Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Dave Click
At an SMA training last year they recommended the following temperature 
adders:


Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good 
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
inverter with a 300V+ tracking window wouldn't work very well during the 
summers for very long. My own rooftop system has a design VMP of around 
294 at 70C module temperature and I've seen it a bit lower than that on 
a sunny day-- I think it's because in irradiances below 1000Wm/2, the 
modules can still get plenty hot but the lower irradiance doesn't bring 
the VMP up to 100%. So all told, maybe plan for an array minimum of:


Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:

Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the low
voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add
a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be pretty
close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 1000
W/sq irradiance, the temperature rise can obviously be more too. Between
the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the temperature coefficient for Vmp is higher
than that the temperature coefficient for Voc. That's particularly true
when the coefficient is expressed as a percentage per °C. Since there
are very few manufacturer's that give both temperature coefficients,
I'll use a value from an old Evergreen module for an example. The
Evergreen ES-195 datasheet shows Voc = 30.5 volts with a coefficient of
-0.34%/°C and Vmp = 27.1 volts with a coefficient of -0.47%/°C. Since
one shouldn't add volts and percents, I'll put the temperature
coefficients in volts/°C: Voc = 30.5 V - 0.10 V/°C and Vmp = 27.1 V -
0.13V/°C. So Vmp is moving faster than Voc, but not a lot faster. That's
generically true for c-Si or poly-Si.

Kent Osterberg

Blue Mountain Solar, Inc.

www.bluemountainsolar.com  http://www.bluemountainsolar.com

t: 541-568-4882


On 11/29/2011 11:48 AM, Kirk Herander wrote:

I am in debate with a PE over calculation of low voltage of a series
string on a hot day. He insists that an arbitrary high cell temp is
factored in, not just ambient temperature. Could someone please give an
accepted formula for this calculation? Thanks. I cannot find a clear
reference to low voltage calculation on a hot day (but every reference
material is clear on how to calculate high voltage on a cold 

Re: [RE-wrenches] Diversion load for AC coupled system

2011-12-01 Thread Hugh

At 12:16 -0700 30/11/11, Larry Crutcher,
Here's a scenario: Sun is up and voltage rises slowly to the 
diversion controller set point. PWM starts and maintains the 
voltage. Current continues to increase but the load is keeping the 
voltage constant until the controller is overloaded.


I think the point that most people don't get is that you can't 
overload the controller if you choose the correct dump load.  You can 
get to the point where the dump load is fully turned on (100% duty 
cycle) and then it is 'overloaded' in the sense that it has not 
further ability to limit the rise in voltage.  However it will not be 
damaged.   Then the voltage will rise further and hopefully another 
controller will start dumping or something good will happen to 
protect the batteries from damage.


If you have 2 controllers with dump loads that can handle 150% of the 
incoming PV current between them then you can be sure of never 
'overloading' them.  But it will not matter if you 'overload' one 
before the other comes on because it will never draw more current 
than the dump load takes at the prevailing voltage.


Here is a calculation:

3.8 kW at float voltage 54 volts gives 3800/54 = 70.4 amps.
According to NEC you multiply this by 1.5 to get 106 amps.
Now you need to choose dump loads that will each dump at least 53 
amps at 54 volts. (1.02 ohms, maybe one ohm plus resistance of leads.)
These will be the same loads as will do 60 amps at 61 volts and they 
are the lowest resistance you can safely use with the TS60.  If you 
plan to EQ at voltages higher than 61 then you need to use higher 
resistance and you cannot meet the NEC target of 150% of incoming 
current at float voltages.


That's how I see it anyway.  It's possible that the NEC thing does 
not required you to look at float voltage.


all the best,
--
Hugh Piggott

Scoraig
http://www.scoraigwind.co.uk
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] OutBack Radian

2011-12-01 Thread penobscotsolar
Hi all,
   We are looking at a busy winter season and there are several systems
I'd like to size using OutBack's Radian. These are all out of the
country jobs and I would be interested in any experiences anyone has
had so far installing and/or using these seemingly great inverters.
   I would likely be using them in HBX mode, so secondary inquiries would
be around susing the Mate3. Is it any more intuitive than the Mate?
Similar in programming?
   Any thoughts from anyone with experience with Radian systems would be
greatly appreciated.

