[RE-wrenches] PENTAMETRIC

2010-01-08 Thread i2p

Input appreciated.

How well does the Pentametric work as a generator control. The spec 
sheet states a control relay based on % charged is available. Any 
experience using the Pentamatic as a gen start control. Does this 
yield better battery control than voltage based approach?


Thanks for any field experience on this control.

Don Loweburg
Offline Solar
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread Joel Davidson
We worked on dozens of commercial PV systems in Southern California Edison 
(SCE), Los Angeles Department of Water  Power (LADWP), and San Diego Gas  
Electric (SDGE) territories. We installed Xantrex, SMA, and SatCon 
inverters and measured power factor on both the grid and the inverters. In 
every case, inverter power factor was 1. In almost every case LADWP's power 
factor was less than 1 and in older parts of Los Angeles power factor was 
often 0.75. SCE and SDGE generally has pretty good power factors. In 
general, PV inverters do not worsen grid power factor. In general, newer 
sections of the grid are better designed and better managed than older grid 
sections. When utility companies or anyone says PV causes grid problems, ask 
for proof.

Joel Davidson

- Original Message - 
From: Darryl Thayer daryl_so...@yahoo.com

To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, January 06, 2010 9:39 PM
Subject: Re: [RE-wrenches] Power Factor and Grid Tied PV


I recently spoke with an inverter manufacture and I left with the following 
opinion.  Normally the inverter takes the unity power factor load and leaves 
the reactive load.  making the power factor worse.  However the power factor 
could be corrected by the inverter, However this would add cost to the 
inverter and would not appear to have value to the solar industry.  There 
are variable reactance devices existing that can correct power factor, is 
there need for another device?


Darryl



Hello Wrenches,

Commercial power customers often are penalized for low
power factors.
Looking for other info I came across this article, which
seems to
cover the subject from an academic standpoint.
http://tinyurl.com/ye5pzrw Does anyone
have real world data which
might shed light on the impact of a DGT PV system on power
factor.

With Regards
Carl Adams
SunRock Solar, LLC.
___





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Best angle - direct grid tie

2010-01-08 Thread David Brearley
Great format for an integrator and its staff. Thanks for sharing, Mike.

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com

On 1/7/10 1:26 PM, Michael Kelly m...@solarflair.com wrote:

 Drake,
  
 I did an analysis for optimum conditions based on tilt and azimuth a while ago
 for our area around Boston.  I did it in such a way as any combination of tilt
 and azimuth gives you % of optimum conditions.  See attached.  All of the data
 was from PVWatts simulations.  Maybe you can make one for your area when you
 have some free time.
  
 - Mike 
 
 --
 Michael Kelly
 Project Manager / Project Engineer
 NABCEP Certified Solar PV Installer 
 
 SolarFlair Energy, Inc.
 11 Mayhew Street
 Framingham, MA 01702
 Direct Mobile: 617-899-9840
 Main Phone: 508-293-4293
 Main Fax: 508-293-4003
 m...@solarflair.com
 
 
 On Wed, Jan 6, 2010 at 9:48 AM, Drake Chamberlin
 drake.chamber...@redwoodalliance.org wrote:
 Thanks for all of the excellent advice regarding the best tilt angle.  It is
 a real privilege to be a part of, and have access to the incredible resource
 of the knowledge and experience represented by this list.
 
 It looks like a 30 degree angle will work fine for 39 degrees N.  This
 corresponds well with the Unirac U-LA, pre engineered designs. 
 
 Drake 
 
 
 
 Drake Chamberlin
 Athens Electric
 OH License 44810
 CO License 3773
 NABCEP TM  Certified PV Installer
 Office - 740-448-7328
 Mobile - 740-856-9648
 
 
 





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] To Megger or not to Megger

2010-01-08 Thread wes kennedy
Hi Bill,

I wanted to follow up on your results finding a ground fault with a lower 
resolution megger. 
    
Do you think the .1MOhm meters will work in field applications? 

Do you know of any .001MOhm meters like the old 1520?

I have taken a  position with a cadtel mfgr as their field application 
engineer.  I hope to be using your consulting services if I get over my head. 

Thanks and Happy New Year!

-Wes Kennedy

303-653-3073

--- On Tue, 4/28/09, Bill Brooks billbroo...@yahoo.com wrote:

From: Bill Brooks billbroo...@yahoo.com
Subject: Re: [RE-wrenches] To Megger or not to Megger
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date: Tuesday, April 28, 2009, 11:39 AM




 
 






Dave, 

   

The issue is definitely resolution. The cool thing about the
Fluke 1520 is that it goes down to 0.001MOhms (1000 Ohms). That is the
resolution you are looking for. Neither of the current Flukes go low enough.
That is why I’m going into the field later this week to see how a 0.1MOhm
meter stacks up to finding faults—I have an array with a pesky fault that
should make it fun. 

