Re: [RE-wrenches] XW FET over-temp errors
I’ve replaced the fan a few times. Mouser.com or digikey will have a good replacement. You’ll need to splice the white fan connector on to the new fan. I’ll look in the mouser history for the brand and model I used last. Thank you, Maverick > On Mar 3, 2020, at 9:39 PM, Mac Lewis wrote: > > > Hi wrenches, > > Does anyone know how to obtain a replacement cooling fan for a 5 yr old XW > 6048 inverter? I suspect that the fan isn't functioning and the FET boards > are heating up, we keep seeing a shutdown when selling near peak. > > I believe the Schneider part is 100-0639-01-01, but Im not seeing anything on > a quick search. > > Thanks > > -- > > > > Mac Lewis > > "Yo solo sé que no sé nada." -Sócrates > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] XW FET over-temp errors
Hi wrenches, Does anyone know how to obtain a replacement cooling fan for a 5 yr old XW 6048 inverter? I suspect that the fan isn't functioning and the FET boards are heating up, we keep seeing a shutdown when selling near peak. I believe the Schneider part is 100-0639-01-01, but Im not seeing anything on a quick search. Thanks -- Mac Lewis *"Yo solo sé que no sé nada." -Sócrates* ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Offgrid Generators?
Ray, Let me try to address some of those issues for you. 1) You can get the activation code before you take it to site, you just need the serial number. Generac has a good warranty policy but they need to know where the generator is and when it is installed to be able to provide that. 2) An electrician can connect the wires but you would not believe the installations we have seen, done by licensed electricians. We have a dealer forum where installers post pictures of installations they find, and the mistakes are criminal and dangerous. I once found a propane 20KW generator running side a shipping container, doors closed. 3) Generac does not do direct support for generators, they require customers call a dealer. The dealer can then call Generac, and often does. I can't even call them if my certification expires. 4) If the generator is under warranty, you may not pay anything, depending on the coverage. Generac is offering up to ten year warranties. But once it is out of warranty, you will have to pay. Dealers don't work for free. The average electrician won't be able to diagnose problems reliably on these generators. The residential air cooled generators are very reliable and rarely have problems if well maintained. Techs should be traveling with common parts, I bring a controller and a few other parts so I can solve the problem in one go. Blown engines are rare, but they do happen. Generally in the first few hours, so under full warranty and replacement is generally done at Generac's expense. If you do have issues, contact me and I will try to help you. On Fri, Feb 28, 2020 at 4:41 PM Ray wrote: > Some of the issues have been Generac not providing a simple wiring > schematic, nor simply labeling the 2 start wires. 2nd is requiring either > internet connection or a call in to get the start code. Both have been > very problematic in remote locations with no phone service. Totally > unnecessary. We don't need a Generac tech just to connect wires, I'm the > licensed electrician. Last time I called Generac, (control error not > listed in the manual) they insisted I needed to call in a service tech, and > offered zero trouble shooting. I fixed the problem by pulling the fuse and > resetting the controller. 3rd, service requires a long expensive trip by > the service tech, who then diagnoses the problem, has to order the parts > and return weeks later. This means every issue takes 2 round trips to > resolve. If its a bigger issue, it requires a truck lift to haul the 500 > lb unit in to the shop. We're hearing $500 just to get the generator to > the shop, then another $500 to reinstall it after. > > Failures have included several catastrophic engine failures, blowing oil > every where, some of these have been in the first few hundred hours. Lots > of control issues, one recently had voltage that varied from 90 to 130, 45 > to 70 Hz, and the inverter wouldn't even connect to it. > > I quit selling generators a long time ago, because I didn't want the > service liability. I'm not a mechanic, and I don't want to be. I do > however, need a generator I can recommend in good faith. The Ecogen has > made us look pretty bad. Glad I didn't sell them, but then I've seen some > large water cooled unit that worked well. > > Ray Walters > Remote Solar > 303 505-8760 > > On 2/28/20 5:14 AM, Chris Mason wrote: > > Ray, > I'm a Generac dealer. Why are you having support problems? Generac has a > large dealer network, if the unit is under warranty you should have no > problem getting it fixed. Did you buy through a dealer and have them > install it? Why are the services expensive? > > What failures are you seeing? > > There is a hole in the market for products in this application. Virtually > no-one makes an affordable ~10KW diesel enclosed 2 wire start 1,800 rpm > reliable diesel generator. I once ordered, on spec, a 9KW Perkins engine > liquid cooled enclosed diesel from a factory in China I deal with. I sold > it to a customer that ran it 18 hours a day on 100% load, to power his > restaurant refrigeration outside service hours. It lasted him years, it > must have thousands of hours on it. > I think the big problem in the US is getting permits for diesel generators. > > > > On Thu, Feb 27, 2020 at 6:25 PM Ray wrote: > >> I know we have covered this before, but I just continue to be >> disappointed with the Generac Ecogen. Very high failure rate, and >> support is poor. Service requires expensive on site service. Also the >> no load AC draw and programming setup is just not off grid ready at >> all. I'm still not seeing any other great choices, though. Here's some >> other possibilities: >> >> 1) Quality portable, like the Honda EU 7000i or Northstar with Honda >> motor. Not the best choice especially for autostart, no propane, but at >> least they can take it in to the shop if it goes down. >> >> 2) Kubota (or MQ) diesel. expensive, and possible cold weather start >> issues? >> >> 3) 20+ kW water
[RE-wrenches] OK, so what iwould happen if I do this...
