Re: [RE-wrenches] TL inverter with long DC Feeder

2014-10-07 Thread Michael Kelly
Hi William,

The 5200TL has two independent MPPT zones, each with two string inputs 
(essentially a two string combiner on each MPPT zone). The 'combiners' can't be 
bypassed at the moment, and the max fuse size that is allowed is 20A. Sorry, 
but fuses greater than 20A are not allowed; they would violate our compliance 
to our product listing.

Also, please be aware that the MPPT zones can't be configured to act as a 
single zone. Any one zone will input limit at 70% of the inverter's nameplate 
output, and the two zones together will limit when the inverter's AC output is 
reached. So, for the 5200TL, one zone is allowed to have a max input of 3640W, 
while the other zone will have the balance to achieve 5200W on the output side. 
In other words, in your example of only two strings, don't put both of your 
strings on one MPPT zone, because you will limit that MPPT zone and your output 
will only be around 3.6kW.

I hope this is helpful. Let me know if I am not understanding your example 
correctly.

Best,
Mike

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of William Miller
Sent: Monday, October 6, 2014 18:27
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder

Mike:

If I have just two strings of Solarworld SW275 modules per inverter, can I use 
one input to the built-in combiner to feed in a combined string?  My 
calculations indicate that I might be able to feed the two strings into one 25 
amp KLKD fuse.  The Isc is 8.94.  times 1.25 = 11.715.  Times 2 = 22.35.

The manual says use of any fuse higher than 20 amps voids the warranty.  Could 
an exception be made if only one set of 25 amp fuses were installed?

William


PS:  I am not sure fuses are required in a combiner with just two strings.  The 
SW275 module can withstand 16 amp external feed (from the max fuse rating).  A 
parallel module will output 8.94 times 1.56 or 13.95. This is less than the 16 
amps.  This used to be allowed in earlier versions of the code,  I will have to 
look and see if it still is.

Wm


[Gradient Cap_mini]
Lic 773985
millersolar.comhttp://www.millersolar.com/
805-438-5600

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Michael Kelly
Sent: Monday, October 06, 2014 3:10 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter with long DC Feeder

Hi William,

I wanted to let you know that currently, there is no bypass terminal to allow 
for combining at the array in this series of inverters. We have gotten a lot of 
feedback from customers that this is a required feature. Working toward that, 
in the next few months, we will phase into production an update that will 
include a bypass, but the existing stock does not have the feature.

I wanted to let you know so you could plan appropriately.

Best,
Mike

Michael Kelly
[Solectria_Yaskawa_signature_logo]http://www.solectria.com/
HQ: 360 Merrimack Street, Bldg 9, Fl 2, Entrance I, Lawrence, MA 01843 USA
O: +1 978-683-9700 x167 | F: +1 978-683-9702
mike.ke...@solectria.commailto:mike.ke...@solectria.com | 
www.solectria.comhttp://www.solectria.com/

NOTICE: This e-mail may contain confidential and/or privileged information. If 
you are not the intended recipient, or an authorized representative of the 
recipient, please be advised that you may not use, copy or disclose its 
contents in part or in whole. If you have received this message in error, 
please advise the sender by replying to this e-mail, and delete the message. 
Thank you.

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of William Miller
Sent: Monday, October 6, 2014 14:40
To: RE-wrenches
Subject: [RE-wrenches] TL inverter with long DC Feeder

Wrenches:

We are getting up to speed on using transformer-less inverters.  I have 
advocated long for the additional safety offered by these inverters but I am 
realizing the trade-offs with the new technology:  The implementation gets more 
complicated with the requirement for PV wire, OCPD and disconnecting means for 
plus and minus and plus providing  Arc Flash rated equipment.

I am currently designing a system that will locate the PV about 400 feet from 
the residence.  The system will utilize 2 Solectria 5200 watt inverters at the 
residence.  I would like to provide disconnecting means for the 4 strings at 
the array, in case of any needed service or excavating.  Preferably I'd like 
the disconnecting means to be deployable by a lay person (i.e. the gardener).

Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy.  I could 
install an Outback 8 circuit combiner with 8 touch-safe fuse holders.  The new 
combiners have had dead-fronts for a while now.  The gardener needs only to 
have a Philips screw driver to open this cover.  Any better ideas out there?

