Re: [RE-wrenches] "Qualified solar electric property"? RE: battery storage limitations

2022-10-29 Thread Kirk Herander via RE-wrenches
Hello Howie -
Unrelated to tax code,
You had a question on Jerry's response referencing battery storage
limitations.

NFPA 855 (referenced in the 2021 NFPA 1 Fire safety rules), does put rules
/ limits on residential storage kwh size and layouts, amongst other things.
An 80kwh storage limit is mentioned here.
check out this link:

https://www.mayfield.energy/blog/fire-codes-and-nfpa-855-for-energy-storage-systems

This blog gives a good summary and history of both NFPA and IBC
requirements in the newest versions. Note Vermont is still working off NFPA
2015 for state-permitted commercial work, so the restrictions should not
apply at this time. That is of course unless a local municipality adopted
2021 on their own, which is how roof access pathway requirements came to be
in many VT towns for residences, first required in NFPA 2009 or thereabouts.



On Fri, Oct 21, 2022 at 5:24 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> This is actually a corporate owned residence - a nice little tax
> write-off...  Jerry, are you saying that from personal/professional
> experience there is a limitation to the size  of the battery bank that a
> residence can take a credit on?  I've never seen reference to anything like
> that before.  Could you possibly elaborate?
> Thanks,
> Howie
>
> *Howie Michaelson**Sun Catcher*
>
> *NABCEP Certified Solar PV Installer™*
>
> *Solar Electric Systems Sales & Service802-272-0004*
>
>
> On Fri, Oct 21, 2022 at 2:46 PM Jerry Shafer via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> On the system size of batteries We have had several issues with resi and
>> 80kWhr limitations, I dont know if this is an issue for you or not just
>> want to through it out there.
>> Jerry
>>
>> On Fri, Oct 21, 2022 at 11:14 AM Howie Michaelson via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> Hi folks,
>>> I have a client that I'm doing a larger inverter and battery upgrade.
>>> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
>>> The client is wanting manufacturer certification that the equipment is
>>> "qualified solar electric property". I don't know that I've ever run across
>>> this type of request before or that I've seen manufacturers supply such
>>> documentation. Is this something that anyone is familiar with? Did I miss
>>> something here?
>>> Thanks,
>>> Howie
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 31st Anniversary 1991-2022!!*

*www.vermont.solar*


dba Vermont Solar Engineering

802.863.1202

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-26 Thread Lloyd Hoffstatter via RE-wrenches
California Energy Commission energy.ca.gov
All the best,
Lloyd

Get Outlook for iOS<https://aka.ms/o0ukef>

From: RE-wrenches  on behalf of 
Kristopher Schmid via RE-wrenches 
Sent: Wednesday, October 26, 2022 9:25:53 PM
To: RE-wrenches 
Cc: Kristopher Schmid 
Subject: Re: [RE-wrenches] "Qualified solar electric property"?

New York Public Service Commission and Conformité Européene listing, Lloyd?

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Wed, Oct 26, 2022, 8:18 PM Lloyd Hoffstatter 
mailto:ll...@sunstruckconsulting.com>> wrote:
For inverters use the NYPSC list or CE for other equipment

Best,
Lloyd

Get Outlook for iOS<https://aka.ms/o0ukef>

From: RE-wrenches 
mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 on behalf of Kristopher Schmid via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>>
Sent: Wednesday, October 26, 2022 9:14:28 PM
To: cwar...@entech-engineering.com<mailto:cwar...@entech-engineering.com> 
mailto:cwar...@entech-engineering.com>>; 
RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Kristopher Schmid mailto:sol...@legacysolar.com>>
Subject: Re: [RE-wrenches] "Qualified solar electric property"?

Yes, but I believe an accountant wants to know how they prove and document that 
it is "solar electric property".

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Wed, Oct 26, 2022, 2:55 PM Christopher Warfel via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:

I agree with Lloyd. It is qualified if listed I would have to believe. Chris

On 10/21/2022 6:36 PM, Lloyd Hoffstatter via RE-wrenches wrote:
Howie,
I think he is referring to the tax language 
https://www.irs.gov/newsroom/energy-incentives-for-individuals-residential-property-updated-questions-and-answers
Best regards,
Lloyd
Lloyd Hoffstatter
Sunstruck Consulting
Get Outlook for iOS<https://aka.ms/o0ukef>

From: RE-wrenches 
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 on behalf of Howie Michaelson via RE-wrenches 
<mailto:re-wrenches@lists.re-wrenches.org>
Sent: Friday, October 21, 2022 6:29:31 PM
To: RE-wrenches 
<mailto:re-wrenches@lists.re-wrenches.org>
Cc: Howie Michaelson 
<mailto:howie.michael...@gmail.com>
Subject: Re: [RE-wrenches] "Qualified solar electric property"?