Thanks,
Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] OutBack Radian

2011-12-01 Thread Orion Thornton
Daryl,

We have not had any hands on experience yet with the Radian series
inverters, and only minimal interaction with the MATE3.  But since you
mentioned that your systems would be out of country I thought I would
bring up the fact that the Radian inverters only come in 60Hz models, no
50Hz output available.

Orion Thornton
Project Manager
Independent Power Systems
NABCEP Certified PV Installer
(Office) 406.587.5295
(Mobile) 406.249.9912
www.solarips.com



-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
penobscotso...@midmaine.com
Sent: Thursday, December 01, 2011 12:25 PM
To: RE-wrenches
Subject: [RE-wrenches] OutBack Radian

Hi all,
   We are looking at a busy winter season and there are several systems
I'd like to size using OutBack's Radian. These are all out of the
country jobs and I would be interested in any experiences anyone has
had so far installing and/or using these seemingly great inverters.
   I would likely be using them in HBX mode, so secondary inquiries would
be around susing the Mate3. Is it any more intuitive than the Mate?
Similar in programming?
   Any thoughts from anyone with experience with Radian systems would be
greatly appreciated.

Thanks,
Daryl DeJoy
NABCEP Certified PV installer
Penobscot Solar Design

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Ray Walters
That's more detailed info, but I still am wondering what ambient temp to 
apply (which AHSRAE #) with the temp adder.  Daryl suggested using a 2% 
high temp.  Also, where are you all getting your weather data?  I found 
the NEC suggested ASHRAE manual to be close to $200.  That's a bit much 
just to get a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely 
codified, and I'm trying to standardize it somewhat for my PV class. Non 
of the design manuals I have currently are even close to this level of 
complexity, yet this is obviously an important calculation.  Should I 
suggest that my students just use the inverter manufacturers' online 
tools, and forget about trying to run this voltage calc themselves?


Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:
At an SMA training last year they recommended the following 
temperature adders:


Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good 
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
inverter with a 300V+ tracking window wouldn't work very well during 
the summers for very long. My own rooftop system has a design VMP of 
around 294 at 70C module temperature and I've seen it a bit lower than 
that on a sunny day-- I think it's because in irradiances below 
1000Wm/2, the modules can still get plenty hot but the lower 
irradiance doesn't bring the VMP up to 100%. So all told, maybe plan 
for an array minimum of:


Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:

Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the low
voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add
a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be pretty
close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 1000
W/sq irradiance, the temperature rise can obviously be more too. Between
the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the temperature coefficient for Vmp is higher
than that the temperature coefficient for Voc. That's particularly true
when the coefficient is expressed as a percentage per °C. Since there
are very few manufacturer's that give both temperature coefficients,
I'll use a value from an old Evergreen module for an example. The
Evergreen ES-195 datasheet shows Voc = 30.5 volts with a coefficient of
-0.34%/°C and Vmp = 27.1 volts with a coefficient of -0.47%/°C. Since
one 

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Gary Willett

Ray:

Look at Appendix F in the Expedited Permit Process for PV Systems - A 
Standardized Process for the Review of Small-Scale PV Systems Prepared 
by Bill Brooks, P.E. Brooks Engineering


This document provides the ASHRE temperatures for a lot of locations 
around the USA.


http://www.solarabcs.org/about/publications/reports/expedited-permit/pdfs/Expermitprocess.pdf


Regards,


Gary Willett, PE


On 12/1/2011 14:48, Ray Walters wrote:
That's more detailed info, but I still am wondering what ambient temp 
to apply (which AHSRAE #) with the temp adder.  Daryl suggested using 
a 2% high temp.  Also, where are you all getting your weather data?  I 
found the NEC suggested ASHRAE manual to be close to $200.  That's a 
bit much just to get a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely 
codified, and I'm trying to standardize it somewhat for my PV class. 
Non of the design manuals I have currently are even close to this 
level of complexity, yet this is obviously an important calculation.  
Should I suggest that my students just use the inverter manufacturers' 
online tools, and forget about trying to run this voltage calc 
themselves?


Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:
At an SMA training last year they recommended the following 
temperature adders:


Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good 
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
inverter with a 300V+ tracking window wouldn't work very well during 
the summers for very long. My own rooftop system has a design VMP of 
around 294 at 70C module temperature and I've seen it a bit lower 
than that on a sunny day-- I think it's because in irradiances below 
1000Wm/2, the modules can still get plenty hot but the lower 
irradiance doesn't bring the VMP up to 100%. So all told, maybe plan 
for an array minimum of:


Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:
Thanks for all the good response. Speaking of monkey wrenches, these 
are

Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the 
low

voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to 
add

a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be 
pretty

close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 
1000
W/sq irradiance, the temperature rise can obviously be more too. 
Between

the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the 

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Glenn Burt
ASHRAE temp data as applicable to PV can be found (with some digging) on the
Solar ABCs website.
http://solarabcs.org/about/publications/reports/expedited-permit/map/map_int
ro.html

-Glenn

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Thursday, December 01, 2011 3:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating low string voltage

That's more detailed info, but I still am wondering what ambient temp to
apply (which AHSRAE #) with the temp adder.  Daryl suggested using a 2% high
temp.  Also, where are you all getting your weather data?  I found the NEC
suggested ASHRAE manual to be close to $200.  That's a bit much just to get
a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely
codified, and I'm trying to standardize it somewhat for my PV class. Non of
the design manuals I have currently are even close to this level of
complexity, yet this is obviously an important calculation.  Should I
suggest that my students just use the inverter manufacturers' online tools,
and forget about trying to run this voltage calc themselves?

Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:
 At an SMA training last year they recommended the following 
 temperature adders:

 Open field: +22°C
 Rooftop, lots of ventilation: +28°C
 Rooftop, some ventilation: +29°C
 Rooftop, little ventilation: +32°C
 Rooftop BIPV, no ventilation: +43°C
 Façade, some ventilation: +35°C
 Façade, little ventilation: +39°C
 Façade BIPV, no ventilation: +55°C

 For your Sanyo project, I'd agree that the pole mount would be a good 
 fit and +25C would seem to be OK. As you know, the 301VDC VMP on an 
 inverter with a 300V+ tracking window wouldn't work very well during 
 the summers for very long. My own rooftop system has a design VMP of 
 around 294 at 70C module temperature and I've seen it a bit lower than 
 that on a sunny day-- I think it's because in irradiances below 
 1000Wm/2, the modules can still get plenty hot but the lower 
 irradiance doesn't bring the VMP up to 100%. So all told, maybe plan 
 for an array minimum of:

 Inverter Tracking Minimum
 /0.85 (degradation and voltage tolerance)
 /0.95 (effect I just described)
 /0.825 (60C operating temp)
 = minimum string VMP at STC

 (similar to what Bill said)

 On 2011/11/30 11:04, Kirk Herander wrote:
 Thanks for all the good response. Speaking of monkey wrenches, these 
 are Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet  
 above the roof surface. They will absorb reflected light on the 
 backside, so I assume the cells will operate at a higher temp. But 
 they are elevated enough to simulate a pole-mount, thus lowering 
 operating cell temp. So what operating temp to use? If I use 25 C as 
 the operating temp, the low voltage calc comes out to 301 vdc 
 (inverter min is 300 – using SMA US8000). If I use 15 C the calc is 
 308 vdc. This is for a 6 panel string. Unfortunately I really don’t 
 want to use 7 panel strings due to the layout. If I used a US7000 it
would work since min vdc in is 250.
 However the inverters are part of a SunnyTower and I can’t swap a 
 7000 for an 8000 without voiding the Tower UL listing.

