[RE-wrenches] LG Battery charger instruction

2024-02-20 Thread david quattro via RE-wrenches
Hi Tom,
  a few years ago I decided to buy my own LG battery charger because we
needed the damn thing so often. Now I only use it once or twice per year,
because I stopped installing LG batteries. Here is the instruction I have
which works on my charger (same charger as the LG-sanctioned :: the
manufacturer is VOLTEQ and the model # is HY20010EX)

On the battery itself, you need to pop the black (aesthetic-only) cover off
the top of the battery.  Under there are several 10mm fasteners that hold
down the actual watertight cover. Inside there are some fuses - if any of
these fuses are blown, LG told me that the battery is toast and LG needs to
take it back and rebuild it. But if your fuses are good then you can
determine the positive and negative leads by red and black conductors.

* The RESU10H battery should be charged at 152 Volts.

*Instructions for Using Volteq DC Power Supply to Charge Batteries*

   1. Make sure the "O.V. Set" knob (second knob from the left) is set to
   the maximum setting before you begin.
   2. Turn the AC power on using the air switch in the back.
   3. Enable the output by pushing the green button to 'IN' position.
   4. Turn the current knob (the leftmost knob) to slightly above minimum
   so that the CV light is on.
   5. Use the two knobs on the right to set the voltage to desired level
   recommended by the battery manufacturer.
   6. Connect the battery to the back terminals, make sure the polarity is
   correct: + to + and - to -.
   7. Turn the current knob to maximum, or the desired current recommended
   by battery manufacturer.
   8. Watch the charging progress, when the current is below 1A or 1/10 of
   the maximum charging current, it is probably time to stop. Make sure the AC
   power never goes offline during the charging process.
   9. Stop the output using the green button, disconnect the battery from
   the power supply, and then turn off the power supply.

-- 

David Quattro
CA License # 954020. C-10, C-46
ph (415) 312-2661
www.quattrosolar.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] EG4 Equipment

2024-02-20 Thread Dave Angelini Offgrid Solar via RE-wrenches
You should start a new thread and not use this one. You will get more 
response! Good Luck!


---

Dave Angelini Offgrid Solar
"we go where powerlines don't"
   [1]https://offgridsolar1.com/ [2]  [1]
e-mail  offgridso...@sti.net
text 209 813 0060

On 2024-02-20 9:42 am, Tom McCalmont via RE-wrenches wrote:

I have an LG RESU-10H Gen2 Type R battery that has discharged so far 
that the display will no longer turn on.  Apparently, there is a 
recovery process for this situation that involves using an 
LG-sanctioned charger that will properly manage the BMS throughout the 
recovery process.  I have access to the correct charger for this 
purpose.


However, I have searched the Internet and Youtube and cannot find any 
instructions that explain how to operate the charger and recover the LG 
battery.


Does anyone on this group have experience with this situation and can 
help?  Is there a service manual for the LG RESU battery that explains 
how to recharge it in this situation (again, can find nothing but the 
installation manual on the internet).


Many thanks for any insights.

Tom McCalmont

On Feb 20, 2024, at 8:59 AM, Dave Angelini Offgrid Solar via 
RE-wrenches  wrote:


Someone asked about the loss on the discover AES rackmount.

"The contactor is bi-stable so it doesn't require extra holding current 
in either state. The ON state loss is 7.49mA."


https://discoverlithium.com/products/lithium-batteries/aes-rackmount

Also below is a response from Schneider on closing the loop with EG4.

Thanks for the feedback Dave.
I visited Signature last year to offer training. The EG4 is available 
in the dropdown menu for BMS Setup in v1.18 InsightLocal firmware.

Integration with XW Pro has worked well from what I have seen.
Eric

Eric Bentsen

Auburn, WA
United States

[3]

[4]

Download mySchneider app [4]

24/7 support. Mobile catalog. Access to expert help.

