Re: [RE-wrenches] Starting fires for fun with string wiring

2012-03-12 Thread Chris Mason
Jeff,
In my limited knowledge of this issue, there is no doubt DC arcs have the
capacity to burn and are difficult to extinguish, and good wiring practices
are essential at these elevated voltages. However, you need to distinguish
between high temperature arcs which can burn, and Arc-Flash risks which
require special PPE and procedures. In order for the there to be a serious
risk of Arc-Flash, there has to be both a high voltage such as 480V and a
very high source current, in the order of 65,000 Symmetrical  Amperes, such
as you find near a HT/LT transformer. The extremely high current is what
creates the explosive heating of the air. Solar PV, being current limited,
has high enough DC voltages but does not have anywhere near the current
capacity and cannot cause arc flash.

Chris
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Starting fires for fun with string wiring

2012-03-12 Thread Dan Fink
The Midnite Classic controllers come with arc-fault protection built in.

-- 
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342 (voicemail)


On Mon, Mar 12, 2012 at 10:09 AM, JRQ quackkc...@yahoo.com wrote:
 I've been wondering about this since I read over the 2011 code:

 Are there any listed DC arc-flash products on the market yet, or scheduled
 to come to market within the next year?

 Also: will arc-flash protection come in the form of breakers that need to be
 installed externally, or will it be something internal to the inverters or
 charge controllers to which source circuits are wired? Will they need to be
 installed on each string, or can they function on a combined circuit?

 Do systems with DC optimizers or with micro-inverters have arc-fault
 protection at the module level?

 Jeffrey Quackenbush
 NABCEP Certified PV Installer
 Peripatetic Solar Technician

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Need info resource re wind hail damage

2012-03-12 Thread Steve McCarney
Hi Allen

For what it is worth I had a house in Puerto Rico with two modules on the
roof. Hurricane Marilyn blew the roof off of the house but the panels
stayed on for the ride. The roof landed upside down pinning the modules
under the debris. These the UniSolar UPM880 (non glass) and they survived
with minor cosmetic damage and still measured full output after they were
salvaged.

In Florida we were hit hard again by Hurricane Charlie, with 145 mph winds
reported nearby our home. This time the roof stayed on and again so did the
pv panels. We were the only place with power that first night since all the
grid was blown down. So, modules can survive some of the big winds if fixed
well enough and if you lucky. I have been lucky since none of our family or
friends were (physically) hurt in these storms.

Steve McCarney
Solar Electric Light Fund

On Thu, Mar 8, 2012 at 11:13 PM, Allan Sindelar 
al...@positiveenergysolar.com wrote:

 **
 Fellow Wrenches,
 We have an engineer-type whose wife wants badly to do a PV system, but he
 puts up barriers. In her words:

 Well, I don't know how long ago it was, surely old technology by now,  but
 some experimental solar panels at Sandia Labs were shattered by hail and it
 caused a big controversy.  My husband says it turned him off solar.It comes
 up every time I talk to him. Either he is complaining about the wind or the
 hail or whatever.

 I get to respond to this, and am seeking specific assistance: Can anyone
 send me a link to any formal standards, or reports of aggregated field
 experiences, indicating that wind and hail (not to leave out whatever)
 are not issues of concern when PV modules are installed correctly? Anything
 that came from Sandia Labs would be ideal, but it just has to be reputable
 enough to satisfy a grouchy retired national lab engineer. Web links,
 reports, product warranties, etc. - all good.

 Thank you in advance.
 Allan
 --
 *Allan Sindelar*
 *al...@positiveenergysolar.com* al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 *Positive Energy, Inc.*
 3201 Calle Marie
 Santa Fe, New Mexico 87507
 *505 424-1112*
 *www.positiveenergysolar.com* http://www.positiveenergysolar.com/

 *
 *


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Starting fires for fun with string wiring

2012-03-12 Thread Steve Jefferson
SMA will have AFCI protection built into the inverters. It is integrated into 
the inside of the inverter, so there are no extra components to install.
They work off of the combined circuit to offer the AFCI protection.

The units are listed but, won't be available for another couple of months. We 
are in the field testing stage now.