 Kirk Herander

 VT Solar, LLC

 dba Vermont Solar Engineering

 NABCEP^TM Certified installer Charter Member

 NYSERDA-eligible Installer

 VT RE Incentive Program Partner

 *From:*re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
 *b...@midnitesolar.com
 *Sent:* Wednesday, November 30, 2011 1:03 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] calculating low string voltage



 If you really want to throw a monkey wrench into the mix, bring up 
 partial shading...

 Or, maybe that's just not allowed in that debate ?? Just a thought.

 boB







 On 11/29/2011 8:39 PM, Kent Osterberg wrote:

 Kirk,

 You've got some good feedback on this from Ray and Bill. I'll try to 
 add a little more. Most module datasheets show a normal operating 
 cell temperature, NOCT, value that's typically 47.5°C. That's 20°C 
 ambient temperature, 800 W/sq m, and calm wind and nothing blocking 
 the airflow on the back of the module. That 27.5°C temperature rise 
 should be pretty close to the temperature rise that occurs for a 
 pole-top mount. It's common to see people use 25°C for modules on a 
 pole and 30°C or 35°C on a roof and there are data that support these 
 typical values. With 1000 W/sq irradiance, the temperature rise can 
 obviously be more too. Between the intensity of the sun, the 
 direction of the sun, the color of the roof, the spacing off the 
 roof, and the wind speed there is a lot that is different from one system
to the next or even one day to the next.

 Most PV module spec sheets don't give you a temperature coefficient 
 for Vmp. I've seen people use the the Voc coefficient, usually 
 expressed as a percentage, 

Re: [RE-wrenches] OutBack Radian

2011-12-01 Thread penobscotsolar
Thanks Orion,
   Most of our work in the winter is in the Caribbean and Mexico and they
all use 60 hz. I appreciate it, though.

Daryl



 Daryl,

 We have not had any hands on experience yet with the Radian series
 inverters, and only minimal interaction with the MATE3.  But since you
 mentioned that your systems would be out of country I thought I would
 bring up the fact that the Radian inverters only come in 60Hz models, no
 50Hz output available.

 Orion Thornton
 Project Manager
 Independent Power Systems
 NABCEP Certified PV Installer
 (Office) 406.587.5295
 (Mobile) 406.249.9912
 www.solarips.com



 -Original Message-
 From: re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
 penobscotso...@midmaine.com
 Sent: Thursday, December 01, 2011 12:25 PM
 To: RE-wrenches
 Subject: [RE-wrenches] OutBack Radian

 Hi all,
We are looking at a busy winter season and there are several systems
 I'd like to size using OutBack's Radian. These are all out of the
 country jobs and I would be interested in any experiences anyone has
 had so far installing and/or using these seemingly great inverters.
I would likely be using them in HBX mode, so secondary inquiries would
 be around susing the Mate3. Is it any more intuitive than the Mate?
 Similar in programming?
Any thoughts from anyone with experience with Radian systems would be
 greatly appreciated.

 Thanks,
 Daryl DeJoy
 NABCEP Certified PV installer
 Penobscot Solar Design

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Dave Click
Ray, I'd use the 2% high temp. The 0.4% high temp would only be reached 
a few hours out of the year. However, the 0.4% high is only a few degC 
warmer than the 2% high, so that would change my fudge factor below by a 
max of 1.8-2.0%.


On 2011/12/1 15:48, Ray Walters wrote:

That's more detailed info, but I still am wondering what ambient temp to
apply (which AHSRAE #) with the temp adder. Daryl suggested using a 2%
high temp. Also, where are you all getting your weather data? I found
the NEC suggested ASHRAE manual to be close to $200. That's a bit much
just to get a couple of numbers for our design.
It seems this calculation of low voltage is far from being entirely
codified, and I'm trying to standardize it somewhat for my PV class. Non
of the design manuals I have currently are even close to this level of
complexity, yet this is obviously an important calculation. Should I
suggest that my students just use the inverter manufacturers' online
tools, and forget about trying to run this voltage calc themselves?