[5]  [6]  [7]  [8]  [9]  [10]  [11]

Genera

-

Dave Angelini Offgrid Solar

"we go where powerlines don't"

[1]https://offgridsolar1.com/ [2]  [1]

e-mail  offgridso...@sti.net

text 209 813 0060

 Original Message 

Subject:
Re: [RE-wrenches] EG4 Equipment

Date:
2024-02-16 3:11 pm

From:
Dave Angelini Offgrid Solar via RE-wrenches 



To:
RE-wrenches 

Cc:
Dave Angelini Offgrid Solar 

Reply-To:
offgridso...@sti.net, RE-wrenches 

Howie, I think you should also look again at the Discover rack mount 
system in the link below. Nice 75 year old company that made it's name 
on Locomotive batteries. Their prices are way down around 14 K for 
30Kwh with heaters. If you have not looked at Lynk2 their gateway 
closed loop into SMA, Schneider, Solark, Morningstar and a few others 
you should.


The only problems I have with Schneider are pretty easy and get 
resolved because I only use them and take all of the training. Conext 
Insight is a home run for my clients. Schneider also hired me to test 
their first closed loop system with LG back in 2017 and it still is 
working fine.


https://discoverlithium.com/products/lithium-batteries/aes-rackmount 
[12]


Dave Angelini Offgrid Solar

"we go where powerlines don't"

[1]https://offgridsolar1.com/ [2]  [1]

e-mail  offgridso...@sti.net

text 209 813 0060

On 2024-02-16 2:02 pm, Michael Morningstar via RE-wrenches wrote:

We gave EG4 and Signature another chance after promises from their 
dealer oriented support department that we could expect better service 
from them. We had an EG4 BMS crap out a couple months ago after only a 
few months. Lots and lots of communications with Signature and we still 
don't have a BMS or replacement battery. It's been a shit show with 
them. I think we are going to remove them and install 3rd party BMS's 
and find some use for them. Maybe donate them. We've only had luck with 
Schneider/Discover pairings in closed loop. A large system we did with 
Sol-Arks never really worked in Closed loop, despite Discover coming to 
the site. Most likely it's a Sol-Ark issue, but we've reached Sol-Arks 
technical expertise limits. Even with Schneider/AES, there have been 
some issues that are causing me to re-consider Li for offgrid. I just 
had a conversation this morning with a long time off-grid pro and he 
said the same thing. It used to be, we'd install a wet lead acid bank 
and then ten years would pass before hearing from the client when it 
was time for another bank. Sometimes fifteen years. Our call backs with 
systems over the last ten years, first with a decline in equipment 
quality and then the switch to Li are costing us too much money and 
causing a lot of heartburn for our clients. Rant Over


On Fri, Feb 16, 2024 at 12:57 PM Howie Michaelson via RE-wrenches 
 wrote:


Hi All,

I've searched the archives for info pertaining to EG4 inverters and 
batteries. The comments have been mostly positive.  I have stayed away 
from EG4 until now in part, for the reason the Michael Morningstar 
suggested last June - that is, they seemed very oriented

Re: [RE-wrenches] EG4 Equipment

2024-02-20 Thread Dave Angelini Offgrid Solar via RE-wrenches
The LG charger probably generates the Heartbeat signal you need to fool 
the contactor to be on for charging.


I Think! My experience is with the 48V RESU 10 and not the  RESU 10H 
that is a 400vdc battery.


There were a few people on here with 10H so hang on.

Dave Angelini Offgrid Solar
"we go where powerlines don't"
   [1]https://offgridsolar1.com/ [2]  [1]
e-mail  offgridso...@sti.net
text 209 813 0060

On 2024-02-20 9:42 am, Tom McCalmont via RE-wrenches wrote:

I have an LG RESU-10H Gen2 Type R battery that has discharged so far 
that the display will no longer turn on.  Apparently, there is a 
recovery process for this situation that involves using an 
LG-sanctioned charger that will properly manage the BMS throughout the 
recovery process.  I have access to the correct charger for this 
purpose.


However, I have searched the Internet and Youtube and cannot find any 
instructions that explain how to operate the charger and recover the LG 
battery.


Does anyone on this group have experience with this situation and can 
help?  Is there a service manual for the LG RESU battery that explains 
how to recharge it in this situation (again, can find nothing but the 
installation manual on the internet).


Many thanks for any insights.

Tom McCalmont

On Feb 20, 2024, at 8:59 AM, Dave Angelini Offgrid Solar via 
RE-wrenches  wrote:


Someone asked about the loss on the discover AES rackmount.

