I had a Nissan Leaf and a 240v charger, we had no problem using our Radian
to charge it during the day.

On Sat, Jun 6, 2020, 22:11 Hilton Dier III  wrote:

> The issue with EV chargers is that they create a lot of reactive power.
> Think of it as "slosh" in the waveform. That means that charging at 2,000
> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from
> the inverter. If you've got a reasonably good sinewave inverter the charger
> will like it fine. However, the inverter might not like the charger if you
> cut things too close. Make sure to have a lot of top end left in your
> inverter. Always use a transformer based inverter. The SW series has a big
> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440
> watts max.
>
> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW, so
> too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE (smart
> charging cord) that comes with the car can draw 8 or 12 amps at 120V or 12
> at 240V. Assume that the 8 amps is really 12 and the 12 is really 15 or a
> bit more. I have seen 15 amp plugs and outlets with the hot prong melting
> plastic around it. The plug on the OEM EVSE is 20A rated but make sure your
> outlet is as well.
>
> --
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a Bolt with an SW

2020-06-07 Thread David Katz
The old SW waveform changes with battery voltage.  On the 24 volt version
there are less steps when the battery is over 28 volts. My washing machine
motor does not run when the battery is over 28.  I just have to turn on the
microwave when I want to do laundry on a sunny day.
David

On Sun, Jun 7, 2020 at 1:05 PM Jay  wrote:

> I’ve got offgrid  2 clients and they have no issues.
>
> They each have a Bolt and can choose the charging rate. They can run it at
> either power. But only use higher power when they have lots of sun.
> Older Stacked vfx and Schneider xw, no issues.
>
> I would expect the SW to work, however it’s an odd beast as it’s waveform
> steps change with load. More load, more steps, therefor cleaner so maybe at
> lower charge rate it’s not clean enough.
>
> As to your issue it could be power factor Being really poor.
> Can you tell us what inverter, yea 5 years ago is a long time.
>
>
>
> Jay
>
> Peltz power.
>
>
>
>
>
> On Jun 7, 2020, at 11:53 AM, Darryl Thayer  wrote:
>
> 
> I think you said it well, about 5 years ago I tried to charge a car from
> an off-grid system.  I did not record my events but the inverter had twice
> the power of the level two charger, yet the inverter would get hot and trip
> out.  I was told a ferroresonant transformer may help, and it might be
> different with different cars.  However, I was warned the ferroresonant was
> to stop input wave problems from arriving at the output not to prevent the
> output wave problems showing up on the input.   The off-grid customer gave
> up.
>
> On Sun, Jun 7, 2020 at 6:36 AM Hilton Dier III 
> wrote:
>
>> The issue with EV chargers is that they create a lot of reactive power.
>> Think of it as "slosh" in the waveform. That means that charging at 2,000
>> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from
>> the inverter. If you've got a reasonably good sinewave inverter the charger
>> will like it fine. However, the inverter might not like the charger if you
>> cut things too close. Make sure to have a lot of top end left in your
>> inverter. Always use a transformer based inverter. The SW series has a big
>> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440
>> watts max.
>>
>> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW,
>> so too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE
>> (smart charging cord) that comes with the car can draw 8 or 12 amps at 120V
>> or 12 at 240V. Assume that the 8 amps is really 12 and the 12 is really 15
>> or a bit more. I have seen 15 amp plugs and outlets with the hot prong
>> melting plastic around it. The plug on the OEM EVSE is 20A rated but make
>> sure your outlet is as well.
>>
>> --
>> Hilton Dier III
>> Missisquoi River Hydro
>> Renewable Energy Design
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> --
David Katz Sent from Gmail Mobile
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a Bolt with an SW

2020-06-07 Thread Darryl Thayer
I was trying to charge a Nissan Leaf with a ? Iam not sure but two VFX i
think old age.. i mostly rember having the problem.  I think the car
harger had a max of 2kw