Thanks,

Ray

On 12/1/2011 6:30 AM, Dave Click wrote:

At an SMA training last year they recommended the following
temperature adders:

Open field: +22°C
Rooftop, lots of ventilation: +28°C
Rooftop, some ventilation: +29°C
Rooftop, little ventilation: +32°C
Rooftop BIPV, no ventilation: +43°C
Façade, some ventilation: +35°C
Façade, little ventilation: +39°C
Façade BIPV, no ventilation: +55°C

For your Sanyo project, I'd agree that the pole mount would be a good
fit and +25C would seem to be OK. As you know, the 301VDC VMP on an
inverter with a 300V+ tracking window wouldn't work very well during
the summers for very long. My own rooftop system has a design VMP of
around 294 at 70C module temperature and I've seen it a bit lower than
that on a sunny day-- I think it's because in irradiances below
1000Wm/2, the modules can still get plenty hot but the lower
irradiance doesn't bring the VMP up to 100%. So all told, maybe plan
for an array minimum of:

Inverter Tracking Minimum
/0.85 (degradation and voltage tolerance)
/0.95 (effect I just described)
/0.825 (60C operating temp)
= minimum string VMP at STC

(similar to what Bill said)

On 2011/11/30 11:04, Kirk Herander wrote:

Thanks for all the good response. Speaking of monkey wrenches, these are
Sanyo HIT Double panels, mounted on a rack which is 5 ½ feet above the
roof surface. They will absorb reflected light on the backside, so I
assume the cells will operate at a higher temp. But they are elevated
enough to simulate a pole-mount, thus lowering operating cell temp. So
what operating temp to use? If I use 25 C as the operating temp, the low
voltage calc comes out to 301 vdc (inverter min is 300 – using SMA
US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
string. Unfortunately I really don’t want to use 7 panel strings due to
the layout. If I used a US7000 it would work since min vdc in is 250.
However the inverters are part of a SunnyTower and I can’t swap a 7000
for an 8000 without voiding the Tower UL listing.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
*b...@midnitesolar.com
*Sent:* Wednesday, November 30, 2011 1:03 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage



If you really want to throw a monkey wrench into the mix, bring up
partial shading...

Or, maybe that's just not allowed in that debate ?? Just a thought.

boB







On 11/29/2011 8:39 PM, Kent Osterberg wrote:

Kirk,

You've got some good feedback on this from Ray and Bill. I'll try to add
a little more. Most module datasheets show a normal operating cell
temperature, NOCT, value that's typically 47.5°C. That's 20°C ambient
temperature, 800 W/sq m, and calm wind and nothing blocking the airflow
on the back of the module. That 27.5°C temperature rise should be pretty
close to the temperature rise that occurs for a pole-top mount. It's
common to see people use 25°C for modules on a pole and 30°C or 35°C on
a roof and there are data that support these typical values. With 1000
W/sq irradiance, the temperature rise can obviously be more too. Between
the intensity of the sun, the direction of the sun, the color of the
roof, the spacing off the roof, and the wind speed there is a lot that
is different from one system to the next or even one day to the next.

Most PV module spec sheets don't give you a temperature coefficient for
Vmp. I've seen people use the the Voc coefficient, usually expressed as
a percentage, for both Voc and Vmp. Big mistake. Data from NREL
indicates as Bill said, the temperature coefficient for Vmp is higher
than that the temperature coefficient for Voc. That's particularly true
when the coefficient is expressed as a percentage per °C. Since there
are very few manufacturer's 

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Bill Brooks
Ray,

There is an explanation on the www.solarabcs.org/permitting webpage for the
interactive solar map. The 2% ASHRAE data represents 14 hours in a
month-meaning temperature will be at or above that value for 14 hours in a
typical month. This is likely to correspond to at least one 3-hour timeframe
which is considered continuous in the NEC. The Copper Development
Association has chosen this number for ambient temperature calculations in
the NEC. The NEC Handbook (not the NEC) uses this number in their example
problems. 

