 What is the output of 'upsd' in the syslog telling you? Note that when
 running in debug mode, a process will terminate as soon as you close the
 terminal it is running in or when you kill it with Ctrl-C.

 Best regards, Arjen

Good catch, I looked more in syslog and saw something that I overlooked:


Apr 29 09:38:53 krshina3 upsd[8297]: Can't connect to UPS [munja]
(megatec-munja): No such file or directory

So somehow even as I restarted my PC I somehow messed up and upsd
still tried to connect to megatec driver.

Then I restarted upsdrv, upsd and upsmon in that order and now it works:

Apr 29 09:39:03 krshina3 blazer_ser[12978]: Startup successful
Apr 29 09:39:28 krshina3 upsd[8297]: mainloop: Interrupted system call
Apr 29 09:39:28 krshina3 upsd[8297]: Signal 15: exiting
Apr 29 09:39:29 krshina3 upsd[13062]: listening on 127.0.0.1 port 3493
Apr 29 09:39:29 krshina3 upsd[13062]: Connected to UPS [munja]: blazer_ser-munja
Apr 29 09:39:29 krshina3 upsd[13063]: Startup successful
Apr 29 09:39:51 krshina3 upsd[13063]: User monuser@127.0.0.1 logged
into UPS [munja]
Apr 29 09:40:27 krshina3 upsd[13063]: User monuser@127.0.0.1 logged
out from UPS [munja]
Apr 29 09:40:36 krshina3 upsmon[13135]: Startup successful
Apr 29 09:40:36 krshina3 upsd[13063]: User monuser@127.0.0.1 logged
into UPS [munja]



upsc munja@localhost
battery.voltage: 54.00
battery.voltage.nominal: 48.0
beeper.status: disabled
device.mfr:
device.model:
device.type: ups
driver.name: blazer_ser
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS0
driver.version: 2.6.0
driver.version.internal: 1.51
input.current.nominal: 0.0
input.frequency: 50.0
input.frequency.nominal: 50
input.voltage: 246.5
input.voltage.fault: 140.0
input.voltage.nominal: 230
output.voltage: 246.5
ups.delay.shutdown: 30
ups.delay.start: 180
ups.firmware: IN03064B
ups.load: 4
ups.mfr:
ups.model:
ups.status: OL
ups.temperature: 25.0  temp never changes
ups.type: offline / line interactive

If you need some more info so you can add this UPS to working list
please tell me.

Oh and sorry for false alarm :)

Have a nice day
Dushan

___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser


Re: [Nut-upsuser] Problem with blazer_ser/megatec when upgrading to 2.6.0 from 2.4

2011-04-29 Thread Arnaud Quette
2011/4/29 Dushan Tcholich dus...@gmail.com

 
  What is the output of 'upsd' in the syslog telling you? Note that when
  running in debug mode, a process will terminate as soon as you close the
  terminal it is running in or when you kill it with Ctrl-C.
 
  Best regards, Arjen

 Good catch, I looked more in syslog and saw something that I overlooked:


 Apr 29 09:38:53 krshina3 upsd[8297]: Can't connect to UPS [munja]
 (megatec-munja): No such file or directory

 So somehow even as I restarted my PC I somehow messed up and upsd
 still tried to connect to megatec driver.

 Then I restarted upsdrv, upsd and upsmon in that order and now it works:

 Apr 29 09:39:03 krshina3 blazer_ser[12978]: Startup successful
 Apr 29 09:39:28 krshina3 upsd[8297]: mainloop: Interrupted system call
 Apr 29 09:39:28 krshina3 upsd[8297]: Signal 15: exiting
 Apr 29 09:39:29 krshina3 upsd[13062]: listening on 127.0.0.1 port 3493
 Apr 29 09:39:29 krshina3 upsd[13062]: Connected to UPS [munja]:
 blazer_ser-munja
 Apr 29 09:39:29 krshina3 upsd[13063]: Startup successful
 Apr 29 09:39:51 krshina3 upsd[13063]: User monuser@127.0.0.1 logged
 into UPS [munja]
 Apr 29 09:40:27 krshina3 upsd[13063]: User monuser@127.0.0.1 logged
 out from UPS [munja]
 Apr 29 09:40:36 krshina3 upsmon[13135]: Startup successful
 Apr 29 09:40:36 krshina3 upsd[13063]: User monuser@127.0.0.1 logged
 into UPS [munja]



