Re: [RE-wrenches] Fortress

2024-02-15 Thread William Miller via RE-wrenches
Jay:



Here is a link

to the study.



The web page needs to be updated with this information:



There are two settings to be changed in the Sunny Boy Inverters:  Backup
mode and Default.  See Below:





I had set the default to OFF_Grid but I had not set the Backup Mode to On
All.  It was in Off.



There is a possibility changing the Backup Mode setting may fix the
Frequency Shift Power Control problem that is the root of this dilemma.
There have not been enough sunny days to see the PV bring SOC up to the
level of near 100% where the problem exhibits.  As soon as the weather gets
sunnier and the days get longer I will see what happens and report back.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* Jay [mailto:jay.pe...@gmail.com]
*Sent:* Thursday, February 15, 2024 5:50 AM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] Fortress



Hi william



Could you share the equipment used and what issues you had?



Thx

Jay



On Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:



Peter:



I have only purchased one set of Fortress batteries.  There have been
issues, I am sure many of them self-induced.  Fortress has been overall
very responsive.  There have been a few days where I could not get through
to technical support but with persistence I always manage.  Fortress has
offered truck–roll compensation at a reasonable rate as well.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Peter Giroux via RE-wrenches
*Sent:* Wednesday, February 14, 2024 6:47 AM
*To:* 'RE-wrenches'
*Cc:* pgir...@mindspring.com
*Subject:* [RE-wrenches] Fortress



Good morning my fellow wrenchers. While I see the comments on SunPower and
the challenges, are any of you having similar issues with Fortress? Their
bms boards from the early classics have not held up and even after
replacement there are still issues ( parallel batteries and stand alone not
showing accurate #’s,  ). While support has been, well supportive, the
issues persist. Any thoughts or fixes you have come up with?? I just had a
customer unplug the coms cable from their sol-ark and bring their readings
to volts VS %% and it is starting to work a bit better. Any and all help or
ideas appreciated.



Thx
peter Giroux

American Solar

Norcross Ga

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the
other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Fortress

2024-02-15 Thread Kirk Herander via RE-wrenches
Yes, the site I mentioned is only for the fortress envy inverter.

I’ve had the same weather as you, being in northern Vermont, that is where
that system crashed that I mentioned in the previous email, definitely did
not reach a full state of charge in January.

 The national weather service reported it was the cloudiest January since
1951.

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 33st Anniversary 1991-2024!!*

dba Vermont Solar Engineering

802.559.1225


On Thu, Feb 15, 2024 at 1:11 PM Dave Tedeyan via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Kirk,
>
> That site looks specifically for the Envy inverters. Do you know if the
> Guardian site is working? My credentials will not get me in at this time.
> www.app.fortresspower.io
>
> My sites have no comms between the batteries and the inverter, since it is
> an Outback system.
>
> And yes, there is certainly an issue with SOC drift over time without
> getting a full charge. I was told by Fortress tech support that the eFlex
> batteries needed to get over 55V to calibrate the SOC. Yet, in their
> settings, the generator is only supposed to bring them to 54.4V. The solar
> will bring it higher. But this was a problem here in upstate NY, where we
> did not have a sunny enough day in the entire month of January.
>
> Cheers,
> Dave
>
>
> On Thu, Feb 15, 2024 at 12:30 PM Dave Angelini Offgrid Solar via
> RE-wrenches  wrote:
>
>> So this is all open loop with outback correct?  I can't even get into
>> Simplyphi. website today. Maybe the windows update...
>>
>> The battery below was suppose to be networkable but it looks like not
>> much progress.
>>
>>- Model: AmpliPHI 3.8kWh
>>- Inverter compatibility: Sol-Ark, SMA (coming soon), Schneider
>>Electric (coming soon)
>>
>> A question, it looks like Outback is not closed loop with any battery
>> company. I hope I am wrong!
>>
>>
>>
>> *Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>>https://offgridsolar1.com/ 
>>   
>> e-mail  offgridso...@sti.net 
>> text 209 813 0060*
>>
>>
>> On 2024-02-15 8:57 am, Darryl Thayer via RE-wrenches wrote:
>>
>> Is it similar to my problem with my Simplify batteries? Over time, the
>> BMS did not allow all cells to charge the same. To correct this, I had to
>> charge each battery separately, and after this, they stayed equivalent for
>> more years.
>>
>> On Thu, Feb 15, 2024 at 7:50 AM Jay via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>
>> Hi william
>>
>> Could you share the equipment used and what issues you had?
>>
>> Thx
>> Jay
>>
>> On Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>> Peter:
>>
>>
>>
>> I have only purchased one set of Fortress batteries.  There have been
>> issues, I am sure many of them self-induced.  Fortress has been overall
>> very responsive.  There have been a few days where I could not get through
>> to technical support but with persistence I always manage.  Fortress has
>> offered truck–roll compensation at a reasonable rate as well.
>>
>>
>>
>> William Miller
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>>
>> 805-438-5600
>>
>> www.millersolar.com
>>
>> CA Lic. 773985
>>
>>
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>> Behalf Of *Peter Giroux via RE-wrenches
>> *Sent:* Wednesday, February 14, 2024 6:47 AM
>> *To:* 'RE-wrenches'
>> *Cc:* pgir...@mindspring.com
>> *Subject:* [RE-wrenches] Fortress
>>
>>
>>
>> Good morning my fellow wrenchers. While I see the comments on SunPower
>> and the challenges, are any of you having similar issues with Fortress?
>> Their bms boards from the early classics have not held up and even after
>> replacement there are still issues ( parallel batteries and stand alone not
>> showing accurate #'s,  ). While support has been, well supportive, the
>> issues persist. Any thoughts or fixes you have come up with?? I just had a
>> customer unplug the coms cable from their sol-ark and bring their readings
>> to volts VS %% and it is starting to work a bit better. Any and all help or
>> ideas appreciated.
>>
>>
>>
>> Thx
>> peter Giroux
>>
>> American Solar
>>
>> Norcross Ga
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.

