Re: [RE-wrenches] Testing AGMs
I agree, I usually steer full time off grid customers away from AGM, but for remote sites that might not be attended for months at a time, AGMs do have a purpose. We've had good luck with Full River. Load testing is one really long way to test; I usually just have the customer do load testing with the system and the Trimetric or other SOC meter. Run a good charge cycle, then turn off the solar for a couple of days, and see what kind of capacity is left. Also always good to check voltages of all the batteries, and see if there are weak or dead cells. Dead cells show up pretty easily, they will test 1.5 to 2 volts lower. My latest toy purchase was a FLIR camera, it has been extremely helpful. You can literally see the dead cells within the packs. They show up noticeably warmer than surrounding cells. If you see anything like that, you know the pack is probably toast. Finally, a really good test is how old they are. If they are rated at 300 cycles to 80% DOD battery and they are 5 years old, they're probably gone as well. Most AGMs do not have long cycle lives. Folks don't call to complain about batteries unless they're not working right. I listen to my customers; they know better than anyone when the system isn't working the same, and after checking for new loads, and proper charge settings, its almost always batteries. Ray Remote Solar On 2/24/18 5:20 PM, Dave Angelini Offgrid Solar wrote: Load test and compare with another known good battery. I also steer away from AGM's. --Dave Wrenches, We have a client with a string of sealed L16s and he believes he may have a weak or failed cell. What’s the best way to test or check these batteries, since there is no electrolyte to draw out. We don’t install many AGMs, in fact, steer the client away from them, usually. Jeremy Rodriguez Solar Installation And Design Expert All Solar, Inc. 1463 M St Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand! ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Testing AGMs
Load test and compare with another known good battery. I also steer away from AGM's. --Dave > Wrenches, > We have a client with a string of sealed L16s and he believes he may have > a weak or failed cell. > > Whatâs the best way to test or check these batteries, since there is no > electrolyte to draw out. > > We donât install many AGMs, in fact, steer the client away from them, > usually. > > > > > Jeremy Rodriguez > Solar Installation And > Design Expert > All Solar, Inc. > 1463 M St > Penrose Colorado 81240 > > Sent by Jeremy's iPhone. Sorry for typos and shorthand! > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Testing AGMs
Wrenches, We have a client with a string of sealed L16s and he believes he may have a weak or failed cell. What’s the best way to test or check these batteries, since there is no electrolyte to draw out. We don’t install many AGMs, in fact, steer the client away from them, usually. Jeremy Rodriguez Solar Installation And Design Expert All Solar, Inc. 1463 M St Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand! ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Radian throughput power
Hello Lones here. When an ac source is accepted by the inverter. The rely connects the ac input directly to the ac output. The relay is (should be) protected by a 50 amp breaker If there is an ac load of 8KW or 33 ac amps the remaining current is available to be used by the inverter for battery charging. If the load increases above 8k charging is reduced to honor the loads first. If the loads chew up all 50 amps charging will be reduced to zero. Above 50 and the breaker should trip or damage to the relay may result. It is possible to use Support Mode. This sets a limit on the amount of current passing through from the source to the loads. Any amount above the set point will be supplied from the batteries. If the ac input current is set to 25 ac amps. Any load above the 25 amps will come from the batteries. Sustained loads above this adjustable set point could possibly deplete the batteries. If the load drops below the 25amp charging will resume. It is possible have an ac source and deplete the batteries. Loads first Charging 2nd. I hope this helps. Take Care All -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Angelini Offgrid Solar Sent: Saturday, February 24, 2018 9:16 AM To: RE-wrenchesSubject: Re: [RE-wrenches] Radian throughput power You are missing the charging of the battery! That is where (your numbers) the 12KW - 8KW can go! Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 > Wrenches, > >          I spoke with tech support at Outback recently > and was told the max output of the Radian at the output terminals is > 8KW, even if there is an external AC source connected to one of the AC > IN terminals of the Radian. > >          However, on page 18 of the GS8048 manual: > "When it (transfer relay) closes the L1 input and output terminals > become electrically common." ...same for L2 input and output. then, > "the relay contacts are limited to 55 amps per phase or leg". Since > there is no 55 amp circuit breaker to protect that relay a 50 amp 2 > pole breaker would be used. This means you would have 50A X 240 Vac > (12KW) at the output terminals, correct? > >          Am I missing something? Thanks, > > Bill > > Feather River Solar Electric > Bill Battagin, Owner > 4291 Nelson St. > Taylorsville, CA 95983 > 530.284.7849 > CA Lic 874049 > www.frenergy.net > > > --- > This email has been checked for viruses by Avast antivirus software. > https://www.avast.com/antivirus > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist > .html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Radian throughput power
You are missing the charging of the battery! That is where (your numbers) the 12KW - 8KW can go! Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 > Wrenches, > >          I spoke with tech support at Outback recently and > was told > the max output of the Radian at the output terminals is 8KW, even if > there is an external AC source connected to one of the AC IN terminals > of the Radian. > >          However, on page 18 of the GS8048 manual: "When it > (transfer relay) closes the L1 input and output terminals become > electrically common." ...same for L2 input and output. then, "the relay > contacts are limited to 55 amps per phase or leg". Since there is no 55 > amp circuit breaker to protect that relay a 50 amp 2 pole breaker would > be used. This means you would have 50A X 240 Vac (12KW) at the output > terminals, correct? > >          Am I missing something? Thanks, > > Bill > > Feather River Solar Electric > Bill Battagin, Owner > 4291 Nelson St. > Taylorsville, CA 95983 > 530.284.7849 > CA Lic 874049 > www.frenergy.net > > > --- > This email has been checked for viruses by Avast antivirus software. > https://www.avast.com/antivirus > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Radian throughput power
Wrenches, I spoke with tech support at Outback recently and was told the max output of the Radian at the output terminals is 8KW, even if there is an external AC source connected to one of the AC IN terminals of the Radian. However, on page 18 of the GS8048 manual: "When it (transfer relay) closes the L1 input and output terminals become electrically common." ...same for L2 input and output. then, "the relay contacts are limited to 55 amps per phase or leg". Since there is no 55 amp circuit breaker to protect that relay a 50 amp 2 pole breaker would be used. This means you would have 50A X 240 Vac (12KW) at the output terminals, correct? Am I missing something? Thanks, Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 www.frenergy.net --- This email has been checked for viruses by Avast antivirus software. https://www.avast.com/antivirus ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org