Re: [Nut-upsuser] APC Modbus support is finally here!

2023-11-22 Thread Jim Klimov via Nut-upsuser
Great! Thanks for the info, and hope the driver author can address the nits
(forwarding now...)

Jim

On Wed, Nov 22, 2023, 15:05 d tbsky  wrote:

> Jim Klimov via Nut-upsuser 
> >
> > Got an update for APC Modbus users: a new PR is waiting for real-life
> testing for settable variables and instant commands support.
> >
> > https://github.com/networkupstools/nut/pull/2184
> >
> > As before, a custom build of libmodbus may be needed for USB support
> (detailed in the earlier PR), but Serial and TCP may already be well served
> by a distro near you!
>
> Hi:
>I got a new APC SRT3000XL and tested the new driver "apc_modbus".
> the ups works fine with nut+apcupsd.  the new driver "apc_modbus" has
> result below:
>
> 1.  upsrw can write the variable "battery.date". but the new value
> will only show after restarting apc_modbus. and in my case the written
> data will shift one day. eg the command "upsrw -s
> battery.date=2023-09-13" will return "2023-09-12" later.
> 2. the upscmd power-off related commands (like load.*, outlet.*,
> shutdown.*) can not work. so it can not shutdown the ups. (I think
> this is the most important feature which needs to be fixed)
> 3. upscmd command works: beeper.mute, bypass.start, bypass.stop,
> test.battery.start, test.battery.stop, test.panel.start
> 4. I can't  attach any load so I can not test calibrate.start. but I
> found the new driver seems missing an import item which apcupsd have:
> "ups.test.result"
>
> below are some raw data:
> > data read from  nut+apcupsd (for reference):
> battery.charge: 99.0
> battery.charge.low: 5
> battery.date: 2023-11-21
> battery.runtime: 57000.0
> battery.runtime.low: 180
> battery.voltage: 109.0
> device.mfr: APC
> device.model: Smart-UPS SRT3000
> device.serial: AS2032296523
> device.type: ups
> driver.debug: 0
> driver.flag.allow_killpower: 0
> driver.name: apcupsd-ups
> driver.parameter.pollinterval: 10
> driver.parameter.port: localhost
> driver.parameter.synchronous: auto
> driver.state: quiet
> driver.version: 2.8.1
> driver.version.internal: 0.71
> input.frequency: 60.0
> input.voltage: 224.7
> output.current: 0.00
> output.frequency: 60.0
> output.voltage: 207.6
> output.voltage.nominal: 208
> power.percent: 0.0
> ups.date: 2023-11-22
> ups.delay.shutdown: 0
> ups.delay.start: 0
> ups.firmware: UPS 15.5
> ups.firmware.aux: 00.5
> ups.id: APC UPS
> ups.load: 0.0
> ups.mfr: APC
> ups.mfr.date: 2020-08-10
> ups.model: Smart-UPS SRT3000
> ups.power.nominal: 3000
> ups.realpower.nominal: 2700.0
> ups.serial: AS2032296523
> ups.status: OL
> ups.temperature: 27.0
> ups.test.result: OK
> ups.time: 17:24:25
>
> > data read from new driver "apc_modbus"
> battery.charge: 99.00
> battery.date: 2023-11-21
> battery.date.maintenance: 2028-05-21
> battery.runtime: 57425
> battery.temperature: 29.00
> battery.voltage: 108.69
> device.mfr: American Power Conversion
> device.model: Smart-UPS SRT3000
> device.serial: AS2032296523
> device.type: ups
> driver.debug: 0
> driver.flag.allow_killpower: 0
> driver.name: apc_modbus
> driver.parameter.pollinterval: 10
> driver.parameter.port: /dev/ttyS0
> driver.parameter.synchronous: yes
> driver.state: quiet
> driver.version: 2.8.1
> driver.version.internal: 0.10
> experimental.output.energy: 7
> input.transfer.high: 220
> input.transfer.low: 184
> input.transfer.reason: TestEnded
> input.voltage: 224.77
> outlet.group.0.delay.reboot: 8
> outlet.group.0.delay.shutdown: 0
> outlet.group.0.delay.start: 0
> outlet.group.0.name: Unswitched Group
> outlet.group.1.delay.reboot: 8
> outlet.group.1.delay.shutdown: 90
> outlet.group.1.delay.start: 0
> outlet.group.1.name: Outlet Group 1
> outlet.group.2.delay.reboot: 8
> outlet.group.2.delay.shutdown: 90
> outlet.group.2.delay.start: 0
> outlet.group.2.name: Outlet Group 2
> outlet.group.3.delay.reboot: 8
> outlet.group.3.delay.shutdown: 90
> outlet.group.3.delay.start: 0
> outlet.group.3.name: Outlet Group 3
> outlet.group.count: 2
> output.current: 0.00
> output.frequency: 60.00
> output.voltage: 207.62
> ups.delay.reboot: 8
> ups.delay.shutdown: 0
> ups.delay.start: 0
> ups.efficiency: LoadTooLow
> ups.firmware: UPS 15.5
> ups.id: APC UPS
> ups.load: 0.00
> ups.mfr: American Power Conversion
> ups.mfr.date: 2020-08-10
> ups.model: Smart-UPS SRT3000
> ups.power: 0.00
> ups.power.nominal: 3000
> ups.realpower: 0.00
> ups.realpower.nominal: 2700
> ups.serial: AS2032296523
> ups.status: OL
> ups.timer.reboot: -1
> ups.timer.shutdown: -1
> ups.timer.start: -1
>
> >upsrw -l myups
> [battery.date]
> Battery change date
> Type: NUMBER
> Value: 2023-11-21
>
> [driver.debug]
> Current debug verbosity level of the driver program
> Type: NUMBER
> Value: 0
>
> [driver.flag.allow_killpower]
> Safety flip-switch to allow the driver daemon to send UPS shutdown
> command (accessible via driver.killpower)
> Type: NUMBER
> Value: 0
>
> [input.transfer.high]
> High voltage transfer point (V)
> Type: NUMBER
> Value: 220
>
> [input.transfer.low]
> Low voltage transfe

