 Drake,
 
 After reading your initial comments, I think you have nailed both the intent 
 of this code section as well as the benefits.  But in reading your second 
 posting, I felt it important to write you.  As one of the representatives 
 from the Fire Service that drafted 690.12, I can tell you that while there is 
 always room for improvement in language, the goal is to have PV that can not 
 start a fire.  As I am not a wrench I can not post to the list (feel free 
 to share any of my comments here if you wish), but I would like to chime in 
 on this conversation.
 
 Your assertion that ALECs are targeting the PV industry is not taking place 
 in this process.   There are many hard-working individuals from the PV 
 industry, electrical inspectors, and the fire service working together to 
 keep PV safe and secure for many years to come.  I for one have both PV and 
 thermal on my home.
 
 While you are correct that no fire fighter fatalities have resulted from a PV 
 system shock, the goal is to prevent the first. One problem is that the PV 
 industry has not adequately addressed the arc and ground fault problems in 
 the US.  Simply put, many rooftop systems are not NEC compliant; they can not 
 detect and interrupt all faults.  This has unfortunately resulted in far too 
 many fires.  The many additions  changes to sec 690 in the 2014 cycle will 
 go far in achieving a much safer system.  
 
 The fire service is becoming increasingly aware, educated, and involved in 
 the code process for PV safety.  It should be clear that the goal for all 
 parties is a safe electrical product.  There is no secret agenda to pull the 
 rug out from under solar. To those that are concerned with the imbedded cost 
 increases, please take a longer view than your current FY.  The systems that 
 fire fighters respond to may be many years old, but in reality most of the 
 fires have occurred on new systems.  We will respond to older systems over 
 time, and some buildings will be lost due to concern over the inability to 
 isolate power down to a safe level.  As I teach firefighters about electrical 
 safety, many express both an interest in PV as well as concern that it should 
 be possible to shut a system down in the event of an emergency either 
 manually, or as a result of a fault.
 
 Thank you,
 Matt
 
 CA Matthew Paiss, E19B
 Bureau of Field Operations
 San Jose Fire Department
 1661 Senter Rd
 San Jose, CA 95113
 (831) 566-3057 c

BTW: the stakeholders who developed the consensus language in 690.12 are listed 
in the NEC 2014 Report on Comments:

This comment is the result of a consensus process established among three 
groups of stakeholders: 1) CMP4 Firefighter SafetyTask Group; 2) SEIA Codes and 
Standards Working Group; and 3) PV Industry Forum. Participants in these groups 
included the following individuals:

CMP4 Firefighter Safety Task Group
1. Ward Bower, CMP4 representing SEIA
2. Bill Brooks, CMP4 representing SEIA and Chair of Task Group
3. Bob Davidson, Davidson Code Concepts
4. Mark Earley, Secretary, NFPA
5. Bob James, UL
6. Matt Paiss, City of San Jose Fire Department
7. Jim Rogers, CMP4 representing IAEI
8. Todd Stafford, CMP4 representing IBEW
9. Ronnie Toomer, Chair of CMP4
10. Peter Willse, Global Asset Protection Services

SEIA Codes and Standards Working Group
1. Mark Albers, SunPower
2. Mark Baldassari, Enphase Energy
3. Ward Bower, SEIA
4. Bill Brooks, Brooks Engineering/SEIA
5. Joe Cain, Chair of SEIA Codes and Standards Working Group
6. Keith Davidson, SunTech
7. Darrel Higgs, Dow Solar
8. Lee Kraemer, First Solar
9. Carl Lenox, SunPower
10. Charles Luebke, Eaton
11. Martin Mesmer, E.ON
12. Steve Pisklak, Dow Solar13. Robert Rynar, First Solar
14. Michael Schenck, First Solar
15. John Smirnow, SEIA
16. Kris VanDerzee, First Solar
17. Leo Wu, SolarCity
18. Tilak Gopalarathnam, REFUsol Incorporated

