Hi Joel,

I believe AEE sells them as well,

jay

peltz power
On Nov 21, 2008, at 12:42 PM, Joel Davidson wrote:


Tyco makes solar labels. See 
www.tycoelectronics.com/AboutUs/news/getpdf.asp?id=1363&f=solar_labels_flyer_final.pdf

At least one reseller offers the labels. See 
http://store.altenergystore.com/Enclosures-Electrical-and-Safety/NEC-Compliant-Safety-Labels/NEC-Compliant-Grid-Tie-Safety-Labels/p6618/
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread Peter Parrish
The only thing I am aware of wrt to fused DC discos is the notion that PV
runs that penetrate a building shell need over current protection. The City
of Santa Monica used to (and may still) have this requirement.

 

The (non) issues as I understand them:

 

(1)   PV modules should be treated as any other independent source,
regardless of the fact that they are inherently current limited. It would be
straightforward to determine whether or not the wire used has the adequate
ampacity.

(2)   Inverters may be capable of back-feeding the PV array . Manufacturers
that continue to sell and market a specific inverter model, are usually
willing to write a letter to the effect that back-feeding will not occur.
The only mfgr that I know of that demurred is Sharp wrt their JH-3500, and
it is no longer sold in the US.

 

Of course the use of an unfused disco makes good sense, prior to penetrating
building shell. 

 

- Peter

 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of ASAP POWER!
2
Sent: Friday, November 21, 2008 10:47 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] DC Rating of Disconnects

 

In 2008, we have had to replace our standard Sq. D HU361RB used since our
beginnings, with the Sq. D H361RB (U stands for unfused).   Was there some
sort of code change NEC or CBC maybe that made most jurisdictions in So Cal
suddenly start requiring fused DC disconnects?  Typically, we fill the fused
Sq. D. box with 15A 5" fuses.

 

Peter D.

 

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of William
Miller
Sent: Friday, November 21, 2008 9:43 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC Rating of Disconnects

Peter:

I am resending, the first version inexplicably deleted some text:

An arc is created in the process of disconnecting any current under load.
DC circuits have an enhanced ability to sustain that arc.  PV circuits
exacerbate this problem as a short or load is disconnected because they can
sustain a short but the voltage rises drastically as a circuit is
disconnected.

This all justifies the added expense of a DC rated disconnect.  We use the
Square D HU361 without hesitation.  There are few alternatives available and
none with any significant cost savings.  In selecting a disconnect, a
design-build contractor must use the highest Voc possible. Make sure you are
entering the 690.7 table with the record low temperature for the location.

If we used a disconnect without the correct rating we would open ourselves
to unacceptable liability exposure and, worse yet, would not experience that
pleasant feeling one gets when you know you've done the job right.

William Miller


At 09:11 AM 11/21/2008, you wrote:

  _  

From: Peter Parrish [mailto:[EMAIL PROTECTED] 
Sent: Friday, November 21, 2008 9:10 AM
To: 'RE-wrenches'
Cc: 'Peter Parrish'
Subject: DC Rating of Disconnects
 
I am looking into using the PV Powered PVP2000 inverter for some small, low
voltage designs. The string Voc will be around 200 Vdc, worst case.
 
Since the PVP2000 doesnt come with a DC disconnect, I am wondered what
other wrenches who install the PVP2000 have been doing about this. I hate to
spend $150 on a 600 V AC/DC disco such as the SD HU361RB to provide the
means of disconnection. I believe that the 240 V AC discos such as the SD
DU221RB have no DC rating.
 
>From an academic point of view, I wonder why the smaller discos are not dual
rated, since we all know that the real-time voltage difference in a 240 V AC
system can be 41% greater than 240 V.
 
In any event, any Code-compliant solutions would be greatly appreciated.
 
