Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter outputs

2011-03-30 Thread Jason Szumlanski
Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system,
this could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense
to locate the subpanel close to the main panel and run multiple sets of
smaller wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection
connected to the inverters, adding a main breaker (theoretically 80A in
this example) in the subpanel doesn't change things. Even though this
wire would be theoretically protected by an 80A breaker at each end, you
can't size the wire for 160A / 1.2 = 133.3A. You have to size for
180A/1.2 = 150A. (not that it makes much of a difference in this
example, but it still must be considered)

 

At least that's how I understand it...

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase
system shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply
per bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not
dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I
calculated for 3 - 50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

Per 705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is
required and the inverters would have to feed the opposite end of the
bus bars. If no, the code is not clear on the requirement, but obviously
the 80-amp breaker in the main panel limits the maximum current flowing
through the sub-panel. 

Kent Osterberg
Blue Mountain Solar



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs

2011-03-30 Thread Mark Frye
Jason,
 
I think, going back to the diagram in the article, the feeder breaker is
rated at 80A, the feeder conductors are rated at 80A, and the subpanel is
rated at 80A, assuming that there are no loads connected in the subpanel.
Even if there were up to 100A of loads in the subpanel, you would not exceed
the allowance for the feeder or the sub-panel. Still, if you do have loads
in the subpanel, you have to up sizes the sub-panel, but not the feeder
conductor.
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 5:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter
outputs



Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system, this
could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense to
locate the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection connected to
the inverters, adding a main breaker (theoretically 80A in this example) in
the subpanel doesn't change things. Even though this wire would be
theoretically protected by an 80A breaker at each end, you can't size the
wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not
that it makes much of a difference in this example, but it still must be
considered)

 

At least that's how I understand it.

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase system
shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply per
bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

Per 705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is required
and the inverters would have to feed the opposite end of the bus bars. If
no, the code is not clear on the requirement, but obviously the 80-amp
breaker in the main panel limits the maximum current flowing through the
sub-panel. 

Kent Osterberg
Blue Mountain Solar



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread Al Frishman
Is a monitoring system installed in the Load Center to measure the
cumulative kWh's of the inverter's considered a load?  

The type of monitoring device I am talking about has CT's that go around the
conductors and the Voltage ref is taken by attaching conductors to each
phase, the Neutral and the ground bar.The digital Meter has a 3-pole 5A
breaker in it so the conductors in the load center can be connected to lugs
on the bus bar directly.

 

Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com http://www.aeonsolar.com/ 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system, this
could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense to
locate the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection connected to
the inverters, adding a main breaker (theoretically 80A in this example) in
the subpanel doesn't change things. Even though this wire would be
theoretically protected by an 80A breaker at each end, you can't size the
wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not
that it makes much of a difference in this example, but it still must be
considered)

 

At least that's how I understand it.

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase system
shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply per
bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

Per 705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is required
and the inverters would have to feed the opposite end of the bus bars. If
no, the code is not clear on the requirement, but obviously the 80-amp
breaker in the main panel limits the maximum current flowing through the
sub-panel. 

Kent Osterberg
Blue Mountain Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverteroutputs

2011-03-30 Thread Jason Szumlanski
Hmmm. That's not the way I understood it. I could be wrong.

 

690(B)(2): The sum of the ampere ratings of overcurrent devices in
circuits supplying power to a busbar or conductor shall not exceed 120
percent of the rating of the busbar or conductor. In systems with
panelboards connected in series, the rating of the first overcurrent
device directly connected to the output of a utility-interactive
inverter(s) shall be used in the calculations for all busbars and
conductors.

 

The way I read it, both the inverters and the feeder circuit are
supplying power to the conductor between the main and subpanels. The sum
of the OC protection is 100A + 80A = 180A per leg. Therefore, the
conductor must be rated for 180A / 1.2 = 150A. Maybe this changes if
there are no loads in the subpanel, but I don't think so. In many cases
we have a circuit for an energy monitoring device in the subpanel, so we
almost always have loads anyway. Another way to read it would be that
ONLY the inverter circuits shall be used for calculations, in which case
the conductors would need to be 100A / 1.2 = 83.3A. However, I don't
think that is the intent.

 

While on the subject, I always wondered about that Lennox Solar A/C
system that uses Enphase backfed through the A/C compressor circuit. It
seemed like the conductor would need to be upgraded.

 

Jason

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Wednesday, March 30, 2011 11:36 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used
tocombinemultipleinverteroutputs

 

Jason,

 

I think, going back to the diagram in the article, the feeder breaker is
rated at 80A, the feeder conductors are rated at 80A, and the subpanel
is rated at 80A, assuming that there are no loads connected in the
subpanel. Even if there were up to 100A of loads in the subpanel, you
would not exceed the allowance for the feeder or the sub-panel. Still,
if you do have loads in the subpanel, you have to up sizes the
sub-panel, but not the feeder conductor.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 5:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used
tocombinemultipleinverter outputs

Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system,
this could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense
to locate the subpanel close to the main panel and run multiple sets of
smaller wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection
connected to the inverters, adding a main breaker (theoretically 80A in
this example) in the subpanel doesn't change things. Even though this
wire would be theoretically protected by an 80A breaker at each end, you
can't size the wire for 160A / 1.2 = 133.3A. You have to size for
180A/1.2 = 150A. (not that it makes much of a difference in this
example, but it still must be considered)

 

At least that's how I understand it...

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase
system shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply
per bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not
dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I
calculated for 3 - 50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: 

Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs

2011-03-30 Thread Philip Boutelle
To echo the wording in Kent's response, John Wiles has always advised that
it doesn't matter if there are currently loads connected to the
panel/conductors; if the panel/conductors are capable of having additional
loads connected to it, you need to apply 609.64(B)(2). I have had luck with
AHJ approval by adding signage indicating that no loads can be added to this
panel/fpr combining PV inverter output only, and in one case installed a
panelboard dead-front that limited the number of breakers to six (for our
six combining inverters).

If you are installing  breaker for a meter, it sounds like the panel is
capable of having additional loads connected to it.

For discussion on code specific combiner panel requirements, or the lack
thereof, I'll quote from this list last year (response is from Bill Brooks):

**


Sent: Tuesday, January 12, 2010 10:57 AM

To: RE-wrenches

Subject: [RE-wrenches] Solar accumulation panel


***

Team wrenches - I feel like I've seen a provision in the Code for
installing a sub-panel to aggregate PV inverter outputs for the
purpose of simplifying the actual grid connection (such as for a
line-side tap) but I can't find it in 690.  I also seem to remember
specific verbiage that needs to be on the panel along the lines of PV
circuits only.  Do not add load breakers. to ensure compliance with
690.64(B).  Does anyone know where I can find this info in the NEC?

Andrew Truitt

Standard Solar Inc.



Response:

 It does not exist. We tried like crazy to get it into the 2011 NEC,
but to no avail. At the last second the proposal was put on hold until
the 2014 NEC. Major bummer. For now it can only be done with AHJ
approval. Many allow it but it is not in the NEC. Alternatively you
must use the sum of supply breakers no greater than 120%. Much more
restrictive.

