Re: New York Crews?
On Tue, Oct 30, 2012 at 9:00 PM, Justin Wilson li...@mtin.net wrote: Just wondering if anyone knew of any resources, groups, contacts. I would also be interested in this (figured I'd comment in case someone wanted to keep this off list)
altdb contact
Dear Nanog member, I would like to know if there is anyone on this mailing list who is volunteering to help manage altdb.net It seems like no one is actually responding to db-ad...@altdb.net We need to update information on our new address block that was originally owned by a different company. Regards, Serajul
75th Broad up/down?
An online magazine I work with is, we believe, hosted at 75 Broad or 111 8th. It dropped out Monday night, right after they announced that the diesel pumps had fried due to flooding at 75 Broad, came back up early Tuesday morning, and then died again this morning. IP address is in 74.63.44.0/24 block (which may be part of a larger block). Pinging 74.63.44.255 gets me replies from 208.122.44.210 only. Anyone know the current status of these facilities? I've got an e-mail in to noc@internap but haven't heard back - and if they have a facility down they're probably too busy to reply to a single web hosting customer. I have seen the report from earlier this morning indicating that 111 8th had an issue that's been fixed - but the Internap NOC line (877.843.4662) still indicates that NYM008 is having a power outage. Thanks! -- Jeff Shultz
Re: 75th Broad up/down?
-BEGIN PGP SIGNED MESSAGE- Hash: SHA256 On 10/31/2012 09:19 AM, Jeff Shultz wrote: An online magazine I work with is, we believe, hosted at 75 Broad or 111 8th. It dropped out Monday night, right after they announced that the diesel pumps had fried due to flooding at 75 Broad, came back up early Tuesday morning, and then died again this morning. IP address is in 74.63.44.0/24 block (which may be part of a larger block). Pinging 74.63.44.255 gets me replies from 208.122.44.210 only. Anyone know the current status of these facilities? I've got an e-mail in to noc@internap but haven't heard back - and if they have a facility down they're probably too busy to reply to a single web hosting customer. I have seen the report from earlier this morning indicating that 111 8th had an issue that's been fixed - but the Internap NOC line (877.843.4662) still indicates that NYM008 is having a power outage. Thanks! - -- http://tracker.outages.org/reports/view/68 and more update on the list. regards, /virendra -BEGIN PGP SIGNATURE- Version: GnuPG v1.4.11 (GNU/Linux) Comment: Using GnuPG with Mozilla - http://www.enigmail.net/ iF4EAREIAAYFAlCRZPgACgkQ3HuimOHfh+HKKgEAhF3Iwx8/LOqAM49MmOsI6uwZ fdHcLpOFMBHFzYyFRoUBAIH91cZKrmzooK/Akhl4IixNEw4fu6P/Yq4D5W0nrcvv =1QUU -END PGP SIGNATURE-
Re: Flood affecting US east coast communication facilities?
Hi Kauto, Internaps LGA11 DC in NYC was knocked out recently by Sandy. Here's the official statement: Please be advised that Internap's LGA11 facility is experiencing significant flooding in the sub-basement of the 75 Broad Street building as a result of Hurricane Sandy. The flooding has submerged and destroyed the site's diesel pumps and is preventing fuel from being pumped to the generators on the mezzanine level. The available fuel reserves on the mezzanine level are estimated to support customer loads for approximately 5-7 hours. Once this fuel supply has been exhausted the generator will no longer be able to sustain operation and critical customer power loads will be lost. The email was sent a while ago and by now the diesel would have run out. Internap shut down server for customers those that they were contractually obligated to. Currently it seems that the AWS stuff is still up and same for Rackspace. However there have been reports of the US East submarine cables going dark. On Tue, Oct 30, 2012 at 6:46 PM, Kauto Huopio ka...@huopio.fi wrote: Greetings all, Any reports on damage to communications facilities on US east coast? --Kauto -- Kauto Huopio - ka...@huopio.fi (dayjob @ CERT-FI ) -- ~Em
Re: New York Crews?