Thanks,

William


[Gradient Cap_mini]
Lic 773985
millersolar.comhttp://www.millersolar.com/
805-438-5600

___
List sponsored

Re: [RE-wrenches] TL inverter with long DC Feeder

2014-10-06 Thread Michael Kelly
Hi William,

I wanted to let you know that currently, there is no bypass terminal to allow 
for combining at the array in this series of inverters. We have gotten a lot of 
feedback from customers that this is a required feature. Working toward that, 
in the next few months, we will phase into production an update that will 
include a bypass, but the existing stock does not have the feature.

I wanted to let you know so you could plan appropriately.

Best,
Mike

Michael Kelly
[Solectria_Yaskawa_signature_logo]http://www.solectria.com/
HQ: 360 Merrimack Street, Bldg 9, Fl 2, Entrance I, Lawrence, MA 01843 USA
O: +1 978-683-9700 x167 | F: +1 978-683-9702
mike.ke...@solectria.commailto:mike.ke...@solectria.com | 
www.solectria.comhttp://www.solectria.com/

NOTICE: This e-mail may contain confidential and/or privileged information. If 
you are not the intended recipient, or an authorized representative of the 
recipient, please be advised that you may not use, copy or disclose its 
contents in part or in whole. If you have received this message in error, 
please advise the sender by replying to this e-mail, and delete the message. 
Thank you.

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of William Miller
Sent: Monday, October 6, 2014 14:40
To: RE-wrenches
Subject: [RE-wrenches] TL inverter with long DC Feeder

Wrenches:

We are getting up to speed on using transformer-less inverters.  I have 
advocated long for the additional safety offered by these inverters but I am 
realizing the trade-offs with the new technology:  The implementation gets more 
complicated with the requirement for PV wire, OCPD and disconnecting means for 
plus and minus and plus providing  Arc Flash rated equipment.

I am currently designing a system that will locate the PV about 400 feet from 
the residence.  The system will utilize 2 Solectria 5200 watt inverters at the 
residence.  I would like to provide disconnecting means for the 4 strings at 
the array, in case of any needed service or excavating.  Preferably I'd like 
the disconnecting means to be deployable by a lay person (i.e. the gardener).

Finding an 8 pole, arc flash, 600 VDC rated disconnect is not easy.  I could 
install an Outback 8 circuit combiner with 8 touch-safe fuse holders.  The new 
combiners have had dead-fronts for a while now.  The gardener needs only to 
have a Philips screw driver to open this cover.  Any better ideas out there?

Thanks,

William


[Gradient Cap_mini]
Lic 773985
millersolar.comhttp://www.millersolar.com/
805-438-5600

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Voltage Drop Calculator Templates

2010-07-26 Thread Michael Kelly
Hi All,

 

I got a request to make my voltage drop excel templates available in both
the new and old excel formats.  I also changed the calculator so you can
input your own Imp multiplier (if desired).  Here they are:

 

Excel 97-2003 version:
http://www.mechanicalmike.com/solar/DC_Voltage_Drop_Calculations_Template_07
_26_2010.xlt

Excel 2007 version:
http://www.mechanicalmike.com/solar/DC_Voltage_Drop_Calculations_Template_07
_26_2010.xltx

 

- Mike

---

Michael Kelly
Applications Engineer

NABCEP Certified Solar PV Installer T

toplogo
Solectria Renewables, LLC

360 Merrimack St.

Building 9, Floor 2

Lawrence, MA 01843
Phone: 978-683-9700 ext. 167
Fax: 978-683-9702

 mailto:m...@solren.com m...@solren.com

 http://www.solren.com/ www.solren.com

 

image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] calculating DC voltage drop

2010-07-22 Thread Michael Kelly
Hi All,

 

I agree with Ray with the exception that I use Imp*1.25 in my calculations.
I developed a simple spreadsheet for either fixed conductor size or for
fixed voltage drop.  You can feel free to use it by downloading here:
http://www.mechanicalmike.com/solar/DC_Voltage_Drop_Calculations_Template_04
_20_2010.xltx.

