Re: [RE-wrenches] 230 50 hz kWh meters

2013-10-24 Thread Chris Worcester
Hi Jay,
You might give the folks at Vision Meters a call;
email: ka...@visionmetering.com 
phone: 803-628-0035 
web: http://www.visionmetering.com

Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Office 530-582-4503
Cell 530-448-9692
Fax 530-582-4603
www.solarwindworks.com
ch...@solarwindworks.com


-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Wednesday, October 23, 2013 3:25 PM
To: RE-wrenches
Subject: [RE-wrenches] 230 50 hz kWh meters

Hi All,

Does anyone know of either dial or EZ read kWh meters that can work with
230v 50 hz,
100 amp is more than enough

thanks

jay 

peltz power
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Adding Charge Controller(s)

2013-10-24 Thread Jesse Dahl
Hello,

Looked at a system today that consisted of the following:

15 - Kyocera 158W modules
3 -   Kyocera 185W modules
1 -   Outback MX60
8 -   New Trojan L16RE (48V system)
1 -   Xantrex SW Plus

6 months ago he swapped out his old charge controller to the new MX60 and
purchased the new batteries at that time.  The array wiring did not change
and is wired in 6 strings of 3.  (confusing to the MX60?)

He is now adding 4 Kyocera 240W modules.  He also purchased another MX60
for this array.

From my perspective, removing the 3 185W modules and getting them on their
own controller would be a better use of the modules.  The system currently
does not have any disconnects on the PV side.  There are fuses in the
combiner boxes on the array, but no disconnects inside at the charge
controller.  So adding 3 charge controllers, and now needing to add GFDI,
means a box of some kind needs to be added to house these breakers.

Outbacks GFPs and panel mount breakers will work, but what is the best
mounting solution for these?  One DC Flexware enclosure? It will of course
allow for all the DC OCPD  and allow for the landing of the output of the
charge controllers.  Or is there another enclosure/OCPD solution I should
look at?


Thanks as always!

Jesse
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding Charge Controller(s)

2013-10-24 Thread jay peltz
Hi Jeffe,

I don't know the specs on those Kyocera, but if they are the same VOC then they 
are fine together.

As to a enclosure for the CC's, I'd look at Midnight.
They have about a million different boxes, you'll find one that will do the job 
for you I'm sure.

Depending on the area, you might look at a midnight 150v, or  200v or 250v 
controller, as you can then run all in series.

jay

peltz power


On Oct 24, 2013, at 1:13 PM, Jesse Dahl wrote:

 Hello,
 
 Looked at a system today that consisted of the following:
 
 15 - Kyocera 158W modules
 3 -   Kyocera 185W modules
 1 -   Outback MX60
 8 -   New Trojan L16RE (48V system)
 1 -   Xantrex SW Plus 
 
 6 months ago he swapped out his old charge controller to the new MX60 and 
 purchased the new batteries at that time.  The array wiring did not change 
 and is wired in 6 strings of 3.  (confusing to the MX60?)
 
 He is now adding 4 Kyocera 240W modules.  He also purchased another MX60 for 
 this array.
 
 From my perspective, removing the 3 185W modules and getting them on their 
 own controller would be a better use of the modules.  The system currently 
 does not have any disconnects on the PV side.  There are fuses in the 
 combiner boxes on the array, but no disconnects inside at the charge 
 controller.  So adding 3 charge controllers, and now needing to add GFDI, 
 means a box of some kind needs to be added to house these breakers. 
 
 Outbacks GFPs and panel mount breakers will work, but what is the best 
 mounting solution for these?  One DC Flexware enclosure? It will of course 
 allow for all the DC OCPD  and allow for the landing of the output of the 
 charge controllers.  Or is there another enclosure/OCPD solution I should 
 look at?  
 
 
 Thanks as always!
 
 Jesse
 
 
 
 
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Security on a ground mount?

2013-10-24 Thread William Dorsett
We've got a system to go up in the student ghetto in the middle of town, so
of course we got drunks and little pirates. Height has always been a
solution but requires a lot beefier (pronounced expensive) support pipes.
What security measures does everyone recommend of a system that is low
enough to unbolt? Thanks all.

