Re: [RE-wrenches] AC coupling and Outback inverters

2012-10-05 Thread Glenn Burt
I would advise against using CAT-5 cabling for any RS-485 data
communications, it is not an appropriate tool for the job. This is a common
poor practice in the solar industry.

4 conductor shielded, 24AWG jacketed cable is what SMA recommends, and is
appropriate for this purpose.

 

Glenn Burt

(many years of data comms experience B4 solar)

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of mac Lewis
Sent: Thursday, October 04, 2012 9:41 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupling and Outback inverters

 

Hi Kirk,

 

I would consider the Sunny Island option.  Everything integrates nicely.
You can use the smartformer to get 240Vac if you need it at the critical
loads.  This would give the Sunny Island Frequency control over the Sunny
Boy (assuming you can run Cat 5 to the Sunny Boy). 

 

Good Luck.

On Thu, Oct 4, 2012 at 3:10 PM, Kirk Herander k...@vtsolar.com wrote:

I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US
inverters and it’s been running fine for 4 years. I used the off-grid
version of Outbacks.

Now I have an application where a customer wants to add battery backup to an
existing SunnyBoy 5000US system. And expand his array by a couple KW. So I’m
thinking of using a GT Outback w/ batteries to handle the critical loads and
feed the extra 2kw of PV (charging the batteries through an MX60) to the
grid. And I’d like to AC-couple the SunnyBoy so the original 5 kw array can
also charge the batteries, BUT I remember, at least I think so, that the GT
inverter cannot be AC-coupled, only the off-grid version. Is this correct?
Thanks.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org







 

-- 

 

 

 

Mac Lewis

Yo solo sé que no sé nada. -Sócrates

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC coupling and Outback inverters

2012-10-05 Thread Kirk Herander
I am leaning towards the SunnyIsland. I assume it backs off the SunnyBoy via
RS485 communications and the factory 240 xformer is a plus. The Outback
setup might be a little less expensive, but as you say a bit of a kludge. I
guess I still need the charge controller for the new PV, as the SunnyIsland
doesn't regulate that.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Friday, October 05, 2012 2:11 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupling and Outback inverters

 

Hi Kirk,

All of the Outback inverters will work AC coupled (GT and FX) as will any
bi-directional H-bridge type inverter.  I have used old Trace SW's,
SunnyIsland, Apollo TSW, Magnum AE and now I am using an Outback Radian to
do exactly what you are talking about.  I have 6 kW of grid tie inverter and
an additional 4kw of modules running through a Xantrex 600 volt charge
controller to the batteries that the Radian runs on. It all works flawless
as long as you have a provision for protecting the batteries when the gid is
down and the grid-tie PV system is making more power than the loads are
using.  

If the customer has SMA inverters, I would recommend using a SunnyIsland
because the battery control when the grid goes down is so elegant.
Everything else is a bit of a kludge.

 

David Katz

CTO  Founder

AEE Solar Inc

P: 707 825-1200

F: 707 825-1202

dk...@aeesolar.com

www.aeesolar.com

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk
Herander
Sent: Thursday, October 04, 2012 2:11 PM
To: RE-wrenches
Subject: [RE-wrenches] AC coupling and Outback inverters

 

I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US
inverters and it's been running fine for 4 years. I used the off-grid
version of Outbacks.

Now I have an application where a customer wants to add battery backup to an
existing SunnyBoy 5000US system. And expand his array by a couple KW. So I'm
thinking of using a GT Outback w/ batteries to handle the critical loads and
feed the extra 2kw of PV (charging the batteries through an MX60) to the
grid. And I'd like to AC-couple the SunnyBoy so the original 5 kw array can
also charge the batteries, BUT I remember, at least I think so, that the GT
inverter cannot be AC-coupled, only the off-grid version. Is this correct?
Thanks.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SunnyIsland - was AC coupling and Outback inverters

2012-10-05 Thread Kirk Herander
One Question: Output of the SunnyBoy is 240vac. So this is fed to the
critical load panel, of which the SunnyIsland 120 vac output is fed to. So
we need a 120/240 step up transformer between the SunnyIsland and the
critical load panel to fully take advantage of the Sunnyboy array for
battery charging, correct?.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Friday, October 05, 2012 2:11 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupling and Outback inverters

 

Hi Kirk,

All of the Outback inverters will work AC coupled (GT and FX) as will any
bi-directional H-bridge type inverter.  I have used old Trace SW's,
SunnyIsland, Apollo TSW, Magnum AE and now I am using an Outback Radian to
do exactly what you are talking about.  I have 6 kW of grid tie inverter and
an additional 4kw of modules running through a Xantrex 600 volt charge
controller to the batteries that the Radian runs on. It all works flawless
as long as you have a provision for protecting the batteries when the gid is
down and the grid-tie PV system is making more power than the loads are
using.  