Re: [RE-wrenches] Fortress

2024-02-15 Thread Dave Tedeyan via RE-wrenches
Kirk,

That site looks specifically for the Envy inverters. Do you know if the
Guardian site is working? My credentials will not get me in at this time.
www.app.fortresspower.io

My sites have no comms between the batteries and the inverter, since it is
an Outback system.

And yes, there is certainly an issue with SOC drift over time without
getting a full charge. I was told by Fortress tech support that the eFlex
batteries needed to get over 55V to calibrate the SOC. Yet, in their
settings, the generator is only supposed to bring them to 54.4V. The solar
will bring it higher. But this was a problem here in upstate NY, where we
did not have a sunny enough day in the entire month of January.

Cheers,
Dave


On Thu, Feb 15, 2024 at 12:30 PM Dave Angelini Offgrid Solar via
RE-wrenches  wrote:

> So this is all open loop with outback correct?  I can't even get into
> Simplyphi. website today. Maybe the windows update...
>
> The battery below was suppose to be networkable but it looks like not much
> progress.
>
>- Model: AmpliPHI 3.8kWh
>- Inverter compatibility: Sol-Ark, SMA (coming soon), Schneider
>Electric (coming soon)
>
> A question, it looks like Outback is not closed loop with any battery
> company. I hope I am wrong!
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
>https://offgridsolar1.com/ 
>   
> e-mail  offgridso...@sti.net 
> text 209 813 0060*
>
>
> On 2024-02-15 8:57 am, Darryl Thayer via RE-wrenches wrote:
>
> Is it similar to my problem with my Simplify batteries? Over time, the BMS
> did not allow all cells to charge the same. To correct this, I had to
> charge each battery separately, and after this, they stayed equivalent for
> more years.
>
> On Thu, Feb 15, 2024 at 7:50 AM Jay via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>
> Hi william
>
> Could you share the equipment used and what issues you had?
>
> Thx
> Jay
>
> On Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Peter:
>
>
>
> I have only purchased one set of Fortress batteries.  There have been
> issues, I am sure many of them self-induced.  Fortress has been overall
> very responsive.  There have been a few days where I could not get through
> to technical support but with persistence I always manage.  Fortress has
> offered truck–roll compensation at a reasonable rate as well.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Peter Giroux via RE-wrenches
> *Sent:* Wednesday, February 14, 2024 6:47 AM
> *To:* 'RE-wrenches'
> *Cc:* pgir...@mindspring.com
> *Subject:* [RE-wrenches] Fortress
>
>
>
> Good morning my fellow wrenchers. While I see the comments on SunPower and
> the challenges, are any of you having similar issues with Fortress? Their
> bms boards from the early classics have not held up and even after
> replacement there are still issues ( parallel batteries and stand alone not
> showing accurate #'s,  ). While support has been, well supportive, the
> issues persist. Any thoughts or fixes you have come up with?? I just had a
> customer unplug the coms cable from their sol-ark and bring their readings
> to volts VS %% and it is starting to work a bit better. Any and all help or
> ideas appreciated.
>
>
>
> Thx
> peter Giroux
>
> American Solar
>
> Norcross Ga
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

Re: [RE-wrenches] Fortress

2024-02-15 Thread Dave Angelini Offgrid Solar via RE-wrenches
So this is all open loop with outback correct?  I can't even get into 
Simplyphi. website today. Maybe the windows update...