Thanks

SMA America, LLC
Steve Jefferson
Sr. Technical Service Specialist, Sunny Family
6020 West Oaks Blvd, Suite 300
Rocklin, CA 95765 - 3714
U.S.A.
Tel:  +1 916 625 0870
Fax: +1 916 624-2445
Service Line +1 877 697 6283 (Toll Free)
Email: steve.jeffer...@sma-america.com
www.SMA-America.comhttp://www.sma-america.com/

This email and any attachments thereto may contain SMA America, LLC 
confidential, privileged and private material for the sole use of the intended 
recipient. Any review, copying, or distribution of this email (or any 
attachments thereto) by others is strictly prohibited. If you are not the 
intended recipient, please contact the sender immediately and permanently 
delete the original and any copies of this email and any attachments thereto. 
Thank you.

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of JRQ
Sent: Monday, March 12, 2012 9:09 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Starting fires for fun with string wiring

I've been wondering about this since I read over the 2011 code:

Are there any listed DC arc-flash products on the market yet, or scheduled to 
come to market within the next year?

Also: will arc-flash protection come in the form of breakers that need to be 
installed externally, or will it be something internal to the inverters or 
charge controllers to which source circuits are wired? Will they need to be 
installed on each string, or can they function on a combined circuit?

Do systems with DC optimizers or with micro-inverters have arc-fault protection 
at the module level?

Jeffrey Quackenbush
NABCEP Certified PV Installer
Peripatetic Solar Technician


From: b...@midnitesolar.com b...@midnitesolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Monday, March 12, 2012 12:37 AM
Subject: Re: [RE-wrenches] Starting fires for fun with string wiring

On 3/11/2012 9:26 PM, Kent Osterberg wrote:
boB,

Most local codes, have granted a delay on implementing arc fault protection. 
Also, the code only requires series faults to be cleared.


I mentioned this because arc fault is already in the 2011 NEC whether it is 
adopted or not.

I have a feeling that Jeff was referring to some of the changes that are in the 
works for 2014.

As far as I understand, the code cannot be required unless there are products 
that fill the requirement.

Also, the UL spec was not quite complete, but that  didn't stop many of us from 
starting to work on it
before even 2011 code was out, even releasing something, even if it did not 
have a spec
to test to yet.

This code is going to get interesting for sure.   It's also going to make 
installations more expensive so
it's good that PV prices are falling some to help make up for it !

boB







Kent Osterberg

Blue Mountain Solar, Inc.

www.bluemountainsolar.comhttp://www.bluemountainsolar.com

t: 541-568-4882

On 3/11/2012 8:28 PM, b...@midnitesolar.commailto:b...@midnitesolar.com wrote:
On 3/11/2012 7:35 PM, Jeff Yago wrote:

I just sent a post about people not understanding the dangers of fire in the

array strings between the modules and before the combiner because its high

voltage DC and there are no fuses or circuit breakers to shut down the power

source (at least not until the next code requires arc-fault sensing!).


Jeff,

Arc fault was required as of NEC2011.

boB





Anyway, we have a 3 string, 4-module per string off-grid test system behind

the shop wired for 88 volts peak into a charge controller and 24 volt

battery bank. Last week as a test I temporarily disconnected the charge

controller and re-wired the 3 strings together into a single string of 12

modules with a 264 volt open circuit voltage DC output at about 7 amps at

dead short.  When compared with most grid-tie systems, this is not that high

a voltage or current, so what happened next would be far worse for a larger

voltage array.



I took a 2 x 4 and attached USE-2 single conductor wires using wire

staples with the (+) and (-) cables routed side by side and down the 2 x 4.