-BEGIN PGP SIGNED MESSAGE- Hash: SHA256 Hi, On 10/30/2012 02:00 PM, Justin Wilson wrote: Anyone know of lists, contacts, etc. for companies looking for I.T. Folks for help with cleanup and such on the eastern seaboard? I am guessing there will be a demand for anyone from cable pullers to Engineers. I have some free time on my hands and would gladly take a cut in pay to go out and work with the cleanup. I can terminate cables, climb towers, etc. I am sure I am not the only underemployed I.T. Guy who could spend a week or two helping a data center, or other entity. Just wondering if anyone knew of any resources, groups, contacts. Thanks, Justin -- Justin Wilson j...@mtin.net Aol Yahoo IM: j2sw http://www.mtin.net/blog xISP News http://www.twitter.com/j2sw Follow me on Twitter - --- If people interested in such effort feel free to drop me a note w/ your location, contact and what are you willing to help w/. I can put a list and plot it on tracker so people reach you if need be. regards, /virendra -BEGIN PGP SIGNATURE- Version: GnuPG v1.4.11 (GNU/Linux) Comment: Using GnuPG with Mozilla - http://www.enigmail.net/ iF4EAREIAAYFAlCRay0ACgkQ3HuimOHfh+G3jQD+NacDHePtULlPQBw4UBRwkl0e DG9igmrlbLR7/6X/kRoA/RNWKwyBDrSJ8BtaB2UcF6MF247wgNCKZZLB9rLTdwAc =IShy -END PGP SIGNATURE-
RE: Flood affecting US east coast communication facilities?
If anyone is in need of emergency connectivity, VM's, colo, showers, whatever, please contact me. All of our offices in Northern NJ are accessible and online and can support any sort of emergency need. -Original Message- From: Emily Ozols [mailto:win...@team-metro.net] Sent: Tuesday, October 30, 2012 3:53 AM To: nanog@nanog.org Subject: Re: Flood affecting US east coast communication facilities? Hi Kauto, Internaps LGA11 DC in NYC was knocked out recently by Sandy. Here's the official statement: Please be advised that Internap's LGA11 facility is experiencing significant flooding in the sub-basement of the 75 Broad Street building as a result of Hurricane Sandy. The flooding has submerged and destroyed the site's diesel pumps and is preventing fuel from being pumped to the generators on the mezzanine level. The available fuel reserves on the mezzanine level are estimated to support customer loads for approximately 5-7 hours. Once this fuel supply has been exhausted the generator will no longer be able to sustain operation and critical customer power loads will be lost. The email was sent a while ago and by now the diesel would have run out. Internap shut down server for customers those that they were contractually obligated to. Currently it seems that the AWS stuff is still up and same for Rackspace. However there have been reports of the US East submarine cables going dark. On Tue, Oct 30, 2012 at 6:46 PM, Kauto Huopio ka...@huopio.fi wrote: Greetings all, Any reports on damage to communications facilities on US east coast? --Kauto -- Kauto Huopio - ka...@huopio.fi (dayjob @ CERT-FI ) -- ~Em
NSA and the exchanges
Anyone knows if there's a way to find out how involved NSA monitors 151 front street at Toronto? NSA allegedly monitors data centres in the US, but does it have the same influence at a building sitting in its neighbor's soil? There's something on the web like www.ixmaps.ca that tries to piece it together. but not sure how helpful the information on there really is? feedback welcome.
Re: NSA and the exchanges
If your talking the NSA I doubt anyone would tell you. That being said: it would mean the US gov't breaking Canadian law I suspect. Now in Canada it is quite possible that the Canadian Fed gov't monitors traffic but I would also say no one would tell you because telling you would also be in violation in wiretap laws. Best advice, assume they do and hope they don't. :) -jim On Wed, Oct 31, 2012 at 3:25 PM, andy lam anwa...@yahoo.com wrote: Anyone knows if there's a way to find out how involved NSA monitors 151 front street at Toronto? NSA allegedly monitors data centres in the US, but does it have the same influence at a building sitting in its neighbor's soil? There's something on the web like www.ixmaps.ca that tries to piece it together. but not sure how helpful the information on there really is? feedback welcome.