On Sun, Jun 7, 2020, 3:41 PM Jay  wrote:

> I’ve got offgrid  2 clients and they have no issues.
>
> They each have a Bolt and can choose the charging rate. They can run it at
> either power. But only use higher power when they have lots of sun.
> Older Stacked vfx and Schneider xw, no issues.
>
> I would expect the SW to work, however it’s an odd beast as it’s waveform
> steps change with load. More load, more steps, therefor cleaner so maybe at
> lower charge rate it’s not clean enough.
>
> As to your issue it could be power factor Being really poor.
> Can you tell us what inverter, yea 5 years ago is a long time.
>
>
>
> Jay
>
> Peltz power.
>
>
>
>
>
> On Jun 7, 2020, at 11:53 AM, Darryl Thayer  wrote:
>
> 
> I think you said it well, about 5 years ago I tried to charge a car from
> an off-grid system.  I did not record my events but the inverter had twice
> the power of the level two charger, yet the inverter would get hot and trip
> out.  I was told a ferroresonant transformer may help, and it might be
> different with different cars.  However, I was warned the ferroresonant was
> to stop input wave problems from arriving at the output not to prevent the
> output wave problems showing up on the input.   The off-grid customer gave
> up.
>
> On Sun, Jun 7, 2020 at 6:36 AM Hilton Dier III 
> wrote:
>
>> The issue with EV chargers is that they create a lot of reactive power.
>> Think of it as "slosh" in the waveform. That means that charging at 2,000
>> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from
>> the inverter. If you've got a reasonably good sinewave inverter the charger
>> will like it fine. However, the inverter might not like the charger if you
>> cut things too close. Make sure to have a lot of top end left in your
>> inverter. Always use a transformer based inverter. The SW series has a big
>> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440
>> watts max.
>>
>> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW,
>> so too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE
>> (smart charging cord) that comes with the car can draw 8 or 12 amps at 120V
>> or 12 at 240V. Assume that the 8 amps is really 12 and the 12 is really 15
>> or a bit more. I have seen 15 amp plugs and outlets with the hot prong
>> melting plastic around it. The plug on the OEM EVSE is 20A rated but make
>> sure your outlet is as well.
>>
>> --
>> Hilton Dier III
>> Missisquoi River Hydro
>> Renewable Energy Design
>>
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a Bolt with an SW

2020-06-07 Thread Jay
I’ve got offgrid  2 clients and they have no issues. 

They each have a Bolt and can choose the charging rate. They can run it at 
either power. But only use higher power when they have lots of sun. 
Older Stacked vfx and Schneider xw, no issues. 

I would expect the SW to work, however it’s an odd beast as it’s waveform steps 
change with load. More load, more steps, therefor cleaner so maybe at lower 
charge rate it’s not clean enough. 

As to your issue it could be power factor Being really poor. 
Can you tell us what inverter, yea 5 years ago is a long time. 



Jay

Peltz power. 





> On Jun 7, 2020, at 11:53 AM, Darryl Thayer  wrote:
> 
> 
> I think you said it well, about 5 years ago I tried to charge a car from an 
> off-grid system.  I did not record my events but the inverter had twice the 
> power of the level two charger, yet the inverter would get hot and trip out.  
> I was told a ferroresonant transformer may help, and it might be different 
> with different cars.  However, I was warned the ferroresonant was to stop 
> input wave problems from arriving at the output not to prevent the output 
> wave problems showing up on the input.   The off-grid customer gave up.
> 
>> On Sun, Jun 7, 2020 at 6:36 AM Hilton Dier III  wrote:
>> The issue with EV chargers is that they create a lot of reactive power. 
>> Think of it as "slosh" in the waveform. That means that charging at 2,000 
>> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from 
>> the inverter. If you've got a reasonably good sinewave inverter the charger 
>> will like it fine. However, the inverter might not like the charger if you 
>> cut things too close. Make sure to have a lot of top end left in your 
>> inverter. Always use a transformer based inverter. The SW series has a big 
>> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440 
>> watts max.
>> 
>> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW, so 
>> too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE (smart 
>> charging cord) that comes with the car can draw 8 or 12 amps at 120V or 12 
>> at 240V. Assume that the 8 amps is really 12 and the 12 is really 15 or a 
>> bit more. I have seen 15 amp plugs and outlets with the hot prong melting 
>> plastic around it. The plug on the OEM EVSE is 20A rated but make sure your 
>> outlet is as well.
>> 
>> -- 
>> Hilton Dier III
>> Missisquoi River Hydro
>> Renewable Energy Design
>> ___
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Charging a Bolt with an SW