Re: [Nut-upsuser] APC Modbus support is finally here!

2023-11-22 Thread d tbsky via Nut-upsuser
Jim Klimov via Nut-upsuser 
>
> Got an update for APC Modbus users: a new PR is waiting for real-life testing 
> for settable variables and instant commands support.
>
> https://github.com/networkupstools/nut/pull/2184
>
> As before, a custom build of libmodbus may be needed for USB support 
> (detailed in the earlier PR), but Serial and TCP may already be well served 
> by a distro near you!

Hi:
   I got a new APC SRT3000XL and tested the new driver "apc_modbus".
the ups works fine with nut+apcupsd.  the new driver "apc_modbus" has
result below:

1.  upsrw can write the variable "battery.date". but the new value
will only show after restarting apc_modbus. and in my case the written
data will shift one day. eg the command "upsrw -s
battery.date=2023-09-13" will return "2023-09-12" later.
2. the upscmd power-off related commands (like load.*, outlet.*,
shutdown.*) can not work. so it can not shutdown the ups. (I think
this is the most important feature which needs to be fixed)
3. upscmd command works: beeper.mute, bypass.start, bypass.stop,
test.battery.start, test.battery.stop, test.panel.start
4. I can't  attach any load so I can not test calibrate.start. but I
found the new driver seems missing an import item which apcupsd have:
"ups.test.result"