 

 



 

image002.jpgattachment: Bill Dorsett.vcf___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Security on a ground mount?

2013-10-24 Thread Larry Crutcher, Starlight Solar Power Systems
Weld 'em in a steel frame. Even then, a battery operated cutoff tool will have 
the frames open in minutes. Height will really slow them down but make sure 
they can't back up a vehicle and pull the array down…...Yes, I have had that 
happen.


Larry 





On Oct 24, 2013, at 1:37 PM, William Dorsett wmdors...@sbcglobal.net wrote:

We’ve got a system to go up in the student ghetto in the middle of town, so of 
course we got drunks and little pirates. Height has always been a solution but 
requires a lot beefier (pronounced “expensive”) support pipes. What security 
measures does everyone recommend of a system that is low enough to unbolt? 
Thanks all.
 
 
image002.jpg
 
Bill Dorsett.vcf___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding Charge Controller(s)

2013-10-24 Thread Jesse Dahl
Jay ,

The modules have different electrical specs... 

I'd like to use the midnight because the new array in series is at 148V. We see 
-40F.  He already has the Outback 60 on site. That's why with 2 existing 
outback products I figure the Flexware route would work best. 

Thanks!

Jesse  

Sent from my iPhone

 On Oct 24, 2013, at 3:26 PM, jay peltz j...@asis.com wrote:
 
 Hi Jeffe,
 
 I don't know the specs on those Kyocera, but if they are the same VOC then 
 they are fine together.
 
 As to a enclosure for the CC's, I'd look at Midnight.
 They have about a million different boxes, you'll find one that will do the 
 job for you I'm sure.
 
 Depending on the area, you might look at a midnight 150v, or  200v or 250v 
 controller, as you can then run all in series.
 
 jay
 
 peltz power
 
 
 On Oct 24, 2013, at 1:13 PM, Jesse Dahl wrote:
 
 Hello,
 
 Looked at a system today that consisted of the following:
 
 15 - Kyocera 158W modules
 3 -   Kyocera 185W modules
 1 -   Outback MX60
 8 -   New Trojan L16RE (48V system)
 1 -   Xantrex SW Plus 
 
 6 months ago he swapped out his old charge controller to the new MX60 and 
 purchased the new batteries at that time.  The array wiring did not change 
 and is wired in 6 strings of 3.  (confusing to the MX60?)
 
 He is now adding 4 Kyocera 240W modules.  He also purchased another MX60 for 
 this array.
 
 From my perspective, removing the 3 185W modules and getting them on their 
 own controller would be a better use of the modules.  The system currently 
 does not have any disconnects on the PV side.  There are fuses in the 
 combiner boxes on the array, but no disconnects inside at the charge 
 controller.  So adding 3 charge controllers, and now needing to add GFDI, 
 means a box of some kind needs to be added to house these breakers. 
 
 Outbacks GFPs and panel mount breakers will work, but what is the best 
 mounting solution for these?  One DC Flexware enclosure? It will of course 
 allow for all the DC OCPD  and allow for the landing of the output of the 
 charge controllers.  Or is there another enclosure/OCPD solution I should 
 look at?  
 
 
 Thanks as always!
 
 Jesse
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding Charge Controller(s)

2013-10-24 Thread William Miller
http://www.millersolar.com/MillerSolar/practices/Technical_Procedures/SW_Upg
rade/_SW_Upgrade.html

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Thursday, October 24, 2013 1:14 PM
To: RE-wrenches
Subject: [RE-wrenches] Adding Charge Controller(s)

 

Hello,

 

Looked at a system today that consisted of the following:

 

15 - Kyocera 158W modules

3 -   Kyocera 185W modules

1 -   Outback MX60

8 -   New Trojan L16RE (48V system)

1 -   Xantrex SW Plus 

 

6 months ago he swapped out his old charge controller to the new MX60 and
purchased the new batteries at that time.  The array wiring did not change
and is wired in 6 strings of 3.  (confusing to the MX60?)

