Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Mark Tinka




On 2/4/23 08:11, William Herrin wrote:


Not for more than a decade now, at least not in the U.S. When you're
up to whole-house generator prices everyone expects electric start.
Half the portables have electric start. Most lawnmowers have electric
start. Once you have that, the cost to make the switch automatic
instead of manual is trivial. And the mass-produced consumer-grade
switches are quite reliable.


Fair point, but it is not uncommon (YMMV) for backup solutions to not be 
whole-home, and this includes generators. I have not lived in the U.S. 
on any meaningfully extended basis, so I can't speak to the degree to 
which folk that install backup power choose their cost/value matrix. But 
in many other places I've lived, especially where the power is 
frequently out, splitting the house loads into different panels a 
generator or small solar/battery system can support is commonplace; 
mainly for convenience but also to reduce the chances of a fire or 
electrical shock from having to run wires ad hoc.


The same would also apply to renewables, especially where budget is 
limited and folk can't afford to backup the entire home.


This is often cheaper than investing in large backup solutions, while 
still providing some degree of convenience to power what one would 
consider critical items, whatever that means to them.


I've been helping quite a number of folk wire small inverters with 
limited power and backup battery time into DB boards that feed only 
lights and plugs to specifically drive wi-fi, TV, an IP phone and a 
fridge. The inverters and accompanying battery aren't terribly expensive 
here (US$500 - US$800 for a Lead Acid system, and up to US$1,400 for a 
Li-Ion one), and labour in Africa is dirt cheap (less than US$100 for an 
installation), so it's budget-friendly, and keeps basics going. One 
could even charge a laptop.


In general, the main things folk will not backup are electric stoves, 
electric ovens, electric water heaters, electric space heaters and air 
conditioners. Obviously, in places with winter periods, serious plans 
have to be made to avoid death from cold.


Mark.


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread William Herrin
On Fri, Feb 3, 2023 at 10:01 PM Mark Tinka  wrote:
> What I mean by "pre-wired" is that, perhaps, the generator is pre-setup
> and wired into the house, but is not in standby mode to manage costs,
> and perhaps, to be reliable since ATS's are often dodgy.
>
> Maybe a manual start is required. Maybe a changeover switch has to be
> flipped. That sort of thing.

Not for more than a decade now, at least not in the U.S. When you're
up to whole-house generator prices everyone expects electric start.
Half the portables have electric start. Most lawnmowers have electric
start. Once you have that, the cost to make the switch automatic
instead of manual is trivial. And the mass-produced consumer-grade
switches are quite reliable.

Regards,
Bill Herrin

-- 
For hire. https://bill.herrin.us/resume/


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Mark Tinka




On 2/4/23 07:48, William Herrin wrote:


Pre-wired makes it a standby generator, which 9 times out of 10 is
automatic start with an automatic transfer switch. It's running within
seconds whether you're home or not. Electricians cost too much and
20kva natural gas / propane generators with an ATS don't cost enough
more than the portables.

Compare:

https://www.costco.com/honeywell-18kw-home-standby-generator-with-transfer-switch.product.4000106705.html

and:

https://www.amazon.com/Honda-2200-Watt-120-Volt-Portable-Generator/dp/B079YF1HF6

understanding that an electrician will cost you $2000-$3000 for the
labor with any genset modification to the house wiring.


Aware of all this - I operate one or two submarine cable landing stations...

What I mean by "pre-wired" is that, perhaps, the generator is pre-setup 
and wired into the house, but is not in standby mode to manage costs, 
and perhaps, to be reliable since ATS's are often dodgy.


Maybe a manual start is required. Maybe a changeover switch has to be 
flipped. That sort of thing.


Of course, we are speculating, and Sabri can answer best.

Mark.


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread William Herrin
On Fri, Feb 3, 2023 at 9:36 PM Mark Tinka  wrote:
> On 2/4/23 07:29, William Herrin wrote:
> > If it's just a little gasoline generator, 30 minutes is about right.
> > It takes 10 minutes to decide the power isn't coming back soon and
> > another 10 to drag the generator out of the shed, hook up the wires
> > and get it going even though it's cold, wet, and hasn't been run for
> > several months. That leaves 10 minutes to spare figuring out how to
> > convince the UPS that the generator power is good enough to retransfer
> > and stay.
>
> Indeed - I was guessing given how reliable PG have been for Sabri, a
> lot is probably pre-wired. I may be wrong.