 

- Mike

---

Michael Kelly
Applications Engineer

NABCEP Certified Solar PV Installer T

toplogo
Solectria Renewables, LLC

360 Merrimack St.

Building 9, Floor 2

Lawrence, MA 01843
Phone: 978-683-9700 ext. 167
Fax: 978-683-9702

m...@solren.com

www.solren.com http://www.solren.com/ 

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray
Walters
Sent: Thursday, July 22, 2010 3:45 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] calculating DC voltage drop

 

I use actual operating current, without multipliers. I also use actual
temperatures, not the worst case temperatures that many use.

I created a spread sheet that uses the NEC adjustments for wire temperature,
(see NEC chapter 9, table 8, FPN 2)

It makes quite a difference!

Volt drop and the accompanying loss of energy production needs to be looked
at realistically under normal operating conditions. Adding worst case
multipliers is necessary for sizing cables and breakers for safety, but it
isn't appropriate when calculating energy losses. We shouldn't do an energy
loss analysis for a situation that might never occur, or for only a very
small % of the time. 

A correct analysis will reflect actual losses over the lifetime of the
system, so that an informed economic decision can be made. Especially on
larger systems with long runs, its worth it to you and the client to use
real world numbers, not blind over sizing.

I got into this over a decade ago, when I noticed that actual measured volt
drop was much less than calculated, now my calculations match real
measurements. 

 

R. Walters

r...@solarray.com

Solar Engineer

 

 





 

On Jul 22, 2010, at 1:22 PM, Marco Mangelsdorf wrote:





When calculating the voltage drop from a PV array to the inverter, what's
the most common accepted practice?  To use the Isc X 1.25 or 1.56 as the
multiplier?

 

Thanks,

marco

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org/ 

 

image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Supply Side Interconnections - Maximum Backfeed

2010-03-04 Thread Michael Kelly
Hi All,

Next to grounding, I find the calculation of the maximum amount of backfeed
current allowed in a supply side connection to be the most vague issue in
Article 690.  Let's assume we have a 400A, 480/277 service in a commercial
building, a 400A main service disconnect, and the jurisdiction is under NEC
2008.  What is the maximum backfeed current allowed in a supply side
connection?  The only place the code points you to is 230.82(6), which is no
help, or to Article 705, which is no help either.  I know that in the draft
version of NEC 2011, there is an expansion of 705.12(A) which states * *Supply
Side. An electric power production source shall be permitted to be connected
to the supply side of the service disconnecting means as permitted in
230.82(6). The sum of the ratings of all overcurrent devices connected to
power production sources shall not exceed the rating of the service.  That
is a helpful sentence from the Code, but as it is in draft form, what do we
do under NEC 2008?  What have you used as a maximum backfeed current for
supply side connections?

Thanks,
Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™

SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Generators and Grid-tie Systems

2010-03-02 Thread Michael Kelly
All,

If the grid-tie inverter is operating under UL1741 (and therefore IEEE1547),
then the inverter has to cease output within 1 second of the voltage going
over 10% of the base voltage.  So in the case where the generator is
outputting and the load is less than the inverter output, the voltage will
rise and the inverter will cease to ouput.  The voltage will then drop, the
inverter will reconnect, and the cycle will repeat itself.  That assumes the
generator's waveform is clean enough for the inverter to connect to in the
first place.  James Worden from Solectria Renewables covered this briefly in
a SolarPro article:
http://solarprofessional.com/article/?file=SP2_5_pg16_QandA_2.

- Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™

SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com


On Tue, Mar 2, 2010 at 9:29 AM, Drake Chamberlin 
drake.chamber...@redwoodalliance.org wrote:

 I was recently told by SMA that in the event that the inverters did connect
 to generator output, and the load was less than the inverter output, that
 the voltage would rise and the inverters would fall off line.  A year or so
 before I'd been told by another SMA representative that generator circuit
 boards had been fried by inverter backfeed.

 It would  be very good to get to the bottom of this one.

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Need (5) Suntech STP200

2010-02-17 Thread Michael Kelly
Hi All,

Looking for (5) Suntech STP200-18/Ub-1 modules to fill out an array.
If you have any, please contact me off-list.

