Re: [RE-wrenches] SolArk and Tigo compatibility

2022-11-16 Thread Dustin Douglas via RE-wrenches
Hello All,



The utilization of the onboard 12v DC power supply is dependent on the Rapid 
Shutdown Device that you are using, whether Tigo/APSystems/Midnite. Tigo has 
many different solutions in their TS4 series of products. The devices that 
utilize the RSS Transmitter only, TS4-A-F and TS4-A-2F receivers, will be able 
to utilize the onboard 12v power supply to power the RSS Transmitter. It is 
possible to power the RSS Transmitter separately from the inverter if it makes 
the most sense for the project.



However, if you are using any of the other TS4 series (TS4-A-O, TS4-A-M and 
TS4-A-S) these require the use of the CCA (Cloud Connect Advance) and the TAP 
(Tigo Access Point) kit provided by Tigo to provide the PTO (permission to 
operate) signal to the receivers. Both the CCA and TAP kit must be powered 
separately from the included 12vDC power supply in the Sol-Ark as this exceeds 
the power supply. We recommend that these items be powered by a 120vAC circuit 
connected to the "Load" breaker of the Sol-Ark so that the CCA and TAP kit are 
powered during a grid outage.



Thank you and have a blessed day,

Dustin Douglas










 On Wed, 16 Nov 2022 16:37:57 -0600 Chris Sparadeo 
 wrote ---



@DustinDouglas do you mind confirming if the Tigo RSS Transmitter is compatible 
with the 12vdc power supply from Sol-Ark, and if not…what should we be doing to 
supply power without having to rely on 120VAC output of the inverter? 



Thanks,



-Chris 





On Wed, Nov 16, 2022 at 4:22 PM Christopher Warfel via RE-wrenches 
<mailto:re-wrenches@lists.re-wrenches.org> wrote:

Hi Nick and List, that was my problem exactly. 
Chris





On 11/16/2022 12:38 PM, Nick A Lucchese
  via RE-wrenches wrote:


All, I believe what Chris is referring to is something I was
  initially confused on during a Solark install I was involved with
  last year. Uncertain if the manual has changed but in the Solark
  12k manual dated April 2, 2021 on page 23 it has a line saying- 



Note: Tigo Optimizers are compatible with the
  Sol-Ark 12k (Do not use the built in 12v Power supply in the
  Sol-Ark user area to power the Tigo Optimizer TX transmitter)



I too had to confirm with Sol-Ark to clarify these
  details. I’ve not looked at any of their newer manuals to see
  if some of these notes have changed.



Enjoy your day, Nick







On Nov 16, 2022, at 8:41 AM, Chris Sparadeo
via RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
wrote:



Hi Chris,



I echo Ronald’s experience. I
  wasn’t aware of any memo from Sol Ark suggesting pins
  15 and 16 should not be used for the Tigo RSS
  Transmitter. The 12K and 15K manuals both refrence a
  12vdc RSS transmitter to achieve rapid shut down. 



Best,



Chris 



On Wed, Nov 16,
  2022 at 11:21 AM Roland - RES via RE-wrenches 
<mailto:re-wrenches@lists.re-wrenches.org>
  wrote:

Aloha Chris, 



We have numerous Sol-Ark systems
  with Tigo TS4Fs where we have the transmitter
  wired to the 12v supply of the inverter, with
  no issues to date.

 

 

Sent from a IPhone, with touch
screen keys on the fly. Please excuse
shortcuts and typos. 



Roland Shackelford
  
NABCEP CERTIFIED PV INSTALLER

President 

Renewable Energy Services
  (RES), Inc. 

Mobile:  http://808-938-9239/

http://www.renewablenergy.com/





On Nov 16,
  2022, at 4:33 AM, Christopher Warfel via
  RE-wrenches 
<mailto:re-wrenches@lists.re-wrenches.org>
  wrote:
 







Hi, We are doing our first
  system with these two devices. The
  inverter is SolArk 12P (mutimode) and
  the Tigo product for RS is the TS4F. 
  Tigo has me a little bit walking in
  circles. 

