Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Chris Mason
I promised a picture of the Sonnen installation. As these units are getting
close to being appliances in the same vein as home audio, we wanted to have
a clean finish so we made some mill work to complete the top of the unit to
the ceiling and hide the ugly conduits.
https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0

On Thu, Jun 16, 2016 at 3:47 PM, Marco Mangelsdorf 
wrote:

> Dunno exactly, Carl.
>
>
>
> Twas not I who installed it.
>
>
>
> marco
>
>
>
> Marco,
>
>
>
> Are the two switch gear boxes integral to the installation.  If so can you
> give me an idea of what their function/purpose is?
>
>
>
> On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf 
> wrote:
>
> Provides an idea of size and scale.
>
> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>
> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear, two
> Tesla Powerwalls.
>
>
>
>
>
>
> --
>
>
> 
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> 
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
>
> --
>
> 
>
> This email has been checked for viruses by Avast antivirus software.
> www.avast.com
> 
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com 
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] 1000V Surge Arrestors

2016-06-17 Thread John Stimac
Can anyone recommend a 1000VDC surge arrestor? Cooper Bussmann has them for
 >$1000. Delta has them for $39. Thanks!
--
John Stimac | Corvallis, OR
Renewable Energy Associates, LLC
541-754-2001 Office
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1000V Surge Arrestors

2016-06-17 Thread Brian Mehalic
Dehn and Citel make them.  

Brian

> On Jun 17, 2016, at 11:11 AM, John Stimac  
> wrote:
> 
> Can anyone recommend a 1000VDC surge arrestor? Cooper Bussmann has them for  
> >$1000. Delta has them for $39. Thanks!
> --
> John Stimac | Corvallis, OR
> Renewable Energy Associates, LLC
> 541-754-2001 Office
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1000V Surge Arrestors

2016-06-17 Thread Dana Solar work
MCG

Dana Orzel 2087217003
"Follow the flow of your internal river, acknowledging the put-ons & put-outs."

On Jun 17, 2016, at 10:11 AM, John Stimac  wrote:

Can anyone recommend a 1000VDC surge arrestor? Cooper Bussmann has them for  
>$1000. Delta has them for $39. Thanks!
--
John Stimac | Corvallis, OR
Renewable Energy Associates, LLC
541-754-2001 Office

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 1000V Surge Arrestors

2016-06-17 Thread John Stimac
Do you know of any that mount to enclosures the way midnite solar surge
suppressors mount to enclosures?

--
John Stimac | Corvallis, OR
Renewable Energy Associates, LLC
541-754-2001 Office


On Fri, Jun 17, 2016 at 10:11 AM, Brian Mehalic 
wrote:

> Dehn and Citel make them.
>
> Brian
>
> > On Jun 17, 2016, at 11:11 AM, John Stimac 
> wrote:
> >
> > Can anyone recommend a 1000VDC surge arrestor? Cooper Bussmann has them
> for  >$1000. Delta has them for $39. Thanks!
> > --
> > John Stimac | Corvallis, OR
> > Renewable Energy Associates, LLC
> > 541-754-2001 Office
> >
> > ___
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Carl Adams
Chris,

Nice finish on the Sonnen install.  It looks fabulous.  My understanding is
the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW
radian.  I assume generator support is fully supported

On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason 
wrote:

> I promised a picture of the Sonnen installation. As these units are
> getting close to being appliances in the same vein as home audio, we wanted
> to have a clean finish so we made some mill work to complete the top of the
> unit to the ceiling and hide the ugly conduits.
> https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0
>
> On Thu, Jun 16, 2016 at 3:47 PM, Marco Mangelsdorf 
> wrote:
>
>> Dunno exactly, Carl.
>>
>>
>>
>> Twas not I who installed it.
>>
>>
>>
>> marco
>>
>>
>>
>> Marco,
>>
>>
>>
>> Are the two switch gear boxes integral to the installation.  If so can
>> you give me an idea of what their function/purpose is?
>>
>>
>>
>> On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf 
>> wrote:
>>
>> Provides an idea of size and scale.
>>
>> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>>
>> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear,
>> two Tesla Powerwalls.
>>
>>
>>
>>
>>
>>
>> --
>>
>>
>> 
>>
>> This email has been checked for viruses by Avast antivirus software.
>> www.avast.com
>> 
>>
>>
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>> --
>>
>> 
>>
>> This email has been checked for viruses by Avast antivirus software.
>> www.avast.com
>> 
>>
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com 
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SolarEdge 7600 and the Powerwall

2016-06-17 Thread Chris Mason
Yes, correct on both. The generator support is there, I did not use it.

