounding wiring is 
defective.  And then someone comes in (maybe you) and plugs in a piece 
of portable test equipment next to your nice grounded rack.  And then
puts one hand on the test equipment (plugged into one of the defective 
outlets) and the other on your well-grounded rack.  Especially in the 
240 volt environment.


There is a serious, potentially fatal, wiring fault in that building. 
Get it fixed properly.


--
Jay Hennigan - CCIE #7880 - Network Administration - [EMAIL PROTECTED]
NetLojix Communications, Inc.  -  http://www.netlojix.com/
WestNet:  Connecting you to the planet.  805 884-6323


RE: Presumed RF Interference

2006-03-05 Thread David Hubbard

From: Jon R. Kibler

 
 I should also add some other points:
-- We have observed failures when the building had zero 
 power, except for the UPS battery power in the server room, 
 so we don't think that we are getting power spikes from 
 anything within the building.

If you had failures before utility power was even applied, it sounds
like multiple building grounds with differences in potential.

David


Re: Presumed RF Interference

2006-03-05 Thread David Lesher




 Greetings:
 
 We have a client site that is driving us nuts...

...
 
 I should also add some other points:
-- We have observed failures when the building had zero power, except for 
 the UPS .
-- The building only operates 0600 to 1800, so many failures are occurring 
 after hours.
-- There are no RF sources in the building.
-- We are not near an airport.
-- The building is steel framed and sided -- and a pretty good RF shield 
 -- 
 
 Given what I have described, would you think this is an RF interference 
 problem? 

No...

Unless you have a Gigawatt radar parked next door, I'm highly dubious
that it's RF-instigated.



   3 DSL routers (cisco 8x7)
   1 edge router (cisco 28xx)
   1 FR router (cisco 36xx)
   1 patch panel
   1 telco smart jack (ATM/FR circuit)
   1 PBX T1 card 
   1 patch panel (all jacks went open on the same pair)

Make that Terawatt...

   6+ NICs 


A) All these things say grounding issues. I have to wonder if
the building is fed from more than one power entrance. The blown
patch panel especially makes me think the router on one end of
the Cat5 was being fed from a different power source than the
one on the other. (Which pair was blown?) Given the UPS mention,
maybe there's a ground differential issue with it.

B) The other, less likely, path into equipment is telco. Those
mile-long pieces of copper from the CO are also called antennas
and they covet static. I have no idea where this location is --
are there thunderstorms around?

C) One more possibility; perhaps some piece of equipment in-house
is putting large spikes on the internal distribution. Twenty years
ago, I read of a building where large [50 HP HVAC] and small
[fridges] motors would regularly die. The high-tech gadgets of
that era, Texas Instruments calculators, would reset themselves
seemingly spontaneously. After MUCH work, they found the BIG
copier was putting nasty spikes back on the grid.

I vote A) 75% B) 20% C) 5%

You do need an EE, one prepared to look at the building wiring/grounding
grid.










-- 
A host is a host from coast to [EMAIL PROTECTED]
 no one will talk to a host that's close[v].(301) 56-LINUX
Unless the host (that isn't close).pob 1433
is busy, hung or dead20915-1433



Re: Presumed RF Interference

2006-03-05 Thread Iljitsch van Beijnum


On 5-mrt-2006, at 23:37, Jon R. Kibler wrote:

   1) How could a bad ground cause DSL line noise that ia  
inaudible? Also, the noise is on the telco side, not the LAN side.
   2) Why would it be blowing DSL routers that are isolated from  
the LAN by a switch and another router? And, all of this equipment  
is in the same rack, on the same ground, and on the same UPS.


This makes me think of a place where they used copper lines that ran  
alongside rail road tracks, and each time a train came by the leased  
line modems would go haywire. Electrical trains put a lot of current  
in the ground...


Re: Presumed RF Interference

2006-03-05 Thread David Lesher


 
 That is already half of a solution:
 
 Go for fiber. That is imune to both ground and RF problems. Avoid
 ground connections between the equipment.
 
 Replace ethernet with fiber. Break serial lines with optical isolators.

Yes, fiber will solve ground loop problems. And this smells like
a ground loop issue. But at this juncture, I don't have enough
specifics to recommend ma$$ive changes.



 Cut the ground wire in your power cords but ground the equipment directly
 to a metal frame.

I would NEVER tell a client to do this. 
That could easily kill someone.

 Avoid ground loops: Between two computers you have a ground connection
 via the powerline ground. Connect them via RS-232 and you have a second
 connection via the RS-232 ground. If your power ground is bad then you
 might run amperes through the RS-232 ground that results in Volts, more
 than your signal level, maybe.

I don't recall mention of RS-232,. but yes, this is the classic
example of ground loops.