At the lower wire staple, I deliberately nailed through the wire insulation

which nicked the insulation but did not cut the wires.  After routing the

array power through these test wires nothing happened since the wire staple

was not making a very good contact with the bare wire at the insulation

nick.  I then moved the wires slowly from side to side by hand, which could

have been caused in a real installation from wind, temperature

expansion/contraction, somebody pulling on them, or just the action of age

on the nicked wire insulation.  Anyway, 

Re: [RE-wrenches] Starting fires for fun with string wiring

2012-03-12 Thread Jeff Yago
Just a point of clarification since this can be a danger to installers.
Chris Mason correctly pointed out that arc-flash and arc-fault are
different and my post may not have made this clear.  However, he stated that
arc-flash requires at least 480 volts which I strongly disagree.   I had
an arc-flash inside a Kohler 240 VAC transfer switch happen when I started
to remove the cover and a small metal shaving fell down across the buss bars
inside.  The explosion bowed out the cover and the sound was like a shotgun.
I then went through some arc-flash training by the military before
inspecting several hundred electrical panels on a military base and was told
this can happen at much lower voltages than the generally accepted 480
volts.

 

To all, regardless of high voltage AC or DC, arc-faults and arc-flash are
still not generally understood by some electricians working on these higher
voltage systems and there are safety equipment made to protect hands and
faces which can receive some really bad burns.   Please review proper safety
procedures for working on this equipment.

 

Jeff yago

 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Starting fires for fun with string wiring

2012-03-12 Thread Chris Mason
I didn't mean to suggest arc flash could only happen at 480V, just that it
is less likely to be very serious at lower voltages.
The PPE needed for work on 480V switchgear looks like the person is in the
hot part of a nuclear reactor. Scary stuff.



-- 
Chris Mason
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] solar accumulation panel

2012-03-12 Thread Dave Click
Nick, I don't see that name (or an alternate term) in the report on 
proposals (do a search for 120% or 4-375a).

http://www.nfpa.org/Assets/files/AboutTheCodes/70/70_A2013_NEC-P04_ROPballot.pdf

On 2012/3/9 16:45, Nick Vida wrote:

Hello,

I was wondering if any of you wise wrenches know if 'solar accumulation
panel' is still the name proposed to be used in the NEC. I think I
remember Bill Brooks mentioning that they couldn't get it in for 2011,
but that it will probably be good for 2014. I was wondering because here
in Los Angeles they are revising the standard plan and they have an
unusualname for the device, so as it is still a draft, I would us like
to align with the future, if at all possible.

Thanks wrenches!

Nick Vida



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Starting fires for fun with string wiring

2012-03-12 Thread Andrew Truitt
MidNite also offers AFCI protection in their disconnecting combiner boxes.
 The switches can also be hard-wired to the MidNite Birdhouse which allows
ground-level personnel to remotely disconnect the PV output circuit at the
combiner.


http://www.midnitesolar.com/pdfs/multi1_inside_outside.pdf



For a brighter energy future,


Andrew Truitt  MSc., LEED GA
NABCEP Certified PV Installerâ„¢ (ID# 032407-66)
 Principal
Truitt Renewable Energy Consulting
(202) 486-7507
http://www.linkedin.com/pub/andrew-truitt/8/622/713



Don't get me wrong: I love nuclear energy! It's just that I prefer fusion
to fission. And it just so happens that there's an enormous fusion reactor
safely banked a few million miles from us. It delivers more than we could
ever use in just about 8 minutes. And it's wireless!

~William McDonough


On Mon, Mar 12, 2012 at 9:13 AM, Dan Fink danbo...@gmail.com wrote:

 The Midnite Classic controllers come with arc-fault protection built in.

 --
 Dan Fink,
 Executive Director;
 Otherpower
 Buckville Energy Consulting
 Buckville Publications LLC
 NABCEP / IREC accredited Continuing Education Providers
 970.672.4342 (voicemail)


 On Mon, Mar 12, 2012 at 10:09 AM, JRQ quackkc...@yahoo.com wrote:
  I've been wondering about this since I read over the 2011 code:
 
  Are there any listed DC arc-flash products on the market yet, or
 scheduled
  to come to market within the next year?
 
  Also: will arc-flash protection come in the form of breakers that need
 to be
  installed externally, or will it be something internal to the inverters
 or
  charge controllers to which source circuits are wired? Will they need to
 be
  installed on each string, or can they function on a combined circuit?
 
  Do systems with DC optimizers or with micro-inverters have arc-fault
  protection at the module level?
 
  Jeffrey Quackenbush
  NABCEP Certified PV Installer
  Peripatetic Solar Technician
 
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org