- Peter

Peter T. Parrish, President

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC compliant solar labels

2008-11-21 Thread Geoff Greenfield


Ahhh yes... I love this NEC signage requirement.  It goes a long way toward 
re-assuring inspectors and others that the inverter does a reliable job 
disconnecting if the grid goes down.  I will put this at the top of my 690 
improvement list. 



Along the same lines: we oughta sell lightbulb base stoppers to keep all those 
electrons from leaking out of lamps without bulbs! 



;-)    Have great weekends all my fellow wrenches!  Its a cold but clear day 
here and I'm gonna go home and cut firewood and play guitar hero with my kids. 

For a brighter energy future, 

Geoff Greenfield 
Founder and CEO 
Third Sun Solar & Wind Power Ltd. 
340 West State Street, Unit 25 
Athens, OH 45701 

740.597.3111     Fax 740.597.1548 
www.Third-Sun.com 

Clean Energy - Expertly Installed 






- "Joel Davidson" <[EMAIL PROTECTED]> wrote: 
> 
> 
Tyco makes solar labels. See www. tyco 
electronics.com/AboutUs/news/getpdf.asp?id=1363&f= solar _ labels 
_flyer_final.pdf 

At least one reseller offers the labels. See 
http://store.altenergystore.com/Enclosures-Electrical-and-Safety/NEC-Compliant-Safety-Labels/NEC-Compliant-Grid-Tie-Safety-Labels/p6618/
 
> ___ List sponsored by Home Power 
> magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: 
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules 
> & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: 
> www.members.re-wrenches.org___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] NEC compliant solar labels

2008-11-21 Thread Joel Davidson
Tyco makes solar labels. See 
www.tycoelectronics.com/AboutUs/news/getpdf.asp?id=1363&f=solar_labels_flyer_final.pdf
 
At least one reseller offers the labels. See 
http://store.altenergystore.com/Enclosures-Electrical-and-Safety/NEC-Compliant-Safety-Labels/NEC-Compliant-Grid-Tie-Safety-Labels/p6618/___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grid-tie inverters & generators

2008-11-21 Thread I2P
 
In a message dated 11/20/2008 9:57:54 A.M. Pacific Standard Time,  
[EMAIL PROTECTED] writes:

It opens  when the genny is on) might be
easier than a NO relay on the grid-side.  Anyone do it this way?






Kelly, I would do this and sleep at night. 
 
Don
**One site has it all. Your email accounts, your social networks, 
and the things you love. Try the new AOL.com 
today!(http://pr.atwola.com/promoclk/10075x1212962939x1200825291/aol?redir=http://www.aol.com/?optin=new-dp
%26icid=aolcom40vanity%26ncid=emlcntaolcom0001)
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread Jeff Blick
If the inverter will not backfeed currents from the grid, and if you have
less than 3 strings I do not see why you would need to use fuses in the DC
disco (assuming 15 amp series fuse rating).  If you are at more than three
strings it seems to me that the fuses in the combiner would take care of the
fusing requirements.

 
 
Jeff Blick
PV installer
Sunlight Solar Inc.
4 NW Franklin
Bend, OR 97701
direct: 541-306-4196
fax: 541-322-1911
[EMAIL PROTECTED]
www.sunlightsolar.com
 
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Friday, November 21, 2008 11:04 AM
To: re-wrenches@lists.re-wrenches.org
Subject: RE-wrenches Digest, Vol 1, Issue 349

Send RE-wrenches mailing list submissions to
re-wrenches@lists.re-wrenches.org

To subscribe or unsubscribe via the World Wide Web, visit

http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
or, via email, send a message with subject or body 'help' to
[EMAIL PROTECTED]

You can reach the person managing the list at
[EMAIL PROTECTED]

When replying, please edit your Subject line so it is more specific
than "Re: Contents of RE-wrenches digest..."


When responding to posts within the Digest, be sure to restore the Subject:
line to the original, and please edit out any extraneous lines from the
quoted message.
 