-- 
A host is a host from coast to [EMAIL PROTECTED]
 no one will talk to a host that's close[v].(301) 56-LINUX
Unless the host (that isn't close).pob 1433
is busy, hung or dead20915-1433



Re: Presumed RF Interference

2006-03-05 Thread Steven M. Bellovin

On Sun, 5 Mar 2006 18:00:36 -0500 (EST)
David Lesher [EMAIL PROTECTED] wrote:

 
  Cut the ground wire in your power cords but ground the equipment directly
  to a metal frame.
 
 I would NEVER tell a client to do this. 
 That could easily kill someone.

Correct.

The safety purpose of the ground cord is to cause a short circuit in
case line voltage energizes the case, in which case the breaker will
trip. If you cut that wire, the metal frame frame can become hot;
unless it's firmly grounded itself, there will be a potential between
it and ground.  Along comes the next well-grounded person to touch it
-- poof!

Even if the frame were grounded properly, that's a local ground, which
may differ in potential from the breaker box's ground.  The neutral
wire in the circuit is tied to ground at the breaker box, which means
there could be a potential difference between it and the frame.  That
also creates a potential shock hazard, though presumably not that great.

What might be useful -- ask an EE, not me -- is a circuit with an
isolated ground.  In that case, the ground wire from the power plug is
routed all the way back to the breaker panel, and isn't connected to,
say, the local electrical box that the cord is plugged into.  I've seen
computer equipment wired that way in the past.


Re: Presumed RF Interference

2006-03-05 Thread Jay Hennigan


Jon R. Kibler wrote:

Greetings:


[snippage]


Given what I have described, would you think this is an RF interference problem?


No.  Many of the devices mentioned are not particularly RF sensitive. 
Those that are will recover when removed from the interference source 
unless you're talking about levels that are harmful to humans.   A 
*PATCH PANEL* ???  Short of putting it inside a microwave oven, I can't 
think of a means of damaging it with RF, particularly from any distance. 
 Google Inverse square law.  If you turn the switch off and the 
fluorescent lights stay on, then you indeed might want to look into RFI.


RF problem or not, how would you track down this problem? 


I'm 99.9% sure you have a grounding problem.  Verify that your power and 
equipment grounds have no significant potential difference.  Likewise 
your telco ground, and the metal building itself.  Is the entire 
building fed from a single electric meter?


We are to the point of bringing in a consulting EE, but I am not sure that 

 most would be equipped to solve this problem; so, what should we look for
 in a potential consulting engineer?

NEC grounding specification compliance, some who knows the difference 
between a groundED and a groundING conductor and is familiar with static 
and lightning protection issues.


--
Jay Hennigan - CCIE #7880 - Network Administration - [EMAIL PROTECTED]
NetLojix Communications, Inc.  -  http://www.netlojix.com/
WestNet:  Connecting you to the planet.  805 884-6323


RE: Presumed RF Interference

2006-03-05 Thread Scott Morris

The isolated grounds are definitely a recommended idea for telco/server
rooms...  Perhaps an array of them depending on the size power feed we're
talking about.  I'm assuming it's a sizeable UPS that runs your telco and
data equipment (or small server room).  The irritation, if you haven't done
this step already, is that adding a TRUE isolated ground after you've
already built your building and room is not exactly a cheap thing to do.  

Especially in nice metal framed buildings that like to have  a tendency of
becoming the nearest path ground themselves.  But I agree that it's
certainly something as a worthwhile first path to look into!

Scott

PS.  I agree it's not good business practice to kill your clients! 

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of
Steven M. Bellovin
Sent: Sunday, March 05, 2006 6:21 PM
To: [EMAIL PROTECTED]
Cc: nanog@merit.edu
Subject: Re: Presumed RF Interference


On Sun, 5 Mar 2006 18:00:36 -0500 (EST)
David Lesher [EMAIL PROTECTED] wrote:

 
  Cut the ground wire in your power cords but ground the equipment 
  directly to a metal frame.
 
 I would NEVER tell a client to do this. 
 That could easily kill someone.

Correct.

The safety purpose of the ground cord is to cause a short circuit in case
line voltage energizes the case, in which case the breaker will trip. If you
cut that wire, the metal frame frame can become hot; unless it's firmly
grounded itself, there will be a potential between it and ground.  Along
comes the next well-grounded person to touch it
-- poof!

Even if the frame were grounded properly, that's a local ground, which may
differ in potential from the breaker box's ground.  The neutral wire in the
circuit is tied to ground at the breaker box, which means there could be a
potential difference between it and the frame.  That also creates a
potential shock hazard, though presumably not that great.

