Re: [RE-wrenches] 10A Charge / load controller

2011-01-23 Thread bob ellison
>From memory it seems that the max voltage listed in the manual for the Sun 
>Saver MPPT is 35 volts but I don’t have it handy.

 

Bob Ellison

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Starlight 
Solar, Larry Crutcher
Sent: Friday, January 21, 2011 8:38 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 10A Charge / load controller

 

I have had failures with the Sunsaver MPPT. I have used them with a single 
Sanyo module in small battery systems. Perhaps they just can't handle the 50.9 
Voc.

 

Larry

Starlight Solar Power Systems

- Original Message - 

From: Maverick Brown [Maverick Solar]   

To: RE-wrenches   

Sent: Thursday, January 20, 2011 5:38 PM

Subject: Re: [RE-wrenches] 10A Charge / load controller

 

Try SunSaver MPPT. 

15 amps, MPPT and load control (or light) control

 

Use the MSC to connect the controller to your PC and adjust many settings and 
get log data. 

 

We use a lot of them and have had very few issues. 


Thank you, 

 

Maverick

 

 

Maverick Brown

BSEET, NABCEP Certified Solar PV Installer ®

President & CEO

Maverick Solar Enterprises, Inc.

Office: 512-919-4493

Cell:512-460-9825

 

Sent from an iPhone. 


On Jan 20, 2011, at 5:37 PM, "Jason Szumlanski"  wrote:

I’m looking for a ~10A charge controller for a 12V battery with adjustable LVD 
that goes up to at least 12V. Priorities in order are:

1.   Small in size

2.   Good

3.   Cheap

The best I can come up with now is the Xantrex C12. Looking for alternatives. 
Recommendations?

Jason Szumlanski

Fafco Solar

 
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


  _  


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Thermal question

2011-01-23 Thread penobscotsolar
I have always bought the El Cid pumps directly from the manufacturer. Ivan
Labs, Jupiter FL
(561) 747-5354

Daryl



> 
> 
>   
>
> 
>   
>   
> Wrenches,
> Who is a good wholesale source for El-Sid DC circulator pumps,
> preferably who also carries replacement drivers?
> Who has been a good source for thermal components and materials in
> general?
> Thanks,
> Allan
> -- 
>   
>   
>   
>   
>   
>   
>   
> 
> 
>   
>  style="">Allan style=""> Sindelar
> mailto:al...@positiveenergysolar.com";
>   target="_blank"> class="il">Allan@positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> http://www.positiveenergysolar.com/";
>   target="_blank">www.positiveenergysolar.com
>   
> 
>   
> 
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Male Whip follow-up

2011-01-23 Thread Nick Soleil
Hello Eric:
Would you please provide a reference to the literature where Enphase says, 
"using a cut extension cable will void the warranty of the entire  
installation."  I didn't see anything in the installation manual.  Also, 
Enphase 
did recommend the application to me.  It was actually pretty easy to make the 
connections without 'crossing phases.'
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:707-769-9037





From: Eric Thomas 
To: re-wrenches@lists.re-wrenches.org
Sent: Sun, January 23, 2011 10:29:08 AM
Subject: [RE-wrenches] Male Whip follow-up


As a (serious) side note, EnPhase says using a cut extension cable will void 
the 
warranty of the entire installation. This is due to the inconsistant color 
coding of the extension cables and whips. The danger of crossing phases within 
the same circuit. Best (and only acceptable) practice is to parallel sub 
arrays. 

Eric


  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Thermal question

2011-01-23 Thread Jonathan Hill
Try AEE 

Jonathan Hill
Solar applications engineer
Sierra Solar Systems
888-ON-SOLAR


On Jan 23, 2011, at 8:57 AM, Allan Sindelar  
wrote:

> Wrenches,
> Who is a good wholesale source for El-Sid DC circulator pumps, preferably who 
> also carries replacement drivers?
> Who has been a good source for thermal components and materials in general?
> Thanks,
> Allan
> -- 
> Allan Sindelar
> al...@positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> www.positiveenergysolar.com
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Male Whip follow-up

2011-01-23 Thread Eric Thomas
As a (serious) side note, EnPhase says using a cut extension cable will void
the warranty of the entire installation. This is due to the inconsistant
color coding of the extension cables and whips. The danger of crossing
phases within the same circuit. Best (and only acceptable) practice is to
parallel sub arrays.

Eric
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Thermal question

2011-01-23 Thread Allan Sindelar


  
  
Wrenches,
Who is a good wholesale source for El-Sid DC circulator pumps,
preferably who also carries replacement drivers?
Who has been a good source for thermal components and materials in
general?
Thanks,
Allan
-- 
  
  
  
  
  
  
  
  
Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
  

  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SunSaver failures; MPPT controller reliability (1A Charge/Load controller)

2011-01-23 Thread Maverick Brown [Maverick Solar]
Larry

Were the failures on 12 or 24v systems?

Thank you,

Maverick


Maverick Brown
BSEET, NABCEP Certified Solar PV Installer ®
President & CEO
Maverick Solar Enterprises, Inc.
Office: 512-919-4493
Cell:512-460-9825

Sent from an iPhone. 