I told them that SolArk says
not to use the 12VDC RS output terminals
for connecting the transmitter.  I gave
them the attached drawing which they ask
for, which shows the transmitter
connected to a 120VAC/12VDC breaker
which they supply.  They told me to wire
the 120VAC source to the main service
panel so the array would shut down on
loss of power. I told them that is

Re: [RE-wrenches] Sol ark 120v issues

2021-02-24 Thread Dustin Douglas
Wrenches,



You can have 4800W on L1 and 0W on L2. It has huge 240V peak power. But you are 
correct that some 120V inductive loads >3/4hp can be an issue. We recommend 
rewiring those massive motors to 240V (most are convertible on the motor). The 
1400W limit is with DC Loads. A heat gun on high is an AC load but on low, it 
only uses 1/2 of the sinewave (DC load). Our limit for DC loads (hair dryer, 
leaf blower, drill, blender, curling iron, heat gun only on low setting) is 
1400W.


Thank you and have a blessed day,

Dustin Douglas

Engineering Support Lead

(972)575-8875 ext. 108

http://www.Sol-Ark.com









 On Tue, 09 Feb 2021 23:23:22 -0600 Nick A Lucchese  
wrote 


I agree with many of you on waiting awhile longer until these issues are sorted 
out. While I definitely think there is plenty of room beyond our usual 
favorites for another robust battery based inverter to offer I don’t intend to 
embark on another frustrating adventure at mostly my expense. At this point I’m 
more excited for the Midnite inverters more than anything and know once they’re 
released I won’t feel like I made a mistake. Meanwhile I’ll definitely be 
sending wishes of success to Sol-Ark. I’ve heard a lot of good things and will 
remain optimistic and hopeful it’s shortcomings will be resolved soon without 
needing to stack multiple units or a transformer.

Nick A Lucchese

On Feb 9, 2021, at 12:17 PM, Dave Angelini Offgrid Solar 
<mailto:offgridso...@sti.net> wrote:


Yes that has happened with 2 of mine Jerry.  I like the Transformer Devils that 
I know. Might check these out in 2 or 3 years. The whole all in one does not 
really appeal to me either but I will keep an open mind, in 2 or 3 years! 

 

Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  mailto:offgridso...@sti.net
text 209 813 0060


On Tue, 9 Feb 2021 10:19:44 -0800, Jerry Shafer 
<mailto:jerrysgarag...@gmail.com> wrote:

It is also interesting how sol ark sells over the counter to end users and also 
through distributors but at nearly the same price so it makes it difficult for 
our distributors to carry the sol ark products. Jerry



On Tue, Feb 9, 2021, 7:42 AM Jay <mailto:jay.pe...@gmail.com> wrote:

It is odd that the 12kw 20kw surge sol ark can't run a 15 amp 120v air 
compressor
 
 I saw a you tube video from what appears to be a pretty well versed installer 
who mentioned that sol ark knows this is an issue and specifically mentioned 
that his small air compressor will shut his 12kw inverter down. He didn't 
mention if there is a fix coming. 
 
 I guess I'll wait to buy one until they have that issue sorted out. 
 
 Jay
 
 Peltz power. 
 
 
 
 
 ___
 List sponsored by Redwood Alliance
 
 List Address: mailto:RE-wrenches@lists.re-wrenches.org
 
 Change listserver email address & settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 There are two list archives for searching. When one doesn't work, try the 
other:
 https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules & etiquette:
 http://www.re-wrenches.org/etiquette.htm
 
 Check out or update participant bios:
 http://www.members.re-wrenches.org/



___
List sponsored by Redwood Alliance

List Address: mailto:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org







___ 
List sponsored by Redwood Alliance 
 
List Address: RE-wrenches@lists.re-wrenches.org 
 
Change listserver email address & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
 
There are two list archives for searching. When one doesn't work, try the 
other: 
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
 
List rules & etiquette: 
http://www.re-wrenches.org/etiquette.htm 
 
Check out or update participant bios: 
http://www.members.re-wrenches.org___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-w

Re: [RE-wrenches] Load imbalance issues with SolArk?

2021-02-03 Thread Dustin Douglas
Hi Nick,



The 1400w difference is in terms of a DC load on an AC output, which is common 
when using variable speed appliances that use internal diodes that modify the 
sine wave. This does not apply to true AC loads where the Sol-Ark can do 4800w 
continuous at 120V.


Dustin Douglas

Engineering Support Lead

(972)575-8875 ext. 108

http://www.Sol-Ark.com









 On Wed, 03 Feb 2021 15:21:33 -0600 Amos Post 
 wrote 


Thanks Larry,

This would be a 240V to 120V step down configuration correct?  So the sub panel 
would be 120V only?