Pre-wired makes it a standby generator, which 9 times out of 10 is
automatic start with an automatic transfer switch. It's running within
seconds whether you're home or not. Electricians cost too much and
20kva natural gas / propane generators with an ATS don't cost enough
more than the portables.

Compare:

https://www.costco.com/honeywell-18kw-home-standby-generator-with-transfer-switch.product.4000106705.html

and:

https://www.amazon.com/Honda-2200-Watt-120-Volt-Portable-Generator/dp/B079YF1HF6

understanding that an electrician will cost you $2000-$3000 for the
labor with any genset modification to the house wiring.


Regards,
Bill Herrin


-- 
For hire. https://bill.herrin.us/resume/


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Mark Tinka




On 2/4/23 07:29, William Herrin wrote:


If it's just a little gasoline generator, 30 minutes is about right.
It takes 10 minutes to decide the power isn't coming back soon and
another 10 to drag the generator out of the shed, hook up the wires
and get it going even though it's cold, wet, and hasn't been run for
several months. That leaves 10 minutes to spare figuring out how to
convince the UPS that the generator power is good enough to retransfer
and stay.


Indeed - I was guessing given how reliable PG have been for Sabri, a 
lot is probably pre-wired. I may be wrong.


Mark.


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread William Herrin
On Fri, Feb 3, 2023 at 9:05 PM Mark Tinka  wrote:
> On 2/3/23 21:11, Sabri Berisha wrote:
> > Living in an area served by PG, I've had my share of power cuts. At home
> > I have a 600va UPS that protects my cable modem, RPI router, and POE switch
> > which serves 2 APs. That lasts about 30 minutes, which gives me enough time
> > to fire up my generator.
>
> I'd assume it doesn't take you that long to fire up the genie, if you
> are home when the power goes out :-).

If it's just a little gasoline generator, 30 minutes is about right.
It takes 10 minutes to decide the power isn't coming back soon and
another 10 to drag the generator out of the shed, hook up the wires
and get it going even though it's cold, wet, and hasn't been run for
several months. That leaves 10 minutes to spare figuring out how to
convince the UPS that the generator power is good enough to retransfer
and stay.

Regards,
Bill Herrin


-- 
For hire. https://bill.herrin.us/resume/


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Mark Tinka




On 2/3/23 21:11, Sabri Berisha wrote:


Living in an area served by PG, I've had my share of power cuts. At home
I have a 600va UPS that protects my cable modem, RPI router, and POE switch
which serves 2 APs. That lasts about 30 minutes, which gives me enough time
to fire up my generator.


I'd assume it doesn't take you that long to fire up the genie, if you 
are home when the power goes out :-).


Out of interest, depending on how long you've had the UPS, how many 
times have you changed the battery?




Tip of the day: I also have a 1000va UPS that protects my garage door opener.
This makes it a lot easier to a. get a car out if needed, and b. get my
generator out of the garage.


In South Africa, garage door motors historically come standard with a 
12V 7Ah Lead Acid battery. What most people don't realize is that within 
1.5 to 2 years, those batteries are dead, and since there was power most 
of the time, they never noticed, until the power went out and the 
battery did not have sufficient energy to drive the motor.


It is not uncommon to see folk here moving to Li-Ion batteries with the 
same capacity to drive garage and gate motors. Personally, I try to only 
use Li-Ion packs in well ventilated, not-too-tight spaces, that come 
with a BMS and a charger that is predictable :-). So I avoid these 
little ones, and feel safer with Lead Acid batteries for garage and gate 
motors.




Lastly, in the spirit of happy wife, happy life, I have another 600va UPS
that covers my tankless water heater. It heats using natural gas, but the
control panel still needs power. That thing lasts pretty long.


There are tankless water heaters that can take standard AA batteries to 
spark the igniter as well, but yes, if yours is electric, makes sense to 
put a UPS on it. At my place, I use both a PV-based controller to heat 
traditional water tanks, and also have just as many tankless water 
heaters. The former is for end-of-day showers and dish washing once the 
sun has done its thing, the latter is for the morning jobs for the same 
things, or if it's cloudy/rainy outside.


Even though I have whole-home backup, I did place a UPS on the PV-based 
controller, because even if it is connected to solar panels, it is 
still, in essence, an inverter, meaning it requires a grid before it can 
generate solar power. That is what the UPS does for it. It was my first 
deployment of renewable energy, so I needed the UPS before I backed up 
the entire home.