If the customer has SMA inverters, I would recommend using a SunnyIsland
because the battery control when the grid goes down is so elegant.
Everything else is a bit of a kludge.

 

David Katz

CTO  Founder

AEE Solar Inc

P: 707 825-1200

F: 707 825-1202

dk...@aeesolar.com

www.aeesolar.com

 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirk
Herander
Sent: Thursday, October 04, 2012 2:11 PM
To: RE-wrenches
Subject: [RE-wrenches] AC coupling and Outback inverters

 

I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US
inverters and it's been running fine for 4 years. I used the off-grid
version of Outbacks.

Now I have an application where a customer wants to add battery backup to an
existing SunnyBoy 5000US system. And expand his array by a couple KW. So I'm
thinking of using a GT Outback w/ batteries to handle the critical loads and
feed the extra 2kw of PV (charging the batteries through an MX60) to the
grid. And I'd like to AC-couple the SunnyBoy so the original 5 kw array can
also charge the batteries, BUT I remember, at least I think so, that the GT
inverter cannot be AC-coupled, only the off-grid version. Is this correct?
Thanks.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SunnyIsland - was AC coupling and Outback inverters

2012-10-05 Thread Dave Click
Check out the new SMA Smartformer, though I'm not sure whether it's 
actually shipping yet. I'm thinking about this for my house eventually 
(SB5000US).


http://www.sma-america.com/en_US/products/off-grid-and-back-up-solutions/smartformer-for-sunny-island.html

Alternatively, the new SMA TL inverters (at least the 3, 4, and 5kW 
units according to the press release) have an Emergency Power Supply 
function that can provide backup power (12A?) during the day when the 
grid is down. This may meet your customer's requirements. No batteries 
required, though since the TLs require ungrounded arrays, you may need 
to rewire the existing array to be compliant with 690.35 (PV Wire or 
raceway).



On 2012/10/5 8:41, Kirk Herander wrote:

One Question: Output of the SunnyBoy is 240vac. So this is fed to the
critical load panel, of which the SunnyIsland 120 vac output is fed to.
So we need a 120/240 step up transformer between the SunnyIsland and the
critical load panel to fully take advantage of the Sunnyboy array for
battery charging, correct?.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

*From:*re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *David Katz
*Sent:* Friday, October 05, 2012 2:11 AM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] AC coupling and Outback inverters

Hi Kirk,

All of the Outback inverters will work AC coupled (GT and FX) as will
any bi-directional H-bridge type inverter.  I have used old Trace SW’s,
SunnyIsland, Apollo TSW, Magnum AE and now I am using an Outback Radian
to do exactly what you are talking about.  I have 6 kW of grid tie
inverter and an additional 4kw of modules running through a Xantrex 600
volt charge controller to the batteries that the Radian runs on. It all
works flawless as long as you have a provision for protecting the
batteries when the gid is down and the grid-tie PV system is making more
power than the loads are using.

If the customer has SMA inverters, I would recommend using a SunnyIsland
because the battery control when the grid goes down is so elegant.
Everything else is a bit of a kludge.

David Katz

CTO  Founder

AEE Solar Inc

P: 707 825-1200

F: 707 825-1202

dk...@aeesolar.com mailto:dk...@aeesolar.com

www.aeesolar.com http://www.aeesolar.com

*From:*re-wrenches-boun...@lists.re-wrenches.org
mailto:re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org]
mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf
Of *Kirk Herander
*Sent:* Thursday, October 04, 2012 2:11 PM
*To:* RE-wrenches
*Subject:* [RE-wrenches] AC coupling and Outback inverters

I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US
inverters and it’s been running fine for 4 years. I used the off-grid
version of Outbacks.

