Re: [Nut-upsuser] Cyberpower CP850PFCLCD 120% battery charge

2011-03-31 Thread Arjen de Korte

Citeren Justin Ellison jus...@techadvise.com:


I have a CyberPower Systems CP850PFCLCD that I'm hooking up to NUT 2.4.3
from apt running under Ubuntu 10.04.  Using the usbhid-ups driver, things
*seem* to work at first glance, but there are some odd issues.  The most
notable issue is that the battery.charge indicator reads 120 when at full
charge.  I came across this post here:
http://lists.alioth.debian.org/pipermail/nut-upsuser/2007-September/003222.htmlbut
it looks like the user never supplied the necessary data.


For whatever reason the people that made the UPS firmware decided that  
they didn't need to follow the USB HID PDC specifications. From the  
data you sent, it looks like the value for battery charge that is  
reported by the UPS needs some conversion (coefficient and/or offset)  
to get to the true battery charge. Most likely, this is present in the  
bundled software for the UPS, but sadly we don't know them. So unless  
you're going to change that, the situation is unlikely to improve. It  
looks like '120' means 100% charge, but one data point is not enough  
to find (at least) two missing parameters.



The other issue that I found was that the LB flag is sent way to early when
I unplugged the UPS from the outlet.


I don't think so. The data you posted indicated that about the time  
the UPS started reporsing LB (low battery), the runtime fell below the  
battery.runtime.low, so this is about right. If you don't need 5  
minutes to shutdown your system, you might try lowering this value (if  
the UPS supports that) and see if this increases the useable time on  
battery.


Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Cyberpower CP850PFCLCD 120% battery charge

2011-03-31 Thread Justin Ellison
Good news, this model appears to work perfectly, save for an odd
factory default.  I only have 55% of a load on this thing, but the
minute I unplug it, I have right around 5 mins of battery time.  That
was causing the LB flag to be set almost immediately(because the
factory default for low runtime was 300).  I was able to set a new
bettery.runtime.low of 120 using upsrw.

On Thu, Mar 31, 2011 at 2:09 PM, Arjen de Korte nut+us...@de-korte.org wrote:
 For whatever reason the people that made the UPS firmware decided that they 
 didn't need to follow the USB HID PDC specifications. From the data you sent, 
 it looks like the value for battery charge that is reported by the UPS needs 
 some conversion (coefficient and/or offset) to get to the true battery 
 charge. Most likely, this is present in the bundled software for the UPS, but 
 sadly we don't know them. So unless you're going to change that, the 
 situation is unlikely to improve. It looks like '120' means 100% charge, but 
 one data point is not enough to find (at least) two missing parameters.

When I tested it out tonight, I made a point to watch the LED on the
unit in comparison to the battery.charge indicator from nut.  Almost
instant I unplugged it, battery.charge went from 120 to 91, and
immediately fell in sync with what the LED was showing.

 The other issue that I found was that the LB flag is sent way to early when
 I unplugged the UPS from the outlet.

 I don't think so. The data you posted indicated that about the time the UPS 
 started reporsing LB (low battery), the runtime fell below the 
 battery.runtime.low, so this is about right. If you don't need 5 minutes to 
 shutdown your system, you might try lowering this value (if the UPS supports 
 that) and see if this increases the useable time on battery.

Aside from the minor annoyance of the 120 battery.charge when full,
this UPS works perfectly with Nut.  Nice work guys!

Justin

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Startup timing issue with CyberPower CP425HG UPS

2011-03-31 Thread Charles Lepple

On Mar 30, 2011, at 9:46 PM, Arun wrote:

I'm not sure how to fix this, other than to perhaps start the ups  
service from the udev rules file if a known USB UPS device has been  
found, but that seems like a rather ugly way to go about this. Does  
anyone have any thoughts?


I have had a sneaking suspicion that in some situations, starting a  
USB driver from hotplug or udev might work better, and this is  
definitely one of those cases.


Before you get too far into this, you probably want to make sure that  
when power returns, your UPS will wait until the battery is charged to  
some threshold before powering on its outlets. Otherwise, if the power  
goes off-on-off (with a shutdown after the first power failure), the  
UPS might try to start the computer up with a discharged battery, and  
due to the delay in connecting to the UPS, NUT would not get the low  
battery signal in time to shut down properly the second time.


The other trick is that the current NUT USB drivers will attempt to  
reattach to a device if it disappears. Especially during testing, it  
is helpful to be able to unplug and re-plug the UPS into the USB port.  
For this to work, the udev script could kill the driver which is  
waiting around for the UPS to come back. (That would only do the right  
thing on a single-UPS system.) Alternatively, you could check in the  
udev script to see if any of the USB drivers are running (look for the  
PID files, and run kill -0 to see if the process is still around  
without actually terminating it).


On the other hand, you can also look into whether your startup scripts  
have configurable dependencies, and tell the NUT init.d script to  
start after the USB service has fully initialized. Not sure how that  
works in Fedora.


___