YMMV, of course, but I went through numerous outages recently. And by
numerous, I mean enough for our City leadership to get pissed off at PG
and demand explanations.


Judging by our situation, I'd take the city leadership demanding 
explanations any day :-). We are way past that, down here. It's so bad, 
folk are deploying self-generation and self-storage by the truck loads. 
It's the gold rush for solar and battery installers right now. People 
have all but given up on the power company (Eskom) ever going back to 
its glory days.




So far, my current ISP (Spectrum cable) has had 0 outages as a result of
power loss. Which is pretty impressive, given the instability of the grid
in this area.


Not bad.

Mark.


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Mark Tinka




On 2/3/23 19:53, Saku Ytti wrote:


In practice I would default to expecting 0 min availability during
power outage, regardless of how resilient my CPE is. We can scarcely
make the Internet work at the best of times.


Agreed, this is a good place to start. It's a bit doom & gloom, but most 
people underestimate just how much work it takes power companies to 
generate and distribute energy. Consequently, they never have to think 
about generation and/or load management, if they had to do it on their 
own, meaning they will usually consider the cheapest solution possible, 
which for electricity, usually ends in tears.


Mark.


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Mark Tinka




On 2/3/23 19:25, Brian Turnbow via NANOG wrote:


They have been discussing it here in Italy as well.
The isp/telecommunication industry here is tryng to get Cos/pops/cabinets 
listed as critical infra and removed from rolling power cuts.


I would say plan for the worst, because there will always be some other 
department or governmental function that says they are more critical 
than the next one. And even if they may designate certain functions as 
critical, electrical distribution grids are not always built to that 
degree of granularity, and those critical functions are often caught in 
the crossfire as other non-critical loads are shed from the network.


And even after all that, if the blackouts need to intensify, all bets 
are off, since the main purpose then becomes preventing grid frequency 
drop, rather than servicing loads.




Here this is mainly ran from pops that have ups and generator systems so 
several hours to days of uptime depending on site.


If major data centres need to spend more on fuel than they planned for, 
I'd suggest making a generous allocation for an increase in co-lo costs 
for your next budget cycle, as the data centres will, invariably, pass 
those costs on the longer the city has to shed power from the grid.




OTOH I have seen providers daisy chain customer sites in a ring that crash 
miserably when 2 customers loose power isolating all in between sites.
But that is not the norm...


This is one of the reasons we refuse to turn customer sites into Metro-E 
PoP's, or PoP's of any kind.




Street cabinets for fttc services here have low times if any.
Same thing for mini dslams mounted on poles in the middle of nowhere.
0 to 2 hours for these.
Most have batteries/capacitors in the cabinet but not all and they are not 
designed for extended power outages 2 hours max.
Some are remotely powered from the CO, but that does not seem to be a thing 
anymore. Too costly
DSL ran from COs are protected as for fiber above.


A lot of this will be driven by what competitors do. If there is no 
competition that can keep their street cabinets going, the others won't. 
It's a great opportunity for anyone willing to make lemonade out of the 
situation.




Don't operate a 4g network, so take this info accordingly ,  but here it 
depends on the tower from what I have seen.
All towers I have seen have  battery backup , a lot have generators too.
I would say they have higher times than the fttc times above.


In dense metro's, mobile sites will be well invested. It starts to get 
tricky when you go out into the sticks.


Also, when the power goes out, so does the wi-fi. That means everybody 
moves their traffic away from the home wi-fi and on to the nearest cell 
tower. While radio bandwidth and signal coverage does not suffer that 
much, it hits the backhaul hard, between the tower and the mobile 
carrier's core. So nice flashing LTE/4G/5G signals on your phone 
translates to GPRS-esque performance. In some cases, we have seen mobile 
operators downgrade radio coverage to 3G, in order to manage this. Who 
knew 3G performed a bad as GPRS or EDGE, in 2023 :-)?


In the most extreme of case, the cell site could run out of power as 
well, as there isn't enough time for the batteries to recharge between 
outage cycles, or the field teams can't replenish fuel for the 
generators in time.


In the absolutely extreme cases (as we see here in South Africa, for 
example), cell sites can be raided and batteries stolen, especially if 
there is darkness all around. I would not expect this to be the case in 
the UK, especially if power outages are not the norm and people live a 
fairly middle-class life, but if I were Vodafone, for example, I'd have 
my risk department planning for such an eventuality already.


Mark.