The 0.4% ASHRAE date represents 3 hours in a month. It is much more
conservative number. I put it in the data to provide a context for the 2%
number and it allows engineers to consider a more conservative number.

Of course, the mean extreme minimum drybulb temperature is also on that
website for 690.7 max system voltage calculations. Enjoy-its free thanks to
SolarABCs.

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Thursday, December 01, 2011 3:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating low string voltage

 

Fantastic Info everyone, I think I've got a full grasp on this topic now,
from using the correct coefficient to the correct weather data, to the
adders for installation type, and a nice link to the applicable data without
spending $180 for the ASHRAE book.  

I'm guessing the 2% number is 2%  of the time year round 24/7, not 2% of the
time the sun is shining, so losses could be higher than 2% of production?
Sorry to keep asking questions, but I know my class will probably ask the
same thing.

Ray

On 12/1/2011 2:57 PM, Gary Willett wrote: 

RAY:

This Solar Reference Guide Map web site is also linked to on the SolarABCs
site and provides the ASHRAE 0.4%   2% high temperatures, as well as the PV
module max temp based on distance above the roof (0.5, 3.5, and 12).

http://www.solarabcs.org/about/publications/reports/expedited-permit/map/ind
ex.html

Regards,

Gary Willett, PE


On 12/1/2011 14:56, Gary Willett wrote: 

Ray:  

Look at Appendix F in the Expedited Permit Process for PV Systems - A
Standardized Process for the Review of Small-Scale PV Systems Prepared by
Bill Brooks, P.E. Brooks Engineering

This document provides the ASHRE temperatures for a lot of locations around
the USA.

http://www.solarabcs.org/about/publications/reports/expedited-permit/pdfs/Ex
permitprocess.pdf



Regards,


Gary Willett, PE

 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread David Brearley
http://www.copper.org/applications/electrical/building/pdf/rooftop.pdf

³ASHRAE bases its ³warm-season temperature conditions² for each city on
annual percentiles of 0.4%, 2 %, 5% and 10%. As an example, the June 2.0%
dry-bulb design temperature for Atlanta is 91.7°F. Therefore, based on a
30-day month (i.e., 720 hours), the actual temperatures can be expected to
exceed 91.7°F for total of 14 hours a month. The corresponding 5.0% design
temperature (89.3°F) can be expected to be exceeded for 36 hours a month;
while the 0.4% design temperature (94.7°F) can be expected to be exceeded
for 3 hours a month.²



On 12/1/11 5:57 PM, Ray Walters r...@solarray.com wrote:

Fantastic Info everyone, I think I've got a full grasp on this topic now,
 from using the correct coefficient to the correct weather data, to the adders
 for installation type, and a nice link to the applicable data without spending
 $180 for the ASHRAE book.
  
  I'm guessing the 2% number is 2%  of the time year round 24/7, not 2% of the
 time the sun is shining, so losses could be higher than 2% of production?
 Sorry to keep asking questions, but I know my class will probably ask the same
 thing.
  
  Ray
  
  On 12/1/2011 2:57 PM, Gary Willett wrote:
   RAY:
  
  This Solar Reference Guide Map web site is also linked to on the SolarABCs
 site and provides the ASHRAE 0.4%   2% high temperatures, as well as the PV
 module max temp based on distance above the roof (0.5, 3.5, and 12).
  
  
 http://www.solarabcs.org/about/publications/reports/expedited-permit/map/inde
 x.html
  
   

  
 
 Regards,
  
  Gary Willett, PE
  
  
  
  On 12/1/2011 14:56, Gary Willett wrote:
   Ray:  
  