 upsc munja@localhost
 battery.voltage: 54.00
 battery.voltage.nominal: 48.0
 beeper.status: disabled
 device.mfr:
 device.model:
 device.type: ups
 driver.name: blazer_ser
 driver.parameter.pollinterval: 2
 driver.parameter.port: /dev/ttyS0
 driver.version: 2.6.0
 driver.version.internal: 1.51
 input.current.nominal: 0.0
 input.frequency: 50.0
 input.frequency.nominal: 50
 input.voltage: 246.5
 input.voltage.fault: 140.0
 input.voltage.nominal: 230
 output.voltage: 246.5
 ups.delay.shutdown: 30
 ups.delay.start: 180
 ups.firmware: IN03064B
 ups.load: 4
 ups.mfr:
 ups.model:
 ups.status: OL
 ups.temperature: 25.0  temp never changes
 ups.type: offline / line interactive

 If you need some more info so you can add this UPS to working list
 please tell me.


as per your information, I've completed the supported VA ratings (Subversion
trunk, r2979).

cheers,
Arnaud
-- 
Linux / Unix Expert RD - Eaton - http://powerquality.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/
___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

[Nut-upsuser] Problem with blazer_ser/megatec when upgrading to 2.6.0 from 2.4

2011-04-28 Thread Dushan Tcholich
Hello

First things first, thanks for great work with NUT.

For years I used Informer compact 3kVA UPS
http://www.informups.com/informer_compact.html with nut/megatec serial
driver, but it stopped working when I switched to blazer_ser with
2.6.0 upgrade.
I'm using 2.6.0 on gentoo.

Blazer_ser seems to connect with UPS, but upsmon reports driver not connected.

uname -a
Linux localhost 2.6.36-gentoo-r7 #3 SMP Tue Feb 8 18:39:54 CET 2011
x86_64 Intel(R) Core(TM)2 CPU 6400 @ 2.13GHz GenuineIntel GNU/Linux

Configuration:
cat ups.conf | grep # -v
[munja]
driver = blazer_ser
port = /dev/ttyS0

 cat upsd.conf | grep # -v

LISTEN 127.0.0.1 3493

cat upsd.users | grep # -v

[monuser]
password  = ###

cat upsmon.conf | grep # -v

MONITOR munja@localhost 1 monuser ## slave
MINSUPPLIES 1
SHUTDOWNCMD /sbin/shutdown -h +0
NOTIFYCMD /usr/local/ups/bin/notifyme
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower
RBWARNTIME 43200
NOCOMMWARNTIME 300
FINALDELAY 5

 /lib64/nut/blazer_ser -D -a munja -i 10
Network UPS Tools - Megatec/Q1 protocol serial driver 1.51 (2.6.0)
   0.00 send_to_all: SETINFO driver.parameter.port /dev/ttyS0
   0.51 debug level is '5'
   0.100836 send_to_all: SETINFO device.type ups
   0.100860 send_to_all: SETINFO driver.version 2.6.0
   0.100870 send_to_all: SETINFO driver.version.internal 1.51
   0.100879 send_to_all: SETINFO driver.name blazer_ser
   0.100886 Trying megatec protocol...
   0.100970 send: Q1
   0.326638 read: (246.0 140.0 246.0 004 50.0 54.0 25.0 1000
   0.326681 send_to_all: SETINFO input.voltage 246.0
   0.326695 send_to_all: SETINFO input.voltage.fault 140.0
   0.326707 send_to_all: SETINFO output.voltage 246.0
   0.326730 send_to_all: SETINFO ups.load 4
   0.326741 send_to_all: SETINFO input.frequency 50.0
   0.326752 send_to_all: SETINFO battery.voltage 54.00
   0.326763 send_to_all: SETINFO ups.temperature 25.0
   0.326772 send_to_all: SETINFO beeper.status disabled
   0.326782 send_to_all: SETINFO ups.type offline / line interactive
   0.326792 send_to_all: SETINFO ups.status OL
   0.326799 Status read in 1 tries
   0.326806 Supported UPS detected with megatec protocol
   0.326877 send: F
   0.446626 read: #230.0 0.0 048.0 50.0
   0.446660 send_to_all: SETINFO input.voltage.nominal 230
   0.446671 send_to_all: SETINFO input.current.nominal 0.0
   0.446683 send_to_all: SETINFO battery.voltage.nominal 48.0
   0.446694 send_to_all: SETINFO input.frequency.nominal 50
   0.446701 Ratings read in 1 tries
   0.446773 send: I
   0.634630 read: #   IN03064B
   0.634659 send_to_all: SETINFO ups.mfr 
   0.634669 send_to_all: SETINFO ups.model 
   0.634679 send_to_all: SETINFO ups.firmware IN03064B
   0.634686 Vendor information read in 1 tries
   0.634693 Battery runtime will not be calculated (runtimecal not set)
   0.634702 send_to_all: SETINFO ups.delay.start 180
   0.634711 send_to_all: SETINFO ups.delay.shutdown 30
   0.634719 send_to_all: ADDCMD beeper.toggle
   0.634726 send_to_all: ADDCMD load.off
   0.634733 send_to_all: ADDCMD load.on
   0.634740 send_to_all: ADDCMD shutdown.return
   0.634748 send_to_all: ADDCMD shutdown.stayoff
   0.634755 send_to_all: ADDCMD shutdown.stop
   0.634763 send_to_all: ADDCMD test.battery.start
   0.634776 send_to_all: ADDCMD test.battery.start.deep
   0.634785 send_to_all: ADDCMD test.battery.start.quick
   0.634793 send_to_all: ADDCMD test.battery.stop
   0.634864 send: Q1
   0.862632 read: (246.0 140.0 246.0 004 50.0 54.0 25.0 1000
   0.862677 send_to_all: DATAOK
   0.862793 dstate_init: sock /var/lib/nut/blazer_ser-munja open on fd 5
   0.862808 send_to_all: SETINFO driver.parameter.pollinterval 10
   0.862818 send_to_all: SETINFO device.mfr 
   0.862827 send_to_all: SETINFO device.model 
   0.862900 send: Q1
   1.090631 read: (246.0 140.0 246.0 003 50.0 54.0 25.0 1000
   1.090670 send_to_all: SETINFO ups.load 3
  10.871363 send: Q1
  11.098641 read: (246.0 140.0 246.0 005 50.0 54.0 25.0 1000
  11.098681 send_to_all: SETINFO ups.load 5