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Mark Tinka




On 2/3/23 16:11, Israel G. Lugo wrote:



Hi folks,

At $day_job, I have a team of engineers who are oncall for critical 
services in the United Kingdom. For $reasons, the national power grid 
is announcing the possibility of rolling power cuts over the coming 
months. Right now it's "unlikely", but possible. If cuts do happen, 
it'll be 3+ hours, possibly several times/day.


I'm looking at the cost/benefit of deploying small UPSes at people's 
homes, to protect their network access when oncall. Just to power the 
home router (+ONT if FTTP), and keep a charged laptop. I figure 
anything smallish should be enough for a few hours.


Question is, how much battery runtime can I typically expect from 
ISPs' last mile infra.


People will have a random mix of DSL, FTTP, DOCSIS. Another 
alternative is tethering with 4G.


- For FTTP, I *think* (but am not sure) that the UK mostly uses PON, 
so guess it would be runtime of OLT and onwards

- For DSL: runtime of DSLAM cabinet and onwards
- For CATV: CMTS and onwards, maybe any active equipments in the HFC 
to the CPE?

- For 4G: BSS and onwards

Could anyone with last mile experience help with some ballpark 
figures? I.e. 15 min vs 8h or 8 days.


Living in South Africa where load shedding is the order of the day since 
the end of last year (and to continue for the next 2 years, at least, if 
not more), I can tell you that until network operators have had to deal 
with this, they are ill-prepared.


For equipment inside major data centres, you will be fine. But for 
equipment in commercial buildings, street cabinets, e.t.c., uptime will 
be directly related to how much faith operators have put into the 
national grid, which translates to some UPS, and whether the building or 
cabinet is serviced by a well maintained generator.


As for the home, a UPS is not a terribly good idea to keep the "wi-fi" 
going... typical UPS's use Lead Acid batteries which are shallow-cycle 
batteries that are not meant to be discharged below 50%. It's the usual 
disclaimer - UPS's are meant to give you time to save your work and 
shutdown, not provide extended backup.


If customers expect the power to be out for 3+ hours at a time, multiple 
times a day, I'd recommend getting a cheap 1.6kW inverter that can power 
a 24V 100Ah Li-Ion battery (either 1x 24V or 2x 12V in series). It's not 
a lot of energy, but if you are powering the CPE + ONU + IP phone, it's 
more than enough (you can easily squeeze 9hrs of continuous run-time on 
a single charge, maybe even more). While these inverters are slow to 
charge Li-Ion batteries (about 10A of charge current), the load is so 
minimal that the battery is being discharged even slower. So it works 
out, even with extended, multiple outages in a 24-hour cycle.


Operators running gear outside of major data centres will want to invest 
in large Li-Ion packs designed for the load and frequency of grid 
outages. Investing in Lead Acid batteries, while cheaper initially, 
will  become operationally expensive, as they don't do well with 
high-cycle counts, even the deep discharge ones. Not to mention, the 
rather poor energy density they possess for the amount of weight they carry.


Depending on the importance of the site, some solar power may be 
necessary, even though the UK is not the most well-lit country in the 
world. For such cases, you can augment the solar plant with a generator, 
mainly to recharge the batteries, rather than to power the load.


Mark.


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Jay Hennigan

On 2/3/23 06:11, Israel G. Lugo wrote:

Question is, how much battery runtime can I typically expect from ISPs' 
last mile infra.


See comments inline, this is my experience in the US. UK may be 
substantially different.


People will have a random mix of DSL, FTTP, DOCSIS. Another alternative 
is tethering with 4G.


- For FTTP, I *think* (but am not sure) that the UK mostly uses PON, so 
guess it would be runtime of OLT and onwards


This is likely to run indefinitely. OLTs are for the most part going to 
be in telco central offices and datacenters with reliable generator 
backup. PON outside plant covers long distances passively, not requiring 
any local power.



- For DSL: runtime of DSLAM cabinet and onwards


If fed directly from the central office, indefinite. If fed from a 
remote terminal, maybe a couple of hours assuming that there are 
batteries installed at the terminal (and that the batteries are 
maintained).


- For CATV: CMTS and onwards, maybe any active equipments in the HFC to 
the CPE?


DOCSIS/CATV is likely to go dark pretty much instantaneously on loss of 
local power unless your customer is very close to the HFC head-end. 
Outside cable plant is fed with AC power injected locally at power poles 
or at pedestals into the center conductor of the coaxial trunk line. 
This powers the trunk amplifiers and fiber-to-coax media converters. 
This isn't typically backed up at all. Cable companies figure that if 
the power is out nobody is watching TV or using the Internet. Sometimes 
there may be a small UPS but I wouldn't expect more than a few minutes 
runtime.