The battery below was suppose to be networkable but it looks like not 
much progress.


* Model: AmpliPHI 3.8kWh
 	* Inverter compatibility: Sol-Ark, SMA (coming soon), Schneider 
Electric (coming soon)


 A question, it looks like Outback is not closed loop with any battery 
company. I hope I am wrong!


Dave Angelini Offgrid Solar
"we go where powerlines don't"
   [2]https://offgridsolar1.com/ [3]  [2]
e-mail  offgridso...@sti.net
text 209 813 0060

On 2024-02-15 8:57 am, Darryl Thayer via RE-wrenches wrote:

Is it similar to my problem with my Simplify batteries? Over time, the 
BMS did not allow all cells to charge the same. To correct this, I had 
to charge each battery separately, and after this, they stayed 
equivalent for more years.


On Thu, Feb 15, 2024 at 7:50 AM Jay via RE-wrenches 
 wrote:


Hi william

Could you share the equipment used and what issues you had?

Thx
Jay

On Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches 
 wrote:


Peter:

I have only purchased one set of Fortress batteries.  There have been 
issues, I am sure many of them self-induced.  Fortress has been overall 
very responsive.  There have been a few days where I could not get 
through to technical support but with persistence I always manage.  
Fortress has offered truck-roll compensation at a reasonable rate as 
well.


William Miller

Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com [1]

CA Lic. 773985

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
Behalf Of Peter Giroux via RE-wrenches

Sent: Wednesday, February 14, 2024 6:47 AM
To: 'RE-wrenches'
Cc: pgir...@mindspring.com
Subject: [RE-wrenches] Fortress

Good morning my fellow wrenchers. While I see the comments on SunPower 
and the challenges, are any of you having similar issues with Fortress? 
Their bms boards from the early classics have not held up and even 
after replacement there are still issues ( parallel batteries and stand 
alone not showing accurate #'s,  ). While support has been, well 
supportive, the issues persist. Any thoughts or fixes you have come up 
with?? I just had a customer unplug the coms cable from their sol-ark 
and bring their readings to volts VS %% and it is starting to work a 
bit better. Any and all help or ideas appreciated.


Thx
peter Giroux

American Solar

Norcross Ga ___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
--
[1] http://www.millersolar.com/
[2] http://members.sti.net/offgridsolar/
[3] https://offgridsolar1.com/___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-w

Re: [RE-wrenches] Fortress

2024-02-15 Thread Darryl Thayer via RE-wrenches
Is it similar to my problem with my Simplify batteries? Over time, the BMS
did not allow all cells to charge the same. To correct this, I had to
charge each battery separately, and after this, they stayed equivalent for
more years.

On Thu, Feb 15, 2024 at 7:50 AM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi william
>
> Could you share the equipment used and what issues you had?
>
> Thx
> Jay
>
> On Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> 
>
> Peter:
>
>
>
> I have only purchased one set of Fortress batteries.  There have been
> issues, I am sure many of them self-induced.  Fortress has been overall
> very responsive.  There have been a few days where I could not get through
> to technical support but with persistence I always manage.  Fortress has
> offered truck–roll compensation at a reasonable rate as well.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Peter Giroux via RE-wrenches
> *Sent:* Wednesday, February 14, 2024 6:47 AM
> *To:* 'RE-wrenches'
> *Cc:* pgir...@mindspring.com
> *Subject:* [RE-wrenches] Fortress
>
>
>
> Good morning my fellow wrenchers. While I see the comments on SunPower and
> the challenges, are any of you having similar issues with Fortress? Their
> bms boards from the early classics have not held up and even after
> replacement there are still issues ( parallel batteries and stand alone not
> showing accurate #’s,  ). While support has been, well supportive, the
> issues persist. Any thoughts or fixes you have come up with?? I just had a
> customer unplug the coms cable from their sol-ark and bring their readings
> to volts VS %% and it is starting to work a bit better. Any and all help or
> ideas appreciated.
>
>
>
> Thx
> peter Giroux
>
> American Solar
>
> Norcross Ga
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Fortress