Thanks,
Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™

SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] Labeling Rooftop Conduit for Fire Department

2010-01-13 Thread Michael Kelly
Hi All,

We recently completed a 63kW grid-tie in MA.  The Fire Department has asked
us to label the rooftop conduit (2 1/2 RMC) with high visibilty labels that
say something to the effect of High Voltage DC or 600 Volts DC or
Warning - Solar DC Circuits.  The trouble is that the Fire Department
doesn't really know what they want to the label to say.  Have any of you
come across this with your Fire Departments?  Any thoughts on the wording
for the label, and how often they should be placed on the conduit run (every
stick, every 6', every 20', etc.)?

Thanks,
Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™

SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Bonding Rails

2009-11-17 Thread Michael Kelly
Peter,

I've never used the ProSolar rails, so I can't speak to 1).

On 2), yes, you must bond the rails with a listed device if they are not
bonded to the modules.  The nice thing about the WEEB is that it allows one
to bond the modules and rails together, and then you can pick up the bond
from the rails (without having to hit every module with a lug and the EGC).

- Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™

SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com


On Tue, Nov 17, 2009 at 2:56 PM, Peter Parrish 
peter.parr...@calsolareng.com wrote:

  We have been using WEEB clips on all of our installations for over a year
 now. We include the WEEB data/installation sheets in our permit package and
 patiently point out the clips to inspectors who haven’t seen the WEEB system
 yet.



 Two questions:



 (1) For ProSolar rails, can we use one WEEB clip to bond two adjacent
 modules (say, modules A and B) on the upper rail (say, rail #1) and then use
 a second WEEB clip to bond the next two adjacent modules (say, modules C and
 D) on the lower rail (say, rail #2) and then use a listed lay-in lug (with
 in our case a WEEB clip) to bond to either rail #1 or #2 to continue the
 grounding?

 (2) If we DON”T use WEEB clips and use the conventional bonding
 methodology per module manufacturer’s instructions (proper location on the
 module, and listed screws, washers and nuts), do we have to ALSO bond the
 rails? We have an inspector in Pasadena, CA that is requiring this, but this
 is the first time we have been required to do so. Perhaps in the past year
 in ignorant bliss we have missed an important development? Or have we been
 dodging bullets for seven years and not even knowing it?



 - Peter

 Peter T. Parrish, Ph.D., President
 California Solar Engineering, Inc.
 820 Cynthia Ave., Los Angeles, CA 90065
 CA Lic. 854779, NABCEP Cert. 031806-26
 peter.parr...@calsolareng.com
 Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885






 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] American made

2009-09-02 Thread Michael Kelly
Mike,

Solectria grid-tie inverters are made in the USA.  They have
three-phase 13kW and 15kW units.  Web site: www.solren.com.

- Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™

SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com


On Wed, Sep 2, 2009 at 5:18 PM, Michael Cook m...@powerupco.com wrote:

 We are running into applications that need American made products for
 stimulus monies.  Modules are easy inverters are the difficult thing.  Has
 anyone gotten any of the big name inverters approved?  Looking for 10KW 3
 phase.  3 - 3KW units would be fine, or a single 10KW as well.


 Mike Cook
 m...@powerupco.com

 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] S-5 clamps on the standing seam roof

2009-08-27 Thread Michael Kelly
Paul,

We have used the S-5! clamps on standing seams in the past.  We like
putting the modules directly on the seams with the S-5! clamps, no
rails.  First, speak with the engineer who designed the building and
roof to make sure the roof is attached securely to the perlins and
building structure.  Second, make sure you obtain the correct S-5!
clamp; they make several styles to fit different seam profiles.
Third, make sure your crew torques each S-5! set screw to the
recommended torque; let the fasteners sit and then make your crew
torque them again.  Fourth, the advised mounting method is to have the
modules' long edge perpendicular to the roof seam (i.e. landscape) and
a clamp on every seam that the module crosses.  This means you need
*six* clamps per module, not four.  Fifth, to help with layout, use a
taught string to lay down all of the clamps that make up the first
row.  Six, with such a low sloped roof and New England conditions, you
are going to see a lot of dirt buildup on the modules after about six
months; you may want to advise your client to clean them (or have them
cleaned) on a regular schedule.  Seventh, wire management on this type
of a system is a real pain because of the limited access space under
the modules; if you find a good way to manage module to module
connections, let me know.