Best,

Amos


       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
    http://www.ienergyvt.com        
https://www.facebook.com/integrityenergyllp?ref=hl



On Feb 3, 2021, at 4:10 PM, mailto:la...@starlightsolar.com wrote:


Amos,

When using it in balancing mode, as seen in the attached image, the PSX will 
provide 120Vac from either leg and the inverter output should stay balanced. A 
240Vac circuit from the main panel goes to the PSX then to a sub panel and any 
240Vac loads stay on the main panel.


Larry Crutcher
Starlight Solar Power Systems









On Feb 3, 2021, at 1:49 PM, Amos Post <mailto:integrityenergy...@gmail.com> 
wrote:


We have had this issue with a recent installation.  It’s a new off-grid house 
build, and so not many loads to speak of yet, except mainly power tools.  The 
Solark 12K will not start any of: portable air compressor, table saw, and 
sometimes struggles with a miter saw, which are each 16amps or less at 120V, 
but I have measured close to 50amps start up for the air compressor and table 
saw.  The air compressor and table saw are 1.5HP each.  What helps is if the 
motors are warmed up, or putting another load on the other leg to balance the 
inverter’s output.  

Was thinking we would install a couple of dedicated 120V outlets for 
“high-current” 120V loads with a PSX-240, stepping down the inverter's 240 to 
120.  My understanding is this will solve the issue for starting these loads, 
but not sure if we might run into issues with inbalance down the road...  Would 
be curious to know if there’s another way to balance all of the house loads 
using the PSX-240?..


       Amos Post
   Integrity Energy
  W 802.763.7023
   C 802.291.2188
    http://www.ienergyvt.com/        
https://www.facebook.com/integrityenergyllp?ref=hl



On Feb 3, 2021, at 2:41 PM, mailto:la...@starlightsolar.com wrote:


If it turns out to be true, could you simply add the Outback PSX-240 to balance 
the loads?

Larry Crutcher
Starlight Solar Power Systems









On Feb 3, 2021, at 10:52 AM, Nick A Lucchese <mailto:luccheseso...@me.com> 
wrote:


Good morning Wrenches,

I’ve strongly been considering using the SolArk 12K unit for awhile but have 
heard from a few folks that there can be somewhat frequent issues with the 
inverter shutting down from line to line imbalance. As little as 1400 watts? I 
could see where these instances would be minimized with attention to detail on 
balancing all the loads but if’s as little as a delta of 1400 watts that might 
occur with something as innocent as a toaster oven. Seems like it would also be 
less of an issue in a grid back up or AC coupled scenario but for off grid I’d 
be bummed to be getting calls every couple weeks from an off grid client that 
trusted me to offer the right equipment.

How much of an issue is this? Is it getting exaggerated? Those that have NOT 
had this happening was it on a full time off grid site?

Has it happened less on sites using the "Limited to Home” mode? I have an 
upcoming project that was going to be setup with a couple Radians in HBX mode 
and my thought was perhaps it might be an ideal solution there but if the 
continuity of electrical service was going to be provided mainly through 
batteries and inverting and not through the pass through relays the majority of 
the time then the site might likely experience this issue with imbalance 
shutdowns.

There are many attractive features of the SolArk and I really like the thought 
of taking advantage of the 185 amp DC charger versus the Radian’s 115 but I’m 
kind of thinking the risks may outweigh the benefits if these shutdowns occur 
even once every couple of months. Any of you have a long enough history with 
them to chime in with your observations? Are they most reliable for AC coupled 
with backup rather than off grid or the “Limited to Home” mode?

Thanks for your time, 
Nick A Lucchese





___
List sponsored by Redwood Alliance

List Address: mailto:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
h

Re: [RE-wrenches] Sol-Ark Gen Exercise Cycle

2020-11-13 Thread Dustin Douglas
It is the same hardware as the dongle we provide with the unit and plugs 
directly into the Sol Ark Wi-fi port just like it would in a normal project, 
however the difference is that we customized the software to auto-update the 
inverter without the need for internet. This dongle is only compatible the 
Sol-Ark unit. We are currently sending them with the most up to date software 
for the units, but will be able to modify the software on the dongle so that it 
can be used for different versions of the Sol-Ark. The cost of the hardware is 
$100. We are wanting to add different options especially for those that are 
truly off grid.