Re: NSA and the exchanges
Allegedly? No, definately. https://www.eff.org/nsa-spying https://www.eff.org/files/filenode/att/presskit/ATT_onepager.pdf -j On Wed, Oct 31, 2012 at 11:25 AM, andy lam anwa...@yahoo.com wrote: Anyone knows if there's a way to find out how involved NSA monitors 151 front street at Toronto? NSA allegedly monitors data centres in the US, but does it have the same influence at a building sitting in its neighbor's soil? There's something on the web like www.ixmaps.ca that tries to piece it together. but not sure how helpful the information on there really is? feedback welcome.
RE: NSA and the exchanges
I'd assume the NSA and CSIS would be talking as needed. Whether CSIS is actually monitoring in there is another question. I'd assume yes, but have never heard anything to confirm or deny. -Original Message- From: jim deleskie [mailto:deles...@gmail.com] Sent: Wednesday, October 31, 2012 2:37 PM To: andy lam Cc: nanog@nanog.org Subject: Re: NSA and the exchanges If your talking the NSA I doubt anyone would tell you. That being said: it would mean the US gov't breaking Canadian law I suspect. Now in Canada it is quite possible that the Canadian Fed gov't monitors traffic but I would also say no one would tell you because telling you would also be in violation in wiretap laws. Best advice, assume they do and hope they don't. :) -jim On Wed, Oct 31, 2012 at 3:25 PM, andy lam anwa...@yahoo.com wrote: Anyone knows if there's a way to find out how involved NSA monitors 151 front street at Toronto? NSA allegedly monitors data centres in the US, but does it have the same influence at a building sitting in its neighbor's soil? There's something on the web like www.ixmaps.ca that tries to piece it together. but not sure how helpful the information on there really is? feedback welcome.
Re: NSA and the exchanges
On 10/31/12 11:25 AM, andy lam wrote: Anyone knows if there's a way to find out how involved NSA monitors 151 front street at Toronto? NSA allegedly monitors data centres in the US, but does it have the same influence at a building sitting in its neighbor's soil? There's something on the web like www.ixmaps.ca that tries to piece it together. but not sure how helpful the information on there really is? feedback welcome. No Such Agency. ~Seth
Re: 75th Broad up/down?
Here's a few notes from Internap which has stuff at 75 Broad and 111 8th: Forwarded Message Hurricane Update: Power Restored at LGA9, 111 8th Ave. Update: We have restored all power to the LGA9 site via generator. Phase 12 UPS UPS modules are in bypass and being investigated at this time. We will be moving the UPS units back inline one at a time as they are verified over the coming hours. There is no impact to customer load expected. Phase 3 load is currently on UPS conditioned power supported by generator. All INAP IP service points are operating normally. Our staff is currently working to bring LGA9 Agile customers back up. Forwarded Message At approximately 23:20 local time, the LGA11 facility returned to service via generator power, including critical customers loads. The generators were refuelled and restarted and are currently operating normally, carrying the critical load. Additionally UPS systems have since been brought back online and are now helping to support power onsite. Additional fuel supply is being arranged and there is ample fuel on site at the moment to maintain operation. As noted, power to customer gear has been restored, however building access is still restricted and customers are not yet able to visit the site. Forwarded Message At approximately 05:45 EDT connectivity to Internap's LGA11 datacenter was lost. This loss was caused by 2 other datacenter power failures that provide fiber to LGA11. We are working with the building personnel at both sites to correct the problems. We will provide more updates as information becomes available. Forwarded Message At approximately 23:20 local time, Internap's LGA11 facility returned to service via generator power, including critical customers loads. The generators were refueled and restarted and are currently operating normally, carrying the critical load. Additionally