In the case of prolonged outages I've occasionally seen a small Honda 
generator chained to a pole feeding one of the power injectors but this 
was very obviously a manual process done a while after the outage 
started where the power outage was localized and there were probably 
some VIP customers unaffected by the power outage.



- For 4G: BSS and onwards


Cell sites typically have generator backup. Figure at least a day. A 
prolonged outage requiring refueling with weather making it difficult to 
get fuel to the site(s) could be a problem.


--
Jay Hennigan - j...@west.net
Network Engineering - CCIE #7880
503 897-8550 - WB6RDV



Contact for androidpolice.com

2023-02-03 Thread Justin Krejci
Any contacts available that are responsible for androidpolice.com website 
hosting? Some of our IP space is not able to access their website. Other IP 
addresses of ours are working just fine. This appears to be some kind HTTP 
protocol layer issue but only affecting certain IP addresses. I am guessing it 
is some kind of web application firewall using outdated IP list data.


Yes I know it is hosted at Amazon but every time I have tried to go through 
Amazon for support with websites they are hosting, they have 100% of the time 
told me they can't and/or won't help me with website hosting issues on their 
web platform; I have to go through their customer... which I don't have any 
good contact info for. I've tried reaching them on twitter, I've tried blindly 
emailing people listed on their website guessing their email addresses, etc. I 
have had zero response.



Thanks!

Justin


Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Sabri Berisha
- On Feb 3, 2023, at 6:11 AM, Israel G. Lugo israel.l...@lugosys.com wrote:

Hi,

> I'm looking at the cost/benefit of deploying small UPSes at people's
> homes, to protect their network access when oncall. Just to power the
> home router (+ONT if FTTP), and keep a charged laptop. I figure anything
> smallish should be enough for a few hours.

Living in an area served by PG, I've had my share of power cuts. At home
I have a 600va UPS that protects my cable modem, RPI router, and POE switch
which serves 2 APs. That lasts about 30 minutes, which gives me enough time
to fire up my generator.

Tip of the day: I also have a 1000va UPS that protects my garage door opener.
This makes it a lot easier to a. get a car out if needed, and b. get my 
generator out of the garage.

Lastly, in the spirit of happy wife, happy life, I have another 600va UPS
that covers my tankless water heater. It heats using natural gas, but the
control panel still needs power. That thing lasts pretty long.

> Question is, how much battery runtime can I typically expect from ISPs'
> last mile infra.

YMMV, of course, but I went through numerous outages recently. And by
numerous, I mean enough for our City leadership to get pissed off at PG
and demand explanations.

So far, my current ISP (Spectrum cable) has had 0 outages as a result of
power loss. Which is pretty impressive, given the instability of the grid
in this area.

Thanks,

Sabri


Weekly Global IPv4 Routing Table Report

2023-02-03 Thread Routing Table Analysis Role Account
This is an automated weekly mailing describing the state of the Global
IPv4 Routing Table as seen from APNIC's router in Japan.

The posting is sent to APOPS, NANOG, AfNOG, SANOG, PacNOG, SAFNOG
TZNOG, MENOG, BJNOG, SDNOG, CMNOG, LACNOG and the RIPE Routing WG.

Daily listings are sent to bgp-st...@lists.apnic.net.

For historical data, please see https://thyme.apnic.net.

If you have any comments please contact Philip Smith .

IPv4 Routing Table Report   04:00 +10GMT Sat 04 Feb, 2023

  BGP Table (Global) as seen in Japan.

Report Website: https://thyme.apnic.net
Detailed Analysis:  https://thyme.apnic.net/current/