   

Many arrays will ring out as a faulted array when, in fact,
everything is fine. This is especially true of a-Si arrays with low quality
glass. They are very leaky. I’ll keep looking and report back on a
recommendation for Christmas shopping. 

   

Just to add punctuation to this thread, I always recommend that
contractors megger their arrays, because it has saved my butt several times.
Also, with exterior wiring systems it is even more important. The problem in
the early days is that people would whine about the $600-$1000 price tag. In my
opinion, that argument is gone. With contractors routinely putting down $1400
for a SunEye, the value of a good megger is similar and costs less. 

   

Bill. 

   





From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David
Palumbo

Sent: Tuesday, April 28, 2009 7:59 AM

To: gilliga...@gmail.com; 'RE-wrenches'

Subject: Re: [RE-wrenches] To Megger or not to Megger 





   

Matt, 

   

“Muggering”, I think that will catch on. The last
post, I think, ol’ Uncle Bill Brooks (4/13/09 8:17 PM) had on this topic
raised a concern about “not having enough resolution in the low impedance
area. PV arrays can have an impedance to ground of a slow as 2kOhms. A
resolution of 0.1MOhms will likely not cut it.” Bill went on to say that
he had bought a cheaper meter to test out “for fun”.  Some of
us do enjoy “muggering around”. 

   

So my question is.  Do  the Fluke 1503’s and
1507’s have enough resolution in the low range?  

   

Dave 

   





From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Matt
Lafferty

Sent: Tuesday, April 28, 2009 9:56 AM

To: 'RE-wrenches'

Subject: Re: [RE-wrenches] To Megger or not to Megger 





   

RE: Suggested replacements for Fluke 1520 and pricey
meters... Good News below! 

  

Another Wrench sent me a note off-list last night, asking how much
a muggering would cost. Here's what I sent him: 

  

When I got that 1520 it was just over $600. I just
checked online and find that it's a discontinued item... Bummer!  

  

Fluke recommends the 1587 or the 1507 or the 1503. They also
mention the 1577, but it's an ugly stepsister, or maybe a retarded adopted
relative, to the 1587.  

  

The 1587 is basically a multimeter that also has a TEST button to
discharge a high voltage shock into the sample under test... It runs about $620
from standard distributors. 
http://us.fluke.com/usen/products/Fluke+1587+1577.htm?catalog_name=FlukeUnitedStates 
 You
can get it for $522 here:  

http://www.testequipmentdepot.com/fluke/megohmmeters/1577_87.htm  NOTE: It
does not test at 10A in DMM mode which means it wouldn't be able to test
short-circuit current in strings. Don't bother with the 1577!  

  

The 1507  1503 are more robust equipment. You can check them
out here: 
http://us.fluke.com/usen/products/features.htm?cs_id=35391(FlukeProducts)category=HMA(FlukeProducts) 
While they do measure AC  DC Voltages to 600V as well as some lower ohm
 continuity work, they are really more tailored to being a megger. The
1503 will suffice for most of what I expect you will get into, but there are
some features on the 1507 that might make it worth considering. Mind you, I
haven't looked at at price on either yet, so that last comment may just be
noises coming out my ass.  

  

The 1507 has a Compare function which basically sets up a Pass/Fail
value so you can quickly run through repeated tests. This would be useful for
doing larger systems where you are testing dozens or hundreds of circuits at a
time. For my purposes, I want my guys to think a little more than Buzz =
OK and I want them to write an actual tested value down on a piece of
paper so this is not a big plus to me. 

  

The 1507 also does Polarization Index and Absorption Ratios. These
are more advanced 

Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread Kent Osterberg




Marco,

Three components of power delivered by the utility company: Watts,
volt-amps-reactive (VAR), and apparent power or volt-amps (VA). Power
factor is the ratio of the watts to the volt-amps. PF = Watts/VA.

To see how this works: draw a right triangle with 8 kW as the
horizontal leg, 6 kVAR as the vertical leg, and 10 kVA as the
hypotenuse. The power factor is 8 kW/10 kVA = 0.8. Now put in a 4-kW
solar system. The 6 kVAR reactive load doesn't change So the solar
system reduces the real power delivered by the utility by 50%, the
reactive power by 0%, and the apparent power by 28%. The power factor
afterwards is PF = 4 kW/7.21 kVA = 0.55. The power factor did get
worse!  To see how that all works just draw a new hypotenuse starting
from the midpoint of the 8-kW horizontal leg. Hardly seems worthy of a
paper. But the utility doesn't like to supply power for a load with a
power factor less than 0.8 because the out of phase current still
causes I-squared x R losses or line losses. 


Joel,

The utility company isn't responsible for the power factor. The
customers' loads determine the power used and the power factor. The
utility company is responsible for the power quality, which is really
poor in lots of locations.

Kent Osterberg
Blue Mountain Solar, Inc.



Marco Mangelsdorf wrote:

  According to an article, written by a utility engineer on O'ahu, PF can be
worsened at the site where a substantial PV system is located.