Good luck,
Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™

SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com


On Wed, Aug 26, 2009 at 11:44 PM, Max Balchowsky m...@seesolar.com wrote:

 check the specs on how the roof is attached to the building.

 
 From: Paul Lyons ly...@zapotecenergy.com
 To: re-wrenches@lists.re-wrenches.org
 Sent: Wednesday, August 26, 2009 3:32:17 PM
 Subject: [RE-wrenches] S-5 clamps on the standing seam roof

 Hello RE-Wrenches –



 We are working on the design details for S-5 clamps on a standing seam roof 
 with the PV modules mounted directly on the clamps at four points (i.e. no 
 horizontal rails).  The roof is made by Metl Span of Lewisville, Texas.  The 
 building is in New England and the roof has a slope of 0.5:12



 Have any of you had experience with these clamps and/or this particular roof 
 manufacturer?



 Paul Lyons, P.E.

 Zapotec Energy Inc.

 675 Massachusetts Ave

 Cambridge, MA 02139-3309

 Tel: 617-547-5900  ext.201

 Fax: 617-547-5901

 Mobile: 617-285-0634

 Email: ly...@zapotecenergy.com





 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Shucco Thermal Collectors

2009-02-25 Thread Michael Kelly
David,

Let me weigh in here.  We installed around eight Schuco SDHW systems last
year.  The one thing about Schuco is that you really need to understand how
their system is assembled, or I guarantee you will miss a component or an
assembly direction that is key to making the system function correctly.
Their manuals cover most of the small details, but you really need to read
the manuals carefully to pick up on everything.  And not just the main text
- read the little side bars too.  Pay particular attention to the
compression fittings: your line set should be perfectly round and free of
any burrs from cutting.  Also, we have found it helpful to use a high-temp
pipe dope or sealing compound with the compression fittings.  Oh, and if you
are using their tanks, note that they are single wall and not OG-300
compliant.

Good luck,
Mike

--
Michael Kelly
Project Engineer
Project Manager

SolarFlair Energy, Inc.
1 Knoll Rd.
Hopkinton, MA 01748
Direct Mobile: 617-899-9840
Direct Fax: 781-272-0748
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com


On Wed, Feb 25, 2009 at 4:25 PM, David Palumbo d...@independentpowerllc.com
 wrote:


 We are planning on doing our first installation with a complete Shuco SDHW
 system in the near future.

 Our thermal manager took Shuco's training in CT recently and was impressed
 with the collectors design and appearance. Shuco has a five year warranty
 on
 the whole package. Does any other thermal manufacturer offer a complete
 five
 year warranty?

 Any other thoughts, comments, complaints about Shuco?

 David Palumbo
 Independent Power LLC
 462 Solar Way Drive
 Hyde Park, VT 05655
 NABCEP Certified PV Installer
 www.independentpowerllc.com http://www.independentpowerllc.com/
 802-888-7194



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] NABCEP Test: Codebook or Handbook?

2009-01-20 Thread Michael Kelly
Michael,

Thanks for passing that along.  And thanks to Rebecca for clearing that up.

- Mike

--
Michael Kelly
Project Engineer
Project Manager

SolarFlair Energy, Inc.
1 Knoll Rd.
Hopkinton, MA 01748
Direct Mobile: 617-899-9840
Direct Fax: 781-272-0748
Main Phone: 508-293-4293
Main Fax: 508-293-4003
m...@solarflair.com


On Tue, Jan 20, 2009 at 6:34 PM, Michael Welch 
michael.we...@re-wrenches.org wrote:

 Hi Gang.

 Rebecca Eaton, Exec. Dir. of NABCEP asked me to pass this on to you. If you
 have any questions about NABCEP policy and regs, please contact her directly
 at rea...@nabcep.org or (800) 654-0021.

 Per the Candidate Information Handbook Section 6.2 on www.nabcep.org,
 following is some detail about what is provided during the exam. Please note
 that NABCEP has always used the Casio fx 260 solar Fraction calculator.
 Fortunately, when supplies need to be replenished, this model has remained
 available, although that may not always be the case.