PV Industry Forum
1. Mark Albers, SunPower
2. Greg Ball, DNV
3. Bill Brooks, Brooks Engineering, lead for 690.12
4. Mark Baldassari, Enphase Energy
5. Ward Bower, SEIA
6. Michael Coddington, NREL
7. Marv Dargatz, SolarEdge
8. Chris Flueckiger. UL
9. Joerg Grosshennig, SMA
10. Darrel Higgs, Dow Solar
11. Dan Lepinski, Exeltech
12. Carl Lenox, SunPower
13. Charles Luebke, Eaton
14. Matt Paiss, City of San Jose Fire Department
15. Steve Pisklak, Dow Solar
16. Jim Rogers, Town of Oak Bluffs
17. Jon Sharp, Ampt
18. Bhima Sheridan, SolarCity
19. John Smirnow, SEIA
20. Holly Thomas, U.S. Dept. of Energy
21. Phil Undercuffler, Outback Power
22. John Wiles, NMSU, Secretary of PV Industry Forum
23. Leo Wu, SolarCity
24. Tim Zgonena, UL


On Jan 24, 2014, at 1:00 PM, re-wrenches-requ...@lists.re-wrenches.org wrote:

 From: Drake drake.chamber...@redwoodalliance.org

Re: [RE-wrenches] Corrugated roof brackets

2014-01-24 Thread William Miller
Jeremy:

 

We used them on one job and did not favor them for these reasons:

 

1.   Don't like having the penetrations in the valleys

2.   The adhesive is fragile and either peels off or significant amounts
wrap around the drill or fasteners

3.   The threaded connections felt fragile and I recall a few stripped

 

The next job we used Snapnrack corrugated roof brackets and were very
pleased.  http://www.snapnrack.com/series-500-metal-roof-mount-system

 

William

 

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of All Solar,
Inc.
Sent: Thursday, January 23, 2014 1:37 PM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Corrugated roof brackets

 

Can anyone comment on the S-5! CorruBracket?

Any other recommendations or comments appreciated. 

 

Jeremy Rodriguez,

President

 

All Solar, Inc. 

1463 M

Penrose Colorado 81240

719-372-3808 office

719-372-3804 fax

 http://www.asolarelectric.com www.asolarelectric.com

 

Sent by Jeremy's iPhone. Sorry for typos and shorthand!

___

List sponsored by Home Power magazine

 

List Address:  mailto:RE-wrenches@lists.re-wrenches.org
RE-wrenches@lists.re-wrenches.org

 

Change email address  settings:

 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 

List rules  etiquette:

 http://www.re-wrenches.org/etiquette.htm
www.re-wrenches.org/etiquette.htm

 

Check out participant bios:

 http://www.members.re-wrenches.org www.members.re-wrenches.org

 

 

 

-

No virus found in this message.

Checked by AVG -  http://www.avg.com www.avg.com

Version: 2013.0.3462 / Virus Database: 3681/7027 - Release Date: 01/23/14

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Temperature Compensation calcs for wire

2014-01-24 Thread William Miller
Dave:

Thanks for this post, although in order to completely understand, it I
sacrificed a significant amount of time working up a spreadsheet and running
various scenarios.  My philosophy is that this will pay off in the long run.
I always create a spreadsheet so I can figure something out once and use it
always.

When analyzing these codes, I was wondering which table to use:  table
310.15(B)(2)(a) or table 310.15(B)(2)(b), and why?  The values are
significantly different.  For example at 62°C the values are 0.65 and 0.71,
respectively.  I deduced that they must be used in conjunction with ampacity
values from the correct 310.15(16) through (20) tables in regards to ambient
temperature.  I noted that for THWN the later tables (40°) do not go below
8AWG, so I figure I need to stick with 30° tables.  Is this correct?

Lastly, has anyone  used the 310.15(C) formula for calculating the values.
This should not be that hard.  What is considered Engineering Supervision?

Thanks again.

William

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Wednesday, January 22, 2014 5:32 PM
To: re-wrenches@lists.re-wrenches.org
Subject: Re: [RE-wrenches] Temperature Compensation calcs for wire

William-

Yes, you can use the 90C column for ampacity adjustment when using 90C wire,
per the awkward 110.14(C)- Conductors with temperature ratings higher than
specified for terminations shall be permitted to be used for ampacity
adjustment, correction, or both.

