Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread William Miller

Allan:

I whipped up three drawings that indicate three overload scenarios possible 
with incorrectly sized distribution equipment.  They are on our web site 
at:  http://millersolar.com/case_studies/case_studies.html  Click on Point 
of connection.  Click on any drawing to see a larger version.


I hope this helps with understanding the concept.

William Miller



At 06:19 PM 8/1/2009, you wrote:

William,
I have been following this back-and-forth thread and need you to please 
explain one thing:


Your 140A point makes perfect sense (from the point of 690.64 in requiring 
that the busbar to which both utility and PV feeds are connected. No 
question there. But you write: It is my understanding that if one is 
going to install a load side tape, the back feed calculations need to work 
for every link of the distribution system upstream to the meter. It seems 
to me that there's still no way to exceed main disconnect current rating.
   * 100A utility (using 100A subpanel main) + 40A PV tied into subpanel 
busbar = 140A, which is OK if the subpanel busbar is rated at least 125A 
(residential) or 150A (commercial).

   * 100A + 40A tapped into subpanel ahead of 100A main breaker:
   * maximum current passing through 100A main breaker = 100A. Adding 
40A of PV only reduces amount through conductors from main AC panel to 60A.

   * no AC load in daytime = 40A of current back to main AC load center
   * some subpanel loads in daytime reduces 2.b. above
   * At the main panel, maximum current flow through breaker feeding 
subpanel is 100A, as any PV reduces load at breaker. However, main panel 
must itself meet 690.64, as it's still possible to feed 40A of PV 
(daytime with no subpanel load) into main panel. So same busbar 
requirements apply in the main panel as in the subpanel. But that's all. 
The subpanel feeders don't need to be upsized.


What am I missing here, please?

Allan Sindelar
mailto:al...@positiveenergysolar.comal...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
http://www.positiveenergysolar.comwww.positiveenergysolar.com

--
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller

Sent: Saturday, August 01, 2009 6:11 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] down-sizing main breaker

Dick:

Your logic is correct but incomplete.  Consider it like this:  The buss 
bars in the service panel can handle 100 amps (they are rated for that 
amount).  The main breaker feeds 100 amps into that buss, maximizing it's 
capabilities.  If you feed an additional 40 amps into that buss bar, you 
have the potential of exceeding the ampacity of that buss assembly.  If no 
other loads are fed from that buss bar, there is no over current 
scenarios.  Say, however, someone puts more breakers on that buss bar and 
draws 140 amps from them.  100 amps comes in from the utility, 40 amps 
comes in from the PV and the buss is overloaded.


This is the scenario for which 690.64(B) was written.  This will occur 
only if the overload amperage is not drawn from a space on the buss bar 
between the utility feeder and the PV feeder.  If, however, the PV feeder 
breaker and the utility feeder are both on one end of the buss and the 
load is on the other end, then the loads are additive on the buss assembly.


Some want the code passage re-written to say that if the feeder is on one 
end of the bus assembly and the PV is on the other, there is no 
possibility of an overdraw on the buss bar and the installation is 
legal.  This has not happened yet.


William
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Surge protector update?

2009-08-02 Thread jason pozner
To piggy-back on the question, and also continue my grounding on a glacier
question is anyone familiar with point dissipators and have used them. Todd
mentioned Nott LTD  http://www.nottltd.com/lightning.html in my last string
and I have come acrooss Lightning Masters
http://www.lightningmaster.com/index.html  Both I believe use some form of
point dissipation.  They are suppose to take ambient static buildup and
dissipate it slower at high voltage levels keeping the current and damage to
equipment at a minimum.  Have anyone of you used these systems, or know much
about using them on an array, glacier, spaceship, marmot, midget, motorhome,
or the like?

Jay

Jay Pozner
Nunatak Alternative Energy Solutions
Crested Butte, CO
970 349-3432






On Sat, Aug 1, 2009 at 10:09 AM, Exeltech exelt...@yahoo.com wrote:


 Jay,

 Installing a part in a factory doesn't make a product ok.  Would be
 nice, but it doesn't work that way...


 I use UL here .. but it can be any Nationally Recognized Testing Lab
 (ETL, CSA, UL, etc)

 Any UL Listed product, or any UL Recognized part or sub-assembly must
 either use components that in of themselves are also Listed and/or
 Recognized to specific UL Standards, or prove during UL testing of the final
 product that any uncertified component(s) used within the product being
 tested fully meet the applicable Standard(s) for such parts.

 Failing that, the unit in question won't qualify for Listing/Recognition,
 and no UL (or equivalent lab) certification will be issued for that product
 by any Nationally Recognized Testing Lab.  UL. ETL. CSA.  etc...

 Just as all grounding components in a system must meet code, which requires
 the use of agency certified parts .. use of a non-certified part as a
 protective element is likely to get the system red-tagged, as Holt pointed
 out earlier in this thread.