 *6.2 What to Bring to the Exam
 *
 The NABCEP certification exam is designed to be completed with the aid of
 the National Electrical Code(R). The text and materials required to take the
 test will be provided for each candidate at the test site, including:

 *1. 2008 National Electrical Code, NFPA 70
 *2. Calculator (For example, a Casio fx260, a Texas Instruments TI-30Xa,
 or a similar model)
 3. Two #2 pencils

 All materials will be returned to the Proctor at the end of the exam, where
 they will be inspected. No changes are to be made to the National Electrical
 Code(R) text or to the calculators, and under no condition will these items
 leave the testing room at any time.

 In addition to the materials that NABCEP will supply, candidates may bring
 water in a closeable container. No other food items are allowed in the
 testing room. Any personal items or supplies needed during the examination
 must be encased in a clear plastic bag, no larger than 8.5 X 11 in size.
 Please be advised that due to circumstances beyond our control, examination
 sites may experience minor disturbances. It is recommended that candidates
 who are sensitive to noise bring earplugs.

 *6.3 What Not to Bring to the Examination
 *
 Unauthorized supplies will be subject to removal by the testing officials
 at the examination site. The following items are NOT allowed in the
 examination room and will be confiscated during the exam and returned
 afterward:

  Watches – a clock will be provided in the room.
  Any part of workbooks and materials, bound or loose-leaf notes.
  Handwritten and typewritten notes are not allowed.
  Pull-off labels, removable tabs, paper clips, or metal clamps.
  Paper, writing tablets, or notepads.
  Highlighters.
  Personal calculators and electronic organizers.
  Cameras, tape recorders, or computers.
  Pagers, electronic transmitting devices, or telephones.
  Canisters of mace, pepper spray, or other personal defense items.
  Purses, briefcases, portfolios, fanny packs, or backpacks – a space
 within the testing room will be provided for you to leave bags of this kind.
 Any personal supplies that you need in the exam with you (inhalers, extra
 glasses, tissues) should be placed in a clear plastic bag no larger than
 8.5 x 11.



 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] wrenches] NABCEP Test: Codebook or Handbook?

2009-01-19 Thread Michael Kelly
Thanks for the replies, guys.  I talked with the NABCEP office, and after
being put on hold a few times to seek the answer, I got a hesitant reply
that the handbook is provided, not the codebook, contrary to Dave's reply.
Anyone who took the exam in September or last March want to weigh in?
Also, I thank myself that the calculator taped to my site visit clipboard is
a Casio fx-260 solar, and I use a TI at my desk, so I think I'll be covered
on that front.

- Mike


On Fri, Jan 16, 2009 at 5:32 PM, cvsol...@aol.com wrote:

 The calculator they gave us up here was a Casio fx-260solar. the first time
 i took the test, i had real problems with their calculator, i was used to my
 ti. totally different logic hiarchy. good luck. db


 -Original Message-
 From: David Brearley david.brear...@solarprofessional.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Sent: Fri, 16 Jan 2009 5:04 pm
 Subject: Re: [RE-wrenches] NABCEP Test: Codebook or Handbook?

 Codebook, not Handbook.



 On 1/16/09 3:48 PM, Michael Kelly m...@solarflair.com wrote:


  All,

 

  Two of us from SolarFlair are signed up to take the exam in March.

  For those that have taken it, is the NEC codebook provided, or is it

  the handbook?  We want to make sure we are studying from the materials

  that we will be using on the test day.

 

  Thanks,

  Mike

 

  --

  Michael Kelly

  Project Engineer

  Project Manager

 

  SolarFlair Energy, Inc.

  1 Knoll Rd.

  Hopkinton, MA 01748

  Direct Mobile: 617-899-9840

  Direct Fax: 781-272-0748

  Main Phone: 508-293-4293

  Main Fax: 508-293-4003

  m...@solarflair.com

  ___






 ___

 List sponsored by Home Power magazine


 List Address: RE-wrenches@lists.re-wrenches.org


 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm


 Check out participant bios:
 www.members.re-wrenches.org


 --
 Which stars will make the biggest headlines in 2009? Get Hollywood
 predictions, celebrity holiday photos and more with the PopEater 
 Toolbarhttp://toolbar.aol.com/popeater/download.html?ncid=emlweusdown0025.


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org