UPS systems have since been brought back online and are now helping to support power onsite. There is ample fuel on site at the moment to maintain operation and there is a scheduled delivery of additional fuel. This will continue until Con Ed restores grid power. Most all servers are not back online and accessible. Please log in and confirm that everything is working as expected in your environment. An online magazine I work with is, we believe, hosted at 75 Broad or 111 8th. It dropped out Monday night, right after they announced that the diesel pumps had fried due to flooding at 75 Broad, came back up early Tuesday morning, and then died again this morning. IP address is in 74.63.44.0/24 block (which may be part of a larger block). Pinging 74.63.44.255 gets me replies from 208.122.44.210 only. Anyone know the current status of these facilities? I've got an e-mail in to noc@internap but haven't heard back - and if they have a facility down they're probably too busy to reply to a single web hosting customer. I have seen the report from earlier this morning indicating that 111 8th had an issue that's been fixed - but the Internap NOC line (877.843.4662) still indicates that NYM008 is having a power outage. Thanks! -- Jeff Shultz
Re: NSA and the exchanges
Andy, Let me recommend the IXmaps project. It is documenting the very question you are asking :) http://www.ixmaps.ca IXmaps is an interactive tool that enables internet users and researchers to study the route(s) that data packets take across North America, with 'interesting' sites highlighted along the way. It is currently under development. It has been supported by a research grant from the Social Sciences and Humanities Research Council of Canada's Image, Text, Sound and Technology program. IXmaps is affiliated with the New Transparency Project and the Information Policy Research Program at theFaculty of Information, University of Toronto. regards Robert -- Robert Guerra Senior Advisor, Citizen Lab Munk School of Global Affairs, University of Toronto Phone: +1 416-893-0377 Cell: +1 202 905 2081 Twitter: twitter.com/netfreedom Email: rob...@citizenlab.org Web: http://citizenlab.org On 2012-10-31, at 2:25 PM, andy lam wrote: Anyone knows if there's a way to find out how involved NSA monitors 151 front street at Toronto? NSA allegedly monitors data centres in the US, but does it have the same influence at a building sitting in its neighbor's soil? There's something on the web like www.ixmaps.ca that tries to piece it together. but not sure how helpful the information on there really is? feedback welcome.
NJ impact
I had to summarize this recently for a news article I was interviewed for, so I figured I forward: -- Of our three datacenters, this is what we saw: Parsippany 1 (OCT) - The worst we saw here was several sub-second power hits. UPS's held without problem, and we did not transfer to generator at all yet. Parsippany 2 (WBR) - Transferred to generator at about 7:55 PM EST Monday as a precautionary measure due to ongoing utility power hits. However, shortly after transfer, utility voltage went to 0 on all phases; around 10p power returned, but abnormally high (seeing about 550 volts on 480 volt bus). We retransferred last night as utility voltage settled down. Cedar Knolls 1 (MMU) - Briefly transferred to generator around 7:10, then back to utility. We then force transferred to generator around 8pm and stayed until this morning. Returned to utility and all systems are normal. We have accommodated many customers (and non-customers) by allowing them to use our conference rooms and some offices, mainly because they lost power at their buildings, lost access to their buildings, or generators ran out of fuel. We literally have card tables setup in hallways and common areas where people sit and use Wifi to conduct business. There has been no service interruption of any sort to any of our datacenter customers, as of this writing. We lost one span of fiber optics between MMU and 165 Halsey, Newark (NWR), network healed in less than 1 second. It was imperceptible. That was early though, Monday afternoon. This has since restored today. We have sales people