If there is a poor or wavering PF due to an abundance of inductive loads at
a particular site, having a large inverter, in relation to the overall power
consumption of the facility, can actually make the PF worse.

I can track down that piece for anyone interested.

Marco
ProVision Solar

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Joel
Davidson
Sent: Thursday, January 07, 2010 5:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Power Factor and Grid Tied PV

We worked on dozens of commercial PV systems in Southern California Edison 
(SCE), Los Angeles Department of Water  Power (LADWP), and San Diego Gas  
Electric (SDGE) territories. We installed Xantrex, SMA, and SatCon 
inverters and measured power factor on both the grid and the inverters. In 
every case, inverter power factor was 1. In almost every case LADWP's power 
factor was less than 1 and in older parts of Los Angeles power factor was 
often 0.75. SCE and SDGE generally has pretty good power factors. In 
general, PV inverters do not worsen grid power factor. In general, newer 
sections of the grid are better designed and better managed than older grid 
sections. When utility companies or anyone says PV causes grid problems, ask

for proof.
Joel Davidson

- Original Message - 
From: "Darryl Thayer" daryl_so...@yahoo.com
To: "RE-wrenches" re-wrenches@lists.re-wrenches.org
Sent: Wednesday, January 06, 2010 9:39 PM
Subject: Re: [RE-wrenches] Power Factor and Grid Tied PV


I recently spoke with an inverter manufacture and I left with the following 
opinion.  Normally the inverter takes the unity power factor load and leaves

the reactive load.  making the power factor worse.  However the power factor

could be corrected by the inverter, However this would add cost to the 
inverter and would not appear to have value to the solar industry.  There 
are variable reactance devices existing that can correct power factor, is 
there need for another device?

Darryl


  
  
Hello Wrenches,

Commercial power customers often are penalized for low
power factors.
Looking for other info I came across this article, which
seems to
cover the subject from an academic standpoint.
http://tinyurl.com/ye5pzrw Does anyone
have real world data which
might shed light on the impact of a DGT PV system on power
factor.

With Regards
Carl Adams
SunRock Solar, LLC.
___

  
  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
No virus found in this incoming message.
Checked by AVG - www.avg.com 
Version: 9.0.725 / Virus Database: 270.14.129/2606 - Release Date: 01/07/10
21:35:00


[RE-wrenches] Xantrex XW4548 noise problem

2010-01-08 Thread ryan
I have a customer that we installed a Xantrex XW4548 on a Midnite 
Epanel. He has 3kw of pv and 400ah of lead acid battery's. The issue is 
he feels the inverter is to noisy. The inverter is hung in a garage on a 
plywood wall that is 2 by 6 constructed with fiberglass and then drywall 
on the house side. The XW is fairly noisy a lot louder then the SW or 
SW+ series and a call to Xantrex got me a response that the transformer 
needs about 30 days of cycling to seat the windings and it will quite 
right down. So has any one else noticed the XW being extra loud? Has 
anyone noticed the XW quite down after 30 days? And if this noise is 
normal what would everyone recommend for a cushion to help keep the 
noise out of the house? I had thought of a sheet of 1 inch foam and then 
another layer of plywood but unsure if that would be worth the effort?

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread swingjunkie

Thanks to all who responded,

The article Marco references, is the one referenced in the tinyurl in my  
original post. I did not find anything of significance in the previous  
Solar Pro issues. Based on the responses it seems there is no good data out  
there to answer the question posted. This may be due to


1) the fact that PV systems are not being installed in commercial  
facilities with large reactive loads
2) those facilities are not penalized for PF therefor the question is  
irrelevant to those system owners
3) the PV systems installed in such facilities are small with respect to  
the overall facilities load and any negative impact on PF is insignificant


Cheers
Carl
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Power Factor and Grid Tied PV

2010-01-08 Thread boB Gudgel

swingjun...@gmail.com wrote:

Thanks to all who responded,

The article Marco references, is the one referenced in the tinyurl in 
my original post. I did not find anything of significance in the 
previous Solar Pro issues. Based on the responses it seems there is no 
good data out there to answer the question posted. This may be due to


1) the fact that PV systems are not being installed in commercial 
facilities with large reactive loads
2) those facilities are not penalized for PF therefor the question is 
irrelevant to those system owners
3) the PV systems installed in such facilities are small with respect 
to the overall facilities load and any negative impact on PF is 
insignificant


Cheers
Carl
  


I don't think there is anything to be concerned about if the PF goes 
down because a grid tie inverter is helping
to support the real power loads.  The I-squared-R losses won't get any 
larger for the utility.  I think it's just
because the Numerator of   Watts / VAR goes down, and the denominator 
staying the same that is

making the measure Power Factor measurement go down.

Also, I believe that this is only for current source inverters, which 
accounts for most GT inverters today...
An older SW inverter,  say, (voltage source) would actually supply VARs 
to the system and probably

wouldn't change the measured PF to the utility very much, if at all.

My 2 cents for today.
boB











___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org