[RE-wrenches] Two NEC questions

2012-10-13 Thread Rebecca Lundberg
Dear fellow wrenches,

Does anyone have suggestions for the 'best' way to keep up with product
availability for meeting 690.11 on DC AFCI? I understand that when this
code section was written there was no available device, and know that at
least several companies are working on devices. How will I know (before the
AHJ knows :-) that residential-scale products are available for purchase,
and at what point would you say now should be required over every other
option?

Second question: I have an inspector insisting that the solar PV system is
the same as a utility service, and is requiring all of the required service
code references to apply. Anybody have a concise reference that might
convince him otherwise? This same inspector has decided that the electrical
permit will have adders for each inverter as service equipment, and each
module as an electrical device. It would sure be nice if there was more
consistency...we're still in the early adopter phase here in Minnesota.

Thanks in advance for your input.

Keep Shining!
Rebecca Lundberg
NABCEP Certified Solar PV Installer ®
Owner/CEO, Powerfully Green
rebecca.lundb...@powerfullygreen.com
763-438-1976
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Two NEC questions

2012-10-13 Thread David Brearley
RE Question #2: 

Article 100 defines a service as:

Service. The conductors and equipment for delivering electric energy from the 
serving utility to the wiring system of the premises served. (emphasis added)

PV system wiring simply does not fit that definition. The PV system is not part 
of the serving utility. And inverters are not service equipment. 

You need to refers them to this definition in Article 705.2 (added in NEC 2011):

Power Production Equipment. The generating source, and all distribution 
equipment associated with it, that generates electricity from a source other 
than a utility supplied service. (emphasis added)

FWIW: Mike Holt has written for SP about the Code requirements for 
interconnecting PV systems, as well as some additional recommendations for 
making supply side connections:

http://solarprofessional.com/article/?file=SP5_1_pg14_QAsearch=


RE Question #1: I had a local inspector ask me about this in late-August  
there were relatively few listed products at that time:

SMA America has dc AFCI in their standard SunnyBoy US-series inverters (SB 
3000-US, SB 3800-US, SB 4000-US, SB 5000-US, SB 6000-US, SB7000-US, SB 
8000-US): 
http://www.sma-america.com/en_US/news-information/current-news/news/news/1487.html
Microinverter systems (Enphase, Enecsys, etc.) typically do not operate above 
80 Vdc and are therefore exempt from 690.11
AC module systems (powered by SolarBridge, Exeltech, etc.) typically do not 
operate above 80 Vdc and are therefore exempt from 690.11
SolarBOS reportedly has a dc AFDI and GFI combiner box: 
http://www.solarbos.com/news/solarbos-puts-out-the-fire-in-pv-systems (However, 
I don't see this product on their website under their regular lists of 
products.)
While module-level dc-to-dc converters—like those from SolarEdge and Tigo 
Energy—presumably have the ability to provide dc AFCI capabilities, last I 
checked it didn't look like any of them were formally listed to do so.

I suspect that most manufacturers are trying to avoid spending additional money 
on testing until the market requires this. 

Have any wrenches here actually had an inspector required dc AFCI? Also, is the 
dc AFCI test standard actually finalized and adopted at this point or are 
companies testing to a draft standard? 

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer ™
david.brear...@solarprofessional.com
Direct: 541.261.6545


On Oct 13, 2012, at 10:12 AM, Rebecca Lundberg wrote:

 Dear fellow wrenches,
 
 Does anyone have suggestions for the 'best' way to keep up with product 
 availability for meeting 690.11 on DC AFCI? I understand that when this code 
 section was written there was no available device, and know that at least 
 several companies are working on devices. How will I know (before the AHJ 
 knows :-) that residential-scale products are available for purchase, and at 
 what point would you say now should be required over every other option?
 
 Second question: I have an inspector insisting that the solar PV system is 
 the same as a utility service, and is requiring all of the required service 
 code references to apply. Anybody have a concise reference that might 
 convince him otherwise? This same inspector has decided that the electrical 
 permit will have adders for each inverter as service equipment, and each 
 module as an electrical device. It would sure be nice if there was more 
 consistency...we're still in the early adopter phase here in Minnesota.
 