Analysis Summary


BGP routing table entries examined:  919404
Prefixes after maximum aggregation (per Origin AS):  347822
Deaggregation factor:  2.64
Unique aggregates announced (without unneeded subnets):  445727
Total ASes present in the Internet Routing Table: 74078
Prefixes per ASN: 12.41
Origin-only ASes present in the Internet Routing Table:   63572
Origin ASes announcing only one prefix:   26134
Transit ASes present in the Internet Routing Table:   10506
Transit-only ASes present in the Internet Routing Table:438
Average AS path length visible in the Internet Routing Table:   4.2
Max AS path length visible:  55
Max AS path prepend of ASN (265020)  50
Prefixes from unregistered ASNs in the Routing Table:   951
Number of instances of unregistered ASNs:   961
Number of 32-bit ASNs allocated by the RIRs:  41183
Number of 32-bit ASNs visible in the Routing Table:   34103
Prefixes from 32-bit ASNs in the Routing Table:  166598
Number of bogon 32-bit ASNs visible in the Routing Table:31
Special use prefixes present in the Routing Table:1
Prefixes being announced from unallocated address space:521
Number of addresses announced to Internet:   3062699648
Equivalent to 182 /8s, 141 /16s and 22 /24s
Percentage of available address space announced:   82.7
Percentage of allocated address space announced:   82.7
Percentage of available address space allocated:  100.0
Percentage of address space in use by end-sites:   99.6
Total number of prefixes smaller than registry allocations:  312179

APNIC Region Analysis Summary
-

Prefixes being announced by APNIC Region ASes:   240580
Total APNIC prefixes after maximum aggregation:   68793
APNIC Deaggregation factor:3.50
Prefixes being announced from the APNIC address blocks:  235600
Unique aggregates announced from the APNIC address blocks:97865
APNIC Region origin ASes present in the Internet Routing Table:   13261
APNIC Prefixes per ASN:   17.77
APNIC Region origin ASes announcing only one prefix:   3847
APNIC Region transit ASes present in the Internet Routing Table:   1771
Average APNIC Region AS path length visible:4.4
Max APNIC Region AS path length visible: 26
Number of APNIC region 32-bit ASNs visible in the Routing Table:   8531
Number of APNIC addresses announced to Internet:  773543680
Equivalent to 46 /8s, 27 /16s and 87 /24s
APNIC AS Blocks4608-4864, 7467-7722, 9216-10239, 17408-18431
(pre-ERX allocations)  23552-24575, 37888-38911, 45056-46079, 55296-56319,
   58368-59391, 63488-64098, 64297-64395, 131072-151865
APNIC Address Blocks 1/8,  14/8,  27/8,  36/8,  39/8,  42/8,  43/8,
49/8,  58/8,  59/8,  60/8,  61/8, 101/8, 103/8,
   106/8, 110/8, 111/8, 112/8, 113/8, 114/8, 115/8,
   116/8, 117/8, 118/8, 119/8, 120/8, 121/8, 122/8,
   123/8, 124/8, 125/8, 126/8, 133/8, 150/8, 153/8,
   163/8, 171/8, 175/8, 180/8, 182/8, 183/8, 202/8,
   203/8, 210/8, 211/8, 218/8, 219/8, 220/8, 221/8,
   222/8, 223/8,

ARIN Region Analysis Summary


Prefixes being announced by ARIN Region ASes:267075
Total ARIN prefixes after maximum aggregation:   121357
ARIN Deaggregation factor: 2.20
Prefixes being announced from the ARIN address blocks:   269014
Unique aggregates announced from the ARIN address blocks:130096
ARIN Region origin ASes present in the Internet Routing Table:19068
ARIN Prefixes per ASN:

Re: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Saku Ytti
On Fri, 3 Feb 2023 at 16:15, Israel G. Lugo  wrote:

> Could anyone with last mile experience help with some ballpark figures?
> I.e. 15 min vs 8h or 8 days.

This would be highly market specific. In many cases, probably most
cases, there is no regulatory requirement for availability for
internet service whatsoever.

One specific case where it is regulated, Finland, the regulation is
available in Finnish, Swedish and English, the English document is
available at:
https://www.finlex.fi/data/normit/47143/05_Regulation_on_resilience_of_communications_networks_and_services_and_of_synchronisation_of_communications_networks.pdf

It classifies service to five priorities with different availability
requirements. From your ballpark, 8h would be the closest fit, but in
theory the higher priorities have indefinite availability before the
system is exhausted by means of generation.

In practice I would default to expecting 0 min availability during
power outage, regardless of how resilient my CPE is. We can scarcely
make the Internet work at the best of times.

-- 
  ++ytti


RE: Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Brian Turnbow via NANOG



Hi,

> At $day_job, I have a team of engineers who are oncall for critical services 
> in
> the United Kingdom. For $reasons, the national power grid is announcing the
> possibility of rolling power cuts over the coming months.
> Right now it's "unlikely", but possible. If cuts do happen, it'll be 3+ hours,
> possibly several times/day.


They have been discussing it here in Italy as well.
The isp/telecommunication industry here is tryng to get Cos/pops/cabinets 
listed as critical infra and removed from rolling power cuts.