On Fri, Jun 17, 2016 at 3:07 PM, Carl Adams  wrote:

> Chris,
>
> Nice finish on the Sonnen install.  It looks fabulous.  My understanding
> is the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW
> radian.  I assume generator support is fully supported
>
> On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason  > wrote:
>
>> I promised a picture of the Sonnen installation. As these units are
>> getting close to being appliances in the same vein as home audio, we wanted
>> to have a clean finish so we made some mill work to complete the top of the
>> unit to the ceiling and hide the ugly conduits.
>> https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0
>>
>> On Thu, Jun 16, 2016 at 3:47 PM, Marco Mangelsdorf 
>> wrote:
>>
>>> Dunno exactly, Carl.
>>>
>>>
>>>
>>> Twas not I who installed it.
>>>
>>>
>>>
>>> marco
>>>
>>>
>>>
>>> Marco,
>>>
>>>
>>>
>>> Are the two switch gear boxes integral to the installation.  If so can
>>> you give me an idea of what their function/purpose is?
>>>
>>>
>>>
>>> On Mon, Jun 13, 2016 at 9:20 PM, Marco Mangelsdorf 
>>> wrote:
>>>
>>> Provides an idea of size and scale.
>>>
>>> [image: Tesla Battery system Aalto residence2. 6 may 2016]
>>>
>>> From left to right—disconnect, kWh meter, SolarEdge 7600, switch gear,
>>> two Tesla Powerwalls.
>>>
>>>
>>>
>>>
>>>
>>>
>>> --
>>>
>>>
>>> 
>>>
>>> This email has been checked for viruses by Avast antivirus software.
>>> www.avast.com
>>> 
>>>
>>>
>>>
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>>
>>> --
>>>
>>> 
>>>
>>> This email has been checked for viruses by Avast antivirus software.
>>> www.avast.com
>>> 
>>>
>>>
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>
>>
>>
>> --
>> Chris Mason
>> NABCEP Certified Solar PV Installer™
>> Solar Design Engineer
>> Generac Generators Industrial technician
>>
>> www.cometsolar.com 
>> 264.235.5670
>> 869.662.5670
>> Skype: netconcepts
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician

www.cometsolar.com 
264.235.5670
869.662.5670
Skype: netconcepts
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Arch

Re: [RE-wrenches] Sonnen Battery & Outback Radian Inverter

2016-06-17 Thread Gary Willett

  
  
Enclosed is a photo of what appears to be a test/lab Sonnen
  system published in the 01/30/2016 edition of "Power Magazine.
Can plainly see the 8kW Outback Radian inverter and I assume four
  12V Sonnen (Sony?) 8kWh Lithium-Ion batteries. Assume this is a
  "standard" 48V Radian inverter.

http://www.powermag.com/german-battery-firm-sonnen-moves-into-u-s-home-solar-storage-market/
Regards,
Gary Willett
Icarus Engineering LLC


  
  On 6/17/16 2:09 PM, Chris Mason wrote:


  Yes, correct on both. The generator support is
there, I did not use it.
  
On Fri, Jun 17, 2016 at 3:07 PM, Carl
  Adams 
  wrote:
  
Chris,
  
  
  Nice finish on the Sonnen install.  It looks
fabulous.  My understanding is the Eco 2-8 integrate the
4kW radian, and the 10-16 incorporates the 8kW radian. 
I assume generator support is fully supported


  

  On Fri, Jun 17, 2016 at 8:35
AM, Chris Mason 
wrote:

  I promised a picture of the Sonnen
installation. As these units are getting close
to being appliances in the same vein as home
audio, we wanted to have a clean finish so we
made some mill work to complete the top of the
unit to the ceiling and hide the ugly conduits.
https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0

  
  

  
  

  

  

  

  

  


  

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Sonnen Battery & Outback Radian Inverter

2016-06-17 Thread Roland - RES
FYI that's a showroom unit with none of their internal wiring, and dummy 
inverter and batteries to keep it light. An actual unit has a tremendous amount 
of factory wiring between contractors, 200a auto transfer switch CT's and 
sensors along with a powder coated steel door in place of plexiglass. The 
Batteries are manufactured by Sony, they come in 48V 2kWh blocks that get 
paralleled together. 

> Sent from a IPhone, with touch screen keys on the fly. Please excuse 
> shortcuts and typos. 
Roland Shackelford
NABCEP CERTIFIED PV INSTALLER
Vice President 
Renewable Energy Services (RES), Inc. 
Mobile:  808-938-9239
www.renewablenergy.com

> On Jun 17, 2016, at 3:54 PM, Gary Willett  
> wrote:
> 
> Enclosed is a photo of what appears to be a test/lab Sonnen system published 
> in the 01/30/2016 edition of "Power Magazine.
> 
> Can plainly see the 8kW Outback Radian inverter and I assume four 12V Sonnen 
> (Sony?) 8kWh Lithium-Ion batteries. Assume this is a "standard" 48V Radian 
> inverter.
> http://www.powermag.com/german-battery-firm-sonnen-moves-into-u-s-home-solar-storage-market/
> 
> Regards,
> 
> Gary Willett
> 
> Icarus Engineering LLC
> 
> 
>> On 6/17/16 2:09 PM, Chris Mason wrote:
>> Yes, correct on both. The generator support is there, I did not use it.
>> 
>> On Fri, Jun 17, 2016 at 3:07 PM, Carl Adams  wrote:
>>> Chris,
>>> 
>>> Nice finish on the Sonnen install.  It looks fabulous.  My understanding is 
>>> the Eco 2-8 integrate the 4kW radian, and the 10-16 incorporates the 8kW 
>>> radian.  I assume generator support is fully supported
>>> 
 On Fri, Jun 17, 2016 at 8:35 AM, Chris Mason 
  wrote:
 I promised a picture of the Sonnen installation. As these units are 
 getting close to being appliances in the same vein as home audio, we 
 wanted to have a clean finish so we made some mill work to complete the 
 top of the unit to the ceiling and hide the ugly conduits.
 https://www.dropbox.com/s/vlh0uumlgf5549g/2016-06-15%2011.00.44-1.jpg?dl=0
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org