Bill.



-Phil



On Wed, Mar 30, 2011 at 8:36 AM, Mark Frye ma...@berkeleysolar.com wrote:

  Jason,

 I think, going back to the diagram in the article, the feeder breaker is
 rated at 80A, the feeder conductors are rated at 80A, and the subpanel is
 rated at 80A, assuming that there are no loads connected in the subpanel.
 Even if there were up to 100A of loads in the subpanel, you would not exceed
 the allowance for the feeder or the sub-panel. Still, if you do have loads
 in the subpanel, you have to up sizes the sub-panel, but not the feeder
 conductor.

 Mark Frye
 Berkeley Solar Electric Systems
 303 Redbud Way
 Nevada City,  CA 95959
 (530) 401-8024
 *www.berkeleysolar.com* http://www.berkeleysolar.com/


  --
 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Jason Szumlanski
 *Sent:* Wednesday, March 30, 2011 5:18 AM

 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] sizing a sub-panel used
 tocombinemultipleinverter outputs

  Another key is to remember that this discussion also applies to the
 conductor between the main panel and subpanel. In a large PV system, this
 could result in a pretty large wire between the two panels, and a
 significant cost that is often overlooked. In some cases it makes sense to
 locate the subpanel close to the main panel and run multiple sets of smaller
 wires from the inverters to the subpanel.



 And because the calculation is based on the first OC protection connected
 to the inverters, adding a main breaker (theoretically 80A in this example)
 in the subpanel doesn’t change things. Even though this wire would be
 theoretically protected by an 80A breaker at each end, you can’t size the
 wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not
 that it makes much of a difference in this example, but it still must be
 considered)



 At least that’s how I understand it…



 Jason Szumlanski

 Fafco Solar





 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Mark Frye
 *Sent:* Wednesday, March 30, 2011 1:33 AM
 *To:* 'RE-wrenches'
 *Subject:* Re: [RE-wrenches] sizing a sub-panel used to
 combinemultipleinverter outputs



 Opps!



 My bad, I was thinking of a single phase system, not the three phase system
 shown in the article.



 For the three phase system Kent is correct in counting 180A of supply per
 bar.



 Mark Frye
 Berkeley Solar Electric Systems
 303 Redbud Way
 Nevada City,  CA 95959
 (530) 401-8024
 www.berkeleysolar.com




  --

 *From:* re-wrenches-boun...@lists.re-wrenches.org [mailto:
 re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Mark Frye
 *Sent:* Tuesday, March 29, 2011 10:17 PM
 *To:* 'RE-wrenches'
 *Subject:* Re: [RE-wrenches] sizing a sub-panel used to combine
 multipleinverter outputs

 I think Kent and I agree. For the case where the subpanel is not dedicated
 a PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3
 - 50A breakers.


 Mark Frye
 Berkeley 

Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter outputs

2011-03-30 Thread Kent Osterberg




Jason,

Now you are opening up a can of worms. 

It's bad enough that 705.12(D) doesn't say anything about a panel that
can't (or shouldn't, or won't) have anything connected but interactive
inverters. But when that is the case, a bus rating of 100% of the
source circuits should apply. For PV systems a 125% factor will already
apply to each inverter circuit.

While it seems logical that the conductors are an extension of the bus
bar and should be treated the same way, 705.12(D) isn't about the
conductors - it's about the bus bars. The conductors are protected by
the breakers -- 80-amp breakers and wire with 80-amp ampacity. 

Getting into the example further, I see flaws in it. If the inverters
are 7500-watt 240-volt, the output current would be 7500/240 = 31.25
amps and 40-amp breakers would be adequate. Then there would have been
no issues, even going directly into the main panel. If the inverters
are 7500-watt 208-volt, the output current is 7500/208 = 36 amps and
the 50-amp breakers make sense. That means the bus bars and feeder
conductor have a continuous current of 72 amps. That means neither the
80-amp breaker nor 80-amp wire is sufficient because 72 x 1.25 = 90
amps. Now the example doesn't resolve the limitation of backfeeding at
the main. Opps!

Kent Osterberg
Blue Mountain Solar






Jason Szumlanski wrote:

  
  

  
  
  Another
key is to remember that this discussion also applies to the conductor
between the main panel and subpanel. In a large PV system, this could
result in a pretty large wire between the two panels, and a significant
cost that is often overlooked. In some cases it makes sense to locate
the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.
  
  And
because the calculation is based on the first OC protection connected
to the inverters, adding a main breaker (theoretically 80A in this
example) in the subpanel doesnt change things. Even though this wire
would be theoretically protected by an 80A breaker at each end, you
cant size the wire for 160A / 1.2 = 133.3A. You have to size for
180A/1.2 = 150A. (not that it makes much of a difference in this
example, but it still must be considered)
  
  At
least thats how I understand it
  
  
  Jason
Szumlanski
  Fafco
Solar
  
  
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
  Sent: Wednesday, March 30, 2011 1:33 AM
  To: 'RE-wrenches'
  Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs
  
  
  
  Opps!
  
  My
bad, Iwas thinking of a singlephase system, not the three phase
system shown in the article.
  
  For
the three phase system Kent is correct in counting 180A of supply per
bar.
  
  Mark Frye
  
  Berkeley
Solar Electric Systems 
  303
Redbud Way 
  Nevada
City, CA 95959 
  (530)
401-8024 
  www.berkeleysolar.com 
  
  
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
  Sent: Tuesday, March 29, 2011 10:17 PM
  To: 'RE-wrenches'
  Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs
  I
think Kent and I agree. For the case where thesubpanel is not
dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I
calculated for 3 - 50A breakers.
  
  Mark
Frye 
  Berkeley
Solar Electric Systems 
  303
Redbud Way 
  Nevada
City, CA 95959 
  (530)
401-8024 
  www.berkeleysolar.com 
  
  
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
  Sent: Tuesday, March 29, 2011 9:26 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multiple inverter outputs
  Per 705.12(D) the sub-panel could be any
distribution equipment on the premises. So the question becomes: is the
sub-panel capable of supplying branch circuits or feeder loads? If yes,
then the sum of the breakers (potentially) feeding the bus is 180 amps
so a 150-amp rating is required and the inverters would have to feed
the opposite end of the bus bars. If no, the code is not clear on the
requirement, but obviously the 80-amp breaker in the main panel limits
the maximum current flowing through the sub-panel. 
  
Kent Osterberg
Blue Mountain Solar
  
  
  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:

Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter outputs

2011-03-30 Thread Mark Frye
Al,
 
I would say that yes the meter is a load and this goes to show the relative
inadequacy of the vocabulary we are using in the discussion. In the example
we have been using with the 80A breaker, wire and sub panel, you could have
up to 80A of loads installed in the sub and still not create an over current
condition in any of that equipment.
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Al Frishman
Sent: Wednesday, March 30, 2011 9:00 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs



Is a monitoring system installed in the Load Center to measure the
cumulative kWh's of the inverter's considered a load?  