> Question is, how much battery runtime can I typically expect from ISPs'
> last mile infra.
> 
> - For FTTP, I *think* (but am not sure) that the UK mostly uses PON, so guess
> it would be runtime of OLT and onwards

Here this is mainly ran from pops that have ups and generator systems so 
several hours to days of uptime depending on site.
OTOH I have seen providers daisy chain customer sites in a ring that crash 
miserably when 2 customers loose power isolating all in between sites.
But that is not the norm...

> - For DSL: runtime of DSLAM cabinet and onwards

Street cabinets for fttc services here have low times if any.
Same thing for mini dslams mounted on poles in the middle of nowhere.
0 to 2 hours for these.
Most have batteries/capacitors in the cabinet but not all and they are not 
designed for extended power outages 2 hours max.
Some are remotely powered from the CO, but that does not seem to be a thing 
anymore. Too costly
DSL ran from COs are protected as for fiber above.

> - For CATV: CMTS and onwards, maybe any active equipments in the HFC to
> the CPE?
> - For 4G: BSS and onwards

Don't operate a 4g network, so take this info accordingly ,  but here it 
depends on the tower from what I have seen.
All towers I have seen have  battery backup , a lot have generators too.
I would say they have higher times than the fttc times above.

HTH

Brian


Re: Spectrum (legacy TWC) Infrastructure - Contact Off List (Patrick Garner)

2023-02-03 Thread Keith Stokes
I think the bright orange is so you don't run over it with your lawn mower, 
especially since it's going to be there for 3 years.

You'd think in the 3 years in the US South it would be grown over and buried 
itself. 


From: NANOG  on behalf of Patrick 
Garner 
Sent: Friday, February 3, 2023 10:16 AM
To: nanog@nanog.org 
Subject: Re: Spectrum (legacy TWC) Infrastructure - Contact Off List (Patrick 
Garner)

We have the same issue here in suburban Atlanta but with Comcast. The Comcast 
ped in my front yard has no cover... it's exposed to the elements. There's a 
bright orange cable running from there to my neighbor's house, it's been there 
for at least 3 years. At the least, it doesn't touch my property. There's other 
spots in my neighborhood where Comcast's bright orange coax just runs on the 
ground, along the road, in the gutter. Not saying AT is the greatest but at 
the very least their peds(they are so old they still say Bellsouth) have covers 
and they come within 3 days of install to bury DSL lines. I don't understand 
why Comcast has to choose the absolute ugliest bright orange cables to leave 
everywhere. If you're going to leave it, at least use a black cable.

Yay duopoly!
--
Patrick Garner
Owner
Cherokee Communications LLC
404-406-9864
patrick@cherokee.network


Re: Spectrum (legacy TWC) Infrastructure - Contact Off List (Patrick Garner)

2023-02-03 Thread Patrick Garner
We have the same issue here in suburban Atlanta but with Comcast. The
Comcast ped in my front yard has no cover... it's exposed to the elements.
There's a bright orange cable running from there to my neighbor's house,
it's been there for at least 3 years. At the least, it doesn't touch my
property. There's other spots in my neighborhood where Comcast's bright
orange coax just runs on the ground, along the road, in the gutter. Not
saying AT is the greatest but at the very least their peds(they are so
old they still say Bellsouth) have covers and they come within 3 days of
install to bury DSL lines. I don't understand why Comcast has to choose the
absolute ugliest bright orange cables to leave everywhere. If you're going
to leave it, at least use a black cable.

Yay duopoly!
-- 
Patrick Garner
Owner
Cherokee Communications LLC
404-406-9864
patrick@cherokee.network


Typical last mile battery runtime (protecting against power cuts)

2023-02-03 Thread Israel G. Lugo

Hi folks,

At $day_job, I have a team of engineers who are oncall for critical 
services in the United Kingdom. For $reasons, the national power grid is 
announcing the possibility of rolling power cuts over the coming months. 
Right now it's "unlikely", but possible. If cuts do happen, it'll be 3+ 
hours, possibly several times/day.


I'm looking at the cost/benefit of deploying small UPSes at people's 
homes, to protect their network access when oncall. Just to power the 
home router (+ONT if FTTP), and keep a charged laptop. I figure anything 
smallish should be enough for a few hours.


Question is, how much battery runtime can I typically expect from ISPs' 
last mile infra.


People will have a random mix of DSL, FTTP, DOCSIS. Another alternative 
is tethering with 4G.