 For notes .. not everyone is aware that agency certification refers to
 UL, ETL, CSA, and a number of other OSHA-certified Nationally Recognized
 Testing Labs.  Product approvals from any of these labs are equivalent,
 though they're not always treated as such by AHJs or others who aren't well
 informed on this issue.  Thankfully, the It must be UL attitude by AHJs
 and others is steadily fading as an issue.  Not gone - but fading...


 Dan


 --- On Sat, 8/1/09, jay peltz j...@asis.com wrote:

  Sure, if you install something electrical that is not UL,
  they can fail it. Even though that same part installed
  in a factory is OK.
 
  jay





 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread Allan Sindelar
William,

Wow - you're a master at whipping up drawings!

 

OK, I get the concept, and it's just as I described. The scenarios in
drawings one and two are OK as long as both busbars are rated 150A
(commercial) or 125A (residential. 

 

You then show that the reason for the upsized feeders is to handle a short.
But wait! Even if the short could produce 140A, as you have indicated, the
conductors will still not carry more than the 100A that they're rated to
carry. One would carry 100A from one panel and 40A from the other, Nowhere
would that conductor carry 140A, and the mate to it would carry at most 60A.
Increasing conductor size wouldn't change anything in that (or any)
scenario. So why would you have to increase conductor size?

 

Thanks, Allan 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Saturday, August 01, 2009 11:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] down-sizing main breaker

 

Allan:

I whipped up three drawings that indicate three overload scenarios possible
with incorrectly sized distribution equipment.  They are on our web site at:
http://millersolar.com/case_studies/case_studies.html  Click on Point of
connection.  Click on any drawing to see a larger version.

I hope this helps with understanding the concept.

William Miller



At 06:19 PM 8/1/2009, you wrote:



William,
I have been following this back-and-forth thread and need you to please
explain one thing:
 
Your 140A point makes perfect sense (from the point of 690.64 in requiring
that the busbar to which both utility and PV feeds are connected. No
question there. But you write: It is my understanding that if one is going
to install a load side tap, the back feed calculations need to work for
every link of the distribution system upstream to the meter. It seems to me
that there's still no way to exceed main disconnect current rating. 

1.  100A utility (using 100A subpanel main) + 40A PV tied into subpanel
busbar = 140A, which is OK if the subpanel busbar is rated at least 125A
(residential) or 150A (commercial). 
2.  100A + 40A tapped into subpanel ahead of 100A main breaker: 

1.  maximum current passing through 100A main breaker = 100A. Adding 40A
of PV only reduces amount through conductors from main AC panel to 60A. 
2.  no AC load in daytime = 40A of current back to main AC load center 
3.  some subpanel loads in daytime reduces 2.b. above 

3.  At the main panel, maximum current flow through breaker feeding
subpanel is 100A, as any PV reduces load at breaker. However, main panel
must itself meet 690.64, as it's still possible to feed 40A of PV (daytime
with no subpanel load) into main panel. So same busbar requirements apply in
the main panel as in the subpanel. But that's all. The subpanel feeders
don't need to be upsized. 


What am I missing here, please?
 
Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Saturday, August 01, 2009 6:11 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] down-sizing main breaker
 
Dick:

Your logic is correct but incomplete.  Consider it like this:  The buss bars
in the service panel can handle 100 amps (they are rated for that amount).
The main breaker feeds 100 amps into that buss, maximizing it's
capabilities.  If you feed an additional 40 amps into that buss bar, you
have the potential of exceeding the ampacity of that buss assembly.  If no
other loads are fed from that buss bar, there is no over current scenarios.
Say, however, someone puts more breakers on that buss bar and draws 140 amps
from them.  100 amps comes in from the utility, 40 amps comes in from the PV
and the buss is overloaded.

This is the scenario for which 690.64(B) was written.  This will occur only
if the overload amperage is not drawn from a space on the buss bar between
the utility feeder and the PV feeder.  If, however, the PV feeder breaker
and the utility feeder are both on one end of the buss and the load is on
the other end, then the loads are additive on the buss assembly.

Some want the code passage re-written to say that if the feeder is on one
end of the bus assembly and the PV is on the other, there is no possibility
of an overdraw on the buss bar and the installation is legal.  This has not
happened yet.

William

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:

Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread William Miller

Allan:

At the point of the short circuit, the amperage will exceed the rating of a 
100 amp feeder.  If the main panel had no extra breaker spaces, it could 
still be subject to a short circuit if, for example, a wrench is dropped 
into it.


I should add that I am not an electrical engineer nor am I trying to 
justify the codes that apply.  I am just trying to explain how I see  the 
codes are applied.  It is necessary to understand this to avoid incorrect 
system design and fruitless discussions with building officials.


William



At 07:22 AM 8/2/2009, you wrote:

William,
Wow – you’re a master at whipping up drawings!

OK, I get the concept, and it’s just as I described. The scenarios in 
drawings one and two are OK as long as both busbars are rated 150A 
(commercial) or 125A (residential.


You then show that the reason for the upsized feeders is to handle a 
short. But wait! Even if the short could produce 140A, as you have 
indicated, the conductors will still not carry more than the 100A that 
they’re rated to carry. One would carry 100A from one panel and 40A from 
the other, Nowhere would that conductor carry 140A, and the mate to it 
would carry at most 60A. Increasing conductor size wouldn’t change 
anything in that (or any) scenario. So why would you have to increase 
conductor size?