You wrote that you would connect the Exeltech to just one of the service phases. But most GT inverters are 240 and require both phases. Is yours different? You did not mention which model it is. Also, as Kent Osterberg mentioned, the Exeltech will not charge its batteries from the AC output. Your scheme with the PLC controlling an SCR leaves unaddressed how any charge current gets directed into the batteries to allegedly raise their voltage. Is there a charger somewhere in this scheme?You still need some way to charge batteries from solar. How about connecting a charge controller to some of the solar panels?Don BarchEnergy Solar Original Message Subject: RE-wrenches Digest, Vol 13, Issue 59 From: re-wrenches-requ...@lists.re-wrenches.org Date: Sun, March 01, 2020 2:19 pm To: re-wrenches@lists.re-wrenches.org Send RE-wrenches mailing list submissions to re-wrenches@lists.re-wrenches.org To subscribe or unsubscribe via the World Wide Web, visit http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org or, via email, send a message with subject or body 'help' to re-wrenches-requ...@lists.re-wrenches.org You can reach the person managing the list at re-wrenches-ow...@lists.re-wrenches.org When replying, please edit your Subject line so it is more specific than "Re: Contents of RE-wrenches digest..." When responding to posts within the Digest, be sure to restore the Subject: line to the original, and please edit out any extraneous lines from the quoted message. Today's Topics: 1. OK, so what iwould happen if I do this... (Mark Frye) 2. Re: OK, so what iwould happen if I do this... (frenergy) 3. Re: OK, so what iwould happen if I do this... (Kent Osterberg) 4. Re: OK, so what iwould happen if I do this... (Jerry Shafer) -- Message: 1 Date: Sat, 29 Feb 2020 15:27:32 -0800 From: Mark FryeTo: RE-wrenches Subject: [RE-wrenches] OK, so what iwould happen if I do this... Message-ID: <93731c38-40b5-7c63-1d74-a879fbdd9...@berkeleysolar.com> Content-Type: text/plain; charset=utf-8; format=flowed I have 2kw of grid tied PV on my house. Suppose I: - Open the main breaker to disconnect from the grid - I open the PV breaker - I connect a small good quality inverter like an Exeltech XP 500 to one of the phases of the service (120 VAC) - I put a small battery pack, 100 AH at 24 VDC on the inverter OK so far, I could run some small loads for a relatively short period of time before the batteries get low -I have a PLC with an AD input and DA output. On the input I measure the battery voltage, on the output I control a SCR. The SCR controls a 2kw immersion heater sitting in a big bucket of water. The PLC has a scan time of 2 mS and I program it to increase the duty cycle of the SCR as voltage of the battery rises above 24 VDC. OK so far nothing has really changed from above. - I close the PV breaker, the GT inverters see the battery inverter, sync and connect after five minutes. Voila, I can run house loads from 0 to 2kw with my existing GT PV with the balance of energy dumped as needed to the immersion heater. Right? Mark Frye -- Message: 2 Date: Sun, 1 Mar 2020 06:26:27 -0800 From: frenergy To: re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] OK, so what iwould happen if I do this... Message-ID: Content-Type: text/plain; charset=utf-8; format=flowed Mark, ??? ??? ??? OR, you change-out your inverter to an SMA with Secure Power Supply and during grid power outage, while there is some sun on the panels, you would have up to 2KW of 120VAC power on the SPS circuit by just flipping a switch. We usually install a 4X outdoor box with a 120 VAC outlet ganged with a switch right under the inverter and let the customer run the power to the : frig, lights, battery charger, TV or whatever during an outage, though some romex could be run to close to the frig. Bill Feather River Solar Electric Bill Battagin, Owner 4291 Nelson St. Taylorsville, CA 95983 530.284.7849 CA Lic 874049 www.frenergy.net On 2/29/2020 3:27 PM, Mark Frye wrote: > I have 2kw of grid tied PV on my house. > > Suppose I: > > - Open the main breaker to disconnect from the grid > > - I open the PV breaker > > - I connect a small good quality inverter like an Exeltech XP 500 to > one of the phases of the service (120 VAC) > > - I put a small battery pack, 100 AH at 24 VDC on the inverter > > OK so far, I could run some small loads for a relatively short period > of time before the batteries get low > > -I have a PLC with an AD input and DA output. On the input I measure > the battery voltage, on the output I control a SCR. The SCR controls a > 2kw immersion heater sitting in a big bucket of water. The PLC has a > scan time of 2 mS and I pr