Today's Topics:

   1. Re: DC Rating of Disconnects (ASAP POWER! 2)


--

Message: 1
Date: Fri, 21 Nov 2008 10:47:12 -0800
From: "ASAP POWER! 2" <[EMAIL PROTECTED]>
Subject: Re: [RE-wrenches] DC Rating of Disconnects
To: "'RE-wrenches'" 
Message-ID: <[EMAIL PROTECTED]>
Content-Type: text/plain; charset="us-ascii"

In 2008, we have had to replace our standard Sq. D HU361RB used since our
beginnings, with the Sq. D H361RB (U stands for unfused).   Was there some
sort of code change NEC or CBC maybe that made most jurisdictions in So Cal
suddenly start requiring fused DC disconnects?  Typically, we fill the fused
Sq. D. box with 15A 5" fuses.
 
Peter D.

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of William
Miller
Sent: Friday, November 21, 2008 9:43 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC Rating of Disconnects


Peter:

I am resending, the first version inexplicably deleted some text:

An arc is created in the process of disconnecting any current under load.
DC circuits have an enhanced ability to sustain that arc.  PV circuits
exacerbate this problem as a short or load is disconnected because they can
sustain a short but the voltage rises drastically as a circuit is
disconnected.

This all justifies the added expense of a DC rated disconnect.  We use the
Square D HU361 without hesitation.  There are few alternatives available and
none with any significant cost savings.  In selecting a disconnect, a
design-build contractor must use the highest Voc possible. Make sure you are
entering the 690.7 table with the record low temperature for the location.

If we used a disconnect without the correct rating we would open ourselves
to unacceptable liability exposure and, worse yet, would not experience that
pleasant feeling one gets when you know you've done the job right.

William Miller


At 09:11 AM 11/21/2008, you wrote:



  _  

From: Peter Parrish [mailto:[EMAIL PROTECTED] 
Sent: Friday, November 21, 2008 9:10 AM
To: 'RE-wrenches'
Cc: 'Peter Parrish'
Subject: DC Rating of Disconnects
 
I am looking into using the PV Powered PVP2000 inverter for some small, low
voltage designs. The string Voc will be around 200 Vdc, worst case.
 
Since the PVP2000 doesnt come with a DC disconnect, I am wondered what
other wrenches who install the PVP2000 have been doing about this. I hate to
spend $150 on a 600 V AC/DC disco such as the SD HU361RB to provide the
means of disconnection. I believe that the 240 V AC discos such as the SD
DU221RB have no DC rating.
 
>From an academic point of view, I wonder why the smaller discos are not
dual
rated, since we all know that the real-time voltage difference in a 240 V AC
system can be 41% greater than 240 V.
 
In any event, any Code-compliant solutions would be greatly appreciated.
 
- Peter

Peter T. Parrish, President

-- next part --
An HTML attachment was scrubbed...
URL:
<http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachme
nts/20081121/5ee8b648/attachment.html>

--

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrench

Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread ASAP POWER! 2
In 2008, we have had to replace our standard Sq. D HU361RB used since our
beginnings, with the Sq. D H361RB (U stands for unfused).   Was there some
sort of code change NEC or CBC maybe that made most jurisdictions in So Cal
suddenly start requiring fused DC disconnects?  Typically, we fill the fused
Sq. D. box with 15A 5" fuses.
 
Peter D.

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of William
Miller
Sent: Friday, November 21, 2008 9:43 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC Rating of Disconnects


Peter:

I am resending, the first version inexplicably deleted some text:

An arc is created in the process of disconnecting any current under load.
DC circuits have an enhanced ability to sustain that arc.  PV circuits
exacerbate this problem as a short or load is disconnected because they can
sustain a short but the voltage rises drastically as a circuit is
disconnected.

This all justifies the added expense of a DC rated disconnect.  We use the
Square D HU361 without hesitation.  There are few alternatives available and
none with any significant cost savings.  In selecting a disconnect, a
design-build contractor must use the highest Voc possible. Make sure you are
entering the 690.7 table with the record low temperature for the location.