 Thanks in advance for your input.
 
 Keep Shining!
 Rebecca Lundberg
 NABCEP Certified Solar PV Installer ®
 Owner/CEO, Powerfully Green
 rebecca.lundb...@powerfullygreen.com
 763-438-1976
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Two NEC questions

2012-10-13 Thread Brian Mehalic
You can see what products UL has listed (though not other NRTLs) at:

www.ul.com

Near the bottom of the page on the right hand side click on:

Online Certifications Directory

Into the UL Category Code box enter:

QIDC (for inverters with integrated dc arc-fault)
or
QIDC2 (for dc arc-fault components)

And hit search.

Only SMA and Eaton presently.  I imagine that as more products become
available more press releases will follow as well.

You can also download a copy of the UL Whitebook to cross check other
standards with the NEC.

Brian Mehalic
NABCEP Certified Solar PV Installer™ R031508-59
IREC ISPQ Certified Affiliated Instructor/PV US-0132

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org



On Sat, Oct 13, 2012 at 11:12 AM, Rebecca Lundberg 
rebecca.lundb...@powerfullygreen.com wrote:

 Dear fellow wrenches,

 Does anyone have suggestions for the 'best' way to keep up with product
 availability for meeting 690.11 on DC AFCI? I understand that when this
 code section was written there was no available device, and know that at
 least several companies are working on devices. How will I know (before the
 AHJ knows :-) that residential-scale products are available for purchase,
 and at what point would you say now should be required over every other
 option?

 Second question: I have an inspector insisting that the solar PV system is
 the same as a utility service, and is requiring all of the required service
 code references to apply. Anybody have a concise reference that might
 convince him otherwise? This same inspector has decided that the electrical
 permit will have adders for each inverter as service equipment, and each
 module as an electrical device. It would sure be nice if there was more
 consistency...we're still in the early adopter phase here in Minnesota.

 Thanks in advance for your input.

 Keep Shining!
 Rebecca Lundberg
 NABCEP Certified Solar PV Installer ®
 Owner/CEO, Powerfully Green
 rebecca.lundb...@powerfullygreen.com
 763-438-1976


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Two NEC questions

2012-10-13 Thread Alex Cozine
Rebecca,

First off, nice install on the four SiE pole mounts!

Second, as long as we are talking strictly grid-tied systems, not AC
coupled or battery backup, it seems like Solar should be viewed more like
an appliance.  It supplements the service at your house.   That being said,
you've got a tough battle ahead.  Hopefully someone else on the list has a
great way of calming this inspector down with some good old code lullibies.

Good luck!  Sometimes it feels like the Solar 'cops', I mean inspectors,
are trying to justify their jobs.

Alex Cozine
NABCEP Certified Solar PV Installer
Journeyman Electrician EL01
www.brotherselectricsolar.com
On Oct 13, 2012 8:13 AM, Rebecca Lundberg 
rebecca.lundb...@powerfullygreen.com wrote:

 Dear fellow wrenches,

 Does anyone have suggestions for the 'best' way to keep up with product
 availability for meeting 690.11 on DC AFCI? I understand that when this
 code section was written there was no available device, and know that at
 least several companies are working on devices. How will I know (before the
 AHJ knows :-) that residential-scale products are available for purchase,
 and at what point would you say now should be required over every other
 option?

 Second question: I have an inspector insisting that the solar PV system is
 the same as a utility service, and is requiring all of the required service
 code references to apply. Anybody have a concise reference that might
 convince him otherwise? This same inspector has decided that the electrical
 permit will have adders for each inverter as service equipment, and each
 module as an electrical device. It would sure be nice if there was more
 consistency...we're still in the early adopter phase here in Minnesota.

 Thanks in advance for your input.

 Keep Shining!
 Rebecca Lundberg
 NABCEP Certified Solar PV Installer ®
 Owner/CEO, Powerfully Green
 rebecca.lundb...@powerfullygreen.com
 763-438-1976


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Two NEC questions

2012-10-13 Thread Ray Walters
Midnite Solar has some DC arc fault equipment both built into their 
charge controllers (for battery based systems) and their Combiner 
boxes.  The nice thing about having AFCI at the combiner is that it 
actually protects the wiring from the array to the inverter, so if an 
arc is occurring in say the attic, it will interrupt the electricity at 
its source, not at the load.