Now I have an application where a customer wants to add battery backup
to an existing SunnyBoy 5000US system. And expand his array by a couple
KW. So I’m thinking of using a GT Outback w/ batteries to handle the
critical loads and feed the extra 2kw of PV (charging the batteries
through an MX60) to the grid. And I’d like to AC-couple the SunnyBoy so
the original 5 kw array can also charge the batteries, BUT I remember,
at least I think so, that the GT inverter cannot be AC-coupled, only the
off-grid version. Is this correct? Thanks.

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEP^TM Certified installer Charter Member

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SunnyIsland - was AC coupling and Outback inverters

2012-10-05 Thread Will White
We've had problems with the Outback auto transformer when used with Sunny 
Islands.  The internal resistance of the transformer bumped the voltage up too 
high on a couple of systems and we were getting over voltage errors in the 
inverter.  We switched to a larger transformer and that fixed the problem.


__
Will White
Regional Field Operations Manager - New England

Real Goods Solar
64 Main St.
Montpelier, VT 05602
Tel: (802) 223-7804
Cell: (802) 234-3167
www.realgoodssolar.com





-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Friday, October 05, 2012 11:14 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] SunnyIsland - was AC coupling and Outback inverters

I'm looking forward to checking out the SMA Smartformer. We're sending one of 
our guys to SMA training later this month to learn more about it is depth. Up 
to date, we used the Outback PSX-240 like the one found here to
120/240 step up:

http://www.altestore.com/store/Enclosures-Electrical-Safety/Miscellaneous-
Electrical-Parts/Transformers/Outback-PSX-240-Autotransformer-with-Fan/p40
89/

My experience with a handful of Sunny Island backup systems has been really 
good. The Sunny Island is a very solid piece of equipment and is easy to 
program if the plan is properly thought through and everything is wired 
properly.

Good luck with your project! -August

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Friday, October 05, 2012 6:01 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] SunnyIsland - was AC coupling and Outback inverters

Check out the new SMA Smartformer, though I'm not sure whether it's actually 
shipping yet. I'm thinking about this for my house eventually (SB5000US).

http://www.sma-america.com/en_US/products/off-grid-and-back-up-solutions/s
martformer-for-sunny-island.html

Alternatively, the new SMA TL inverters (at least the 3, 4, and 5kW units 
according to the press release) have an Emergency Power Supply
function that can provide backup power (12A?) during the day when the grid is 
down. This may meet your customer's requirements. No batteries required, though 
since the TLs require ungrounded arrays, you may need to rewire the existing 
array to be compliant with 690.35 (PV Wire or raceway).


On 2012/10/5 8:41, Kirk Herander wrote:
 One Question: Output of the SunnyBoy is 240vac. So this is fed to the 
 critical load panel, of which the SunnyIsland 120 vac output is fed to.
 So we need a 120/240 step up transformer between the SunnyIsland and 
 the critical load panel to fully take advantage of the Sunnyboy array 
 for battery charging, correct?.

 Kirk Herander

 VT Solar, LLC

 dba Vermont Solar Engineering

 NABCEP^TM Certified installer Charter Member

 NYSERDA-eligible Installer

 VT RE Incentive Program Partner

 802.863.1202

 *From:*re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of 
 *David Katz
 *Sent:* Friday, October 05, 2012 2:11 AM
 *To:* RE-wrenches
 *Subject:* Re: [RE-wrenches] AC coupling and Outback inverters

 Hi Kirk,

 All of the Outback inverters will work AC coupled (GT and FX) as will 
 any bi-directional H-bridge type inverter.  I have used old Trace 
 SW's, SunnyIsland, Apollo TSW, Magnum AE and now I am using an Outback 
 Radian to do exactly what you are talking about.  I have 6 kW of grid 
 tie inverter and an additional 4kw of modules running through a 
 Xantrex 600 volt charge controller to the batteries that the Radian 
 runs on. It all works flawless as long as you have a provision for 
 protecting the batteries when the gid is down and the grid-tie PV 
 system is making more power than the loads are using.

 If the customer has SMA inverters, I would recommend using a 
 SunnyIsland because the battery control when the grid goes down is so
elegant.
 Everything else is a bit of a kludge.

 David Katz

 CTO  Founder

 AEE Solar Inc

 P: 707 825-1200

 F: 707 825-1202

 dk...@aeesolar.com mailto:dk...@aeesolar.com

 www.aeesolar.com http://www.aeesolar.com

 *From:*re-wrenches-boun...@lists.re-wrenches.org
 mailto:re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org]
 mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf 
 Of *Kirk Herander
 *Sent:* Thursday, October 04, 2012 2:11 PM
 *To:* RE-wrenches
 *Subject:* [RE-wrenches] AC coupling and Outback inverters

 I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US 
 inverters and it's been running fine for 4 years. I used the off-grid 
 version of Outbacks.

