Citeren "Anton E. Panchenko" <p...@chernigovka.org>:
[...]
upsshed-cmd
#!/bin/sh
MSG="The UPS is running on battery about 2 minutes, doing force shutdown"
case $1 in
fsd)
logger -t upssched-cmd $MSG
/sbin/upsmon -c fsd
;;
*)
logger -t upssched-cmd "ERROR!! $0 Unrecognized command: $1"
;;
esac
Assuming the message is logged (and you thereby having confirmed that
indeed the 'fsd' timer is elapsed, the problem is that upssched will
run with the same UID as upsmon (that started this timer). In that
case, the command
/sbin/upsmon -c fsd
will also run as this user. So in order to test this, you must make
sure that the above command when running as a non-privileged user will
shutdown your system or you must run upsmon as a privileged user. You
might be able to do something similar by allowing this user to use
'sudo' for just this command. Choose your poison.
Best regards, Arjen
--