The type of monitoring device I am talking about has CT's that go around the
conductors and the Voltage ref is taken by attaching conductors to each
phase, the Neutral and the ground bar.The digital Meter has a 3-pole 5A
breaker in it so the conductors in the load center can be connected to lugs
on the bus bar directly.

 

Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com http://www.aeonsolar.com/ 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system, this
could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense to
locate the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection connected to
the inverters, adding a main breaker (theoretically 80A in this example) in
the subpanel doesn't change things. Even though this wire would be
theoretically protected by an 80A breaker at each end, you can't size the
wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not
that it makes much of a difference in this example, but it still must be
considered)

 

At least that's how I understand it.

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase system
shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply per
bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

Per 705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is required
and the inverters would have to feed the opposite end of the bus bars. If
no, the code is not clear on the requirement, but obviously the 80-amp
breaker in the main panel limits the maximum current flowing through the
sub-panel. 

Kent Osterberg
Blue Mountain Solar

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread Kent Osterberg




Al,

How about a 15-amp single-pole breaker for power line carrier
communications equipment to talk to the inverters?
Technically, I think either way they are loads and that changes
everything. But in my opinion they are minor and should be allowed
without considering the sum of all sources.

Kent Osterberg
Blue Mountain Solar


Al Frishman wrote:

  
  

  
  
  Is
a monitoring system installed in the Load Center to measure the
cumulative kWhs of the inverters considered a load? 
  The
type of monitoring device I am talking about has CTs that go around
the conductors and the Voltage ref is taken by attaching conductors to
each phase, the Neutral and the ground bar. The digital Meter has a
3-pole 5A breaker in it so the conductors in the load center can be
connected to lugs on the bus bar directly.
  
  
  Al
Frishman
  AeonSolar
  (917)
699-6641 - cell
  (888)
460-2867
  www.aeonsolar.com
  
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
  Sent: Wednesday, March 30, 2011 8:18 AM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs
  
  
  
  Another
key is to remember that this discussion also applies to the conductor
between the main panel and subpanel. In a large PV system, this could
result in a pretty large wire between the two panels, and a significant
cost that is often overlooked. In some cases it makes sense to locate
the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.
  
  And
because the calculation is based on the first OC protection connected
to the inverters, adding a main breaker (theoretically 80A in this
example) in the subpanel doesnt change things. Even though this wire
would be theoretically protected by an 80A breaker at each end, you
cant size the wire for 160A / 1.2 = 133.3A. You have to size for
180A/1.2 = 150A. (not that it makes much of a difference in this
example, but it still must be considered)
  
  At
least thats how I understand it
  
  
  Jason
Szumlanski
  Fafco
Solar
  
  
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
  Sent: Wednesday, March 30, 2011 1:33 AM
  To: 'RE-wrenches'
  Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs
  
  
  
  Opps!
  
  My
bad, Iwas thinking of a singlephase system, not the three phase
system shown in the article.
  
  For
the three phase system Kent is correct in counting 180A of supply per
bar.
  
  Mark Frye
  
  Berkeley
Solar Electric Systems 
  303
Redbud Way 
  Nevada
City, CA 95959 
  (530)
401-8024 
  www.berkeleysolar.com 
  
  
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
  Sent: Tuesday, March 29, 2011 10:17 PM
  To: 'RE-wrenches'
  Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs
  I
think Kent and I agree. For the case where thesubpanel is not
dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I
calculated for 3 - 50A breakers.
  
  Mark
Frye 
  Berkeley
Solar Electric Systems 
  303
Redbud Way 
  Nevada
City, CA 95959 
  (530)
401-8024 
  www.berkeleysolar.com 
  
  
  
  
  
  
  From:
re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
  Sent: Tuesday, March 29, 2011 9:26 PM
  To: RE-wrenches
  Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multiple inverter outputs
  Per 705.12(D) the
sub-panel could be any distribution equipment on the premises. So the
question becomes: is the sub-panel capable of supplying branch circuits
or feeder loads? If yes, then the sum of the breakers (potentially)
feeding the bus is 180 amps so a 150-amp rating is required and the
inverters would have to feed the opposite end of the bus bars. If no,
the code is not clear on the requirement, but obviously the 80-amp
breaker in the main panel limits the maximum current flowing through
the sub-panel. 
  
Kent Osterberg
Blue Mountain Solar
  
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread David Brearley
This is diagram is based on a 3-phase 208 V service, as clarified in the
text accompanying the diagrams. There is a mistake of sorts, however. The
authors¹ original manuscript called out a ³generic² 7500W inverter connected
to 50A, 2-P breaker. We then added more detail, calling out a Fronius 7500W
IG Plus inverter. However, according to the most recent product data from
the manufacturer, the max AC OCPD rating for this inverter is 45A, not 50A.
The example still works w/ 45A breakers: 400A + 90A = 490A, which is larger
than the 480A allowed under the 120% rule. Apply the subpanel  that problem
is eliminated.

RE: the question about which breaker to count. Code experts like Bill Brooks
 John Wiles have clarified that when a dedicated inverter aggregation panel
is used, the breaker on the output of the panel can be considered ³the
output of the utility interactive inverter(s).² The intent of the language
in 690.64(B)(2) in NEC 2008 about series connected panels is not to make you
count all of the breakers in a dedicated inverter aggregation panel. Rather
it is to clarify that it is unnecessary use the progressively larger
upstream breakers ratings, which can be ³fed² by the inverters, in your
point of connection calculations.

RE: the original question. I think the most correct answer is ³It depends.²
It depends on your jurisdiction and your PE. A literal interpretation of the
Code would appear to have you upsize the inverter aggregation panel and the
feeder conductor. But there is certainly precedent for AHJs not requiring
this. If you propose labeling the inverter aggregation panel ³PV Only ‹ Do
Not Add Loads² and mark the feeder conductor with warnings ³PV Only ‹ Do Not
Tap² wherever it is exposed, you may find that the AHJ will not require you
to upsize these. 

Hope that¹s cleared than mud,

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com
Direct: 541.261.6545


On 3/30/11 11:12 AM, Kent Osterberg k...@coveoregon.com wrote:

 Jason,
 
 Now you are opening up a can of worms.
 
 It's bad enough that 705.12(D) doesn't say anything about a panel that can't
 (or shouldn't, or won't) have anything connected but interactive inverters.
 But when that is the case, a bus rating of 100% of the source circuits should
 apply. For PV systems a 125% factor will already apply to each inverter
 circuit.
 
 While it seems logical that the conductors are an extension of the bus bar and
 should be treated the same way, 705.12(D) isn't about the conductors - it's
 about the bus bars. The conductors are protected by the breakers -- 80-amp
 breakers and wire with 80-amp ampacity.
 