 Now I have an application where a customer wants to add battery backup 
 to an existing SunnyBoy 5000US system. And expand his array by a 
 couple KW. So I'm 

Re: [RE-wrenches] AC coupling and Outback inverters

2012-10-05 Thread David Katz
You customer might consider using two Sunnyislands instead of a transformer.
I used the Sunnyislands without 485 and it still backed of the grid tie 
inverters. 485 let's the SI put the grid tie inverters in off grid mode, making 
them less sensative to the UL parameters.
David

Sent from my HTC smartphone on the Now Network from Sprint!


- Reply message -
From: Kirk Herander k...@vtsolar.com
To: apos;RE-wrenchesapos; re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] AC coupling and Outback inverters
Date: Fri, Oct 5, 2012 5:08 am



I am leaning towards the SunnyIsland. I assume it backs off the SunnyBoy via 
RS485 communications and the factory 240 xformer is a plus. The Outback setup 
might be a little less expensive, but as you say a bit of a kludge. I guess I 
still need the charge controller for the new PV, as the SunnyIsland doesn’t 
regulate that.

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner
802.863.1202

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Friday, October 05, 2012 2:11 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupling and Outback inverters

Hi Kirk,
All of the Outback inverters will work AC coupled (GT and FX) as will any 
bi-directional H-bridge type inverter.  I have used old Trace SW’s, 
SunnyIsland, Apollo TSW, Magnum AE and now I am using an Outback Radian to do 
exactly what you are talking about.  I have 6 kW of grid tie inverter and an 
additional 4kw of modules running through a Xantrex 600 volt charge controller 
to the batteries that the Radian runs on. It all works flawless as long as you 
have a provision for protecting the batteries when the gid is down and the 
grid-tie PV system is making more power than the loads are using.
If the customer has SMA inverters, I would recommend using a SunnyIsland 
because the battery control when the grid goes down is so elegant.  Everything 
else is a bit of a kludge.

David Katz
CTO  Founder
AEE Solar Inc
P: 707 825-1200
F: 707 825-1202
dk...@aeesolar.commailto:dk...@aeesolar.com
www.aeesolar.comhttp://www.aeesolar.com


From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 
[mailto:re-wrenches-boun...@lists.re-wrenches.org]mailto:[mailto:re-wrenches-boun...@lists.re-wrenches.org]
 On Behalf Of Kirk Herander
Sent: Thursday, October 04, 2012 2:11 PM
To: RE-wrenches
Subject: [RE-wrenches] AC coupling and Outback inverters

I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US inverters 
and it’s been running fine for 4 years. I used the off-grid version of Outbacks.
Now I have an application where a customer wants to add battery backup to an 
existing SunnyBoy 5000US system. And expand his array by a couple KW. So I’m 
thinking of using a GT Outback w/ batteries to handle the critical loads and 
feed the extra 2kw of PV (charging the batteries through an MX60) to the grid. 
And I’d like to AC-couple the SunnyBoy so the original 5 kw array can also 
charge the batteries, BUT I remember, at least I think so, that the GT inverter 
cannot be AC-coupled, only the off-grid version. Is this correct? Thanks.

Kirk Herander
VT Solar, LLC
dba Vermont Solar Engineering
NABCEPTM Certified installer Charter Member
NYSERDA-eligible Installer
VT RE Incentive Program Partner
802.863.1202

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Sunny Control software on Windows 7?

2012-10-05 Thread William Miller

Friends:

Can I run the Sunny control Software, circa early 2000s on Windows 7?

Thanks in advance...

William Miller


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sunny Control software on Windows 7?

2012-10-05 Thread David Katz
I am using SunnyControl on my Windows 7 machine.
David Katz

Sent from my HTC smartphone on the Now Network from Sprint!


- Reply message -
From: William Miller will...@millersolar.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Sunny Control software on Windows 7?
Date: Fri, Oct 5, 2012 9:14 am



Friends:

Can I run the Sunny control Software, circa early 2000s on Windows 7?

Thanks in advance...

William Miller


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htmhttp://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.orghttp://www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org