upsmon -D
Network UPS Tools upsmon 2.6.0
   0.00 UPS: munja@localhost (slave) (power value 1)
   0.000153 Using power down flag file /etc/killpower
   0.000261 debug level is '5'
   0.001301 Trying to connect to UPS [munja@localhost]
   0.002166 Logged into UPS munja@localhost
   0.002184 pollups: munja@localhost
   0.002197 get_var: munja@localhost / status
   0.002279 Poll UPS [munja@localhost] failed - Driver not connected
   0.002290 do_notify: ntype 0x0005 (COMMBAD)
   0.002297 Communications with UPS munja@localhost lost
   5.002588 pollups: munja@localhost
   5.002617 get_var: 

Re: [Nut-upsuser] Problem with blazer_ser/megatec when upgrading to 2.6.0 from 2.4

2011-04-28 Thread Arjen de Korte

Citeren Dushan Tcholich dus...@gmail.com:

[...]


 /lib64/nut/blazer_ser -D -a munja -i 10
Network UPS Tools - Megatec/Q1 protocol serial driver 1.51 (2.6.0)
   0.00 send_to_all: SETINFO driver.parameter.port /dev/ttyS0


Looks fine.

[...]


upsmon -D
Network UPS Tools upsmon 2.6.0
   0.00 UPS: munja@localhost (slave) (power value 1)
   0.000153 Using power down flag file /etc/killpower
   0.000261 debug level is '5'
   0.001301 Trying to connect to UPS [munja@localhost]
   0.002166 Logged into UPS munja@localhost
   0.002184 pollups: munja@localhost
   0.002197 get_var: munja@localhost / status
   0.002279 Poll UPS [munja@localhost] failed - Driver not connected
   0.002290 do_notify: ntype 0x0005 (COMMBAD)
   0.002297 Communications with UPS munja@localhost lost
   5.002588 pollups: munja@localhost
   5.002617 get_var: munja@localhost / status
   5.002758 Poll UPS [munja@localhost] failed - Driver not connected
   5.002771 do_notify: ntype 0x0008 (NOCOMM)
   5.002781 UPS munja@localhost is unavailable
  10.003015 pollups: munja@localhost
  10.003048 get_var: munja@localhost / status
  10.003191 Poll UPS [munja@localhost] failed - Driver not connected
  15.003280 pollups: munja@localhost
  15.003309 get_var: munja@localhost / status
  15.003450 Poll UPS [munja@localhost] failed - Driver not connected

What am I missing?


What is the output of 'upsd' in the syslog telling you? Note that when  
running in debug mode, a process will terminate as soon as you close  
the terminal it is running in or when you kill it with Ctrl-C.


Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)


___
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser