I second Dana's response. I have observed that the MS4448 waveform
quality degenerates quite rapidly with imbalanced loading of one or
the other of the 120 volt output legs. I can't give a quantitative
(% distortion/amps) number to it, but I would classify it as
severe. I first noticed it when doing some test measurements in the
shop, and found large discrepancies between various current metering
devices I was using, as some of the meters were not measuring RMS,
and the distortion was throwing them way off. And when using 120
volt motors, even though their surge may be well within specified
load limits, count on things not going well.
I'm generally satisfied with the Magnum MS4448, but this is one the
two key shortcomings that I see with the product. The other is the
idle power draw when not in search.
John Raynes
RE Solar
Torrey, UT
At 11:16 AM 2/9/2009, you wrote:
Wrenches,
We have an unusual problem, and I need to know if anyone else has
had this or a related problem, and what to do about it.
This concerns a new off-grid residential system, very conventional:
1,800W PV, Midnite E-Panel with Magnum MS4448-AE inverter, MX60, 16
S-460s, installed summer 2008. This existing home is being
extensively remodeled, and the home is not yet occupied. A local
mechanical contractor installed a new infloor radiant (gypcrete)
hydronic heating system using a Netherlands-made (German company)
Buderus GB142 high-efficiency boiler. The problem is that the boiler
won't start reliably on the inverter. It appears that the
hot-surface igniter does not get full AC voltage (it runs on
straight 120V AC, but is supplied through the boiler's control
circuitry). We tested the igniter by disconnecting it and plugging
it straight into inverter AC and it lit right up.
The mechanical contractor has tried a replacement Buderus GB142
boiler with the same result. I was told that they brought out a
generator and it also failed to ignite on generator AC, but not
knowing the generator used or the way it was wired (I believe an
extension cord to a portable) I don't put much weight on this data.
They also took a Lochinvar Boiler to the site to test the theory
that a different manufacturer's boiler might work. The Lochinvar
boiler, which uses a different control and a spark ignition rather
than a hot surface igniter, worked on site without any problems.
I'm looking for solutions. Magnum tech support had not heard of
this. Have you?
Also, if indeed we have an inverter that is incapable of running
this load, how do we make it right to the homeowner and the
mechanical contractor? What should be Magnum's obligation? What
should be ours? This issue hasn't come up here since the days when
the Trace SW mod-sine series was the waveform standard.
Thanks,
Allan Sindelar
mailto:al...@positiveenergysolar.comallan_(at)_positiveenergysolar.com
NABCEP certified solar PV installer
Positive Energy, Inc.
3225A Richards Lane
Santa Fe NM 87507
505 424-1112
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org