onsite who are actively taking sales calls, and there is a measurable amount of customers moving equipment into our facilities as I write this. Many are moving equipment from offices with no power and no ETR in sight. We have electricians onsite to help accommodate. The facilities department has been manning all locations around the clock. All sites remain accessible by road. There was never a situation where you could not over the last 48 hours. We have no equipment in 111 8th, so I cannot offer any telemetry there. However, our gear in 60 Hudson St (Tel-X 9th floor) is still online. We saw no interruption at 165 Halsey, except for some very brief utility hits. UPS's held. We are seeing hundreds, if not thousands, of DSL / T1 / T3 / Ethernet customers down - presumably mostly power loss on the CPE. We lost our connection to Covad, presumably they have gear in a building which lost power. These are only just starting to come back. We have seen substantial interruption to the cellular networks; in many cases, ATT Wireless (who NAC uses) is unable to complete a call. In certain areas, there is no signal at all. Where I live, in 07874 (Byram), many roads are impassable and most everyone does not have power. Trees are down everywhere. I heard that a Byram squad car had a tree land on it while responding to a call. Schools are closed, Halloween has been rescheduled according to our governor. My cable is down, cable modem is down, POTS service is out - yet I still have xDSL (loop by Verizon, IP by NAC) and I run on that successfully. I am unable to get any ATT cell service at my house (usually at least three bars). I am on generator at my house, consuming about 2 gal/hour (propane), with a little over 500 gallons left. Gasonline is becoming an issue. As I understand, having talked to our oil supplier, there is 0 refinery capacity in NJ at this time. All gasoline is being imported from PA, DE, MD, etc. Most stations don't have power. Ones that do are generally out of gas. If they have gas, they have mile long lines and are rationing. Diesel is unavailable if you had not pre-arranged for it. Widespread power outages remain. I am running on generator at my house (Generac QT048) on a 1000 gallon tank of propane, have been since Monday about 7pm. It is estimated at least 7 to 10 days before power restoration. I have yet to see one JCPL truck anywhere near where I live. That is all I have. This is the road leading to the Byram Police Dept - I took this yesterday morning: https://sphotos-a.xx.fbcdn.net/hphotos-prn1/12696_4311181250657_900557870_n.jpg This is typically what Northern NJ looks like: https://sphotos-a.xx.fbcdn.net/hphotos-ash3/548544_4311185050752_1011136048_n.jpg https://sphotos-b.xx.fbcdn.net/hphotos-ash3/61115_4317167440308_289655722_n.jpg (not the top of the telephone pole hanging from the wires)
Re: NSA and the exchanges
On 10/31/2012 2:53 PM, Erik Soosalu wrote: I'd assume the NSA and CSIS would be talking as needed. Communications Security Establishment to NSA, but point taken. Whether CSIS is actually monitoring in there is another question. I'd assume yes, but have never heard anything to confirm or deny. -Original Message- From: jim deleskie [mailto:deles...@gmail.com] Sent: Wednesday, October 31, 2012 2:37 PM To: andy lam Cc: nanog@nanog.org Subject: Re: NSA and the exchanges If your talking the NSA I doubt anyone would tell you. That being said: it would mean the US gov't breaking Canadian law I suspect. Now in Canada it is quite possible that the Canadian Fed gov't monitors traffic but I would also say no one would tell you because telling you would also be in violation in wiretap laws. Best advice, assume they do and hope they don't. :) -jim On Wed, Oct 31, 2012 at 3:25 PM, andy lam anwa...@yahoo.com wrote: Anyone knows if there's a way to find out how involved NSA monitors 151 front street at Toronto? NSA allegedly monitors data centres in the US, but does it have the same influence at a building sitting in its neighbor's soil? There's something on the web like www.ixmaps.ca that tries to piece it together. but not sure how helpful the information on there really is? feedback welcome.