Ray Walters


On 10/13/2012 9:12 AM, Rebecca Lundberg wrote:

Dear fellow wrenches,

Does anyone have suggestions for the 'best' way to keep up with 
product availability for meeting 690.11 on DC AFCI? I understand that 
when this code section was written there was no available device, and 
know that at least several companies are working on devices. How will 
I know (before the AHJ knows :-) that residential-scale products are 
available for purchase, and at what point would you say now should be 
required over every other option?


Second question: I have an inspector insisting that the solar PV 
system is the same as a utility service, and is requiring all of the 
required service code references to apply. Anybody have a concise 
reference that might convince him otherwise? This same inspector has 
decided that the electrical permit will have adders for each inverter 
as service equipment, and each module as an electrical device. It 
would sure be nice if there was more consistency...we're still in the 
early adopter phase here in Minnesota.


Thanks in advance for your input.

Keep Shining!
Rebecca Lundberg
NABCEP Certified Solar PV Installer ®
Owner/CEO, Powerfully Green
rebecca.lundb...@powerfullygreen.com
763-438-1976



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread Hilton Dier III
I have an off-grid client who is having trouble with his aging Xantrex 
SW4024 inverter and is considering an upgrade. I need some advice.


One of his problems with his present system is that he can't run his 3 
HP 240VAC table saw on the 4024. He'd be content to run his generator 
for any long sessions of sawing, but he'd like the capability to do a 
cut or two without firing it up.


I was thinking about stacking a couple of Outbacks. I'd like to know 
people's real-world experiences with the relationship between motor HP, 
rated inverter watts, and surge watts. How much wattage does he need to 
actually do the job? That is, without flailing the inverter(s) into a 
shortened life span.


Also, how do Outbacks compare with Magnums or whatever? I have been 
using Outbacks for a while with good results, but I have been hearing 
murmurs and grumbling since they were bought out. I haven't used 
Xantrex/Schneider for a while and I have no experience with Magnums. I 
notice that the Magnums offer split phase 240.


I should note that he has his inverter setup in his wood shop. I am 
theorizing that some of his inverter trouble could be from a tree's 
worth of sawdust in the case. He presently has a 24V system, but he is 
considering a battery replacement, which would be an opportunity to 
switch to 48V if necessary. The sawdust issue makes me lean towards the 
sealed Outbacks, but he does have a partially finished box for the 
inverter with filters and a fan.


Opinions?

Many thanks.

Hilton

--
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
Tel: 802-223-6652

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread jay peltz
HI Hilton,

Before you go anywhere you need to know what the draw on this motor is.

I've seen 3 hp motors not be able to start on a 15kw genny.
Why?  Just horrible motors thats all.

jay

peltz power
On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:

 I have an off-grid client who is having trouble with his aging Xantrex SW4024 
 inverter and is considering an upgrade. I need some advice.
 
 One of his problems with his present system is that he can't run his 3 HP 
 240VAC table saw on the 4024. He'd be content to run his generator for any 
 long sessions of sawing, but he'd like the capability to do a cut or two 
 without firing it up.
 
 I was thinking about stacking a couple of Outbacks. I'd like to know people's 
 real-world experiences with the relationship between motor HP, rated inverter 
 watts, and surge watts. How much wattage does he need to actually do the job? 
 That is, without flailing the inverter(s) into a shortened life span.
 
 Also, how do Outbacks compare with Magnums or whatever? I have been using 
 Outbacks for a while with good results, but I have been hearing murmurs and 
 grumbling since they were bought out. I haven't used Xantrex/Schneider for a 
 while and I have no experience with Magnums. I notice that the Magnums offer 
 split phase 240. 
 
