Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread William Miller

Jeremy:

You are welcome, but credit belongs to Kent Osterberg.

wm





At 09:02 PM 12/30/2012, you wrote:

William,
They are using the 2011 code, so we should be good.
705.12D2 exception is a little confusing at first, but I got it.

Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.5.455 / Virus Database: 271.1.1/5496 - Release Date: 12/29/12 
18:42:00


Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread Jeremy Rodriguez- All Solar Inc.
William,
They are using the 2011 code, so we should be good. 
705.12D2 exception is a little confusing at first, but I got it. 

Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread William Miller

Jeremy:

Bingo!  You have discovered the hard truth of grid tie with battery point 
of connection compliance (GTWB POC).  Your inverter will through-transfer 
up to 60 Amps (A), so to use all of that capability, you should feed it 
with 60A.  However, you are not allowed to feed the inverter with greater 
than 40A dedicated over-current protection (OCPD).  The arithmetic is:


Buss rating:  200A
Allowed total buss feed:  200A X 120% = 240A
Main breaker: 200A
Allowed PV feed:  240A-200A= 40A*


If you can downgrade the main breaker to 150A you can back feed up to 
90A.  The arithmetic then is:


Buss rating:  200A
Allowed total buss feed:  200A X 120% = 240A
Main breaker: 150A
Allowed PV feed:  240A-150A= 90A

Downgrading the main breaker is not easy.  Most meter/main/combos (MMCs) 
will not allow the downgrade-- there is not a 150A breaker made that is 
designed and listed to fit in the 200 A panel.  I have contacted various 
manufacturers and requested that 200 (MMCs) be made that will readily 
accept a 150A main breaker, but large corporations do not seem to care 
about the needs of a small part of the market..


I had found a 200 A MMC that I could downgrade the main breaker to 150 A, 
but not easily.  The fit was not perfect -- I had to modify the hold down 
bracket, but it passed inspection.  Technically I suppose the MMC was no 
longer compliant with the listing once I modified it, but sometimes you 
gotta do what you gotta do.


Good Luck.

William Miller

* PS:  I believe the 2011 NEC has an exception that applies, but I do not 
believe any jurisdictions are using that code.  I have convinced my local 
building officials to pre-adopt certain future code sections.  Maybe you 
can make the case to your local inspectors.  Meet with them, explain the 
limitations of the XW as far as intertie amperage and maybe they will allow 
use of a 60A breaker.


Wm

At 04:27 PM 12/30/2012, you wrote:
I'm concerned that the inspector will not allow a 60A back fed breaker in 
the 200A main panel as it exceeds the 120% rule

Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread William Miller

Kent:

I do not have that document handy at this moment.  Can you send the 
citation, please?


Thanks,

William Miller


At 04:56 PM 12/30/2012, you wrote:
If you are using the 2011 NEC, 705.12(D)(2) has an exception to the 120% 
rule for inverters with energy storage to allow for operation of loads.


Kent Osterberg


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread Kent Osterberg
If you are using the 2011 NEC, 705.12(D)(2) has an exception to the 120% 
rule for inverters with energy storage to allow for operation of loads.


Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com
t: 541-568-4882

On 12/30/2012 4:27 PM, Jeremy Rodriguez- All Solar Inc. wrote:

I'm concerned that the inspector will not allow a 60A back fed breaker in the 
200A main panel as it exceeds the 120% rule
Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread Jeremy Rodriguez- All Solar Inc.
I'm concerned that the inspector will not allow a 60A back fed breaker in the 
200A main panel as it exceeds the 120% rule
Jeremy
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread Gary Willett

Jeremy:

The XW-6048 spec for maximum AC Input Current (maximum 75% imbalance 
between L1-N, L2-N) is:

L-N: 41.2 AL-L: 27.5 A

So, with a Line to Neutral current of 41.2A x 1.25 = 51.5A or rounds up 
to 60A 2-pole breaker.


This condition could occur in a grid-tied configuration when the 
inverter is in AC BYPASS mode and the batteries are being charged from 
the grid.



Regards,

Gary Willett


On 12/30/2012 4:48 PM, Jeremy Rodriguez- All Solar Inc. wrote:

Ok, so 35A min., but what about maximum?
A 200A mains panels allows 120% max back feed correct?
Confused.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!

-Original Message-
From: John Berdner 
Date: Sun, 30 Dec 2012 23:54:17
To: allso...@scswifi.net; 
RE-wrenches
Subject: RE: [RE-wrenches] Point of Connection 705.12D2 Exception

Jeremy:

31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp 
breaker would be the minimum size per Code.
The inverter may have a higher "pass through rating" to support the loads and 
so is likely the reason a 60 Amp breaker is specified.
The pass through rating is typically based on the size of the isolation relay 
and is usually higher than the inverter's continuous power rating.

Best Regards,

John Berdner
General Manager, North America



3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy 
Rodriguez- All Solar Inc.
Sent: Sunday, December 30, 2012 10:35 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Point of Connection 705.12D2 Exception

Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are 
connecting back to the load side of a 200A panel is this correct. 
6000÷240=25X1.25=31.25A. We cannot exceed a 30A breaker?  Help me understand 
this.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread Jeremy Rodriguez- All Solar Inc.
Ok, so 35A min., but what about maximum?
A 200A mains panels allows 120% max back feed correct?
Confused.
Jeremy
All Solar 
Sent via BlackBerry. Sorry for typos and shorthand!

-Original Message-
From: John Berdner 
Date: Sun, 30 Dec 2012 23:54:17 
To: allso...@scswifi.net; 
RE-wrenches
Subject: RE: [RE-wrenches] Point of Connection 705.12D2 Exception

Jeremy:

31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp 
breaker would be the minimum size per Code.
The inverter may have a higher "pass through rating" to support the loads and 
so is likely the reason a 60 Amp breaker is specified.
The pass through rating is typically based on the size of the isolation relay 
and is usually higher than the inverter's continuous power rating.

Best Regards,

John Berdner
General Manager, North America



3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy 
Rodriguez- All Solar Inc.
Sent: Sunday, December 30, 2012 10:35 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Point of Connection 705.12D2 Exception

Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are 
connecting back to the load side of a 200A panel is this correct. 
6000÷240=25X1.25=31.25A. We cannot exceed a 30A breaker?  Help me understand 
this.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread John Berdner
Jeremy:

31.25 is the minimum allowable Ampacity (25 Amps continuous) so a 35 Amp 
breaker would be the minimum size per Code.
The inverter may have a higher "pass through rating" to support the loads and 
so is likely the reason a 60 Amp breaker is specified.
The pass through rating is typically based on the size of the isolation relay 
and is usually higher than the inverter's continuous power rating.

Best Regards,

John Berdner
General Manager, North America



3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3201 ext 747
M: 530.277.4894

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeremy 
Rodriguez- All Solar Inc.
Sent: Sunday, December 30, 2012 10:35 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Point of Connection 705.12D2 Exception

Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are 
connecting back to the load side of a 200A panel is this correct. 
6000÷240=25X1.25=31.25A. We cannot exceed a 30A breaker?  Help me understand 
this.
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P Please think of the environment before printing this email
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Point of Connection 705.12D2 Exception

2012-12-30 Thread Jeremy Rodriguez- All Solar Inc.
Wrenches,
Since the XW6048 calls for a 60A breaker to feed the inverter input and we are 
connecting back to the load side of a 200A panel is this correct. 
6000÷240=25X1.25=31.25A. We cannot exceed a 30A breaker?  Help me understand 
this. 
Jeremy
All Solar
Sent via BlackBerry. Sorry for typos and shorthand!
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org