If we used a disconnect without the correct rating we would open ourselves
to unacceptable liability exposure and, worse yet, would not experience that
pleasant feeling one gets when you know you've done the job right.

William Miller


At 09:11 AM 11/21/2008, you wrote:



  _  

From: Peter Parrish [mailto:[EMAIL PROTECTED] 
Sent: Friday, November 21, 2008 9:10 AM
To: 'RE-wrenches'
Cc: 'Peter Parrish'
Subject: DC Rating of Disconnects
 
I am looking into using the PV Powered PVP2000 inverter for some small, low
voltage designs. The string Voc will be around 200 Vdc, worst case.
 
Since the PVP2000 doesnt come with a DC disconnect, I am wondered what
other wrenches who install the PVP2000 have been doing about this. I hate to
spend $150 on a 600 V AC/DC disco such as the SD HU361RB to provide the
means of disconnection. I believe that the 240 V AC discos such as the SD
DU221RB have no DC rating.
 
>From an academic point of view, I wonder why the smaller discos are not dual
rated, since we all know that the real-time voltage difference in a 240 V AC
system can be 41% greater than 240 V.
 
In any event, any Code-compliant solutions would be greatly appreciated.
 
- Peter

Peter T. Parrish, President

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread Peter Parrish
Yes we have T-corrected the Voc. One of the nice things we have going for us
in the LA area, is the moderating influence of the ocean. 90% + of our
systems never see record cold temperatures below 14 def F.

 

You are correct about the Vdc rising upon disconnection (from Vmp to Voc)
and DC arcs being a different beast than AC arcs. It is perhaps this latter
reason which so few medium duty discos have a DC rating.

 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _  

From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of William
Miller
Sent: Friday, November 21, 2008 9:43 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC Rating of Disconnects

 

Peter:

I am resending, the first version inexplicably deleted some text:

An arc is created in the process of disconnecting any current under load.
DC circuits have an enhanced ability to sustain that arc.  PV circuits
exacerbate this problem as a short or load is disconnected because they can
sustain a short but the voltage rises drastically as a circuit is
disconnected.

This all justifies the added expense of a DC rated disconnect.  We use the
Square D HU361 without hesitation.  There are few alternatives available and
none with any significant cost savings.  In selecting a disconnect, a
design-build contractor must use the highest Voc possible. Make sure you are
entering the 690.7 table with the record low temperature for the location.

If we used a disconnect without the correct rating we would open ourselves
to unacceptable liability exposure and, worse yet, would not experience that
pleasant feeling one gets when you know you've done the job right.

William Miller


At 09:11 AM 11/21/2008, you wrote:



 
 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _  

From: Peter Parrish [mailto:[EMAIL PROTECTED] 
Sent: Friday, November 21, 2008 9:10 AM
To: 'RE-wrenches'
Cc: 'Peter Parrish'
Subject: DC Rating of Disconnects
 
I am looking into using the PV Powered PVP2000 inverter for some small, low
voltage designs. The string Voc will be around 200 Vdc, worst case.
 
Since the PVP2000 doesnt come with a DC disconnect, I am wondered what
other wrenches who install the PVP2000 have been doing about this. I hate to
spend $150 on a 600 V AC/DC disco such as the SD HU361RB to provide the
means of disconnection. I believe that the 240 V AC discos such as the SD
DU221RB have no DC rating.
 
>From an academic point of view, I wonder why the smaller discos are not dual
rated, since we all know that the real-time voltage difference in a 240 V AC
system can be 41% greater than 240 V.
 
In any event, any Code-compliant solutions would be greatly appreciated.
 
- Peter

Peter T. Parrish, President

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread William Miller

Peter:

I am resending, the first version inexplicably deleted some text:

An arc is created in the process of disconnecting any current under 
load.  DC circuits have an enhanced ability to sustain that arc.  PV 
circuits exacerbate this problem as a short or load is disconnected because 
they can sustain a short but the voltage rises drastically as a circuit is 
disconnected.