 Getting into the example further, I see flaws in it. If the inverters are
 7500-watt 240-volt, the output current would be 7500/240 = 31.25 amps and
 40-amp breakers would be adequate. Then there would have been no issues, even
 going directly into the main panel. If the inverters are 7500-watt 208-volt,
 the output current is 7500/208 = 36 amps and the 50-amp breakers make sense.
 That means the bus bars and feeder conductor have a continuous current of 72
 amps.  That means neither the 80-amp breaker nor 80-amp wire is sufficient
 because 72 x 1.25 = 90 amps. Now the example doesn't resolve the limitation of
 backfeeding at the main. Opps!
 
 Kent Osterberg
 Blue Mountain Solar
 
 
 
 
 
 
 Jason Szumlanski wrote:
 
  
 
 Another key is to remember that this discussion also applies to the conductor
 between the main panel and subpanel. In a large PV system, this could result
 in a pretty large wire between the two panels, and a significant cost that is
 often overlooked. In some cases it makes sense to locate the subpanel close
 to the main panel and run multiple sets of smaller wires from the inverters
 to the subpanel.
  
  
  
 And because the calculation is based on the first OC protection connected to
 the inverters, adding a main breaker (theoretically 80A in this example) in
 the subpanel doesn¹t change things. Even though this wire would be
 theoretically protected by an 80A breaker at each end, you can¹t size the
 wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not that
 it makes much of a difference in this example, but it still must be
 considered)
  
  
  
 At least that¹s how I understand itŠ
  
  
  
  
 
 Jason Szumlanski
  
 Fafco Solar 
  
  
  
  
  
  
  
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
  Sent: Wednesday, March 30, 2011 1:33 AM
  To: 'RE-wrenches'
  Subject: Re: [RE-wrenches] sizing a sub-panel used to
 combinemultipleinverter outputs
  
  
  
  
  
 Opps!
  
  
  
 My bad, I was thinking of a single phase system, not the three phase system
 shown in the article.
  
  
  
 For the three phase system Kent is correct in counting 180A of supply per
 bar.
  
  
  
 Mark Frye 
  Berkeley Solar Electric Systems
  303 Redbud Way 
  

[RE-wrenches] NABCEP Stamp

2011-03-30 Thread Troy Harvey
I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have a 
city agency who is comfortable with the NABCEP certification as a 
qualification, but would like to see a stamp. Has anyone out there done this? 

Troy

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter outputs

2011-03-30 Thread Brian Teitelbaum
Wouldn't a fault in that conductor between the main and the sub have a 
potential for up to 160A of current? I would think that at noon on a sunny day, 
the inverter system could produce 80A from one direction (albeit really only 
the max amperage outputs of the inverters) and 80A of grid current from the 
main into a partial fault.

Brian Teitelbaum
AEE Solar

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 9:49 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter 
outputs

Al,

I would say that yes the meter is a load and this goes to show the relative 
inadequacy of the vocabulary we are using in the discussion. In the example we 
have been using with the 80A breaker, wire and sub panel, you could have up to 
80A of loads installed in the sub and still not create an over current 
condition in any of that equipment.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.comhttp://www.berkeleysolar.com/



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Al Frishman
Sent: Wednesday, March 30, 2011 9:00 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter 
outputs
Is a monitoring system installed in the Load Center to measure the cumulative 
kWh's of the inverter's considered a load?
The type of monitoring device I am talking about has CT's that go around the 
conductors and the Voltage ref is taken by attaching conductors to each phase, 
the Neutral and the ground bar.The digital Meter has a 3-pole 5A breaker in 
it so the conductors in the load center can be connected to lugs on the bus bar 
directly.

Al Frishman
AeonSolar
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.comhttp://www.aeonsolar.com/


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter 
outputs

Another key is to remember that this discussion also applies to the conductor 
between the main panel and subpanel. In a large PV system, this could result in 
a pretty large wire between the two panels, and a significant cost that is 
often overlooked. In some cases it makes sense to locate the subpanel close to 
the main panel and run multiple sets of smaller wires from the inverters to the 
subpanel.

And because the calculation is based on the first OC protection connected to 
the inverters, adding a main breaker (theoretically 80A in this example) in the 
subpanel doesn't change things. Even though this wire would be theoretically 
protected by an 80A breaker at each end, you can't size the wire for 160A / 1.2 
= 133.3A. You have to size for 180A/1.2 = 150A. (not that it makes much of a 
difference in this example, but it still must be considered)

At least that's how I understand it...

Jason Szumlanski
Fafco Solar


From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter 
outputs

Opps!

My bad, I was thinking of a single phase system, not the three phase system 
shown in the article.

For the three phase system Kent is correct in counting 180A of supply per bar.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.comhttp://www.berkeleysolar.com/



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter 
outputs
I think Kent and I agree. For the case where the subpanel is not dedicated a PV 
sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 - 50A 
breakers.

Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City,  CA 95959
(530) 401-8024
www.berkeleysolar.comhttp://www.berkeleysolar.com/



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter 
outputs
Per 705.12(D) the sub-panel could be any distribution equipment on the 
premises. So the question becomes: is the sub-panel capable of supplying branch 
circuits or feeder loads? If yes, then the sum of the breakers (potentially) 
feeding the bus is 180 amps so a 

Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter outputs

2011-03-30 Thread Andrew Truitt
 I concur with Jason and Brian's interpretation of 690.64(B)(2).  I think
one of the intents of the code is to ensure that if there is a fault in a
busbar or conductor and the maximum amperage is being delivered to that
fault from all OCPDs supplying it (solar + utility), the busbar or conductor
should be able to handle the sum of those fault currents.  I have
encountered numerous jurisdictions that interpret it this way, and it is
hard to argue with them from a strictly code perspective.

However, Jason Fisher once pointed out to me that if the fault occurs in a
feeder between the main service panel and a subpanel (solar accumulation
panel or otherwise) it is impossible for any part of that conductor to carry
more current than allowed by the largest OCPD feeding the conductor.  Its
the same principle behind the 690.64(B)(7) requirement to locate the solar
interconnection breaker at the opposite end of the busbar from the incoming
feeders.  This argument obviously doesn't apply to accumulation panel
busbars where you have more than 2 OCPDs supplying current, but I think it
is a valid argument for basing your feeder conductor sizing on the largest
OCPD protecting that conductor.



For a brighter energy future,

Andrew Truitt
Principal
Truitt Renewable Energy Consulting
NABCEP Certified PV Installer™ (ID# 032407-66)
(202) 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713

[image: 24 copy.jpg]

Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough







On Wed, Mar 30, 2011 at 10:12 AM, Kent Osterberg k...@coveoregon.comwrote:

 Jason,

 Now you are opening up a can of worms.

 It's bad enough that 705.12(D) doesn't say anything about a panel that
 can't (or shouldn't, or won't) have anything connected but interactive
 inverters. But when that is the case, a bus rating of 100% of the source
 circuits should apply. For PV systems a 125% factor will already apply to
 each inverter circuit.

 While it seems logical that the conductors are an extension of the bus bar
 and should be treated the same way, 705.12(D) isn't about the conductors -
 it's about the bus bars. The conductors are protected by the breakers --
 80-amp breakers and wire with 80-amp ampacity.