 I should note that he has his inverter setup in his wood shop. I am 
 theorizing that some of his inverter trouble could be from a tree's worth of 
 sawdust in the case. He presently has a 24V system, but he is considering a 
 battery replacement, which would be an opportunity to switch to 48V if 
 necessary. The sawdust issue makes me lean towards the sealed Outbacks, but 
 he does have a partially finished box for the inverter with filters and a fan.
 
 Opinions?
 
 Many thanks.
 
 Hilton
  -- 
 Hilton Dier III
 Renewable Energy Design
 Partner, Solar Gain LLC
 453 East Hill Rd.
 Middlesex, VT 05602
 Tel: 802-223-6652
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

2012-10-13 Thread bob ellison
I have had inverters ruined by drywall dust, it literally filled them within
a couple years as the owner worked on his house. Next thing I am getting a
call that it would not work..

I doubt that sawdust would be any different.

 

Later,

Bob Ellison

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Saturday, October 13, 2012 5:28 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Off-grid 1nverter replacement for 3 HP

 

HI Hilton,

 

Before you go anywhere you need to know what the draw on this motor is.

 

I've seen 3 hp motors not be able to start on a 15kw genny.

Why?  Just horrible motors thats all.

 

jay

 

peltz power

On Oct 13, 2012, at 11:16 AM, Hilton Dier III wrote:





I have an off-grid client who is having trouble with his aging Xantrex
SW4024 inverter and is considering an upgrade. I need some advice.

One of his problems with his present system is that he can't run his 3 HP
240VAC table saw on the 4024. He'd be content to run his generator for any
long sessions of sawing, but he'd like the capability to do a cut or two
without firing it up.

I was thinking about stacking a couple of Outbacks. I'd like to know
people's real-world experiences with the relationship between motor HP,
rated inverter watts, and surge watts. How much wattage does he need to
actually do the job? That is, without flailing the inverter(s) into a
shortened life span.

Also, how do Outbacks compare with Magnums or whatever? I have been using
Outbacks for a while with good results, but I have been hearing murmurs and
grumbling since they were bought out. I haven't used Xantrex/Schneider for a
while and I have no experience with Magnums. I notice that the Magnums offer
split phase 240. 

I should note that he has his inverter setup in his wood shop. I am
theorizing that some of his inverter trouble could be from a tree's worth of
sawdust in the case. He presently has a 24V system, but he is considering a
battery replacement, which would be an opportunity to switch to 48V if
necessary. The sawdust issue makes me lean towards the sealed Outbacks, but
he does have a partially finished box for the inverter with filters and a
fan.

Opinions?

Many thanks.

Hilton



-- 
Hilton Dier III
Renewable Energy Design
Partner, Solar Gain LLC
453 East Hill Rd.
Middlesex, VT 05602
Tel: 802-223-6652

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] AC (only) Diversion

2012-10-13 Thread Michael Welch
Hi Nathan and Wrenches. Sharkey asked me to post this for him:

In response to Nathan Stumpff, I designed and use a microprocessor-based dump 
load to keep my RE power off the grid: 
http://www.mrsharkey.com/solar-power-diversion-load-controller (see links at 
the top of this page for previous editions covering development of the design).

Also, have him take a look at http://openenergymonitor.org/emon/node/841 for a 
phase-control system that uses a triac device.

Tell him to beware, if he is connected through a modern digital meter, not only 
will it not credit him for power fed back to the grid, he'll be charged the 
retail rate for every KwH that he places on the utilities lines!!!


Nathan Stumpff wrote at 12:36 PM 10/12/2012:
Wrenches,
 
We are working on the design for a system where we will be using grid-tied 
wind and solar but will not be able to net-meter the project (we can 
interconnect but the meter only runs one way.) Anything we use on site is 
worth 100%, any production that goes back to the grid is lost forever to the 
customer. What we would like to do is monitor all solar and wind production, 
monitor all usage, and then be able to dump every watt-hour of over production 
as heat, there is plenty of (thermal) storage capacity.
 
If this were a battery based system I know how I would approach this and what 
equipment I would spec, but so far I am having a hard time coming up with a  
solution. Anyone have any suggestions for products or strategies in this case? 
Something like an eGauge with programmable PWM relay outputs?
 
Any thoughts or suggestions are most appreciated,
-Nathan

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org