"The contactor is bi-stable so it doesn't require extra holding current 
in either state. The ON state loss is 7.49mA."


https://discoverlithium.com/products/lithium-batteries/aes-rackmount

Also below is a response from Schneider on closing the loop with EG4.

Thanks for the feedback Dave.
I visited Signature last year to offer training. The EG4 is available 
in the dropdown menu for BMS Setup in v1.18 InsightLocal firmware.

Integration with XW Pro has worked well from what I have seen.
Eric

Eric Bentsen

Auburn, WA
United States

[3]

[4]

Download mySchneider app [4]

24/7 support. Mobile catalog. Access to expert help.

[5]  [6]  [7]  [8]  [9]  [10]  [11]

Genera

-

Dave Angelini Offgrid Solar

"we go where powerlines don't"

[1]https://offgridsolar1.com/ [2]  [1]

e-mail  offgridso...@sti.net

text 209 813 0060

 Original Message 

Subject:
Re: [RE-wrenches] EG4 Equipment

Date:
2024-02-16 3:11 pm

From:
Dave Angelini Offgrid Solar via RE-wrenches 



To:
RE-wrenches 

Cc:
Dave Angelini Offgrid Solar 

Reply-To:
offgridso...@sti.net, RE-wrenches 

Howie, I think you should also look again at the Discover rack mount 
system in the link below. Nice 75 year old company that made it's name 
on Locomotive batteries. Their prices are way down around 14 K for 
30Kwh with heaters. If you have not looked at Lynk2 their gateway 
closed loop into SMA, Schneider, Solark, Morningstar and a few others 
you should.


The only problems I have with Schneider are pretty easy and get 
resolved because I only use them and take all of the training. Conext 
Insight is a home run for my clients. Schneider also hired me to test 
their first closed loop system with LG back in 2017 and it still is 
working fine.


https://discoverlithium.com/products/lithium-batteries/aes-rackmount 
[12]


Dave Angelini Offgrid Solar

"we go where powerlines don't"

[1]https://offgridsolar1.com/ [2]  [1]

e-mail  offgridso...@sti.net

text 209 813 0060

On 2024-02-16 2:02 pm, Michael Morningstar via RE-wrenches wrote:

We gave EG4 and Signature another chance after promises from their 
dealer oriented support department that we could expect better service 
from them. We had an EG4 BMS crap out a couple months ago after only a 
few months. Lots and lots of communications with Signature and we still 
don't have a BMS or replacement battery. It's been a shit show with 
them. I think we are going to remove them and install 3rd party BMS's 
and find some use for them. Maybe donate them. We've only had luck with 
Schneider/Discover pairings in closed loop. A large system we did with 
Sol-Arks never really worked in Closed loop, despite Discover coming to 
the site. Most likely it's a Sol-Ark issue, but we've reached Sol-Arks 
technical expertise limits. Even with Schneider/AES, there have been 
some issues that are causing me to re-consider Li for offgrid. I just 
had a conversation this morning with a long time off-grid pro and he 
said the same thing. It used to be, we'd install a wet lead acid bank 
and then ten years would pass before hearing from the client when it 
was time for another bank. Sometimes fifteen years. Our call backs with 
systems over the last ten years, first with a decline in equipment 
quality and then the switch to Li are costing us too much money and 
causing a lot of heartburn for our clients. Rant Over


On Fri, Feb 16, 2024 at 12:57 PM Howie Michaelson via RE-wrenches 
 wrote:


Hi All,

I've searched the archives for info pertaining to EG4 inverters and 
batteries. The comments hav

Re: [RE-wrenches] EG4 Equipment

2024-02-20 Thread Tom McCalmont via RE-wrenches
I have an LG RESU-10H Gen2 Type R battery that has discharged so far that the 
display will no longer turn on.  Apparently, there is a recovery process for 
this situation that involves using an LG-sanctioned charger that will properly 
manage the BMS throughout the recovery process.  I have access to the correct 
charger for this purpose.

However, I have searched the Internet and Youtube and cannot find any 
instructions that explain how to operate the charger and recover the LG battery.

Does anyone on this group have experience with this situation and can help?  Is 
there a service manual for the LG RESU battery that explains how to recharge it 
in this situation (again, can find nothing but the installation manual on the 
internet).

Many thanks for any insights.

Tom McCalmont


> On Feb 20, 2024, at 8:59 AM, Dave Angelini Offgrid Solar via RE-wrenches 
>  wrote:
> 
> Someone asked about the loss on the discover AES rackmount. 
> 
> "The contactor is bi-stable so it doesn’t require extra holding current in 
> either state. The ON state loss is 7.49mA."
> 
> https://discoverlithium.com/products/lithium-batteries/aes-rackmount
> 
> 
> 
> Also below is a response from Schneider on closing the loop with EG4.
> 
> 
> 
> Thanks for the feedback Dave.
> I visited Signature last year to offer training. The EG4 is available in the 
> dropdown menu for BMS Setup in v1.18 InsightLocal firmware.
> Integration with XW Pro has worked well from what I have seen.
> Eric
>  
>  
>  
> Eric Bentsen
>   
> Auburn, WA
> United States
>  
>  
> Download mySchneider app 
> 24/7 support. Mobile catalog. Access to expert help.
>  
>    
>    
>    
>   
>   
> 
>  
>  
>  
>  
> 
> Genera
> 
> Dave Angelini Offgrid Solar
> 
> "we go where powerlines don't"
>    https://offgridsolar1.com/  
> 
> e-mail  offgridso...@sti.net 
> text 209 813 0060
>  
>  Original Message 
> 
> Subject:
> Re: [RE-wrenches] EG4 Equipment
> Date:
> 2024-02-16 3:11 pm
> From:
> Dave Angelini Offgrid Solar via RE-wrenches 
> mailto:re-wrenches@lists.re-wrenches.org>>
> To:
> RE-wrenches  >
> Cc:
> Dave Angelini Offgrid Solar  >
> Reply-To:
> offgridso...@sti.net , RE-wrenches 
> mailto:re-wrenches@lists.re-wrenches.org>>
>  
> Howie, I think you should also look again at the Discover rack mount system 
> in the link below. Nice 75 year old company that made it's name on Locomotive 
> batteries. Their prices are way down around 14 K for 30Kwh with heaters. If 
> you have not looked at Lynk2 their gateway closed loop into SMA, Schneider, 
> Solark, Morningstar and a few others you should.
>  
> The only problems I have with Schneider are pretty easy and get resolved 
> because I only use them and take all of the training. Conext Insight is a 
> home run for my clients. Schneider also hired me to test their first closed 
> loop system with LG back in 2017 and it still is working fine.
>  
> https://discoverlithium.com/products/lithium-batteries/aes-rackmount
>  
>  
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
>    https://offgridsolar1.com/  
> 
> e-mail  offgridso...@sti.net 
> text 209 813 0060
>  
> On 2024-02-16 2:02 pm, Michael Morningstar via RE-wrenches wrote:
> 
> We gave EG4 and Signature another chance after promises from their dealer 
> oriented support department that we could expect better service from them. We 
> had an EG4 BMS crap out a couple months ago after only a few months. Lots and 
> lots of communications with Signature and we still don't have a BMS or 
> replacement battery. It's been a shit show with them. I think we are going to 
> remove them and install 3rd party BMS's and find some use for them. Maybe 
> donate them. We've only had luck with Schneider/Discover pairings in closed 
> loop. A large system we did with Sol-Arks never really worked in Closed loop, 
> despite Discover coming to the site. Most likely it's a Sol-Ark issue, but 
> we've reached Sol-Arks technical expertise limits. Even with Schneider/AES, 
> there have been some issues that are causing me to re-consider Li for 
> offgrid. I just had a conversation this morning with a long time off-grid pro 
> and he said the same thing. It used to be, we'

Re: [RE-wrenches] EG4 Equipment

2024-02-20 Thread Dave Angelini Offgrid Solar via RE-wrenches

Someone asked about the loss on the discover AES rackmount.

"The contactor is bi-stable so it doesn't require extra holding current 
in either state. The ON state loss is 7.49mA."


https://discoverlithium.com/products/lithium-batteries/aes-rackmount

Also below is a response from Schneider on closing the loop with EG4.

Thanks for the feedback Dave.

I visited Signature last year to offer training. The EG4 is available in 
the dropdown menu for BMS Setup in v1.18 InsightLocal firmware.


Integration with XW Pro has worked well from what I have seen.

Eric

Eric Bentsen

Auburn, WA
United States

 [9]

 [10]

Download mySchneider app [10]

24/7 support. Mobile catalog. Access to expert help.

 [11]  [12]  [13]  [14]  [15]  [16]  [17]

Genera

-

Dave Angelini Offgrid Solar

"we go where powerlines don't"

   [7]https://offgridsolar1.com/ [8]  [7]

e-mail  offgridso...@sti.net

text 209 813 0060

 Original Message 

Subject:

Re: [RE-wrenches] EG4 Equipment

Date:

2024-02-16 3:11 pm

From:

Dave Angelini Offgrid Solar via RE-wrenches 



To:

RE-wrenches 

Cc:

Dave Angelini Offgrid Solar 

Reply-To:

offgridso...@sti.net, RE-wrenches 

Howie, I think you should also look again at the Discover rack mount 
system in the link below. Nice 75 year old company that made it's name 
on Locomotive batteries. Their prices are way down around 14 K for 30Kwh 
with heaters. If you have not looked at Lynk2 their gateway closed loop 
into SMA, Schneider, Solark, Morningstar and a few others you should.


The only problems I have with Schneider are pretty easy and get resolved 
because I only use them and take all of the training. Conext Insight is 
a home run for my clients. Schneider also hired me to test their first 
closed loop system with LG back in 2017 and it still is working fine.


https://discoverlithium.com/products/lithium-batteries/aes-rackmount 
[18]


Dave Angelini Offgrid Solar

"we go where powerlines don't"

   [7]https://offgridsolar1.com/ [8]  [7]

e-mail  offgridso...@sti.net

text 209 813 0060

On 2024-02-16 2:02 pm, Michael Morningstar via RE-wrenches wrote:

We gave EG4 and Signature another chance after promises from their 
dealer oriented support department that we could expect better service 
from them. We had an EG4 BMS crap out a couple months ago after only a 
few months. Lots and lots of communications with Signature and we still 
don't have a BMS or replacement battery. It's been a shit show with 
them. I think we are going to remove them and install 3rd party BMS's 
and find some use for them. Maybe donate them. We've only had luck with 
Schneider/Discover pairings in closed loop. A large system we did with 
Sol-Arks never really worked in Closed loop, despite Discover coming to 
the site. Most likely it's a Sol-Ark issue, but we've reached Sol-Arks 
technical expertise limits. Even with Schneider/AES, there have been 
some issues that are causing me to re-consider Li for offgrid. I just 
had a conversation this morning with a long time off-grid pro and he 
said the same thing. It used to be, we'd install a wet lead acid bank 
and then ten years would pass before hearing from the client when it 
was time for another bank. Sometimes fifteen years. Our call backs with 
systems over the last ten years, first with a decline in equipment 
quality and then the switch to Li are costing us too much money and 
causing a lot of heartburn for our clients. Rant Over


On Fri, Feb 16, 2024 at 12:57 PM Howie Michaelson via RE-wrenches 
 wrote:



Hi All,

I've searched the archives for info pertaining to EG4 inverters and 
batteries. The comments have been mostly positive.  I have stayed away 
from EG4 until now in part, for the reason the Michael Morningstar 
suggested last June - that is, they seemed very oriented to the DIY 
market and not real serious contenders in the lasting marketplace. 
However, I was at RE+ Boston this week and was quite surprised to see 
that the EG4 18k inverter is, for all I could tell, identical to the 
Fortress Envy 12k, in both physical layout as well as menu structure. 
I have very limited experience with the Envy (having just installed my 
1st one last week, in order to compare it to the Sol-Ark 15). I don't 
have any thoughts about it yet, except that the font on the screen is 
quite small and the opening screen is not as intuitive as the Sol-Ark, 
but that might just take familiarizing myself more to the Envy (and/or 
the EG4).


My question is, for folks who have had either the Envy or the EG4 
inverters installed for a decent period of time, what is your current 
take on their functionality, durability, and for the EG4, the quality 
of support? Also, what experience have folks had similarly with the 
EG4 LLI batteries? I'm not unhappy with the Sol-Ark or in general the 
Fortress eVault Max battery, but there are some attractive things 
about the Envy and potentially the EG4 18k, and the price point and 
seemingly smart conf