 Getting into the example further, I see flaws in it. If the inverters are
 7500-watt 240-volt, the output current would be 7500/240 = 31.25 amps and
 40-amp breakers would be adequate. Then there would have been no issues,
 even going directly into the main panel. If the inverters are 7500-watt
 208-volt, the output current is 7500/208 = 36 amps and the 50-amp breakers
 make sense. That means the bus bars and feeder conductor have a continuous
 current of 72 amps.  That means neither the 80-amp breaker nor 80-amp wire
 is sufficient because 72 x 1.25 = 90 amps. Now the example doesn't resolve
 the limitation of backfeeding at the main. Opps!


 Kent Osterberg
 Blue Mountain Solar






 Jason Szumlanski wrote:

   Another key is to remember that this discussion also applies to the
 conductor between the main panel and subpanel. In a large PV system, this
 could result in a pretty large wire between the two panels, and a
 significant cost that is often overlooked. In some cases it makes sense to
 locate the subpanel close to the main panel and run multiple sets of smaller
 wires from the inverters to the subpanel.



 And because the calculation is based on the first OC protection connected
 to the inverters, adding a main breaker (theoretically 80A in this example)
 in the subpanel doesn’t change things. Even though this wire would be
 theoretically protected by an 80A breaker at each end, you can’t size the
 wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not
 that it makes much of a difference in this example, but it still must be
 considered)



 At least that’s how I understand it…



 Jason Szumlanski

 Fafco Solar





 *From:* re-wrenches-boun...@lists.re-wrenches.org [
 mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org]
 *On Behalf Of *Mark Frye
 *Sent:* Wednesday, March 30, 2011 1:33 AM
 *To:* 'RE-wrenches'
 *Subject:* Re: [RE-wrenches] sizing a sub-panel used to
 combinemultipleinverter outputs



 Opps!



 My bad, I was thinking of a single phase system, not the three phase system
 shown in the article.



 For the three phase system Kent is correct in counting 180A of supply per
 bar.



 Mark Frye
 Berkeley Solar Electric Systems
 303 Redbud Way
 Nevada City,  CA 95959
 (530) 401-8024
 www.berkeleysolar.com




  --

 *From:* re-wrenches-boun...@lists.re-wrenches.org [
 mailto:re-wrenches-boun...@lists.re-wrenches.orgre-wrenches-boun...@lists.re-wrenches.org]
 *On Behalf Of *Mark Frye
 *Sent:* Tuesday, 

Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread Jason Szumlanski
Here is a 690.64(B)(2) opinion from Wiles that may help. 

http://www.fafcosolar.com/download/409/690%2064%28B%29%282%29TECH-1.pdf

 

It's still my contention that the conductors need to be sized for 150A
in this example, unless an exception is made by the AHJ. If David
Brearley's post about Wiles' clarification is accurate, them the 80A
main breaker in the subpanel can be used for calculations, but the
conductor still needs to be sized for 80A + 80A =160A / 1.2 = 133.3A.

 

Jason

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Wednesday, March 30, 2011 12:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

 

Al,

How about a 15-amp single-pole breaker for power line carrier
communications equipment to talk to the inverters?
Technically, I think either way they are loads and that changes
everything. But in my opinion they are minor and should be allowed
without considering the sum of all sources.

Kent Osterberg
Blue Mountain Solar


Al Frishman wrote: 

Is a monitoring system installed in the Load Center to measure the
cumulative kWh's of the inverter's considered a load?  

The type of monitoring device I am talking about has CT's that go around
the conductors and the Voltage ref is taken by attaching conductors to
each phase, the Neutral and the ground bar.The digital Meter has a
3-pole 5A breaker in it so the conductors in the load center can be
connected to lugs on the bus bar directly.

 

Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com http://www.aeonsolar.com/ 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system,
this could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense
to locate the subpanel close to the main panel and run multiple sets of
smaller wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection
connected to the inverters, adding a main breaker (theoretically 80A in
this example) in the subpanel doesn't change things. Even though this
wire would be theoretically protected by an 80A breaker at each end, you
can't size the wire for 160A / 1.2 = 133.3A. You have to size for
180A/1.2 = 150A. (not that it makes much of a difference in this
example, but it still must be considered)

 

At least that's how I understand it...

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase
system shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply
per bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not
dedicated a PV sub-panel he is calculating for 2 - 50A breakers and I
calculated for 3 - 50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com http://www.berkeleysolar.com/   

 

 



From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

Per 705.12(D) the sub-panel could be any distribution equipment on the
premises. So the question becomes: is the sub-panel capable of supplying
branch circuits or feeder loads? If yes, then the sum of the breakers
(potentially) feeding the bus is 180 amps so a 150-amp rating is
required and the inverters would have to feed the opposite end of the
bus bars. If no, the code is not clear on the requirement, but obviously
the 80-amp breaker in the main panel limits the maximum current flowing
through the sub-panel. 

Kent 

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Andrew Truitt
Troy - I have not encountered this before but would you mind sharing what
city agency you are refering to?  NABCEP is always interested in hearing
about these types of unconventional uses of the certification.


For a brighter energy future,

Andrew Truitt
Principal
Truitt Renewable Energy Consulting
NABCEP Certified PV Installer™ (ID# 032407-66)
(202) 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713

[image: 24 copy.jpg]

Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough




On Wed, Mar 30, 2011 at 11:04 AM, Troy Harvey tahar...@heliocentric.orgwrote:

 I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have
 a city agency who is comfortable with the NABCEP certification as a
 qualification, but would like to see a stamp. Has anyone out there done
 this?

 Troy

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


24 copy.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] sizing a sub-panel used to combine multiple inverter outputs

2011-03-30 Thread David Brearley
Agreed:

http://solarprofessional.com/article/?file=SP2_3_pg16_QandA_2search=

You¹ll notice that none of the more permissive proposals that John mentions
here actually made it into NEC 2011.


On 3/30/11 1:07 PM, Jason Szumlanski ja...@fafcosolar.com wrote:

 Here is a 690.64(B)(2) opinion from Wiles that may help.
 http://www.fafcosolar.com/download/409/690%2064%28B%29%282%29TECH-1.pdf
  
 It¹s still my contention that the conductors need to be sized for 150A in this
 example, unless an exception is made by the AHJ. If David Brearley¹s post
 about Wiles¹ clarification is accurate, them the 80A main breaker in the
 subpanel can be used for calculations, but the conductor still needs to be
 sized for 80A + 80A =160A / 1.2 = 133.3A.
  
 
 Jason
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
 Sent: Wednesday, March 30, 2011 12:57 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
 inverter outputs
  
 Al,
 
 How about a 15-amp single-pole breaker for power line carrier communications
 equipment to talk to the inverters?
 Technically, I think either way they are loads and that changes everything.
 But in my opinion they are minor and should be allowed without considering the
 sum of all sources.
 