Thank you and have a blessed day,

Dustin Douglas

Sol Ark Engineering Support

(972) 575-8875 x 108

http://www.sol-ark.com/






 On Fri, 13 Nov 2020 10:05:37 -0600 jay  wrote 



HI Dustin,



Can you elaborate on the custom dongle for the non internet people.  As its 
custom it sounds like its not a standard USB or SD or MSD?



How much does it cost and can it be updated from a computer and then taken to 
the job site?



Many if not most of my clients have no to limited internet and many that do,  
don’t want internet connection for their equipment. 



thanks



Jay



Peltz Power















On Nov 13, 2020, at 8:57 AM, Dustin Douglas <mailto:dus...@sol-ark.com> wrote:



The Time of Use feature can support this request. I do understand that 
programming can be somewhat confusing in completely covering what you are 
wanting the generator can do. However, if you are wanting the generator to turn 
on only when the batteries are low and getting through the night then we can 
set the Time of Use to only turn on with specific  hours and also charge up to 
specific SOC. We implemented this setting so that there is the ability to 
control how much fuel is used and not run the gen for long periods of time. The 
Time of Use settings are very customizable, if you would like to give our 
support team a call and we can help customize it to best fit your scenario.



As for updating the system itself, we offer different avenues of doing so. The 
first is the Wi-fi dongle that is connected to the inverter and to the 
customers home network. We also offer different aftermarket versions for 
customers with specific needs or if they don't have internet altogether. There 
is a ethernet version for those that don't want the over the air (OTA) 
connection to there wireless network or possibly if there router itself is a 
little to far away from where the unit is located. Simply running a ethernet 
cable to this specific dongle will connect them for monitoring and also allow 
for updates. The final version is for those true off grid installs where they 
are not worried about monitoring but do need to get the system updated. We have 
developed a custom design dongle that once inserted into the unit will perform 
the update on the inverter locally. Plug it in and wait for the final part of 
the software to finish and now your system will have the current version of 
software. You can then remove it and adjust the settings for the new features 
that were added.



Thank you and have a blessed day,

Dustin Douglas

Sol Ark Engineering Support

(972) 575-8875 x 108

http://www.sol-ark.com/






 On Fri, 13 Nov 2020 08:46:31 -0600 Jay <mailto:jay.pe...@gmail.com> wrote 




I’m wondering how the firmware is updated?  USB or other?  I’ve looked on the 
website but I couldn’t find any instructions. 



Thx

Jay







On Nov 12, 2020, at 7:58 PM, Jeff Clearwater 
<mailto:je...@villagepowerdesign.com> wrote:



  Thanks Dustin for keeping 
us up to date on Sol-Arks feature progress.



While you are upgrading your firmware: :)



So an essential feature for off-grid with a generator is to be able to 
program various SOC levels for generator start AND shuf-off after 
charge.  90% is way too high for many sunny climes and other 
configurations.  Often batteries need a boost in the wee morning hours -
 when they drop below the preferred recharge point but that's only 
perhaps a few hours before the sun comes up - So say you want to start a
 gen to charge a Lead-acid battery at 50% or an LFP batter at 20% SOC 
but you only want to bring it through to the next often or possibly 
sunny morning.  So you set it to run from 50% to 65% (or from 20%-40% 
for LFP) - knowing that the morning sun will take it the rest of the 
way.  90% would waste a ton of fuel in this scenario not too mention 
unwanted noise and wear and tear on the genny.  Depending on the clients
 use profile, the climate, and relative size of the array and battery 
and gen, these figures could vary anywhere from 20% to 100%.  So it's 
essential us off-grid installers have that flexibility.



Also I know that your TOU settings might cover this (though not in all 
modes I believe) but another nice feature is to have 2 or 3 time periods
 with different start and stop settings (Sunny Island does 

Re: [RE-wrenches] Sol-Ark Gen Exercise Cycle

2020-11-13 Thread Dustin Douglas
The Time of Use feature can support this request. I do understand that 
programming can be somewhat confusing in completely covering what you are 
wanting the generator can do. However, if you are wanting the generator to turn 
on only when the batteries are low and getting through the night then we can 
set the Time of Use to only turn on with specific  hours and also charge up to 
specific SOC. We implemented this setting so that there is the ability to 
control how much fuel is used and not run the gen for long periods of time. The 
Time of Use settings are very customizable, if you would like to give our 
support team a call and we can help customize it to best fit your scenario.