- For FTTP, I *think* (but am not sure) that the UK mostly uses PON, so 
guess it would be runtime of OLT and onwards

- For DSL: runtime of DSLAM cabinet and onwards
- For CATV: CMTS and onwards, maybe any active equipments in the HFC to 
the CPE?

- For 4G: BSS and onwards

Could anyone with last mile experience help with some ballpark figures? 
I.e. 15 min vs 8h or 8 days.


Thank you,
Israel


Re: Spectrum (legacy TWC) Infrastructure - Contact Off List

2023-02-03 Thread Mike Hammett
Yet the independents are doing it anyway. 




- 
Mike Hammett 
Intelligent Computing Solutions 

Midwest Internet Exchange 

The Brothers WISP 

- Original Message -

From: "Eric Kuhnke"  
To: "Forrest Christian (List Account)"  
Cc: "nanog list"  
Sent: Thursday, February 2, 2023 6:46:01 PM 
Subject: Re: Spectrum (legacy TWC) Infrastructure - Contact Off List 



It might look low cost until you look at a post-1980s suburb in the USA or 
Canada where 100% of the utilities are underground. There may be no fiber or 
duct routes. Just old coax used for DOCSIS3 owned/run by the local cable 
incumbent and copper POTS wiring belonging to the ILEC. The cost to retrofit 
such a neighborhood and reach every house with a fiber architecture can be 
quite high in construction and labor. 







On Thu, Feb 2, 2023 at 9:14 AM Forrest Christian (List Account) < 
li...@packetflux.com > wrote: 



The cost to build physical layer in much of the suburban and somewhat rural US 
is low enough anymore that lots of smaller, independent, ISPs are overbuilding 
the incumbent with fiber and taking a big chunk of their customer base because 
they are local and care. And making money while doing it. 




On Thu, Feb 2, 2023, 8:22 AM Masataka Ohta < mo...@necom830.hpcl.titech.ac.jp > 
wrote: 


Mike Hammett wrote: 

> I selfishly hope they don't because that's where independent 
> operators will succeed. ;-) 

Because of natural regional monopoly at physical layer (cabling 
cost for a certain region is same between competitors but their 
revenues are proportional to their regional market shares), they 
can't succeed unless the physical layer is regulated to be 
unbundled, which is hard with PON. 

But, in US where regional telephone network has been operated 
by, unlike Europe/Japan, a private company enjoying natural 
regional monopoly, economic situation today should be no worse 
than that at that time. 

Masataka Ohta 







Re: Spectrum (legacy TWC) Infrastructure - Contact Off List

2023-02-03 Thread Clayton Zekelman

At 08:43 PM 02/02/2023, Eric Kuhnke wrote:
There is "microtrenching" and then there is 
microtrenching. Very different things are 
sometimes described by the same name. Some of 
what Google tried to go was exceedingly shallow, 
like 4 inches down. Cheap microtrenching done 
too quick and too shallow has given the concept a bad name.


The local ILEC is doing that here - they use a 
spade to make a little slot in the customer's 
lawn and shove the cable in.  If they have to 
cross a driveway or sidewalk, they dig out the 
expansion joint, shove the cable in and dump some 
cold patch in the gap.  If they have to run 
multiple cables, they use a concrete saw to make the gap a bit wider.


There is microtrenched fiber in Vancouver BC 
that is close to 20 years old now throughout the 
downtown core that is nearly problem-free. The 
difference is that it is 12+ inches down and was 
installed using large, noisy, water cooled 
diamond-grit concrete saws cutting deep slits 
into the joints between streets and curbs, or 
concrete curbs and sidewalks,  duct inserted, 
then backfilled with grouting. It's deep enough 
where it crosses roads that re-paving the road 
by first grinding off the top several inches of 
surface is extremely unlikely to disturb the duct.


I'm familiar with the slightly more robust 
technique deployed by companies like 
Teraspan.  I'm sure it works much better in the 
milder climate in BC.   There are microtrench/VIF 
networks in Toronto and Ottawa as well.  A few 
years ago, they were re-building one of the roads 
in the downtown core in Toronto, and the entire 
microtrenched network (mini handholes and all) 
had been lifted out of the street area and laid 
on the sidewalk, and protected with barriers and 
safety cones, etc.I just shook my head...




--

Clayton Zekelman
Managed Network Systems Inc. (MNSi)
3363 Tecumseh Rd. E
Windsor, Ontario
N8W 1H4

tel. 519-985-8410
fax. 519-985-8409