Assuming copper wiring and the NEC '11 T310.15(B)(16):
Let's say you have a 40A breaker with a 75C terminal rating and you're
looking to land THWN-2 on it. Since the terminal has a 75C rating, you need
to make sure that this terminal rating is rated for at least 40A in the 75C
column. Since a 75C terminal with a #10 can only handle 35A, you'd have to
go to a #8 to get a rating of at least 40A-- in this case, a #8/75C can
handle 50A.

So why install 90C-rated conductors at all? When using 90C conductors you
can use the 90C ampacity column to apply your derate factors. Let's say your
#8 conductor (selected above) is in 50C ambient with 4 conductors in the
raceway.

If using #8 THWN, use 75C columns:
50A x 0.75 (T310.15(B)(2)(a)) x 0.8 = 30A That's too small for a 40A
breaker, so you're stuck with a #6:
65A x 0.75 x 0.8 = 39A (OK)

IF using #8 THWN-2, can use 90C columns:
55A x 0.82 x 0.8 = 36A (OK per 240.4(B))

And I'll beat Mr. Brearley to posting a relevant SolarPro article:
http://solarprofessional.com/articles/design-installation/code-compliant-con
ductor-sizing?v=disable_pagination

DKC

On 2014/1/22, 19:32, William Miller wrote:
 Friends:

 I try to be rigorous in application of NEC codes to everything I do, 
 including wire sizing.  I understand that even though I am using 
 conductors rated at 90°C, the breakers I use have terminals rated at 
 75°C so when deriving the values for ampacity for a given gauge from 
 the tables, I have to use the 75°C column.

 What is not clear, however, is which column I use when applying 
 temperature derating.  Table 315(B)(2)(b) has a column for 75 and a 
 column for 90.  I am using 90° wire.  The values for 90° are much more 
 generous than the 75° values and I would like to use them.  Which is 
 correct?

 As always, thanks to everyone on this list for all of the help and advice.

 William

 Gradient Cap

 Lic 773985

 millersolar.com http://www.millersolar.com/

 805-438-5600



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3462 / Virus Database: 3681/7024 - Release Date: 01/22/14


-
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3462 / Virus Database: 3681/7024 - Release Date: 01/22/14

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 

[RE-wrenches] astropower panels

2014-01-24 Thread Kirk Herander
If anyone has any Astropower panels, AP-110 or AP-120, hiding somewhere pls
contact me off-list.

 

Kirk Herander

VT Solar, LLC

dba Vermont Solar Engineering

NABCEPTM Certified Inaugural Certificant

NYSERDA-eligible Installer

VT RE Incentive Program Partner

802.863.1202

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NEC 2014 690.12 Rapid Shutdown

2014-01-24 Thread Drake
Here is the email that I sent to Matt Paiss in response to his 
contact with me.


Matt,

Thanks for your email. I was in the midst of answering it yesterday 
when my reply disappeared into cyberspace.  Maybe it found its way to 
your mailbox.


We agree strongly that PV should be made as safe as possible, and 
that firefighters need to be educated about these systems.  The issue 
I raise is that the new rule came through with no lead time, no NRTL 
listed equipment available to satisfy the requirement, and no 
prescribed way to implement it.  Through the work of many, maybe 
including you, the ruling fortunately was not far more damaging.


There is no emergency requiring immediate implementation of a 
methodology that will create so many problems for the PV 
industry.  The dangers of rooftop PV do not show up on the radar 
compared to even the use of extension cords; much less traffic deaths 
and fatalities related to mis-prescribed medicines; and diseases 
suffered by the general public, caused by the extractive industries.


This new code requirement presents a major new issue for the industry 
to deal with. It is yet another block in the way of solar cost 
effectiveness, and with it the success ratio of the industry.  This 
requirement has come with no set solution, and will continue to cause 
considerable financial loss and stress until all the details are 
eventually worked out.


It is the fact that the PV industry has been wounded in this way that 
makes it seem like an ALEC-supported operation. This assault works 
well for the group's agenda. ALEC is not a matter of secret agendas; 
it is very visible, with an extremely well-orchestrated assault on 
the PV 
industry. 
http://ecowatch.com/2014/01/22/largest-power-company-alec-solar/http://ecowatch.com/2014/01/22/largest-power-company-alec-solar/ 

You may well be right that no committee members were lobbied. You 
were there and I was not. Nevertheless, I would really like to know 
who proposed the module level rapid disconnect requirement. Some may 
be alarmed about PV rooftop systems for good reason, and / or they 
may have been influenced to consider this relatively safe technology 
to be a threat.


