Marco,
 
The applicability of your statement ...
 
... what’s beyond dispute is that when we size the solar array higher than the 
nameplate inverter output, there will be clipping that takes place….i.e., 
harvestable solar power that goes nowhere.
 
depends to a great extent on the site climate .. as I'm sure you're aware.  
Overall, the blanket statement you make in this respect is not correct.


Using Hawaii, and 65F/85F as low and high respectively, Solar World SW270 
photovoltaic modules will nominally generate 243 watts at 65F, and 225 watts at 
85F under conditions of 1 kW/m^2 irradiance and perfectly orthogonal to the sun.

Microinverters rated 225 watts AC output at ~95% efficiency will input 
nominally 237 watts DC.  Subsequently, the maximum amount of limiting that 
could take place under these conditions is approximately 6 watts.  However, 
that too will not happen, as the 65F condition does not occur during mid-day.

Since 65F occurs early morning, during periods of decreased irradiance, the sun 
angle will be fairly low, thus the SW270 photovoltaic modules won't be 
orthogonal to the sun .. nor will there be 1 kW/m^2 irradiance.  Thus the PV 
module won't be producing 243 watts, but instead will be much less, depending 
on irradiance and sun angle (among other things).

In your own Hawaiian climate, the SW270 is in fact an almost perfect energy 
match for the Enphase 225.

Move the scenario to Phoenix, Arizona, and the cold/hot PV power output (using 
5C/40F low, and 50C/120F high), the PV power output would be 249W and 202W 
respectively, again with 1 kW/m^2 and orthogonal to the sun.  The likelihood of 
40F during mid-day in Phoenix is exceedingly rare.  Thus you can see that the 
SW270 module is actually a bit UNDERSIZED for an Enphase 225 in Phoenix.  The 
amount of energy not harvested due to limiting in the Phoenix environment is 
essentially zero, even with a 270 watt PV module.

Conversely, the SW270 / Enphase 225 combination in Minneapolis would not be 
optimal due to the extremely cold winter weather.  Here, power limiting within 
the inverter WOULD occur when cold, resulting in less than 100% of the 
available DC energy converted to AC at an ambient temperatures of ~50F or 
cooler, and under conditions of 1 kW/m^2 irradiance with the sun perfectly 
orthogonal to the PV module.  This would not be thermally harmful to the 
microinverter because it would be taking place during extremely cold weather.  
Conversely, during summer months, using 35C (95F) as the typical high 
temperature in Minneapolis, the PV module output would be reduced to 220 watts, 
all other conditions being equal .. thus LESS than is needed for maximum output 
by the microinverter.


In summary, in warm-to-hot climates, the SW270 would in fact be a nearly ideal 
match for the Enphase 225 from an energy perspective.



Regards to all,



Dan Lepinski




On Tue, 8/26/14, Marco Mangelsdorf ma...@pvthawaii.com wrote:

Subject: [RE-wrenches] Inverters Maximum Input Ratings
To: 'RE-wrenches' re-wrenches@lists.re-wrenches.org
Date: Tuesday, August 26, 2014, 1:10 AM
 
Look, guys, what’s beyond dispute is that when we size the solar array higher 
than the nameplate inverter output, there will be clipping that takes 
place….i.e., harvestable solar power that goes nowhere.  The higher that 
oversize percentage, the more clipping will take place. 

If the design choice, as noted below, is to use a 270-watt module (from a 
manufacturer that learned last week that a recall notice was published by the 
U.S. Consumer Product Safety Commission 
https://www.cpsc.gov/en/Recalls/2014/SolarWorld-Recalls-Solar-Systems-with-Copper-Grounding-Lugs/
 ), does it make sense to use a micro inverter that has a max output of about 
225 watts (M215) or 250 watts (M250) when there are micros (e.g., ABB 300) that 
can handle the full output of the 270 which guarantees NO clipping?

 marco
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Rapid shutdown questions

2014-08-29 Thread Dave Click
While I share Robin's optimism, I should also note the NEC 2017 690.12 
committee referred to is not the code making panel. While it does have 
(at least) one firefighter representative among a majority of PV 
industry personnel, there's no guarantee that the Code Making Panel 
approves this committee's proposal. There could very well be a competing 
proposal from firefighters that requires cell-level shutdown every time 
a red truck drives within 1/4 mile of an array, because SAFETY!


DKC


On 2014/8/28, 15:16, b...@midnitesolar.com wrote:


[Robin chiming in, below]

Dan, The 2014 690.12 is worded poorly. That is why there is so much 
confusion. MidNite Solar is sitting on the NEC2017 690.12 committee. 
There are a lot of smart people in this group. The 2017 version says 
ALL PV SYSTEMS, not just on or in buildings. The 10 foot space gets 
reduced to 1 foot like it always should have been.


There will be a lot of other clarifications too. The systems that use 
shunt trip breakers [with Remote Trip coil] and contactors are for 
string inverters. Shunt trip breakers will be used for battery based 
systems and grid tie inverters with an AC outlet like the SMA TL 
series. Micro inverters do not require anything like what our system 
is. They can use the existing backfed breaker in the main distribution 
box as long as it is labeled accordingly.  Solar Edge has a system 
that meets the Rapid Shutdown requirement also.


The UL standard for Rapid Shutdown has been written. It is going to go 
out to a task force for review, comment and changes soon. MidNite 
Solar will be on that task force. The MidNite Birdhouse is going 
through UL now and is being evaluated to this new standard. All of our 
disconnecting combiners and SOBs are already ETL listed. UL is 
modifying the new Rapid Shutdown Draft standard as they come upon 
things in the Birdhouse that the standard didn't consider. One of the 
biggies that has not been sorted out is a requirement for feedback. 
Contactors, power supplies and a switch will meet the requirement for 
2014. The issue with this type of system is that when you push the 
button to turn off the contactors, there is no way to tell that they 
actually opened up. Without feedback that verifies that the contactors 
are actually open, you are taking a chance with people's lives. 600VDC 
contactors can weld themselves closed. If first responders don't trust 
the Rapid Shutdown system, they are going to let the house burn. We do 
have feedback on the birdhouse system. Contactors do not have 
feedback. It is not simple to add this feature to a contactor based 
system.


Installing a switch 15 feet up on the side of a building or on the 
roof is not the intent of 690.12. This will not be allowed in 2017. 
The exact placement of the initiating device (Birdhouse) is not cast 
in concrete due to the differences in where main panel boards are 
located, but it will not allow things like mentioned here 15 feet up 
in the air or in the attic or on the roof.


Battery based systems are the most complicated to meet 690.12. The NEC 
committee is deferring a lot of this to MidNite as we are already 
doing it and have gone over all the different ways things can go 
wrong. We started designing our system right after the Bakersfield 
fire 5 years ago. The Bakersfield fire is what got the NEC to require 
disconnecting combiners. We couldn't imagine why a fire fighter would 
want to get up on the roof of a burning building to look for a 
combiner? This is why we started the birdhouse project way before 
anyone ever thought of the words Rapid Shutdown. Turns out this was a 
good thing since battery backed up systems make the issue ten times 
more complicated. We spent years working out issues and there were 
lots of them that required a start from scratch approach numerous times.


AC coupling to a battery based inverter does not automatically meet 
690.12 as someone mentioned in this thread. That battery based 
inverter must also be shut off. The micro inverters would of course 
shut off when the utility is shut down, but the battery based 
inverters job is to keep things powered up when the grid is down. So 
the battery based inverter has to be shut down also.


 It would also make sense to shut off an auto start generator with the 
Rapid Shutdown button. Some generators are designed to start up upon 
loss of grid. Once the first responders have the meter pulled, that 
could start up a generator and cause risk of shock. If the generator 
is designed to start on low battery, it could start a day later when 
the fire has been put out, but that also poses risk of electrical 
shock when unexpectedly the part of the house that is left all of a 
sudden comes live with juice.


The cost for a Rapid Shutdown system will vary a lot depending on what 
you want to shut down. You do not need to run conduit to all the boxes 
and switches. There is 600V Cat5e 90C USE-2 cable available that will 
suffice. I don't see a 

[RE-wrenches] BP Solar Point of Contact

2014-08-29 Thread Peter Parrish
Has anyone a point of contact at BP Solar to discuss warranty issues of
SX170Bs installed in January 2006?

Thanks

Peter T. Parrish, Ph.D. 
President, SolarGnosis
1107 Fair Oaks Ave.
South Pasadena, CA 91107
Ph. (323) 839-6108, Fax. (323) 258-8827

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] BP Solar Point of Contact

2014-08-29 Thread Marco Mangelsdorf
I've just been having contact with them this week in fact.

laura.koutsostama...@bp.com 

-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Peter Parrish
Sent: Friday, August 29, 2014 8:05 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] BP Solar Point of Contact

Has anyone a point of contact at BP Solar to discuss warranty issues of
SX170Bs installed in January 2006?

Thanks

Peter T. Parrish, Ph.D. 
President, SolarGnosis
1107 Fair Oaks Ave.
South Pasadena, CA 91107
Ph. (323) 839-6108, Fax. (323) 258-8827

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org