Google burp
I guess I'll be the one to ask...what's going on over at Google? Service interruptions and front-end errors all over the place across what appears to be all services, though Gmail seems to have bounced back up. Google's service disruption is about to bring Twitter's service to its knees as people complain and try to figure out what's going on. Blair Trosper Updraft Networks The North Texas GigaPOP
Re: Google burp
Hey now, we're doing fine over here at Twitter. :P -j On Wed, Oct 31, 2012 at 2:55 PM, Blair Trosper blair.tros...@updraftnetworks.com wrote: I guess I'll be the one to ask...what's going on over at Google? Service interruptions and front-end errors all over the place across what appears to be all services, though Gmail seems to have bounced back up. Google's service disruption is about to bring Twitter's service to its knees as people complain and try to figure out what's going on. Blair Trosper Updraft Networks The North Texas GigaPOP
Re: Google burp
I was editorializing the quantity of tweets about the Google outage more so than the quality of service of Twitter. :) Apologies. On Wed, Oct 31, 2012 at 5:01 PM, John Adams j...@retina.net wrote: Hey now, we're doing fine over here at Twitter. :P -j On Wed, Oct 31, 2012 at 2:55 PM, Blair Trosper blair.tros...@updraftnetworks.com wrote: I guess I'll be the one to ask...what's going on over at Google? Service interruptions and front-end errors all over the place across what appears to be all services, though Gmail seems to have bounced back up. Google's service disruption is about to bring Twitter's service to its knees as people complain and try to figure out what's going on. Blair Trosper Updraft Networks The North Texas GigaPOP
Re: Google burp
On Wed, Oct 31, 2012 at 5:55 PM, Blair Trosper blair.tros...@updraftnetworks.com wrote: I guess I'll be the one to ask...what's going on over at Google? Service interruptions and front-end errors all over the place across what appears to be all services, though Gmail seems to have bounced back up. Google's It's just the annual exercise to remind people how reliant they are on a single company/infrastructure. -- Darius Jahandarie
Re: Google burp
Same in uk as well just got service back On Wednesday, 31 October 2012, Blair Trosper wrote: I was editorializing the quantity of tweets about the Google outage more so than the quality of service of Twitter. :) Apologies. On Wed, Oct 31, 2012 at 5:01 PM, John Adams j...@retina.net javascript:; wrote: Hey now, we're doing fine over here at Twitter. :P -j On Wed, Oct 31, 2012 at 2:55 PM, Blair Trosper blair.tros...@updraftnetworks.com javascript:; wrote: I guess I'll be the one to ask...what's going on over at Google? Service interruptions and front-end errors all over the place across what appears to be all services, though Gmail seems to have bounced back up. Google's service disruption is about to bring Twitter's service to its knees as people complain and try to figure out what's going on. Blair Trosper Updraft Networks The North Texas GigaPOP -- -- Martin Hepworth, CISSP Oxford, UK
Re: Google burp
On 10/31/12 2:55 PM, Blair Trosper wrote: I guess I'll be the one to ask...what's going on over at Google? Service interruptions and front-end errors all over the place across what appears to be all services, though Gmail seems to have bounced back up. Google's service disruption is about to bring Twitter's service to its knees as people complain and try to figure out what's going on. Blair Trosper Updraft Networks The North Texas GigaPOP It's back working for me (after just a few minutes of brokenness), but I have to say I really loved the out of order splash page I got when my calendar went down: Sorry, there seems to be a problem. The service you're looking for is temporarily unavailable. Please try again in a few hours. Thanks for your patience. Ahem, a few *hours*?
Re: Google burp
I had my service go down and come back and when it came back i have the new reply/compose features of the new gmail system http://techcrunch.com/2012/10/30/googles-gmail-launches-new-compose-email-view-and-reply-experience-that-will-save-you-time/ It wasn't there before On Wed, Oct 31, 2012 at 10:06 PM, Michael Sinatra mich...@rancid.berkeley.edu wrote: On 10/31/12 2:55 PM, Blair Trosper wrote: I guess I'll be the one to ask...what's going on over at Google? Service interruptions and front-end errors all over the place across what appears to be all services, though Gmail seems to have bounced back up. Google's service disruption is about to bring Twitter's service to its knees as people complain and try to figure out what's going on. Blair Trosper Updraft Networks The North Texas GigaPOP It's back working for me (after just a few minutes of brokenness), but I have to say I really loved the out of order splash page I got when my calendar went down: Sorry, there seems to be a problem. The service you're looking for is temporarily unavailable. Please try again in a few hours. Thanks for your patience. Ahem, a few *hours*?