  Look at Appendix F in the Expedited Permit Process for PV Systems - A
 Standardized Process for the Review of Small-Scale PV Systems Prepared by
 Bill Brooks, P.E. Brooks Engineering
  
  This document provides the ASHRE temperatures for a lot of locations around
 the USA.
  
  
 http://www.solarabcs.org/about/publications/reports/expedited-permit/pdfs/Ex
 permitprocess.pdf
  
  
   

  
 
 Regards,
  
  
  Gary Willett, PE
  
  
  
  On 12/1/2011 14:48, Ray Walters wrote:
 That's  more detailed info, but I still am wondering what ambient temp to
 apply (which AHSRAE #) with the temp adder.  Daryl suggested using a 2%
 high temp.  Also, where are you all getting your weather data?  I found the
 NEC suggested ASHRAE manual to be close to $200.  That's a bit much just to
 get a couple of numbers for our design.
  It seems this calculation of low voltage is far from being entirely
 codified, and I'm trying to standardize it somewhat for my PV class. Non of
 the design manuals I have currently are even close to this level of
 complexity, yet this is obviously an important calculation.  Should I
 suggest that my students just use the inverter manufacturers' online tools,
 and forget about trying to run this voltage calc themselves?
  
  Thanks, 
  
  Ray 
  
  On 12/1/2011 6:30 AM, Dave Click wrote:
  
 At an SMA training last year they recommended the following temperature
 adders: 
  
  Open field: +22°C
  Rooftop, lots of ventilation: +28°C
  Rooftop, some ventilation: +29°C
  Rooftop, little ventilation: +32°C
  Rooftop BIPV, no ventilation: +43°C
  Façade, some ventilation: +35°C
  Façade, little ventilation: +39°C
  Façade BIPV, no ventilation: +55°C
  
  For your Sanyo project, I'd agree that the pole mount would be a good fit
 and +25C would seem to be OK. As you know, the 301VDC VMP on an inverter
 with a 300V+ tracking window wouldn't work very well during the summers
 for very long. My own rooftop system has a design VMP of around 294 at 70C
 module temperature and I've seen it a bit lower than that on a sunny day--
 I think it's because in irradiances below 1000Wm/2, the modules can still
 get plenty hot but the lower irradiance doesn't bring the VMP up to 100%.
 So all told, maybe plan for an array minimum of:
  
  Inverter Tracking Minimum
  /0.85 (degradation and voltage tolerance)
  /0.95 (effect I just described)
  /0.825 (60C operating temp)
  = minimum string VMP at STC
  
  (similar to what Bill said)
  
  On 2011/11/30 11:04, Kirk Herander wrote:
  
 Thanks for all the good response. Speaking of monkey wrenches, these are
  Sanyo HIT Double panels, mounted on a rack which is 5 1Ž2 feet  above 
 the
  roof surface. They will absorb reflected light on the backside, so I
  assume the cells will operate at a higher temp. But they are elevated
  enough to simulate a pole-mount, thus lowering operating cell temp. So
  what operating temp to use? If I use 25 C as the operating temp, the low
  voltage calc comes out to 301 vdc (inverter min is 300 ­ using SMA
  US8000). If I use 15 C the calc is 308 vdc. This is for a 6 panel
  string. Unfortunately I really don¹t want to use 7 panel strings due to
  the layout. If I used a US7000 it would work since min vdc in is 250.
  However the inverters are part of a SunnyTower and I can¹t 

Re: [RE-wrenches] calculating low string voltage

2011-12-01 Thread Ray Walters

Again Thanks Bill and David;

Continued excellent information.
I just jumped on Solectria'a string sizing online tool, and what are 
they using for the Vmpp coefficent? just a tiny bit higher than the Voc 
coefficient.  SMAs new design tool just lists the Voc coeff.   I think 
some manus might need to be following this thread as well, and tweak 
their sizing tools appropriately.