 Kent Osterberg
 Blue Mountain Solar
 
 
 Al Frishman wrote:
 Is a monitoring system installed in the Load Center to measure the cumulative
 kWh¹s of the inverter¹s considered a load?
 The type of monitoring device I am talking about has CT¹s that go around the
 conductors and the Voltage ref is taken by attaching conductors to each phase,
 the Neutral and the ground bar.The digital Meter has a 3-pole 5A breaker
 in it so the conductors in the load center can be connected to lugs on the bus
 bar directly.
  
 
 Al Frishman
 AeonSolar
 (917) 699-6641 - cell
 (888) 460-2867
 www.aeonsolar.com http://www.aeonsolar.com/
  
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
 Szumlanski
 Sent: Wednesday, March 30, 2011 8:18 AM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter
 outputs
  
 Another key is to remember that this discussion also applies to the conductor
 between the main panel and subpanel. In a large PV system, this could result
 in a pretty large wire between the two panels, and a significant cost that is
 often overlooked. In some cases it makes sense to locate the subpanel close to
 the main panel and run multiple sets of smaller wires from the inverters to
 the subpanel.
  
 And because the calculation is based on the first OC protection connected to
 the inverters, adding a main breaker (theoretically 80A in this example) in
 the subpanel doesn¹t change things. Even though this wire would be
 theoretically protected by an 80A breaker at each end, you can¹t size the wire
 for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not that it
 makes much of a difference in this example, but it still must be considered)
  
 At least that¹s how I understand itŠ
  
 
 Jason Szumlanski
 Fafco Solar 
  
  
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
 Sent: Wednesday, March 30, 2011 1:33 AM
 To: 'RE-wrenches'
 Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultipleinverter
 outputs
  
 Opps!
  
 My bad, I was thinking of a single phase system, not the three phase system
 shown in the article.
  
 For the three phase system Kent is correct in counting 180A of supply per bar.
  
 Mark Frye 
 Berkeley Solar Electric Systems
 303 Redbud Way 
 Nevada City,  CA 95959
 (530) 401-8024 
 www.berkeleysolar.com http://www.berkeleysolar.com/
 
  
  
 
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
 Sent: Tuesday, March 29, 2011 10:17 PM
 To: 'RE-wrenches'
 Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multipleinverter
 outputs
 I think Kent and I agree. For the case where the subpanel is not dedicated a
 PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
 50A breakers.
 
 Mark Frye 
 Berkeley Solar Electric Systems
 303 Redbud Way 
 Nevada City,  CA 95959
 (530) 401-8024 
 www.berkeleysolar.com http://www.berkeleysolar.com/
 
  
  
 
 
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
 Sent: Tuesday, March 29, 2011 9:26 PM
 To: RE-wrenches
 Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
 inverter outputs
 Per 705.12(D) the sub-panel could be any distribution equipment on the
 premises. So the question becomes: is the sub-panel capable of supplying
 branch circuits or feeder loads? If yes, then the sum of the breakers
 (potentially) feeding the bus is 180 

Re: [RE-wrenches] sizing a sub-panel used to combinemultiple inverter outputs

2011-03-30 Thread Kristopher Schmid
By this argument, wouldn't it be necessary to check every conductor in the
backfeed path adding potential PV amps to their required ampacity including
the utility conductor from the transformer?
 
Kris

Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
sol...@legacysolar.com
www.legacysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 1:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combinemultiple
inverter outputs



Here is a 690.64(B)(2) opinion from Wiles that may help. 

http://www.fafcosolar.com/download/409/690%2064%28B%29%282%29TECH-1.pdf

 

It's still my contention that the conductors need to be sized for 150A in
this example, unless an exception is made by the AHJ. If David Brearley's
post about Wiles' clarification is accurate, them the 80A main breaker in
the subpanel can be used for calculations, but the conductor still needs to
be sized for 80A + 80A =160A / 1.2 = 133.3A.

 

Jason

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Wednesday, March 30, 2011 12:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine multiple
inverter outputs

 

Al,

How about a 15-amp single-pole breaker for power line carrier communications
equipment to talk to the inverters?
Technically, I think either way they are loads and that changes everything.
But in my opinion they are minor and should be allowed without considering
the sum of all sources.

Kent Osterberg
Blue Mountain Solar


Al Frishman wrote: 

Is a monitoring system installed in the Load Center to measure the
cumulative kWh's of the inverter's considered a load?  

The type of monitoring device I am talking about has CT's that go around the
conductors and the Voltage ref is taken by attaching conductors to each
phase, the Neutral and the ground bar.The digital Meter has a 3-pole 5A
breaker in it so the conductors in the load center can be connected to lugs
on the bus bar directly.

 

Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com http://www.aeonsolar.com/ 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Another key is to remember that this discussion also applies to the
conductor between the main panel and subpanel. In a large PV system, this
could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense to
locate the subpanel close to the main panel and run multiple sets of smaller
wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection connected to
the inverters, adding a main breaker (theoretically 80A in this example) in
the subpanel doesn't change things. Even though this wire would be
theoretically protected by an 80A breaker at each end, you can't size the
wire for 160A / 1.2 = 133.3A. You have to size for 180A/1.2 = 150A. (not
that it makes much of a difference in this example, but it still must be
considered)

 

At least that's how I understand it.

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Opps!

 

My bad, I was thinking of a single phase system, not the three phase system
shown in the article.

 

For the three phase system Kent is correct in counting 180A of supply per
bar.

 

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Tuesday, March 29, 2011 10:17 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

I think Kent and I agree. For the case where the subpanel is not dedicated a
PV sub-panel he is calculating for 2 - 50A breakers and I calculated for 3 -
50A breakers.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, March 29, 2011 9:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel 

Re: [RE-wrenches] sizing a sub-panel used tocombinemultiple inverter outputs

2011-03-30 Thread Jason Szumlanski
I hope there are no potential loads between the meter and the
transformer, so no! Technically, if it is a supply side tap, the
evaluation would include the conductor from the meter to the main
distribution panel I believe, but if it is a load side connection it
does not matter because of the main breaker in the main distribution
panel. Honestly, I've never closely scrutinized the meter-MDP wiring
for supply side connections, but I am confident that a limitation never
came into play.

 

Jason

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
Kristopher Schmid
Sent: Wednesday, March 30, 2011 2:28 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombinemultiple
inverter outputs

 

By this argument, wouldn't it be necessary to check every conductor in
the backfeed path adding potential PV amps to their required ampacity
including the utility conductor from the transformer?

 

Kris

Legacy Solar, LLC
864 Clam Falls Trail
Frederic, WI 54837
715-653-4295
sol...@legacysolar.com
www.legacysolar.com 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 1:08 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultiple inverter outputs

Here is a 690.64(B)(2) opinion from Wiles that may help. 


http://www.fafcosolar.com/download/409/690%2064%28B%29%282%29TECH-1.pdf

 

It's still my contention that the conductors need to be sized
for 150A in this example, unless an exception is made by the AHJ. If
David Brearley's post about Wiles' clarification is accurate, them the
80A main breaker in the subpanel can be used for calculations, but the
conductor still needs to be sized for 80A + 80A =160A / 1.2 = 133.3A.