Re: Google burp
On Wed, Oct 31, 2012 at 10:35 PM, Jeremy stealth...@gmail.com wrote: I had my service go down and come back and when it came back i have the new reply/compose features of the new gmail system http://techcrunch.com/2012/10/30/googles-gmail-launches-new-compose-email-view-and-reply-experience-that-will-save-you-time/ yeah, be careful with their new compose feature. i'm used to vim, so i hit esc half way through an email which generally does nothing. however, with this new feature, it closed the email. then it took it longer to appear in drafts than it did to compose a new email. so, now i've disabled it. i hope they don't force the issue until they give me vim key bindings in my email editor :)
Re: Google burp
Once upon a time, shawn wilson ag4ve...@gmail.com said: yeah, be careful with their new compose feature. i'm used to vim, so i hit esc half way through an email which generally does nothing. however, with this new feature, it closed the email. then it took it longer to appear in drafts than it did to compose a new email. so, now i've disabled it. i hope they don't force the issue until they give me vim key bindings in my email editor :) Have you tried the Firefox add-on that can turn input boxes into vi mode? Does that work with Gmail? -- Chris Adams cmad...@hiwaay.net Systems and Network Administrator - HiWAAY Internet Services I don't speak for anybody but myself - that's enough trouble.
Re: Google burp
And if you are a Chrome user have a look at Vimium [1] [1] http://vimium.github.com/ On 31 October 2012 23:43, Chris Adams cmad...@hiwaay.net wrote: Once upon a time, shawn wilson ag4ve...@gmail.com said: yeah, be careful with their new compose feature. i'm used to vim, so i hit esc half way through an email which generally does nothing. however, with this new feature, it closed the email. then it took it longer to appear in drafts than it did to compose a new email. so, now i've disabled it. i hope they don't force the issue until they give me vim key bindings in my email editor :) Have you tried the Firefox add-on that can turn input boxes into vi mode? Does that work with Gmail? -- Chris Adams cmad...@hiwaay.net Systems and Network Administrator - HiWAAY Internet Services I don't speak for anybody but myself - that's enough trouble. -- ??? BaconZombie LOAD *,8,1
Re: Google burp
On Thu, Nov 1, 2012 at 12:03 AM, Bacon Zombie baconzom...@gmail.com wrote: And if you are a Chrome user have a look at Vimium [1] [1] http://vimium.github.com/ looks promising: i enter insert mode -- all commands will be ignored until you hit esc to exit i might be able to handle this - i could never get vimperator (sorry for hijacking the thread :) )
IPv6 Netowrk Device Numbering BP
We're working out our dual stacked IPv4-IPv6 network. One issue that recently has arisen is how to number the management interfaces on the network devices themselves. I have always been kind of partial to the idea of taking advantage IPv6 features and letting hosts set their own addresses with EUI-64 interface numbers. For the management interface on a network device, it's more like a normal host. I'd just as well tell the device its prefix, and let it build the address itself. For IPv6, my opinion is that I'm not even going to try to remember 128-bit addresses. It's not something reasonable to expect humans to do. I'm going to depend on some name-to-number service (DNS or a hosts file), and as far as a computer goes, 2001:db8::80:abff:fe45:6789 is just as easy to remember as, 2001:db8::12:34. The other approach is to assign addresses. To me, that's more of a hold over from IPv4 thinking, but there are legitimate reasons I can think of. It's nice to have the IPv6 address tied to the configuration rather than the hardware. If you need to drop in a replacement device, you copy the configuration and no addresses change. But OTOH, others might consider it a feature that the IP follows the device rather than the role. And the real reason I think people want to do it is that they want to be able to memorize IP addresses of important hosts like these. Another option would be to do both. Assign a fixed address and also let it chose EUI-64. However, I see that leading to confusion. Not sure what good it would do. Is there anything like a standard, best practice for this (yet)? What are other people doing and their reasons? Anyone have operational experience with what works and what does not (and the what does not is probably really of more interest)? -- Crist J. Clark