2024-02-15 Thread Dave Tedeyan via RE-wrenches
I also have been having some issues with reported SOC through the Guardian
with Fortress. Fortress is generally responsive, although no one has
specifically addressed my concern yet. What I have seen with two recent
eFlex installations (replacing an existing battery bank on an off-grid
system) is that the reported SOC in the Guardian app for some batteries is
way lower than it should be. For example, one system is at 92%, 92%, 92%,
62%. Yet the lights on the batteries all indicate that they are in the
75-100% range. The other system is reporting 23%, 63%, 62%, 25%, 48%, and
again, all the LED's on the batteries are in sync. This has led one
customer to keep disconnecting the batteries and trying to charge just one
of them up and then fiddling with it until they are all back within a good
voltage range, when I am nearly certain that they are all the same voltage
even though they are reporting different SOC on the Guardian app only.

I am looking forward to when they have the website up and I can look at
historical data to see whether this battery is actually doing more work. I
suspect it is not, but then maybe I can get Fortress to look more closely
at it. And for all these batteries, the cables are exactly the same length
and going to a bus bar.

Has anyone else noticed this discrepancy between the guardian app and (what
I think is) reality with the SOC?

Cheers,
Dave

On Thu, Feb 15, 2024 at 8:52 AM Jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi william
>
> Could you share the equipment used and what issues you had?
>
> Thx
> Jay
>
> On Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> 
>
> Peter:
>
>
>
> I have only purchased one set of Fortress batteries.  There have been
> issues, I am sure many of them self-induced.  Fortress has been overall
> very responsive.  There have been a few days where I could not get through
> to technical support but with persistence I always manage.  Fortress has
> offered truck–roll compensation at a reasonable rate as well.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Peter Giroux via RE-wrenches
> *Sent:* Wednesday, February 14, 2024 6:47 AM
> *To:* 'RE-wrenches'
> *Cc:* pgir...@mindspring.com
> *Subject:* [RE-wrenches] Fortress
>
>
>
> Good morning my fellow wrenchers. While I see the comments on SunPower and
> the challenges, are any of you having similar issues with Fortress? Their
> bms boards from the early classics have not held up and even after
> replacement there are still issues ( parallel batteries and stand alone not
> showing accurate #’s,  ). While support has been, well supportive, the
> issues persist. Any thoughts or fixes you have come up with?? I just had a
> customer unplug the coms cable from their sol-ark and bring their readings
> to volts VS %% and it is starting to work a bit better. Any and all help or
> ideas appreciated.
>
>
>
> Thx
> peter Giroux
>
> American Solar
>
> Norcross Ga
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
[image: Logo] 
Dave Tedeyan, P.E.
Owner | Sungineer Solar
p: he | him | his
a: 1653 Slaterville Rd. | Ithaca, NY 14850
w: www.sungineersolar.com 
c: (607) 270-0370
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserve

Re: [RE-wrenches] Fortress

2024-02-15 Thread Jay via RE-wrenches
Hi williamCould you share the equipment used and what issues you had?ThxJayOn Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches  wrote:Peter: I have only purchased one set of Fortress batteries.  There have been issues, I am sure many of them self-induced.  Fortress has been overall very responsive.  There have been a few days where I could not get through to technical support but with persistence I always manage.  Fortress has offered truck–roll compensation at a reasonable rate as well. William Miller Miller Solar17395 Oak Road, Atascadero, CA 93422805-438-5600www.millersolar.comCA Lic. 773985  From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Peter Giroux via RE-wrenchesSent: Wednesday, February 14, 2024 6:47 AMTo: 'RE-wrenches'Cc: pgir...@mindspring.comSubject: [RE-wrenches] Fortress Good morning my fellow wrenchers. While I see the comments on SunPower and the challenges, are any of you having similar issues with Fortress? Their bms boards from the early classics have not held up and even after replacement there are still issues ( parallel batteries and stand alone not showing accurate #’s,  ). While support has been, well supportive, the issues persist. Any thoughts or fixes you have come up with?? I just had a customer unplug the coms cable from their sol-ark and bring their readings to volts VS %% and it is starting to work a bit better. Any and all help or ideas appreciated. Thxpeter GirouxAmerican SolarNorcross Ga
___List sponsored by Redwood AlliancePay optional member dues here: http://re-wrenches.orgList Address: RE-wrenches@lists.re-wrenches.orgChange listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgThere are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.orgList rules & etiquette:http://www.re-wrenches.org/etiquette.htmCheck out or update participant bios:http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org