 

Jason

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Wednesday, March 30, 2011 12:57 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multiple inverter outputs

 

Al,

How about a 15-amp single-pole breaker for power line carrier
communications equipment to talk to the inverters?
Technically, I think either way they are loads and that changes
everything. But in my opinion they are minor and should be allowed
without considering the sum of all sources.

Kent Osterberg
Blue Mountain Solar


Al Frishman wrote: 

Is a monitoring system installed in the Load Center to measure
the cumulative kWh's of the inverter's considered a load?  

The type of monitoring device I am talking about has CT's that
go around the conductors and the Voltage ref is taken by attaching
conductors to each phase, the Neutral and the ground bar.The digital
Meter has a 3-pole 5A breaker in it so the conductors in the load center
can be connected to lugs on the bus bar directly.

 

Al Frishman
(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com http://www.aeonsolar.com/ 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter outputs

 

Another key is to remember that this discussion also applies to
the conductor between the main panel and subpanel. In a large PV system,
this could result in a pretty large wire between the two panels, and a
significant cost that is often overlooked. In some cases it makes sense
to locate the subpanel close to the main panel and run multiple sets of
smaller wires from the inverters to the subpanel.

 

And because the calculation is based on the first OC protection
connected to the inverters, adding a main breaker (theoretically 80A in
this example) in the subpanel doesn't change things. Even though this
wire would be theoretically protected by an 80A breaker at each end, you
can't size the wire for 160A / 1.2 = 133.3A. You have to size for
180A/1.2 = 150A. (not that it makes much of a difference in this
example, but it still must be considered)

 

At least that's how I understand it...

 

Jason Szumlanski

Fafco Solar 

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Wednesday, March 30, 2011 1:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to
combinemultipleinverter 

Re: [RE-wrenches] sizing a sub-panel used tocombine multipleinverter outputs

2011-03-30 Thread Exeltech
Per your question:

 1 - What does a UL1741 inverter do when it is connected
 to a 
line that is experiencing a short-circuit or ground fault?

Presuming a hard short, the voltage in that circuit would be essentially zero, 
and a UL1741 compliant inverter would cease producing power in less than 0.1 
second.


Dan
Sr. Engineer
Exeltech








--- On Wed, 3/30/11, Mark Frye ma...@berkeleysolar.com wrote:

From: Mark Frye ma...@berkeleysolar.com
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombine multipleinverter 
outputs
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date: Wednesday, March 30, 2011, 12:37 PM



 
 
 _filtered #yiv1283215088 {
font-family:Helvetica;}
 _filtered #yiv1283215088 {
font-family:Helvetica;}
 _filtered #yiv1283215088 {
font-family:Calibri;}
 _filtered #yiv1283215088 {
font-family:Tahoma;}
 _filtered #yiv1283215088 {
}
That is a really good question Brian.
 
Mostly when thinking about these sizing issues I think about 
overload conditions and not so much about short-circuit and ground fault 
conditions.
 
So two questions come up:
 
1 - What does a UL1741 inverter do when it is connected to a 
line that is experiencing a short-circuit or ground fault?
 
2 - What does the feeder breaker do when it is connected to a 
line that is experiencing a short-circuit or ground fault?
 
As far as number two, thanks to all the great work we do 
establishing low impedence fault paths back to circuirt protectors, the breaker 
is going to trip at it's rating and protect the wire at the same 
rating. But that doesn't mean that the conductor won't see more 
than rated amps during the fault. It will see alot more than for a 
very short time. During this very short time frame, the actual currents flowing 
into the fault from the utility side of the equation far far exceed the 
currents 
contributed by the power limited inverter side.
 
Mark Frye 

Berkeley Solar Electric 
Systems 
303 Redbud 
Way 
Nevada 
City,  CA 95959 
(530) 401-8024 
www.berkeleysolar.com  
 



From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian 
Teitelbaum
Sent: Wednesday, March 30, 2011 10:02 AM
To: 
RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used 
tocombine multipleinverter outputs




Wouldn’t 
a fault in that conductor between the main and the sub have a potential for up 
to 160A of current? I would think that at noon on a sunny day, the inverter 
system could produce 80A from one direction (albeit really only the max 
amperage 
outputs of the inverters) and 80A of grid current from the main into a partial 
fault. 
   
Brian 
Teitelbaum 
AEE 
Solar  
   


From: 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark 
Frye
Sent: Wednesday, March 30, 2011 9:49 AM
To: 
'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to 
combine multipleinverter outputs 
   
Al, 
  
I would 
say that yes the meter is a load and this goes to show the relative inadequacy 
of the vocabulary we are using in the discussion. In the example we have been 
using with the 80A breaker, wire and sub panel, you could have up to 80A of 
loads installed in the sub and still not create an over current condition in 
any 
of that equipment. 

Mark 
Frye 
Berkeley 
Solar Electric Systems 
303 
Redbud Way 
Nevada 
City,  CA 95959 
(530) 
401-8024 
www.berkeleysolar.com   

  
   



From: 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Al 
Frishman
Sent: Wednesday, March 30, 2011 9:00 AM
To: 
'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to 
combine multipleinverter outputs 
Is 
a monitoring system installed in the Load Center to measure the cumulative 
kWh’s 
of the inverter’s considered a load?   
The 
type of monitoring device I am talking about has CT’s that go around the 
conductors and the Voltage ref is taken by attaching conductors to each phase, 
the Neutral and the ground bar.    The digital Meter has a 3-pole 
5A breaker in it so the conductors in the load center can be connected to lugs 
on the bus bar directly. 
   

Al 
Frishman
AeonSolar 
(917) 699-6641 
- cell
(888) 
460-2867
www.aeonsolar.com 
   
   


From: 
re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason 
Szumlanski
Sent: Wednesday, March 30, 2011 8:18 AM
To: 
RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used to 
combinemultipleinverter outputs 
   
Another 
key is to remember that this discussion also applies to the conductor between 
the main panel and subpanel. In a large PV system, this could result in a 
pretty 
large wire between the two panels, and a significant cost that is often 
overlooked. In some cases it makes sense to locate the subpanel close to the 
main panel and run multiple sets of smaller wires from the inverters to the 
subpanel. 
   
And 
because the 

Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter outputs

2011-03-30 Thread Mark Frye
Right, so going totally on the fly at the white board, let's say we have an
inverter with a 45A AC output, it see's the short and pours it's little
heart out at 45A for 0.1 sec before shutting out, delivering 4.5 A-sec of
energy into the fault.  Meanwhile we take out a clearing time curve for the
generic 60A breaker that the inverter would be backfeed at the other end of
the feeder. It will deliver 10 times it's rating or 600A for 0.5 secs before
clearing. That's 300 A-sec of energy, 66 times more than the inverter.
 
So can we say that when looking at sizing the AC side of these inverters we
need more to concern ourselves with continuous overload conditions and not
so much with short-circuit/ground fault conditions?
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Exeltech
Sent: Wednesday, March 30, 2011 12:04 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombinemultipleinverter
outputs


Per your question:

 1 - What does a UL1741 inverter do when it is connected
 to a line that is experiencing a short-circuit or ground fault?

