Re: [RE-wrenches] Battery disconnect solution

2022-05-09 Thread bob--- via RE-wrenches


I understand that MidNite is working on a new product to replace the BDM.

Makes sense actually.   I don't know any more than that though.

Robin Gudgel would know more.

boB 🌜


boB Gudgel 🌜

On 5/9/2022 5:43 PM, Jeremy Rodriguez via RE-wrenches wrote:
Does anyone have a solution for operating a remote trip MN battery 
breaker since the BDM is gone?


We do have a birdhouse, so maybe someone has a BDM, but otherwise,
what to do?

Batteries in a dwelling


Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand.

___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Battery disconnect solution

2022-05-09 Thread Darryl Thayer via RE-wrenches
I want to comment, maybe without value.  The breaker you mention is called
a "shunt trip" breaker.  This is common type breaker in the electrical
industry.  The MN breaker has a 24 volt solenoid that trips the breaker.
Shunt Trip breakers have the solenoid voltage for the system voltage.  BUT
the way it works!! (load side of breaker is connected to one side of the
trip solenoid the other side is connected to switch and then to (neutral).
When the switch is closed current rushes through the solenoid, triping the
breaker stoping the solenoid current.  But what to do with solar
equipment?  Often when the bsttery is dis onnected the losd side of the
breaker does not go to neutral and the solenoid can carry current and will
fsil

On Mon, May 9, 2022, 7:43 PM Jeremy Rodriguez via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Does anyone have a solution for operating a remote trip MN battery breaker
> since the BDM is gone?
>
> We do have a birdhouse, so maybe someone has a BDM, but otherwise,
> what to do?
>
> Batteries in a dwelling
>
>
> Jeremy Rodriguez
> Solar Installation / Design Expert
> All Solar, Inc.
> 1453 M St
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Battery disconnect solution

2022-05-09 Thread Jeremy Rodriguez via RE-wrenches
Does anyone have a solution for operating a remote trip MN battery breaker 
since the BDM is gone?

We do have a birdhouse, so maybe someone has a BDM, but otherwise,
what to do?

Batteries in a dwelling


Jeremy Rodriguez
Solar Installation / Design Expert
All Solar, Inc.
1453 M St
Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand.
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol-Ark 15k

2022-05-09 Thread Jason Szumlanski via RE-wrenches
I think the idea here is that 690.9 allows the inverter output conductors
to be sized based on the maximum ampacity and an OCPD is actually not
required is the conductor ampacity is sufficient. So in an off-grid
scenario, the wires could be as small as #4. In a grid interconnected
situation where there is potential pass-through current exceeding the
inverter output current, the wire would need to be protected according to
the available current on the grid input terminals. If there is a generator,
the inverter output circuit would need to be protected based on the
generator rating. The fixed 200A rating of the inverter load disconnect is
the confusing part. It seems like it would be more functional if it were
replaceable with various ratings of main breaker. You need additional
circuit protection in most cases unless it's completely off-grid with no
generator input it seems.

Jason Szumlanski

On Fri, Apr 15, 2022, 8:44 PM Chris Sparadeo 
wrote:

> Hi Jason,
>
> You bring up a valid point….in an off-grid scenario with the 15k do you
> size the conductors to the continuous capacity, surge capacity or the OCPD
> of the unit?
>
> -Chris
>
> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>
>>
>>
>>
>>
>>
>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>> ja...@floridasolardesigngroup.com> wrote:
>>
>>> I'm not following the wiring diagrams for this new inverter. It has 200A
>>> pass-through capability with an integrated 200A load disconnect. But then
>>> it says the wire gauge for the load out wiring can be #4 to 2/0.
>>>
>>> In an off-grid scenario where there is no generator, the max continuous
>>> output is 62.5A, so I assume 80A circuit protection could be used with 80A
>>> rated wire (#4), but how is that circuit protection implemented if the 200A
>>> breaker is integrated? Do you have to run a short piece of 2/0 to an
>>> external 80A rated OCPD and then step down to #4?
>>>
>>> Jason Szumlanski
>>>
>>>
>>>
>>>
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol-Ark 15k

2022-05-09 Thread Jerry Shafer via RE-wrenches
Wrenches
The new solark 15 has a 200 amp rated contactor this is so if you want to
have whole home pass through you can but if you only have an inverter then
use that as your starting point and if the genny is contributing then add
that is, you do not need 2/0 for a single 15 k off grid but you may grid
tied. this opens up other issues that are not part of this conversation
like multiple 15 and 3/0 grid tied remember KIS!

On Fri, Apr 15, 2022 at 8:00 AM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I'm not following the wiring diagrams for this new inverter. It has 200A
> pass-through capability with an integrated 200A load disconnect. But then
> it says the wire gauge for the load out wiring can be #4 to 2/0.
>
> In an off-grid scenario where there is no generator, the max continuous
> output is 62.5A, so I assume 80A circuit protection could be used with 80A
> rated wire (#4), but how is that circuit protection implemented if the 200A
> breaker is integrated? Do you have to run a short piece of 2/0 to an
> external 80A rated OCPD and then step down to #4?
>
> Jason Szumlanski
>
>
>
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org