As for updating the system itself, we offer different avenues of doing so. The 
first is the Wi-fi dongle that is connected to the inverter and to the 
customers home network. We also offer different aftermarket versions for 
customers with specific needs or if they don't have internet altogether. There 
is a ethernet version for those that don't want the over the air (OTA) 
connection to there wireless network or possibly if there router itself is a 
little to far away from where the unit is located. Simply running a ethernet 
cable to this specific dongle will connect them for monitoring and also allow 
for updates. The final version is for those true off grid installs where they 
are not worried about monitoring but do need to get the system updated. We have 
developed a custom design dongle that once inserted into the unit will perform 
the update on the inverter locally. Plug it in and wait for the final part of 
the software to finish and now your system will have the current version of 
software. You can then remove it and adjust the settings for the new features 
that were added.


Thank you and have a blessed day,

Dustin Douglas

Sol Ark Engineering Support

(972) 575-8875 x 108

http://www.sol-ark.com/






 On Fri, 13 Nov 2020 08:46:31 -0600 Jay  wrote 



I’m wondering how the firmware is updated?  USB or other?  I’ve looked on the 
website but I couldn’t find any instructions. 



Thx

Jay







On Nov 12, 2020, at 7:58 PM, Jeff Clearwater 
<mailto:je...@villagepowerdesign.com> wrote:



  Thanks Dustin for keeping 
us up to date on Sol-Arks feature progress.

 

 While you are upgrading your firmware: :)

 

 So an essential feature for off-grid with a generator is to be able to 
program various SOC levels for generator start AND shuf-off after 
charge.  90% is way too high for many sunny climes and other 
configurations.  Often batteries need a boost in the wee morning hours -
 when they drop below the preferred recharge point but that's only 
perhaps a few hours before the sun comes up - So say you want to start a
 gen to charge a Lead-acid battery at 50% or an LFP batter at 20% SOC 
but you only want to bring it through to the next often or possibly 
sunny morning.  So you set it to run from 50% to 65% (or from 20%-40% 
for LFP) - knowing that the morning sun will take it the rest of the 
way.  90% would waste a ton of fuel in this scenario not too mention 
unwanted noise and wear and tear on the genny.  Depending on the clients
 use profile, the climate, and relative size of the array and battery 
and gen, these figures could vary anywhere from 20% to 100%.  So it's 
essential us off-grid installers have that flexibility.

 

 Also I know that your TOU settings might cover this (though not in all 
modes I believe) but another nice feature is to have 2 or 3 time periods
 with different start and stop settings (Sunny Island does this 
nicely).  So if the minimum SOC is reached in the evening you might as 
well bring it up to a higher SOC for gen shut down as it needs to get 
through the entire night whereas if that minimum SOC start trigger is 
met after 3 AM  it needs to only bring it to a lower SOC as described 
above.

 

 I'm loving the Sol-Ark product so far but it is obvious the
 software is a work in progress - the architecture and thought behind it
 is an excellent foundation - thanks for your work and openness for 
input to make it even better.

 

 Best,

 

 Jeff

 

 ~~~
  
Jeff Clearwater
 Village Power Design
 https://www.linkedin.com/in/jeff-clearwater-0622a312/ 
 http://www.villagepowerdesign.com
 cell - 413-559-9763
 ~~~






mailto:dus...@sol-ark.com

November
 12, 2020 at 11:46 AM



Hi All,



First and foremost 
thank you for sharing your experiences the the Sol-Ark system. We try 
very hard to have different capabilities and add new features that make 
it flexible for the customer. The two-wire start is a feature however 
that we want to be seamless. In the instance where the customer is 
seeing the system shutdown once the generator shuts off has been 
addressed and fixed with a software update. With this update we are able
 to handle larger generators that tend to drift from 60hz. Please give 
our support team a call so that we can 

Re: [RE-wrenches] Sol-Ark Gen Exercise Cycle

2020-11-12 Thread Dustin Douglas
Hi All,



First and foremost thank you for sharing your experiences the the Sol-Ark 
system. We try very hard to have different capabilities and add new features 
that make it flexible for the customer. The two-wire start is a feature however 
that we want to be seamless. In the instance where the customer is seeing the 
system shutdown once the generator shuts off has been addressed and fixed with 
a software update. With this update we are able to handle larger generators 
that tend to drift from 60hz. Please give our support team a call so that we 
can update the customer accordingly. We are also looking at adding more 
features including the ability exercise the generator in the near feature. 