Presuming a hard short, the voltage in that circuit would be essentially
zero, and a UL1741 compliant inverter would cease producing power in less
than 0.1 second.


Dan
Sr. Engineer
Exeltech








--- On Wed, 3/30/11, Mark Frye ma...@berkeleysolar.com wrote:




From: Mark Frye ma...@berkeleysolar.com
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombine
multipleinverter outputs
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date: Wednesday, March 30, 2011, 12:37 PM


That is a really good question Brian.
 
Mostly when thinking about these sizing issues I think about overload
conditions and not so much about short-circuit and ground fault conditions.
 
So two questions come up:
 
1 - What does a UL1741 inverter do when it is connected to a line that is
experiencing a short-circuit or ground fault?
 
2 - What does the feeder breaker do when it is connected to a line that is
experiencing a short-circuit or ground fault?
 
As far as number two, thanks to all the great work we do establishing low
impedence fault paths back to circuirt protectors, the breaker is going to
trip at it's rating and protect the wire at the same rating. But that
doesn't mean that the conductor won't see more than rated amps during the
fault. It will see alot more than for a very short time. During this very
short time frame, the actual currents flowing into the fault from the
utility side of the equation far far exceed the currents contributed by the
power limited inverter side.

Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  
 

  _  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Brian
Teitelbaum
Sent: Wednesday, March 30, 2011 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] sizing a sub-panel used tocombine
multipleinverter outputs



Wouldn't a fault in that conductor between the main and the sub have a
potential for up to 160A of current? I would think that at noon on a sunny
day, the inverter system could produce 80A from one direction (albeit really
only the max amperage outputs of the inverters) and 80A of grid current from
the main into a partial fault.

 

Brian Teitelbaum

AEE Solar 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, March 30, 2011 9:49 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

 

Al,

 

I would say that yes the meter is a load and this goes to show the relative
inadequacy of the vocabulary we are using in the discussion. In the example
we have been using with the 80A breaker, wire and sub panel, you could have
up to 80A of loads installed in the sub and still not create an over current
condition in any of that equipment.


Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 http://www.berkeleysolar.com/ www.berkeleysolar.com  

 

 


  _  


From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Al Frishman
Sent: Wednesday, March 30, 2011 9:00 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] sizing a sub-panel used to combine
multipleinverter outputs

Is a monitoring system installed in the Load Center to measure the
cumulative kWh's of the inverter's considered a load?  

The type of monitoring device I am talking about has CT's that go around the
conductors and the Voltage ref is taken by attaching conductors to each
phase, the Neutral and the ground bar.The 

Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Bob-O Schultze
Troy,
On Mar 30, 2011, at 10:04 AM, Troy Harvey wrote:

I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have a 
city agency who is comfortable with the NABCEP certification as a 
qualification, but would like to see a stamp. Has anyone out there done this? 

Troy
I'm with Andrew here. If a NABCEP stamp of some kind makes the city happy and 
greases your permit approval, that's OK. If it is a city requirement, then we'd 
sure like to know about that. IF you do have one made, please remember to 
follow the NABCEP guidelines as to the use of our Mark. IE, your name -not 
the company name and not nothing- has to appear next to the Mark.
Cheers, bob-O

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Erika Weliczko
I hate to mention the evil insurance industry. However, a stamp implies some
professional liability insurance to me.

There are other professional membership organizations (RESNET) that have
developed a tailored professional liability insurance package for its
credentialed members with a preferred vendor.
Is NABCEP looking toward this? I do not know if there is a need, but may be
an advantage under certain circumstances.

Peace,
Erika

REpower SOLUTIONS
www.repowersolutions.com
P: 216.268.2275
C: 216.402.4458

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob-O
Schultze
Sent: Wednesday, March 30, 2011 5:47 PM
To: RE-wrenches
Subject: [SPAM] Re: [RE-wrenches] NABCEP Stamp

Troy,
On Mar 30, 2011, at 10:04 AM, Troy Harvey wrote:

I am wondering if anyone has had a NABCEP stamp made to stamp plans. I have
a city agency who is comfortable with the NABCEP certification as a
qualification, but would like to see a stamp. Has anyone out there done
this? 

Troy
I'm with Andrew here. If a NABCEP stamp of some kind makes the city happy
and greases your permit approval, that's OK. If it is a city requirement,
then we'd sure like to know about that. IF you do have one made, please
remember to follow the NABCEP guidelines as to the use of our Mark. IE,
your name -not the company name and not nothing- has to appear next to the
Mark.
Cheers, bob-O

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Expansion joints

2011-03-30 Thread Erika Weliczko
I recently used a Hubbell Killark product for rigid/IMC and was not happy with 
how the threads of the coupling engaged in factory conduit threads.

 

Crousehinds XJG-EMT series is intended for EMT. And is described as being used 
indoors or outdoors. The EMT couplings mostly seem to be compression.

 

 

REpower SOLUTIONS

www.repowersolutions.com

P: 216.268.2275

C: 216.402.4458

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jamie Johnson
Sent: Tuesday, March 29, 2011 2:33 PM
To: RE-wrenches
Subject: [SPAM] Re: [RE-wrenches] Expansion joints

 

Peter,

 

Cooper makes one for 1.5 emt, not sure if it is rated for wet locations or not.

 

part #XJG54 EMT, it allows for up to 4 max of conduit movement.

 

Jamie Johnson

NABCEP Certified PV Technical Sales Professional

NABCEP Certified Solar PV Installer

 

General Manager

SOLAR POWER ELECTRIC



 



 

 

 Original Message 
Subject: [RE-wrenches] Expansion joints
From: Peter Parrish peter.parr...@calsolareng.com 
http://peter.parr...@calsolareng.com%3e ;
Date: Tue, March 29, 2011 1:04 pm
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org

Does anyone have information (manu and part number) for expansion joints for
1-1/2 EMT? I have also heard that many EJs are designed for rigid conduit
(RMC) and may not be directly applicable to EMT.

- Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com 
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NABCEP Stamp

2011-03-30 Thread Bill Brooks
Andrew and Troy,

 

While I can't speak for NABCEP, I would expect that NABCEP should be very
opposed to this type of use of their logo. NABCEP does not certify the work
that a NABCEP certificant does. They only certify that the installer has met
the obligations for certification. There is a HUGE difference between the
two. NABCEP cannot, and should not, be held accountable for work that
someone does in the field. A contactor's work is covered by the state laws
and the licenses required to perform that work in that state. 

 

Just because a local jurisdictions thinks that getting a certification from
NABCEP means something to the installation, does not mean that the
information should be on the plan set. Information about the certification
of the installer should be provided separately. 

 

Don't make a stamp, whatever you do.

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Andrew
Truitt
Sent: Wednesday, March 30, 2011 10:57 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] NABCEP Stamp

 

Troy - I have not encountered this before but would you mind sharing what
city agency you are refering to?  NABCEP is always interested in hearing
about these types of unconventional uses of the certification.

 

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org