Would it be possible for you to put me in contact with the people who 
presented this idea, and those who argued passionately for it? If 
they want to contact me, please forward my contact information to them.


Best regards,

Drake





At 02:11 PM 1/24/2014, you wrote:

Wrenches,

Matt Paiss is wanted to chime in here. He's a member of the 
Code-Making Panel No. 4 Firefighter Safety Task Group, as well as 
SEIA's PV Industry Forum.


Since he can't post to the list, I am sharing his comments with the group:



Drake,

After reading your initial comments, I think you have nailed both 
the intent of this code section as well as the benefits.  But in 
reading your second posting, I felt it important to write you.  As 
one of the representatives from the Fire Service that drafted 
690.12, I can tell you that while there is always room for 
improvement in language, the goal is to have PV that can not start 
a fire.  As I am not a wrench I can not post to the list (feel 
free to share any of my comments here if you wish), but I would 
like to chime in on this conversation.


Your assertion that ALECs are targeting the PV industry is not 
taking place in this process.   There are many hard-working 
individuals from the PV industry, electrical inspectors, and the 
fire service working together to keep PV safe and secure for many 
years to come.  I for one have both PV and thermal on my home.


While you are correct that no fire fighter fatalities have resulted 
from a PV system shock, the goal is to prevent the first. One 
problem is that the PV industry has not adequately addressed the 
arc and ground fault problems in the US.  Simply put, many rooftop 
systems are not NEC compliant; they can not detect and interrupt 
all faults.  This has unfortunately resulted in far too many 
fires.  The many additions  changes to sec 690 in the 2014 cycle 
will go far in achieving a much safer system.


The fire service is becoming increasingly aware, educated, and 
involved in the code process for PV safety.  It should be clear 
that the goal for all parties is a safe electrical product.  There 
is no secret agenda to pull the rug out from under solar. To those 
that are concerned with the imbedded cost increases, please take a 
longer view than your current FY.  The systems that fire fighters 
respond to may be many years old, but in reality most of the fires 
have occurred on new systems.  We will respond to older systems 
over time, and some buildings will be lost due to concern over the 
inability to isolate power down to a safe level.  As I teach 
firefighters about electrical safety, many express both an interest 
in PV as well as concern that it should be possible to shut a 
system down in the event of an emergency either manually, or as a 
result of a 

[RE-wrenches] Static shock

2014-01-24 Thread jay peltz
Hi all,

Here is a new question. 
I believe it's static electricity. 

System:  standalone 2 x 44voc  165 watt modules in parallel
Powering a pump sq flex( yea installer didn't do it right) dry ground. 
No batteries or any other power in the area, no LCB or other electronics. 
Pole mount, dpw in concrete with galvy pole
Wires are not attached to pole/ rack in any way
It's been very low humidity 5-10%, with 10-20 mph wind
No rain totally dry

Here is what happened. 
Person with one hand touched pole and and other hand touched the USE-2 
insulated wire from the modules, got way shocked. Checked the wire no cracks 
etc and again 44voc max

Happened a second time, but this time his sleeve brushed the pole while he was 
moving the wires, again shocked. 

Again, I think it's static as I have no other explanation. This kind of weather 
is unknown where I live. I now live in a true desert vs a rain forest and never 
moved. 

Thoughts?

Thanks

Jay

Peltz power 


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Corrugated roof brackets

2014-01-24 Thread Jerry Shafer
Go look at sunmodo  they also have some solutions tell them jerry from
affinity sent you, great price point. The are in Washington state check it
out
On Jan 23, 2014 1:37 PM, All Solar, Inc. allso...@scswifi.net wrote:

 Can anyone comment on the S-5! CorruBracket?
 Any other recommendations or comments appreciated.

 Jeremy Rodriguez,
 President

 All Solar, Inc.
 1463 M
 Penrose Colorado 81240
 719-372-3808 office
 719-372-3804 fax
 www.asolarelectric.com

 Sent by Jeremy's iPhone. Sorry for typos and shorthand!
 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Change email address  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org