Thank you and have a blessed day,

Dustin Douglas

Sol Ark Engineering Support

(972) 575-8875 x 108

http://www.sol-ark.com/




 On Thu, 12 Nov 2020 08:08:51 -0600 Jay  wrote 


Hi Bill



In the past I’ve had similar issues with generators/inverters. Usually a relay 
on the output power wires that opens( disconnects) when the stop signal is sent 
works as the frequency doesn’t slowly go down, it drops to 0 instantly. 

I don’t know if it will fix your issue. 



Seems like solark needs to greatly improve their firmware. 



Jay



Peltz power. 










On Nov 11, 2020, at 8:03 PM, Bill Hennessy <mailto:b...@berkssolar.com> wrote:



Hi folks--We've also been disappointed with the Sol-Ark two-wire generator 
start. The unit starts at the charge set point, but the inverter will shut down 
for about a minute every time the generator stops running. After the minute 
wait, the inverter restarts and everything is fine. But it is aggravating for 
the homeowners to be left wondering in the dark.



Sol-Ark says that when the generator shuts off, the frequency drops out of the 
Sol-Ark range and causes the inverter shut down. 

They suggested we find a way to increase the generator speed to avoid the 
frequency drop at shutdown. This seems like a lame suggestion, since the 
generator has no idea of when the batteries will be satisfied--it only responds 
to the on/off signal from the Sol-Ark. I would think that the unit could be 
programmed to ignore the frequency drop when it sends the shut off signal to 
the generator. The system has an an Ecogen 15kW.



Not having an exercise function is also a miss. As mentioned below, the time of 
use can be used, but one has to go out and play with the programming to check 
the generator.



regards, bill



Bill Hennessy
Berks Solar, LLC
371 Centennial Rd
Mertztown, PA 19539

o 610 682 4300
c 484 560 4666
NABCEP certified installer
PA contractor #44411
www.berkssolar.com







On Wednesday, November 11, 2020, 8:20:57 PM EST, Chris Sparadeo 
<mailto:sparadeo.ch...@gmail.com> wrote:





Thanks for the suggestion, Jay. 

Yes, the Sol-Ark has a very basic and limited AGS for 2 wire compatible gen 
sets. Gen start can be programmed with voltage or SOC, however gen stop is not 
a function that can not be readily programmed. Instead, the Sol-Ark is 
programmed to charge the battery bank to 90% of  the rated Ah capacity of the 
battery bank before turning off the generator. You can ultimately adjust this 
gen stop parameter to be based on a specific SOC or voltage, but I believe that 
doing so requires a call into tech support. The tech I spoke with updated a 
setting (having to do with a TOU parameter I believe) that was not accessible 
via the system interface. AGS  from Schnieder, Outback and even Magnum are less 
clunky, but I am hoping that Sol-Ark will eventually come out with new 
programming to remediate these minor but nevertheless, important issues




-Chris



On Wed, Nov 11, 2020 at 3:58 PM Jay <mailto:jay.pe...@gmail.com> wrote:

Hi Chris



I would install a timer. There are many dry contact dc or ac powered with a 
high degree of programmability. 



A question about the normal function of the AGS. I’ve talked to a few people 
that have mentioned that the ags has its own fuzzy logic, with limited 
programming. And they have had issues with it not turning on or not turning off 



What do you say?



Jay


On Nov 11, 2020, at 10:43 AM, Glenn Burt <mailto:glenn.b...@glbcc.com> wrote:



 I believe the Atkinson GSCM could be used to do this.



-Glenn

Sent from my 'smart'phone, so please excuse typos and spelling errors.





-- Original message--

From: Chris Sparadeo

Date: Wed, Nov 11, 2020 11:16 AM

To: RE-wrenches;

Cc:

Subject:[RE-wrenches] Sol-Ark Gen Exercise Cycle




Hi all,

According to Sol-Ark tech support, they do not currently have a programmable 
exercise cycle for

its two-wire start function. When paired with a generator like a Generac Ecogen 
(exercise cycle is automatically disabled when configured with two wire start) 
this means that the only way to effectively run an exercise cycle on your 
generator would be to do it manually. I am wondering if anyone has run into 
this issue and if there are work a