Re: [RE-wrenches] Low grid voltage fix

2010-12-20 Thread Peter Parrish
No one should put up with grid voltages out of range. Immediately inform
your utility: tell them where, when and how often you measured (or your
inverter registered) the out of range voltages. It turns out that you are
doing them a favor and they often appreciate the information.

What we measure with a DMM is an average of a second or so, and there are
short term transients on top of this average that often are as much as +/- 5
Volts. Since inverters measure and respond on the order of 10 milliseconds,
they can provide a means of assessing the health of the grid, which goes
beyond DMM measurements.

A couple of stories:

We responded to a bad inverter call where the inverter in question kept
shutting down in the AM. We measured Vac = 252 V around 10 AM pretty
consistently, but the transients kept taking out the inverter. SCE traced
the problem to a nearby firm that was throwing a lot of transients onto the
grid from their equipment.

At our home office, we had our inverter trip a couple of times (thanks to a
TED monitor, we saw it happen in real time) and we called LADWP. To their
credit, they had a technician out THE SAME DAY. They also called us the
following day to say that they looked into the situation and discovered that
they had recently bumped the voltage in our neighborhood, and consequently
backed it off a bit. We then got a call a couple of days later to inquire if
everything was okay (it was). I may be critical of some of the things LADWP
does, but in this case I was very impressed.

As for a high or low (but still compliant) average voltage, the utilities
constantly adjust the taps on their distribution transformers, sometimes
for seasonal reasons and sometimes for changing demand (imagine a bunch of
apartments complexes being built in a previously single family dwelling
neighborhood).

Again, don't be shy. If (a) your inverters are shutting down and indicating
out of range grid voltages or (b) you measure Vac within five volts or so of
264 or 216 V, let your utility know.

- Peter

 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of frenergy
Sent: Sunday, December 19, 2010 4:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Low grid voltage fix

Joel,

Unrelated, mostly.  I got a call from a customer a few weeks ago 
that was claiming his inverter had failed working.  When I arrived it was in

fact not working and gave a code that the grid voltage was too high.  I 
called Fronius and they said they sometimes have had to replace a card to 
fix this sometimes, but also suggested that I check the grid voltage first, 
just in case.

I was a bit surprised to find 270 VAC L-L, 135VAC L-Gnd.  Out of 
disbelief, I checked it with another meter and got the same readings.  This 
was PGE, NE Ca.  Service dude came at customer's request and claimed the 
voltage reg was not adjusted properly. Problem fixed.

Bill

Feather River Solar Electric
4291 Nelson St.
Taylorsville, CA  95983
530-284-7849/6544 fax


- Original Message - 
From: Joel Davidson joel.david...@sbcglobal.net
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Sunday, December 19, 2010 9:24 AM
Subject: [RE-wrenches] Low grid voltage fix


 Wrenches,

 It's Christmas time again in Southern California Edison (SCE) territory 
 which means low insolation and high regional electric consumption. Every 
 night SCE voltage drops to around 105 VAC or lower. Our grid-tie SW4048 
 inverter sees SCE's low voltage as a brownout and switches to autonomous 
 mode which is normal. However, we have only 4 kWh of battery storage so 
 the combination of nightly brownouts and a series of cloudy days 
 eventually depletes our battery bank causing the inverter to do a 
 low-voltage shut down which is normal. Power goes off in our home and we 
 have to switch over to SCE power, reset the inverter, and wait until the 
 battery bank is recharged. How do we set the SW4048 to accept as low as 
 100 VAC from the grid before switching to autonomous mode?

 Joel Davidson
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:

Re: [RE-wrenches] Battery based hydrogen incidents

2010-12-20 Thread Nick Soleil
 Robb Cary was dealing with a lot of large scale telecomm systems with CD 
Technologies, so his scary photos were probably not from solar projects, (if 
that is any comfort!)  He spoke of some projects with 50,000 2V industrial 
cells.  I have worked with him for a long time and served on the board of Solar 
Sebastopol with him 5-6 years ago.  I too have lost touch.  I tried to reach 
him 
four or five years ago but his office said that he was retired and his cell 
number was disconnected.

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: Darryl Thayer daryl_so...@yahoo.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wed, December 15, 2010 9:14:15 AM
Subject: Re: [RE-wrenches] Battery based hydrogen incidents


Yes they happen, Robb Cary of Battery Testing Co. has some frightening photos.  
I have lost contact with him however.  I have had an experiance, but I did not 
take pictures.  When you find the top of the battery and or battery enclousure 
blowen to smitherens it was a hydrogen explosion.  Sorry I am on road today, 
would love to comment more.  maybe later
Darryl

--- On Wed, 12/15/10, Warren Lauzon war...@wind-sun.com wrote:


From: Warren Lauzon war...@wind-sun.com
Subject: Re: [RE-wrenches] Battery based hydrogen incidents
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Wednesday, December 15, 2010, 11:05 AM


 
In the 30+ years that we have been in the solar business, we have never seen 
or 
even heard of a single one.
  
From: Dana 
Sent: Wednesday, December 15, 2010 9:10 AM
To: 'RE-wrenches' 
Subject: [RE-wrenches] Battery based hydrogen incidents
  Ken – 
  
To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the 
fan 
into a 4” header with a matching 2.5” inlet as far away on the lowest portion 
of 
the battery box.
 
 
In 22+ years in off grid installations I have yet to see or even hear of one 
hydrogen explosion. I get repeatedly asked why we have to go to the efforts we 
go to for box and venting. I am not able to provide even one incident that I 
have heard rumor of. 

  
Q - How many battery based hydrogen incidents have happened in our collective 
experience? 

  
  
  
Dana Orzel
Great Solar Works, Inc 
E - d...@solarwork.com 
V - 970.626.5253 
F - 970.626.4140 
C - 970.209.4076 
web - www.solarwork.com 
  
Responsible Technologies for Responsible People since 1988 
Do not ever belive anything, but seriously trust through action. 
  
From:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Tuesday, December 14, 2010 12:07 PM
To: Wrenches
Subject: [RE-wrenches] Battery Venting
  
Fellow Wrenches,

The discussion about battery venting reminds me of a useful and inexpensive 
program, BattMV, for determining ventilation requirements per EN-50272.  
EN-50272 is a European standard used to determine how much air flow is needed 
for a room, I don't know of a equivalent standard used in the U.S.  It takes a 
surprising amount of ventilation.  For a 400-AH 48-volt L16 bank charged at 
57.6 
volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%.  A 
12-volt 
Zephyr vent is good for about 5 CFM!   If you think you are venting enough, 
take 
some time and study this issue.

Kent Osterberg
Blue Mountain Solar 


 ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


Northern Arizona Wind  Sun - Electricity from the sun since 1979

Online Solar Store
Free Solar Discussion Forum

-Inline Attachment Follows-


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 



  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette: