Re: [RE-wrenches] SMA Sunny Storage AC-coupled with SB6.0 won't recharge LG Resu batteries during backup ops

2020-07-10 Thread Jerry Shafer
Scott, Wrenches
We have had systems with the SMA storage but we have used the BYD and have
had no problems so far with recharge and operations all as expected, it may
be an issue with LG programming and the SMA not communicating properly
JUerry

On Fri, Jul 10, 2020 at 2:57 PM  wrote:

> We have a design with Sunny Storage 6.0 inverter, SB 6.0 PV inverter, the
> SMA Automatic Backup Unit, and three LG Resu batteries. Works like a charm
> during normal grid ops but when it goes into backup ops, the Sunny Storage
> increases frequency to between 60.6 with blips up to 61 hertz, resulting in
> the PV inverter throttling back from 5,000+ watts to between 1,300 to 345
> watts.
>
>
>
> The result is that the batteries do not recharge from the PV during backup
> mode, even when SoC is less than half capacity. This also means the max
> power through the ABU to the “whole house backup” is the 6,000 watts from
> the Sunny Storage plus the (very) retarded power output of the SB PV
> inverter.
>
>
>
> SMA tech support just said, “that is normal, the LG Battery is the culprit
> and  does not charge from PV in this setup.”
>
>
>
> I was stunned because why else would I buy this ABU coupling setup…Anybody
> have any ideas? I’m hoping the Sunny Storage freq shifting ramp-up
> parameters can be adjusted so that PV inverter operations continue when the
> battery is at a less than full SoC.
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Admin post, please read: Wrench List archives

2020-07-10 Thread Michael Welch
Hi there Wrenches. If you have any questions about this, please contact me 
off-list.

A member has discovered that there are message gaps in the third-party message 
archive we've been using. It shouldn't be happening, but it is.

So, I've changed the archive link in the message footers back to an older one 
we used to use, and it should be fairly complete, at least for recent years. 

While I've got you here, it would be helpful for both readability and bandwidth 
if Wrenches would edit out old parts of the messages in their replies. For 
example, sometimes there might be 5 or more copies of the Wrench List footer in 
replies to replies. 

Also, copies of embedded photos in replies are usually not needed, they just 
create more clutter on Wrench members' hard drives.

Finally, if there is a message you cannot find in the archives, please let me 
know and I will try to find it for you. I keep ALL old Wrench list messages on 
my computer, going back to Oct. 1999 when I started this list. 

Thanks, and keep on Wrenchin'. You all are making a difference in this world.




___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA Sunny Storage AC-coupled with SB6.0 won't recharge LG Resu batteries during backup ops

2020-07-10 Thread Vic Guillot
Dear Wrenches,
We too are having issues with sma sunnyboy storage sbs6.0
I would like to discuss with anyone off line.
Vic Guillot
solsier...@gmail.com

Vic Guillot
Sol Sierra, Inc.
209.795.3554 office
209.768.3560 mobile/text



On Fri, Jul 10, 2020 at 11:56 AM  wrote:

> We have a design with Sunny Storage 6.0 inverter, SB 6.0 PV inverter, the
> SMA Automatic Backup Unit, and three LG Resu batteries. Works like a charm
> during normal grid ops but when it goes into backup ops, the Sunny Storage
> increases frequency to between 60.6 with blips up to 61 hertz, resulting in
> the PV inverter throttling back from 5,000+ watts to between 1,300 to 345
> watts.
>
>
>
> The result is that the batteries do not recharge from the PV during backup
> mode, even when SoC is less than half capacity. This also means the max
> power through the ABU to the “whole house backup” is the 6,000 watts from
> the Sunny Storage plus the (very) retarded power output of the SB PV
> inverter.
>
>
>
> SMA tech support just said, “that is normal, the LG Battery is the culprit
> and  does not charge from PV in this setup.”
>
>
>
> I was stunned because why else would I buy this ABU coupling setup…Anybody
> have any ideas? I’m hoping the Sunny Storage freq shifting ramp-up
> parameters can be adjusted so that PV inverter operations continue when the
> battery is at a less than full SoC.
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA Sunny Storage AC-coupled with SB6.0 won't recharge LG Resu batteries during backup ops

2020-07-10 Thread Dave Angelini Offgrid Solar


Hi Howard, 

I am sure that the SMA guy here on wrenches will give you a
better answer. If not I would escalate this at SMA as you are right. 