This all justifies the added expense of a DC rated disconnect.  We use the 
Square D HU361 without hesitation.  There are few alternatives available 
and none with any significant cost savings.  In selecting a disconnect, a 
design-build contractor must use the highest Voc possible. Make sure you 
are entering the 690.7 table with the record low temperature for the location.


If we used a disconnect without the correct rating we would open ourselves 
to unacceptable liability exposure and, worse yet, would not experience 
that pleasant feeling one gets when you know you've done the job right.


William Miller


At 09:11 AM 11/21/2008, you wrote:




Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED]

--
From: Peter Parrish [mailto:[EMAIL PROTECTED]
Sent: Friday, November 21, 2008 9:10 AM
To: 'RE-wrenches'
Cc: 'Peter Parrish'
Subject: DC Rating of Disconnects

I am looking into using the PV Powered PVP2000 inverter for some small, 
low voltage designs. The string Voc will be around 200 Vdc, worst case.


Since the PVP2000 doesn't come with a DC disconnect, I am wondered what 
other wrenches who install the PVP2000 have been doing about this. I hate 
to spend $150 on a 600 V AC/DC disco such as the SD HU361RB to provide the 
means of disconnection. I believe that the 240 V AC discos such as the SD 
DU221RB have no DC rating.


From an academic point of view, I wonder why the smaller discos are not 
dual rated, since we all know that the real-time voltage difference in a 
240 V AC system can be 41% greater than 240 V.


In any event, any Code-compliant solutions would be greatly appreciated.

- Peter

Peter T. Parrish, President
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread William Miller

Peter:

An arc is created in the process of disconnecting any current under 
load.  DC circuits have an enhanced ability to sustain that arc.  PV 
circuits exacerbate this problem as a short or load is disconnected because 
they can sustain a short but the voltage rises drastically as a circuit is 
disconnected.


This all justifies the added expense of a DC rated disconnect.  We use the 
Square D HU361 without hesitation.  There are few alternatives available 
and none with any significant cost savings.  In selecting a disconnect, a 
design-build contractor must use the highest Voc possible. Make sure you 
are entering the


If we used a disconnect without the correct rating we would open ourselves 
to unacceptable liability exposure and, worse yet, would not experience 
that pleasant feeling one gets when you know you've done the job right.


William Miller


At 09:11 AM 11/21/2008, you wrote:




Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED]

--
From: Peter Parrish [mailto:[EMAIL PROTECTED]
Sent: Friday, November 21, 2008 9:10 AM
To: 'RE-wrenches'
Cc: 'Peter Parrish'
Subject: DC Rating of Disconnects

I am looking into using the PV Powered PVP2000 inverter for some small, 
low voltage designs. The string Voc will be around 200 Vdc, worst case.


Since the PVP2000 doesn't come with a DC disconnect, I am wondered what 
other wrenches who install the PVP2000 have been doing about this. I hate 
to spend $150 on a 600 V AC/DC disco such as the SD HU361RB to provide the 
means of disconnection. I believe that the 240 V AC discos such as the SD 
DU221RB have no DC rating.


From an academic point of view, I wonder why the smaller discos are not 
dual rated, since we all know that the real-time voltage difference in a 
240 V AC system can be 41% greater than 240 V.


In any event, any Code-compliant solutions would be greatly appreciated.

- Peter

Peter T. Parrish, President



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread Kent Osterberg

Peter,

Many general duty safety switches, such as the Siemens GNF321R, are 
rated for 250 volts dc.  They usually require the use of two switch poles.


Kent Osterberg
Blue Mountain Solar



Peter Parrish wrote:
 

 


Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED]



*From:* Peter Parrish [mailto:[EMAIL PROTECTED]
*Sent:* Friday, November 21, 2008 9:10 AM
*To:* 'RE-wrenches'
*Cc:* 'Peter Parrish'
*Subject:* DC Rating of Disconnects

 

I am looking into using the PV Powered PVP2000 inverter for some small, 
low voltage designs. The string Voc will be around 200 Vdc, worst case.