Ray

On 12/1/2011 5:54 PM, Bill Brooks wrote:


Ray,

There is an explanation on the www.solarabcs.org/permitting 
http://www.solarabcs.org/permitting webpage for the interactive 
solar map. The 2% ASHRAE data represents 14 hours in a month---meaning 
temperature will be at or above that value for 14 hours in a typical 
month. This is likely to correspond to at least one 3-hour timeframe 
which is considered continuous in the NEC. The Copper Development 
Association has chosen this number for ambient temperature 
calculations in the NEC. The NEC Handbook (not the NEC) uses this 
number in their example problems.


The 0.4% ASHRAE date represents 3 hours in a month. It is much more 
conservative number. I put it in the data to provide a context for the 
2% number and it allows engineers to consider a more conservative number.


Of course, the mean extreme minimum drybulb temperature is also on 
that website for 690.7 max system voltage calculations. Enjoy---its 
free thanks to SolarABCs.


Bill.

*From:*re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray 
Walters

*Sent:* Thursday, December 01, 2011 3:58 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] calculating low string voltage

Fantastic Info everyone, I think I've got a full grasp on this topic 
now, from using the correct coefficient to the correct weather data, 
to the adders for installation type, and a nice link to the applicable 
data without spending $180 for the ASHRAE book.


I'm guessing the 2% number is 2%  of the time year round 24/7, not 2% 
of the time the sun is shining, so losses could be higher than 2% of 
production?  Sorry to keep asking questions, but I know my class will 
probably ask the same thing.


Ray

On 12/1/2011 2:57 PM, Gary Willett wrote:

RAY:

This Solar Reference Guide Map web site is also linked to on the 
SolarABCs site and provides the ASHRAE 0.4%  2% high temperatures, as 
well as the PV module max temp based on distance above the roof (0.5, 
3.5, and 12).


http://www.solarabcs.org/about/publications/reports/expedited-permit/map/index.html

Regards,

Gary Willett, PE


On 12/1/2011 14:56, Gary Willett wrote:

Ray:

Look at Appendix F in the Expedited Permit Process for PV Systems - A 
Standardized Process for the Review of Small-Scale PV Systems Prepared 
by Bill Brooks, P.E. Brooks Engineering


This document provides the ASHRE temperatures for a lot of locations 
around the USA.


http://www.solarabcs.org/about/publications/reports/expedited-permit/pdfs/Expermitprocess.pdf

Regards,


Gary Willett, PE

  



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] old trace manual

2011-12-01 Thread Howie Michaelson
Hi All,

Does anyone know of a link to the old Trace 2624 inverter/Charger (the one
with the plexiglass front. I believe the model number was U2624, but I'm
not positive.  I'm trying to remember what the maximum bulk voltage
setting was on it.  Also wondering how sensitive to lower gennie voltage
output (113 vAC) the charger was.  How much would that cut down on the
current output capacity?

Thanks,
Howie
-- 
Howie Michaelson
NABCEP Certified Solar PV Installer™

Catamount Solar, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric  Hot Water Incentive Partner
http://www.CatamountSolar.com
802-272-0004





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] SMA Sunny Design temperature/voltage calculations

2011-12-01 Thread Howie Michaelson
Apropos to the great discussion about temperature voltage calculations,
has anyone else been frustrated by the removal of output information on
the Sunny Design tool compared to the old on-line string sizing
calculator?  It was very useful to me to have the string sizer show the
temperature voltage calculations for low and high temperature - as far as
I know the only string sizing application that showed this info.

The defunct online sizer allowed me to quickly look at a variety stringing
options, see the impact on voltage, narrow down the possibilities and then
run my own voltage calculations to verify.  Sunny Design makes quickly
scanning various string options not so easy, and it buries the results
behind more obscure output info.  It is quite a sophisticated program, but
I wish they gave a way to see the calculations behind the choices it
makes.  Or am I just missing something?

Howie
-- 
Howie Michaelson
NABCEP Certified Solar PV Installer™

Catamount Solar, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric  Hot Water Incentive Partner
http://www.CatamountSolar.com
802-272-0004





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org