Re: [RE-wrenches] Magnum 4448 PAE whimpy charge rate.

2023-12-06 Thread Maverick Brown via RE-wrenches
John

I would try the Victron Cerbo GX for remote control of stuff. It has plethora 
of ports (I/O and temperature) and they can connect to lots of different 
devices, especially other Victron items like inverters and charge controllers 
and smart shunts (that one I’d also add to the Cerbo right away for SOC). 


1. Cerbo GX
2. SmartShunt 500 amp Battery Monitor (Bluetooth)
3. Temperature sensor BMV-702/712 for the shunt. 
4. VE.direct cable of correct length to go from Cerbo to SmartShunt


Cerbo GX connects to the internet via wired or wireless internet ports 
provided.  
They have a cellular modem add on as well. 

Victron offers a VRM virtual remote monitoring via the web. 




Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
maver...@mavericksolar.com
512-460-9825


> On Dec 6, 2023, at 8:08 PM, John Blittersdorf via RE-wrenches 
>  wrote:
> 
> 
> I have noticed on several Magnum Installations that the charge rate is low 
> compared to the inverter rated output.  Typically I would assume the charge 
> rate should be up to about 70 to 80 % of the inverter capacity, but I am 
> getting only about 1400 watts (26 amps DC) from it with a 14kw generator.  Is 
> there some setting I am missing that would limit it other than the charge %.  
> I know of one system where they added a 2nd Magnum inverter and then had 
> problems with them working together consistently.  I have used the 8 kilowatt 
> Radians for any off grid with significant loads and battery capacity and 
> easily get 6000 charging watts from a large generator. I also needed remote 
> control of the generator (Generac EcoGen 15 kw so a quick inexpensive but 
> clunky solution I came up with was to add an old (2003 vintage) used MX-60 to 
> the system purely to use the Aux relay with a used HUB and old but good 
> Mate3.  Works perfectly giving us AGS start and stop voltage settings and 
> basic battery voltage graph. I would be interested in other ways to remote 
> control generators with non Outback inverters. FlexNet DC?
> 
> John Blittersdorf
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Magnum 4448 PAE whimpy charge rate.

2023-12-06 Thread John Blittersdorf via RE-wrenches
I have noticed on several Magnum Installations that the charge rate is low
compared to the inverter rated output.  Typically I would assume the charge
rate should be up to about 70 to 80 % of the inverter capacity, but I am
getting only about 1400 watts (26 amps DC) from it with a 14kw generator.
Is there some setting I am missing that would limit it other than the
charge %.  I know of one system where they added a 2nd Magnum inverter and
then had problems with them working together consistently.  I have used the
8 kilowatt Radians for any off grid with significant loads and battery
capacity and easily get 6000 charging watts from a large generator. I also
needed remote control of the generator (Generac EcoGen 15 kw so a quick
inexpensive but clunky solution I came up with was to add an old (2003
vintage) used MX-60 to the system purely to use the Aux relay with a used
HUB and old but good Mate3.  Works perfectly giving us AGS start and stop
voltage settings and basic battery voltage graph. I would be interested in
other ways to remote control generators with non Outback inverters. FlexNet
DC?

John Blittersdorf
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Fortress remote monitoring

2023-12-06 Thread William Miller via RE-wrenches
Friends:



The Guardian app does not provide any historical data.  Fortress says they
are working on that.  They claim that on request they can provide
historical data but the one time I asked there was an hours-long gap in the
data at the exact time I needed.  Maybe Rose Mary Woods’ incarnation is
working for them.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Kirk Herander via RE-wrenches
*Sent:* Wednesday, December 6, 2023 9:40 AM
*To:* RE-wrenches
*Cc:* Kirk Herander
*Subject:* Re: [RE-wrenches] Fortress remote monitoring



Yep, I found this out when I installed my first Fortress Evault / Envy
inverter combo last month.



What was also a bit different at first is the fact there are -2- different
apps: the Guardian gateway app and the Envy inverter app. I bought the
guardian thinking it was the only way to see the system remotely, but this
is not true IF you've installed the Envy inverter also. The limitation of
no "fleet" monitoring is puzzling.



But now I'm glad there's a unique app for the inverter. The inverter app is
much more detailed and allows most parameters to be tweaked remotely. The
Guardian app id for basic system monitoring only.



So the single-user per app has worked out OK. My customer uses the
at-a-glance Guardian app, and I use the Envy app for more detailed
monitoring and programming.



On Wed, Dec 6, 2023 at 12:11 PM Sam Haraldson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

Here is an official communication from Fortress that we received recently
when inquiring about monitoring Fortress batteries as an Installer.  Some
of you may find the info relevant.



-- Forwarded message -
From:  
Date: Mon, Dec 4, 2023 at 12:37 PM
Subject: Re:[## 5635 ##] Remote Monitoring Access
To: -@---.com



Hi -,



As of right now, the Guardian app is designed to be used by the end user
only and does not have "fleet management" capabilities as you have
described. This is a highly demanded feature so we are working on getting
this added by Q2 2024.



If you would like to view the info from their Guardian, you can use their
login info and log in using their credentials on your phone.



Best,

- --

Applications Engineer II

Fortress Power

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Fortress remote monitoring

2023-12-06 Thread Kirk Herander via RE-wrenches
Yep, I found this out when I installed my first Fortress Evault / Envy
inverter combo last month.

What was also a bit different at first is the fact there are -2- different
apps: the Guardian gateway app and the Envy inverter app. I bought the
guardian thinking it was the only way to see the system remotely, but this
is not true IF you've installed the Envy inverter also. The limitation of
no "fleet" monitoring is puzzling.

But now I'm glad there's a unique app for the inverter. The inverter app is
much more detailed and allows most parameters to be tweaked remotely. The
Guardian app id for basic system monitoring only.

So the single-user per app has worked out OK. My customer uses the
at-a-glance Guardian app, and I use the Envy app for more detailed
monitoring and programming.

On Wed, Dec 6, 2023 at 12:11 PM Sam Haraldson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Here is an official communication from Fortress that we received recently
> when inquiring about monitoring Fortress batteries as an Installer.  Some
> of you may find the info relevant.
>
> -- Forwarded message -
> From:  
> Date: Mon, Dec 4, 2023 at 12:37 PM
> Subject: Re:[## 5635 ##] Remote Monitoring Access
> To: -@---.com
>
>
> Hi -,
>
> As of right now, the Guardian app is designed to be used by the end user
> only and does not have "fleet management" capabilities as you have
> described. This is a highly demanded feature so we are working on getting
> this added by Q2 2024.
>
> If you would like to view the info from their Guardian, you can use their
> login info and log in using their credentials on your phone.
>
> Best,
> - --
> Applications Engineer II
> Fortress Power
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Fortress remote monitoring

2023-12-06 Thread Sam Haraldson via RE-wrenches
Here is an official communication from Fortress that we received recently
when inquiring about monitoring Fortress batteries as an Installer.  Some
of you may find the info relevant.

-- Forwarded message -
From:  
Date: Mon, Dec 4, 2023 at 12:37 PM
Subject: Re:[## 5635 ##] Remote Monitoring Access
To: -@---.com


Hi -,

As of right now, the Guardian app is designed to be used by the end user
only and does not have "fleet management" capabilities as you have
described. This is a highly demanded feature so we are working on getting
this added by Q2 2024.

If you would like to view the info from their Guardian, you can use their
login info and log in using their credentials on your phone.

Best,
- --
Applications Engineer II
Fortress Power
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org