2020-06-07 Thread Darryl Thayer
I think you said it well, about 5 years ago I tried to charge a car from an
off-grid system.  I did not record my events but the inverter had twice the
power of the level two charger, yet the inverter would get hot and trip
out.  I was told a ferroresonant transformer may help, and it might be
different with different cars.  However, I was warned the ferroresonant was
to stop input wave problems from arriving at the output not to prevent the
output wave problems showing up on the input.   The off-grid customer gave
up.

On Sun, Jun 7, 2020 at 6:36 AM Hilton Dier III  wrote:

> The issue with EV chargers is that they create a lot of reactive power.
> Think of it as "slosh" in the waveform. That means that charging at 2,000
> watts sloshes a lot more than 2kW through the cable, plug, outlet, and from
> the inverter. If you've got a reasonably good sinewave inverter the charger
> will like it fine. However, the inverter might not like the charger if you
> cut things too close. Make sure to have a lot of top end left in your
> inverter. Always use a transformer based inverter. The SW series has a big
> chunk of metal in it, so that's good. At 120V the Bolt will only draw 1440
> watts max.
>
> An aftermarket Bolt 240V charger can draw up to 32 amps. That's 7.7 kW, so
> too big for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE (smart
> charging cord) that comes with the car can draw 8 or 12 amps at 120V or 12
> at 240V. Assume that the 8 amps is really 12 and the 12 is really 15 or a
> bit more. I have seen 15 amp plugs and outlets with the hot prong melting
> plastic around it. The plug on the OEM EVSE is 20A rated but make sure your
> outlet is as well.
>
> --
> Hilton Dier III
> Missisquoi River Hydro
> Renewable Energy Design
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Outback question

2020-06-07 Thread Dave Angelini Offgrid Solar


You think it is interesting? I hate problems like this.

You are doing
the right thing in my opinion. Disconnect the network and try to duplicate.
This is a troubleshoot halfsplit to an engineer/technician, or you and
me

The other choice at this point would be a complete DC disconnect
for as long as it takes to get the DC system wide to below 2vdc.

Your
question on programming? Did someone/something put the CC into float only
mode? I had a customer who did weird things and I set-up logging on an SD
card and it recorded system changes. He paid me a bit of money for me to
prove he was the problem. 

Nice and cool! Gonna play "highway to hell" and
wack the weeds.

Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/
e-mail
offgridso...@sti.net
text 209 813 0060

On Sat, 6 Jun 2020 18:35:30 -0700,
Jay  wrote:
> I've got a interesting problem I've not seen before. 
> 
>
Mate 3
> Hub
> Radian
> Fm-80
> 
> It's been installed for 5 + years. 
> 
>
Recently the caretaker noticed every other day it wasn't charging. This
is
> confirmed on the CC and logging. 
> It was in float all day. 
> 
> We
disconnected it from the hub and it's charging normally. 
> 
> I'm not
aware of any mate 3 settings that would make this happen. 
> 
> Comments?
>

> Thx
> 
> Jay
> 
> 
> ___
>
List sponsored by Redwood Alliance
> 
> List Address:
RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address &
settings:
>
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
>
List-Archive:
>
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>

> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check
out or update participant bios:
> www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org