The
LG will do what you want. Something is not programmed correctly. Three of
the Resu 10H are going to take some time to replace near 30KWH.  

Dave
Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Fri, 10 Jul 2020 12:50:04 -0500,
scot.a...@solarcentex.com wrote:   

We have a design with Sunny Storage
6.0 inverter, SB 6.0 PV inverter, the SMA Automatic Backup Unit, and three
LG Resu batteries. Works like a charm during normal grid ops but when it
goes into backup ops, the Sunny Storage increases frequency to between 60.6
with blips up to 61 hertz, resulting in the PV inverter throttling back
from 5,000+ watts to between 1,300 to 345 watts. 

The result is that the
batteries do not recharge from the PV during backup mode, even when SoC is
less than half capacity. This also means the max power through the ABU to
the "whole house backup" is the 6,000 watts from the Sunny Storage plus the
(very) retarded power output of the SB PV inverter. 

SMA tech support just
said, "that is normal, the LG Battery is the culprit and does not charge
from PV in this setup." 

I was stunned because why else would I buy this
ABU coupling setup…Anybody have any ideas? I'm hoping the Sunny Storage
freq shifting ramp-up parameters can be adjusted so that PV inverter
operations continue when the battery is at a less than full SoC. 

  


Links:
--
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridso...@sti.net
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] SMA Sunny Storage AC-coupled with SB6.0 won't recharge LG Resu batteries during backup ops

2020-07-10 Thread Mark Frye

Did SMA give anymore explanation as to why this set up does not work?

On 7/10/2020 10:50 AM, scot.a...@solarcentex.com wrote:


We have a design with Sunny Storage 6.0 inverter, SB 6.0 PV inverter, 
the SMA Automatic Backup Unit, and three LG Resu batteries. Works like 
a charm during normal grid ops but when it goes into backup ops, the 
Sunny Storage increases frequency to between 60.6 with blips up to 61 
hertz, resulting in the PV inverter throttling back from 5,000+ watts 
to between 1,300 to 345 watts.


The result is that the batteries do not recharge from the PV during 
backup mode, even when SoC is less than half capacity. This also means 
the max power through the ABU to the “whole house backup” is the 6,000 
watts from the Sunny Storage plus the (very) retarded power output of 
the SB PV inverter.


SMA tech support just said, “that is normal, the LG Battery is the 
culprit and  does not charge from PV in this setup.”


I was stunned because why else would I buy this ABU coupling 
setup…Anybody have any ideas? I’m hoping the Sunny Storage freq 
shifting ramp-up parameters can be adjusted so that PV inverter 
operations continue when the battery is at a less than full SoC.



___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] SMA Sunny Storage AC-coupled with SB6.0 won't recharge LG Resu batteries during backup ops

2020-07-10 Thread scot.arey
We have a design with Sunny Storage 6.0 inverter, SB 6.0 PV inverter, the
SMA Automatic Backup Unit, and three LG Resu batteries. Works like a charm
during normal grid ops but when it goes into backup ops, the Sunny Storage
increases frequency to between 60.6 with blips up to 61 hertz, resulting in
the PV inverter throttling back from 5,000+ watts to between 1,300 to 345
watts.

 

The result is that the batteries do not recharge from the PV during backup
mode, even when SoC is less than half capacity. This also means the max
power through the ABU to the "whole house backup" is the 6,000 watts from
the Sunny Storage plus the (very) retarded power output of the SB PV
inverter.

 

SMA tech support just said, "that is normal, the LG Battery is the culprit
and  does not charge from PV in this setup."

 

I was stunned because why else would I buy this ABU coupling setup.Anybody
have any ideas? I'm hoping the Sunny Storage freq shifting ramp-up
parameters can be adjusted so that PV inverter operations continue when the
battery is at a less than full SoC.

 



 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org