 

Since the PVP2000 doesn’t come with a DC disconnect, I am wondered what 
other wrenches who install the PVP2000 have been doing about this. I 
hate to spend $150 on a 600 V AC/DC disco such as the SD HU361RB to 
provide the means of disconnection. I believe that the 240 V AC discos 
such as the SD DU221RB have no DC rating.


 

 From an academic point of view, I wonder why the smaller discos are not 
dual rated, since we all know that the real-time voltage difference in a 
240 V AC system can be 41% greater than 240 V.


 


In any event, any Code-compliant solutions would be greatly appreciated.

 


- Peter

Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED]


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] DC Rating of Disconnects

2008-11-21 Thread Peter Parrish
 

 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

  _  

From: Peter Parrish [mailto:[EMAIL PROTECTED] 
Sent: Friday, November 21, 2008 9:10 AM
To: 'RE-wrenches'
Cc: 'Peter Parrish'
Subject: DC Rating of Disconnects

 

I am looking into using the PV Powered PVP2000 inverter for some small, low
voltage designs. The string Voc will be around 200 Vdc, worst case.

 

Since the PVP2000 doesn't come with a DC disconnect, I am wondered what
other wrenches who install the PVP2000 have been doing about this. I hate to
spend $150 on a 600 V AC/DC disco such as the SD HU361RB to provide the
means of disconnection. I believe that the 240 V AC discos such as the SD
DU221RB have no DC rating.

 

>From an academic point of view, I wonder why the smaller discos are not dual
rated, since we all know that the real-time voltage difference in a 240 V AC
system can be 41% greater than 240 V.

 

In any event, any Code-compliant solutions would be greatly appreciated.

 

- Peter

Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
[EMAIL PROTECTED] 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] box fill calcs

2008-11-21 Thread Carl Hansen
I believe you would just determine the size of the J-Box based on the largest 
sized conduit entering and leaving the box.
Code: 314.28 A 1&2

 Carl Hansen___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] box fill calcs

2008-11-21 Thread Drake Chamberlin

At 05:40 AM 11/21/2008, you wrote:
I brought this subject up in class. Chuck says he doesn't think 
there's anything in the code about it. the closest thing I could 
come up with was clamps -- so you'd relate it to the largest 
conductor in the box. But I'm a baby too. i like over sized boxes. db


The Code doesn't cover every possible aspect.  The size of the 
splicing devices does not seem to be covered.  You could have a 
minimum sized junction box, and connect the wires with big blue wire 
nuts and have trouble getting it all in.


I'm also a believer in oversized boxes.  The code minimum size box is 
the smallest box that everything can be stuffed into.  Labor saved 
will usually be more than money spent on a bit more comfortable fit.




Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] box fill calcs

2008-11-21 Thread Cvsolar2
I brought this subject up in class. Chuck says he doesn't think there's 
anything in the code about it. the closest thing I could come up with was 
clamps -- 
so you'd relate it to the largest conductor in the box. But I'm a baby too. i 
like over sized boxes. db

Dan Brown
President
Foxfire Energy Corp.
Renewable Energy Systems 
(802)-483-2564
www.Foxfire-Energy.com
NABCEP #092907-44


**
One site has it all. Your email accounts, your 
social networks, and the things you love. Try the new AOL.com 
today!(http://pr.atwola.com/promoclk/10075x1212962939x1200825291/aol?redir=http://www.aol.
com/?optin=new-dp%26icid=aolcom40vanity%26ncid=emlcntaolcom0001)
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Shoes

2008-11-21 Thread mark
The Amish builders in our area swear by "Faded Glory" from Walmart.  
Cheap in price and best for traction, especially on steel roofs.
 
Mark
 

 Original Message Subject: [RE-wrenches] ShoesFrom: "Mark Frye" <[EMAIL PROTECTED]>Date: Thu, November 20, 2008 4:29 pmTo: "'RE-wrenches'" 
Any thoughts on the best type of shoe for working on comp shingle roof? 
Good traction, least wear and tear on shingles? 
Has anyone tried a felt soled fishing boot?   Mark Frye Berkeley Solar Electric Systems 303 Redbud Way Nevada City,  CA 95959 (530) 401-8024 www.berkeleysolar.com  

___List sponsored by Home Power magazineList Address: RE-wrenches@lists.re-wrenches.orgOptions & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:www.re-wrenches.org/etiquette.htmCheck out participant bios:www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] grid-tie inverters & generators

2008-11-21 Thread Tump
How close is the transfer panel from the main panel? If the distance is not
to far then actuate the relay (nc) from the generator source NOT the
utility. Generator running the relay is opened, only need to switch one leg
of the SMA stuff as the reduced  input voltage would keep it from
connecting.

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kelly
Keilwitz, Whidbey Sun & Wind
Sent: Thursday, November 20, 2008 12:31 PM
To: RE Wrenches listserve
Subject: Re: [RE-wrenches] grid-tie inverters & generators


Jay, Drake, Don, Jeff & Wrenches,

The relay seems like a reasonable solution. However, if the main panel is
entirely backed up by the genny, to power the relay from the grid (only)
requires a line-side tap, yes? Is there a simple solution that I¹m missing?

We have another, similar system completed, just waiting for 2009 to
commission. So, I'd like to know if it's really needed, and the best
procedure, before investing the time and cost to go back.

There must be many Wrenches who have encountered such generator backup
systems. Come on, how many of you, besides Don, have connected the inverter
to the gen-tran main panel (with no disconnection relay) without a problem?
Anyone else had a bad experience, like Jeff?


Thanks,
-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind, LLC
Renewable Energy Systems
NABCEP Certified PV Installer
987 Wanamaker Rd, 
Coupeville, WA 98239
PH & FAX 360-678-7131
[EMAIL PROTECTED]


On 11/19/08 9:21 PM, "Jay Peltz" <[EMAIL PROTECTED]> wrote:

> Hi Kelly
> 
> I think what happens if the inverter backfeeds the genny, the 
> generator voltage will go up, if it goes up enough, it will go outside 
> the window of the inverter and the inverter will drop out, voltage 
> will them return to normal, inverter will reconnect and repeat.
> 
> But I sure wouldn't want to fix the generator.  A relay powered from 
> the grid will take care of the problem.
> 
> jay
> 
> peltz power
___
> 
On 11/19/08 8:52 PM, "Drake Chamberlin"
<[EMAIL PROTECTED]>
 wrote:
> It is recommended to use a relay to disconnect the inverter when the 
> panel is being fed by the generator.
___ 

On 11/19/08 7:28 PM, "[EMAIL PROTECTED]" <[EMAIL PROTECTED]> wrote:
>That is the way I see it. I have tested systems with gens and had no  
>issues. The Sunny Boy would not boot to a gen source.  However, you can  
>understand what the official position must be. There exist gensets with  
>accuracy or it might just happen by chance. Low probability, but not 
>zero.
>  
> Don Loweburg
___
 
On 11/19/08 9:42 PM, "Jeff Clearwater, Village Power Design"
<[EMAIL PROTECTED]> wrote:
> 
> We burnt up a gen set's voltage regulator on an off-grid system sunny 
> island/sunny boy system when we took the sunny island's off-line but 
> didn't shut off the sunny boy.  So the SB backfed the genny and fried 
> the very expensive voltage regulator on a 30 KW system. SMA had us 
> install a relay to tell the SB to shut down as soon as the AC 
> reference from the SI was gone. Same situation as grid-tie really in 
> terms of your question.
> 
> Jeff



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org