below are some raw data:
> data read from  nut+apcupsd (for reference):
battery.charge: 99.0
battery.charge.low: 5
battery.date: 2023-11-21
battery.runtime: 57000.0
battery.runtime.low: 180
battery.voltage: 109.0
device.mfr: APC
device.model: Smart-UPS SRT3000
device.serial: AS2032296523
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: apcupsd-ups
driver.parameter.pollinterval: 10
driver.parameter.port: localhost
driver.parameter.synchronous: auto
driver.state: quiet
driver.version: 2.8.1
driver.version.internal: 0.71
input.frequency: 60.0
input.voltage: 224.7
output.current: 0.00
output.frequency: 60.0
output.voltage: 207.6
output.voltage.nominal: 208
power.percent: 0.0
ups.date: 2023-11-22
ups.delay.shutdown: 0
ups.delay.start: 0
ups.firmware: UPS 15.5
ups.firmware.aux: 00.5
ups.id: APC UPS
ups.load: 0.0
ups.mfr: APC
ups.mfr.date: 2020-08-10
ups.model: Smart-UPS SRT3000
ups.power.nominal: 3000
ups.realpower.nominal: 2700.0
ups.serial: AS2032296523
ups.status: OL
ups.temperature: 27.0
ups.test.result: OK
ups.time: 17:24:25

> data read from new driver "apc_modbus"
battery.charge: 99.00
battery.date: 2023-11-21
battery.date.maintenance: 2028-05-21
battery.runtime: 57425
battery.temperature: 29.00
battery.voltage: 108.69
device.mfr: American Power Conversion
device.model: Smart-UPS SRT3000
device.serial: AS2032296523
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: apc_modbus
driver.parameter.pollinterval: 10
driver.parameter.port: /dev/ttyS0
driver.parameter.synchronous: yes
driver.state: quiet
driver.version: 2.8.1
driver.version.internal: 0.10
experimental.output.energy: 7
input.transfer.high: 220
input.transfer.low: 184
input.transfer.reason: TestEnded
input.voltage: 224.77
outlet.group.0.delay.reboot: 8
outlet.group.0.delay.shutdown: 0
outlet.group.0.delay.start: 0
outlet.group.0.name: Unswitched Group
outlet.group.1.delay.reboot: 8
outlet.group.1.delay.shutdown: 90
outlet.group.1.delay.start: 0
outlet.group.1.name: Outlet Group 1
outlet.group.2.delay.reboot: 8
outlet.group.2.delay.shutdown: 90
outlet.group.2.delay.start: 0
outlet.group.2.name: Outlet Group 2
outlet.group.3.delay.reboot: 8
outlet.group.3.delay.shutdown: 90
outlet.group.3.delay.start: 0
outlet.group.3.name: Outlet Group 3
outlet.group.count: 2
output.current: 0.00
output.frequency: 60.00
output.voltage: 207.62
ups.delay.reboot: 8
ups.delay.shutdown: 0
ups.delay.start: 0
ups.efficiency: LoadTooLow
ups.firmware: UPS 15.5
ups.id: APC UPS
ups.load: 0.00
ups.mfr: American Power Conversion
ups.mfr.date: 2020-08-10
ups.model: Smart-UPS SRT3000
ups.power: 0.00
ups.power.nominal: 3000
ups.realpower: 0.00
ups.realpower.nominal: 2700
ups.serial: AS2032296523
ups.status: OL
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1

>upsrw -l myups
[battery.date]
Battery change date
Type: NUMBER
Value: 2023-11-21

[driver.debug]
Current debug verbosity level of the driver program
Type: NUMBER
Value: 0

[driver.flag.allow_killpower]
Safety flip-switch to allow the driver daemon to send UPS shutdown
command (accessible via driver.killpower)
Type: NUMBER
Value: 0

[input.transfer.high]
High voltage transfer point (V)
Type: NUMBER
Value: 220

[input.transfer.low]
Low voltage transfer point (V)
Type: NUMBER
Value: 184

[outlet.group.0.delay.reboot]
Description unavailable
Type: NUMBER
Value: 8

[outlet.group.0.delay.shutdown]
Description unavailable
Type: NUMBER
Value: 0

[outlet.group.0.delay.start]
Description unavailable
Type: NUMBER
Value: 0

[outlet.group.0.name]
Description unavailable
Type: STRING
Maximum length: 16
Value: Unswitched Group

[outlet.group.1.delay.reboot]
Description unavailable
Type: NUMBER
Value: 8

[outlet.