On Jan 23, 2011, at 9:58 AM,  wrote:

> Jason,
> Not much to elaborate on. A single 200 watt Sanyo module, about 25' of 8 
> gauge wire, lowest temperature 20 degrees. When the SunSaver controllers 
> fail, they cause a short circuit at the battery terminals. Morningstar 
> handled the warranty as they do all SunSaver warranty's, quickly sending 
> replacements with return postage for the defective unit. We have had 4 
> SunSaver failures since November 1.
> 
> I sell 150+ charge controllers at our retail store each season (Nov. ~ Dec.), 
> most of which are MPPT. Reliability is critical to me and I pay very close 
> attention to failures. Most of my customers are mobile and not able to return 
> to our store if a product fails. I have tested and sold many MPPT models. The 
> Phocos MPPT controller I was evaluating failed and we have had our share of 
> Outback and BZ controller failures. Blue Sky Energy has had a few bad 
> controllers but compared to the volume of BSE products we sell (over 1100) 
> they have been the most reliable. I have not yet tested Steca, TriStar, or 
> Xantrex MPPT controllers.
> 
> Larry
> Starlight Solar Power Systems
>  Original Message 
> Subject: Re: [RE-wrenches] 10A Charge / load controller
> From: Jason Lerner 
> Date: Sat, January 22, 2011 11:56 am
> To: RE-wrenches 
> 
> Hi Larry,
> 
> I am curious about the failures you have had,  could you elaborate?
> 
> Thanks,
> 
> Jason Lerner
> Waldron Power and Light Co.
> 
> 
> On Jan 21, 2011, at 5:37 PM, Starlight Solar, Larry Crutcher wrote:
> 
>> I have had failures with the Sunsaver MPPT. I have used them with a single 
>> Sanyo module in small battery systems. Perhaps they just can't handle the 
>> 50.9 Voc.
>>  
>> Larry
>> Starlight Solar Power Systems
> 
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SunSaver failures; MPPT controller reliability (1A Charge/Load controller)

2011-01-23 Thread Darryl Thayer
Thanks Larry for all the good info, I have not had any problem with SSMPPT but 
my volume is 2, a few years back I had trouble with a Morningstar product, and 
they were very fast and complete in the replace ment service.  Also if they 
know 
of a problem they are very through ingetting to the source and will make 
product 
changes (as they did for the priduct that I used) to prevent it in the future.  
You by getting this back to them have probibly caused an evaluation and maybe a 
change in design.  I have been most happy with them. I use their sunlight and 
similar small controllers.  

Darryl





From: "la...@starlightsolar.com" 
To: RE-wrenches 
Sent: Sun, January 23, 2011 9:58:46 AM
Subject: Re: [RE-wrenches] SunSaver failures; MPPT controller reliability (1A 
Charge/Load controller)

Jason,
Not much to elaborate on. A single 200 watt Sanyo module, about 25' of 8 gauge 
wire, lowest temperature 20 degrees. When the SunSaver controllers fail, they 
cause a short circuit at the battery terminals. Morningstar handled the 
warranty 
as they do all SunSaver warranty's, quickly sending replacements with return 
postage for the defective unit. We have had 4 SunSaver failures since November 
1.

I sell 150+ charge controllers at our retail store each season (Nov. ~ Dec.), 
most of which are MPPT. Reliability is critical to me and I pay very close 
attention to failures. Most of my customers are mobile and not able to return 
to 
our store if a product fails. I have tested and sold many MPPT models. The 
Phocos MPPT controller I was evaluating failed and we have had our share of 
Outback and BZ controller failures. Blue Sky Energy has had a few bad 
controllers but compared to the volume of BSE products we sell (over 1100) they 
have been the most reliable. I have not yet tested Steca, TriStar, or Xantrex 
MPPT controllers.

Larry 
Starlight Solar Power Systems
 Original Message 
>Subject: Re: [RE-wrenches] 10A Charge / load controller
>From: Jason Lerner 
>Date: Sat, January 22, 2011 11:56 am
>To: RE-wrenches 
>
>Hi Larry, 
>
>
>I am curious about the failures you have had,  could you elaborate?
>
>
>Thanks,
>
>
>Jason Lerner
>Waldron Power and Light Co.
>
>
>
>
>On Jan 21, 2011, at 5:37 PM, Starlight Solar, Larry Crutcher wrote:
>
>I have had failures with the Sunsaver MPPT. I have used them with a single 
>Sanyo 
>module in small battery systems. Perhaps they just can't handle the 50.9 Voc.
>> 
>>Larry
>>Starlight Solar Power Systems
>


  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SunSaver failures; MPPT controller reliability (1A Charge/Load controller)

2011-01-23 Thread larry
Jason,Not much to elaborate on. A single 200 watt Sanyo module, about 25' of 8 gauge wire, lowest temperature 20 degrees. When the SunSaver controllers fail, they cause a short circuit at the battery terminals. Morningstar handled the warranty as they do all SunSaver warranty's, quickly sending replacements with return postage for the defective unit. We have had 4 SunSaver failures since November 1.I sell 150+ charge controllers at our retail store each season (Nov. ~ Dec.), most of which are MPPT. Reliability is critical to me and I pay very close attention to failures. Most of my customers are mobile and not able to return to our store if a product fails. I have tested and sold many MPPT models. The Phocos MPPT controller I was evaluating failed and we have had our share of Outback and BZ controller failures. Blue Sky Energy has had a few bad controllers but compared to the volume of BSE products we sell (over 1100) they have been the most reliable. I have not yet tested Steca, TriStar, or Xantrex MPPT controllers.Larry Starlight Solar Power Systems


 Original Message 
Subject: Re: [RE-wrenches] 10A Charge / load controller
From: Jason Lerner 
Date: Sat, January 22, 2011 11:56 am
To: RE-wrenches 

Hi Larry,I am curious about the failures you have had,  could you elaborate?Thanks,Jason LernerWaldron Power and Light Co.On Jan 21, 2011, at 5:37 PM, Starlight Solar, Larry Crutcher wrote:I have had failures with the Sunsaver MPPT. I have used them with a single Sanyo module in small battery systems. Perhaps they just can't handle the 50.9 Voc. LarryStarlight Solar Power Systems



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org