Thanks, Allan

--
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller

Sent: Saturday, August 01, 2009 11:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] down-sizing main breaker

Allan:

I whipped up three drawings that indicate three overload scenarios 
possible with incorrectly sized distribution equipment.  They are on our 
web site at:  http://millersolar.com/case_studies/case_studies.html  Click 
on Point of connection.  Click on any drawing to see a larger version.


I hope this helps with understanding the concept.

William Miller
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread Richard L Ratico
Wlliam,

If there were to be a short circuit in the feeder or the main service panel (
the one with no extra breaker spaces ), the solar's maximum 50 amp contribution
would be about the last thing to be concerned about. A short is going to result
in perhaps 1000s of amps coming from the grid into the short. The service 100
amp breaker will trip immediately and clear the fault. The inverter will lose
the grid and drop offline. End of story.

Dick

--- You wrote:
Allan:

At the point of the short circuit, the amperage will exceed the rating of a 
100 amp feeder.  If the main panel had no extra breaker spaces, it could 
still be subject to a short circuit if, for example, a wrench is dropped 
into it.

I should add that I am not an electrical engineer nor am I trying to 
justify the codes that apply.  I am just trying to explain how I see  the 
codes are applied.  It is necessary to understand this to avoid incorrect 
system design and fruitless discussions with building officials.

William



At 07:22 AM 8/2/2009, you wrote:
William,
Wow $F6 you$E2re a master at whipping up drawings!

OK, I get the concept, and it$E2s just as I described. The scenarios in 
drawings one and two are OK as long as both busbars are rated 150A 
(commercial) or 125A (residential.

You then show that the reason for the upsized feeders is to handle a 
short. But wait! Even if the short could produce 140A, as you have 
indicated, the conductors will still not carry more than the 100A that 
they$E2re rated to carry. One would carry 100A from one panel and 40A from 
the other, Nowhere would that conductor carry 140A, and the mate to it 
would carry at most 60A. Increasing conductor size wouldn$E2t change 
anything in that (or any) scenario. So why would you have to increase 
conductor size?

Thanks, Allan

--
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Saturday, August 01, 2009 11:13 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] down-sizing main breaker

Allan:

I whipped up three drawings that indicate three overload scenarios 
possible with incorrectly sized distribution equipment.  They are on our 
web site at:  http://millersolar.com/case_studies/case_studies.html  Click 
on Point of connection.  Click on any drawing to see a larger version.

I hope this helps with understanding the concept.

William Miller
__
--- end of quote ---
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread Richard L Ratico
William,

You may well find inspectors and others who will agree with you on this. I
remain firmly unconvinced. Yes, the code may be taken literally. . . . .and
also, sometimes, be taken out of context. I believe you are doing that here. It
is impossible to use words in such an airtight manner that they cannot be
misinterpreted. The NEC is riddled with wording that often serves mostly to
muddy the waters. 

I truly respect your desire and record of doing things safely and professionally
to the highest standards, or if you deem those standards inadequate, to improve
on them yourself.
As regards our discussion here, I respectfully suggest you speak with the
electrical inspector or AHJ, before you bid, so you don't include line items
that may not be required. Then you may decide if you wish to include them in
your bid anyhow. Or not.

Thanks for your sincere concern that things be done well. 
I've got to get back to work.

Dick


--- You wrote:
 My goal is to interpret the code such that my designs 
are unassailable by building officials.  I don't want unpleasant surprises 
after I have signed a contract and begun work for a fixed price.
--- end of quote ---
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] down-sizing main breaker

2009-08-02 Thread William Miller

Dick:

I do not desire to find building official who insist on a strict 
interpretation of the code, but it is a reality in our jurisdictions.  We 
have to be pro-active and know the code better than they do, or we lose 
money when we are assessed corrective actions that increase our 
costs.  Bruce is a living example of this (I think I incorrectly called him 
Brian, sorry).  I hope our discussion and Bruce's experience is a lesson 
for other wrenches.  This is, after all, the purpose of this forum.


Thanks for the kind words. It is a pleasure talking shop with you.

Sincerely,

William Miller




At 02:47 PM 8/2/2009, you wrote:

William,

You may well find inspectors and others who will agree with you on this. I
remain firmly unconvinced. Yes, the code may be taken literally. . . . .and
also, sometimes, be taken out of context. I believe you are doing that 
here. It

is impossible to use words in such an airtight manner that they cannot be
misinterpreted. The NEC is riddled with wording that often serves mostly to
muddy the waters.

I truly respect your desire and record of doing things safely and 
professionally
to the highest standards, or if you deem those standards inadequate, to 
improve

on them yourself.
As regards our discussion here, I respectfully suggest you speak with the
electrical inspector or AHJ, before you bid, so you don't include line items
that may not be required. Then you may decide if you wish to include them in
your bid anyhow. Or not.

Thanks for your sincere concern that things be done well.
I've got to get back to work.

Dick
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org