What might be useful -- ask an EE, not me -- is a circuit with an isolated
ground.  In that case, the ground wire from the power plug is routed all the
way back to the breaker panel, and isn't connected to, say, the local
electrical box that the cord is plugged into.  I've seen computer equipment
wired that way in the past.



Re: Presumed RF Interference

2006-03-05 Thread Martin Hannigan


At 05:32 PM 3/5/2006, Peter Dambier wrote:


David Lesher wrote:




Cut the ground wire in your power cords but ground the equipment directly
to a metal frame.


[ I am not a PE - IANAPE ]

I don't think that is good advice. You can't possibly have the
as-builts, existing condition, or line drawings in front of you.

Safety first. Call the consulting engineers.


-M





--
Martin Hannigan(c) 617-388-2663
Renesys Corporation(w) 617-395-8574
Member of Technical Staff  Network Operations
   [EMAIL PROTECTED]  



Re: Presumed RF Interference

2006-03-05 Thread Robert Boyle


At 06:20 PM 3/5/2006, Steven M. Bellovin wrote:

What might be useful -- ask an EE, not me -- is a circuit with an
isolated ground.  In that case, the ground wire from the power plug is
routed all the way back to the breaker panel, and isn't connected to,
say, the local electrical box that the cord is plugged into.  I've seen
computer equipment wired that way in the past.


In the US, the NEC code states that the only place a neutral and a 
ground should be bonded together is in the primary service entrance 
facility or where the neutral is created. All subpanels will have 
isolated grounds and neutrals. If you have three phase service and 
use a delta (wye without the neutral) to wye transformer to create 
the neutral, the neutral will be bonded to ground inside the 
transformer cabinet. Eliminating the neutral is typically done to 
save money when converting 277/480V to 120/208V (no neutral means a 
reduced conductor count inside the conduit so smaller conduit can be 
used since the extra copper for the neutral is eliminated on the 
input side.) All grounds must be connected to the first metal box or 
conduit they touch. If you are using plastic boxes with Romex, your 
grounds will go all the back to your subpanel ground bar which will 
not meet the neutral until the main breaker panel. More often in a 
datacenter environment or a commercial facility, the wiring will be 
BX under a raised floor or BX or EMT with THHN overhead. Either way, 
the ground is connected inside the outlet box and wired directly back 
to the breaker panel. The bonding in the box is to ensure there is no 
voltage potential carried on any metal conduit. My NEC book is at the 
office now and I'm home, but I'm pretty sure everything I have stated 
from memory is accurate.


-Robert


Tellurian Networks - The Ultimate Internet Connection
http://www.tellurian.com | 888-TELLURIAN | 973-300-9211
Well done is better than well said. - Benjamin Franklin



Re: Presumed RF Interference

2006-03-05 Thread Steven M. Bellovin

On Sun, 05 Mar 2006 23:30:13 -0500
Robert Boyle [EMAIL PROTECTED] wrote:

 
 At 06:20 PM 3/5/2006, Steven M. Bellovin wrote:
 What might be useful -- ask an EE, not me -- is a circuit with an
 isolated ground.  In that case, the ground wire from the power plug is
 routed all the way back to the breaker panel, and isn't connected to,
 say, the local electrical box that the cord is plugged into.  I've seen
 computer equipment wired that way in the past.
 
 In the US, the NEC code states that the only place a neutral and a 
 ground should be bonded together is in the primary service entrance 
 facility or where the neutral is created. All subpanels will have 
 isolated grounds and neutrals. If you have three phase service and 
 use a delta (wye without the neutral) to wye transformer to create 
 the neutral, the neutral will be bonded to ground inside the 
 transformer cabinet. Eliminating the neutral is typically done to 
 save money when converting 277/480V to 120/208V (no neutral means a 
 reduced conductor count inside the conduit so smaller conduit can be 
 used since the extra copper for the neutral is eliminated on the 
 input side.) All grounds must be connected to the first metal box or 
 conduit they touch. If you are using plastic boxes with Romex, your 
 grounds will go all the back to your subpanel ground bar which will 
 not meet the neutral until the main breaker panel. More often in a 
 datacenter environment or a commercial facility, the wiring will be 
 BX under a raised floor or BX or EMT with THHN overhead. Either way, 
 the ground is connected inside the outlet box and wired directly back 
 to the breaker panel. The bonding in the box is to ensure there is no 
 voltage potential carried on any metal conduit. My NEC book is at the 
 office now and I'm home, but I'm pretty sure everything I have stated 
 from memory is accurate.
 

Yes, I believe that that's correct, though I'm not going to dig out my
copy of the NEC right now, either.  I chose to leave out the part about
separate panels.

--Steven M. Bellovin, http://www.cs.columbia.edu/~smb