Re: [Nut-upsuser] upsmon shutdown based on Time since power fail.

2009-05-25 Thread Arjen de Korte

Citeren Richard Chapman :

This sounds like one way to do it. If I do it this way - do you know  
whether the file:


/etc/killpower

will be created before the shut-down is issued (as it would if the  
battery low event occurs). If not - the UPS may not be shut down -  
and therefore the system may not start up again if the power returns  
before the battery is completely flat.


I guess if the flag file isn't created - then we could run a short  
script to create it - then issue the shut-down Does that sound  
right to you? Indeed - if we do write a short script - we could do  
the delay in the script - somehow test whether we are still on  
battery - and if so - issue the shut-down immediately.


Don't do this. As written in the FAQ, in some cases you may wish/need  
to use 'upssched' to start shutting down your systems before the UPS  
indicates the battery is low. In that case, you probably want to call  
'upsmon -c fsd' instead, which will initiate a shutdown on the upsmon  
master (in your case, your server). This means that you will have to  
configure the upsmon on the server (FINALDELAY) to allow for enough  
time for your clients to shutdown. This will put your master at risk  
in case of repeated power failures however, so don't overdo this.


Best regards, Arjen
--
Please keep list traffic on the list



___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


[Nut-upsuser] APC Smart UPS 900i

2009-05-25 Thread Rene Bartsch
Hi,

I'm running an old APC Smart UPS 900i. As there isn't any software from APC 
which supports this
UPS anymore, I've installed NUT (Gentoo Ebuilds), but version 2.0.5 and version 
2.2.2 loose
connection to the UPS while version 2.4.1 and SVN version don't show any 
settings and there are no
instant commands.

The only information I can get are:

driver.name: apcsmart
driver.parameter.cable: 940-0024C
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyUSB0
driver.version: 2.4.1
driver.version.internal: 2.03
input.voltage: 226.9
ups.mfr: APC
ups.model: Smart-UPS
ups.serial: 00016325
ups.status: OL


How can I use the UPS (battery test, configuration)?


Best regards,

Renne



___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] upsmon shutdown based on Time since power fail.

2009-05-25 Thread Jon Bendtsen

Hi

I am sorry, but i can not answer any of your technical NUT questions,  
i just wrote with an idea that might or might not work.


As for starting the machine if power returns, then i can think of some  
remote power management that can turn the power on/off to the machine  
and then sit between the UPS and the machine(s). WAKE on LAN might be  
an option too.




JonB

On 22/05/2009, at 03.07, Richard Chapman wrote:


Thanks Jon

This sounds like one way to do it. If I do it this way - do you know  
whether the file:


/etc/killpower

will be created before the shut-down is issued (as it would if the  
battery low event occurs). If not - the UPS may not be shut down -  
and therefore the system may not start up again if the power returns  
before the battery is completely flat.


I guess if the flag file isn't created - then we could run a short  
script to create it - then issue the shut-down Does that sound  
right to you? Indeed - if we do write a short script - we could do  
the delay in the script - somehow test whether we are still on  
battery - and if so - issue the shut-down immediately.


Out of interest - do you know what the ups parameter:

battery.runtime: 120

Means - and where might it be documented?

Thanks Jon


Richard.


Jon Bendtsen wrote:

On 20/05/2009, at 12.11, Richard Chapman wrote:

For various reasons - I have been trying to get my Desktops and/or  
servers to shut-down a fixed time after a power fail - or better  
still a fixed time - or a low battery whichever comes first.


[cut]

Is there another parameter somewhere - probably in upsmon - which  
would allow me to specify a shut-down after (say) 3 minutes  
running on battery regardless of battery status?


In the upsmon.conf file you use NOTIFYCMD and ONBATT to execute a  
shutdown $time


Then you use a ONLINE to execute a -c to cancel a shutdown if the  
power returns.




JonB








___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


[Nut-upsuser] FreeBSD installation procedure (updated)

2009-05-25 Thread forsite
The purpose of this posting is to summarize the FreeBSD installation
procedure from the beginning till the very end.

1. Follow the instructions provided in the How-To prepared by Thierry
Thomas (http://people.freebsd.org/~thierry/nut_FreeBSD_HowTo.txt).
Please note the following:

a) if you are using an USB device, as of NUT 2.2 usbhid-ups completely
replaces the legacy hidups driver and provides support for various
manufacturers. At that time, it will be renamed to usbhid-ups;

b) if your USB device is claimed by the uhid and not by ugen driver,
this should be fixed, since libusb-based packages such as NUT can't
work with uhid* device nodes.  Therefore, you need to either
de-configure the uhid driver (in FreeBSD a separate driver handles
USB/HID keyboard and mouse) or blacklist that specific USB VID/PID
combination. Please refer to the following thread for more details on
the issue: 
http://lists.alioth.debian.org/pipermail/nut-upsuser/2009-May/005058.html

c) 'allowfrom' in upsd.users is obsolete and is no longer used;

d) you may need to insert additional instructions into ups.conf - e.g.
if you need a decent grace delay on the UPS for the shutdown
procedure.  See below for more details on the issue.

2. After you have followed the above How-To instructions and have
tested your configuration, you will need to configure the automatic
UPS shutdown (http://www.networkupstools.org/doc/2.2.0/shutdown.html).
 Put the following sentence either into /etc/rc.shutdown script, or
into /usr/local/etc/rc.d/nut (inside the 'nut_poststop' section,
straight after the '${nut_prefix}/libexec/nut/upsdrvctl stop'
instruction):

# uncomment for rc.shutdown script
#
# nut_prefix=${nut_prefix-"/usr/local"}

if [ -r /etc/killpower ]; then

rm -f /etc/killpower

echo "Killing the power, bye!"
${nut_prefix}/libexec/nut/upsdrvctl -v shutdown

if [ $? -ne 0 ]; then
${nut_prefix}/libexec/nut/UPS_DRIVER -k -D -a UPS_NAME
fi

# increase this timeout (to, say, 120 sec) if your 
configuration is
vulnerable to a power race
# *** see the section on power races below ***
sleep 5

# uh oh... the UPS poweroff failed!
# you probably should reboot here to avoid getting stuck
# *** see the section on power races below ***
#
# /sbin/reboot

fi

Arguably rc.shutdown is a better place for this but it's not very
ports friendly.  If you you decide to put this into
/usr/local/etc/rc.d/nut, you need a decent grace delay on the UPS so
the rest of the system will shut down properly.  This can be done by
adding two variables into ups.conf:

 [UPS_NAME]
driver = UPS_DRIVER
port = UPS_PORT
# Give the system enough time to shutdown when the power fails
offdelay = 120
# ondelay must be greater than offdelay so change it
ondelay = 130

3. Test whether your configuration is able to handle a power race
successfully as described in
http://www.networkupstools.org/doc/2.2.0/shutdown.html and add the
"reboot after timeout" hack, if required.

4. That's it.  At this stage you may wish to add some
post-installation procedures, like cgi-scripts for web-access or any
other.

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org