 

He is now adding 4 Kyocera 240W modules.  He also purchased another MX60 for
this array.

 

From my perspective, removing the 3 185W modules and getting them on their
own controller would be a better use of the modules.  The system currently
does not have any disconnects on the PV side.  There are fuses in the
combiner boxes on the array, but no disconnects inside at the charge
controller.  So adding 3 charge controllers, and now needing to add GFDI,
means a box of some kind needs to be added to house these breakers. 

 

Outbacks GFPs and panel mount breakers will work, but what is the best
mounting solution for these?  One DC Flexware enclosure? It will of course
allow for all the DC OCPD  and allow for the landing of the output of the
charge controllers.  Or is there another enclosure/OCPD solution I should
look at?  

 

 

Thanks as always!

 

Jesse

 

 

 

 

 

 

 

 

  _  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4158 / Virus Database: 3615/6777 - Release Date: 10/24/13

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Adding Charge Controller(s)

2013-10-24 Thread Roy Rakobitsch
Not sure what this is worth, but with most Kyocera modules that used the
same size cells (but different amount of cells per module) you could wire
many different VOC modules in series as long as the total number of CELLS
per string was the same. It wouldnt matter what the individual module
ratings were (as long as the total array was mounted at the same tilt and
azimuth, an MPPT charge controller wouldnt know the difference. Ive done
this many times with grid tie inverters, and honestly it wouldnt make a
difference with a charge controller either. Different age cells/modules
may make a slight difference. But what Im suggesting is to count the cells
in the strings.

Hope that made sense.


Roy Rakobitsch
NABCEP Certified Small Wind Installer®
NABCEP Certified Solar PV Installer®
NYSERDA eligible Small Wind installer
Certified Advanced Tower Climbing, Safety  Rescue
Wind/PV Design Engineer
Windsine Inc.
631-514-4166
www.windsine.org


On Thu, October 24, 2013 8:51 pm, toddc...@finestplanet.com wrote:

 VMP not VOC

 todd



 On Thursday, October 24, 2013 1:26pm, jay peltz j...@asis.com said:



 Hi Jeffe,

 I don't know the specs on those Kyocera, but if they are the same VOC
 then they
 are fine together.

 As to a enclosure for the CC's, I'd look at Midnight.
 They have about a million different boxes, you'll find one that will do
 the job
 for you I'm sure.

 Depending on the area, you might look at a midnight 150v, or  200v or
 250v
 controller, as you can then run all in series.

 jay

 peltz power


 On Oct 24, 2013, at 1:13 PM, Jesse Dahl wrote:

  Hello,
 
  Looked at a system today that consisted of the following:
 
  15 - Kyocera 158W modules
  3 -   Kyocera 185W modules
  1 -   Outback MX60
  8 -   New Trojan L16RE (48V system)
  1 -   Xantrex SW Plus
 
  6 months ago he swapped out his old charge controller to the new MX60
 and
 purchased the new batteries at that time.  The array wiring did not
 change and is
 wired in 6 strings of 3.  (confusing to the MX60?)
 
  He is now adding 4 Kyocera 240W modules.  He also purchased another
 MX60 for
 this array.
 
  From my perspective, removing the 3 185W modules and getting them on
 their
 own controller would be a better use of the modules.  The system
 currently does
 not have any disconnects on the PV side.  There are fuses in the
 combiner boxes on
 the array, but no disconnects inside at the charge controller.  So
 adding 3 charge
 controllers, and now needing to add GFDI, means a box of some kind needs
 to be
 added to house these breakers.
 
  Outbacks GFPs and panel mount breakers will work, but what is the best
 mounting solution for these?  One DC Flexware enclosure? It will of
 course allow
 for all the DC OCPD  and allow for the landing of the output of the
 charge
 controllers.  Or is there another enclosure/OCPD solution I should look
 at?
 
 
  Thanks as always!
 
  Jesse
 
 
 
 
 

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org




 Sent from Finest Planet WebMail.
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org







___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org