Kris,
I found your query in the archives and Marcos follow-up question, but not the 
reply, apparently from George McClellan. I just called Sol-Ark and the sales 
person I talked with knew nothing about such a letter.  Fortress didn't have 
anything on their website and didn;'t answer their phone.
Do you still have the email response from George?
Thanks,
Howie
Howie Michaelson
Sun Catcher
NABCEP Certified Solar PV Installer™
[https://drive.google.com/uc?id=1MQF8aTcFNnBR59ia5JAm1DsPHCxzNkPx=download]
Solar Electric Systems Sales & Service
802-272-0004


On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Search the archives, Howie.  I posted the same question this year and got a 
good response.  The documents should be available from the manufacturer.

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Hi folks,
I have a client that I'm doing a larger inverter and battery upgrade. We're are 
putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units. The client is 
wanting manufacturer certification that the equipment is "qualified solar 
electric property". I don't know that I've ever run across this type of request 
before or that I've seen manufacturers supply such documentation. Is this 
something that anyone is familiar with? Did I miss something here?
Thanks,
Howie
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-w

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-26 Thread Kristopher Schmid via RE-wrenches
New York Public Service Commission and Conformité Européene listing, Lloyd?

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Wed, Oct 26, 2022, 8:18 PM Lloyd Hoffstatter <
ll...@sunstruckconsulting.com> wrote:

> For inverters use the NYPSC list or CE for other equipment
>
> Best,
> Lloyd
>
> Get Outlook for iOS <https://aka.ms/o0ukef>
> --
> *From:* RE-wrenches  on behalf
> of Kristopher Schmid via RE-wrenches 
> *Sent:* Wednesday, October 26, 2022 9:14:28 PM
> *To:* cwar...@entech-engineering.com ;
> RE-wrenches 
> *Cc:* Kristopher Schmid 
> *Subject:* Re: [RE-wrenches] "Qualified solar electric property"?
>
> Yes, but I believe an accountant wants to know how they prove and document
> that it is "solar electric property".
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
> On Wed, Oct 26, 2022, 2:55 PM Christopher Warfel via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> I agree with Lloyd. It is qualified if listed I would have to believe.
> Chris
> On 10/21/2022 6:36 PM, Lloyd Hoffstatter via RE-wrenches wrote:
>
> Howie,
> I think he is referring to the tax language
> https://www.irs.gov/newsroom/energy-incentives-for-individuals-residential-property-updated-questions-and-answers
> Best regards,
> Lloyd
> Lloyd Hoffstatter
> Sunstruck Consulting
> Get Outlook for iOS <https://aka.ms/o0ukef>
> --
> *From:* RE-wrenches 
>  on behalf of Howie Michaelson
> via RE-wrenches 
> 
> *Sent:* Friday, October 21, 2022 6:29:31 PM
> *To:* RE-wrenches 
> 
> *Cc:* Howie Michaelson 
> 
> *Subject:* Re: [RE-wrenches] "Qualified solar electric property"?
>
> Kris,
> I found your query in the archives and Marcos follow-up question, but not
> the reply, apparently from George McClellan. I just called Sol-Ark and the
> sales person I talked with knew nothing about such a letter.  Fortress
> didn't have anything on their website and didn;'t answer their phone.
> Do you still have the email response from George?
> Thanks,
> Howie
>
> *Howie Michaelson **Sun Catcher*
>
> *NABCEP Certified Solar PV Installer™ *
>
> *Solar Electric Systems Sales & Service 802-272-0004*
>
>
> On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Search the archives, Howie.  I posted the same question this year and got
> a good response.  The documents should be available from the manufacturer.
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
> On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Hi folks,
> I have a client that I'm doing a larger inverter and battery upgrade.
> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
> The client is wanting manufacturer certification that the equipment is
> "qualified solar electric property". I don't know that I've ever run across
> this type of request before or that I've seen manufacturers supply such
> documentation. Is this something that anyone is familiar with? Did I miss
> something here?
> Thanks,
> Howie
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
>

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-26 Thread Lloyd Hoffstatter via RE-wrenches
For inverters use the NYPSC list or CE for other equipment

Best,
Lloyd

Get Outlook for iOS<https://aka.ms/o0ukef>

From: RE-wrenches  on behalf of 
Kristopher Schmid via RE-wrenches 
Sent: Wednesday, October 26, 2022 9:14:28 PM
To: cwar...@entech-engineering.com ; 
RE-wrenches 
Cc: Kristopher Schmid 
Subject: Re: [RE-wrenches] "Qualified solar electric property"?

Yes, but I believe an accountant wants to know how they prove and document that 
it is "solar electric property".

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Wed, Oct 26, 2022, 2:55 PM Christopher Warfel via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:

I agree with Lloyd. It is qualified if listed I would have to believe. Chris

On 10/21/2022 6:36 PM, Lloyd Hoffstatter via RE-wrenches wrote:
Howie,
I think he is referring to the tax language 
https://www.irs.gov/newsroom/energy-incentives-for-individuals-residential-property-updated-questions-and-answers
Best regards,
Lloyd
Lloyd Hoffstatter
Sunstruck Consulting
Get Outlook for iOS<https://aka.ms/o0ukef>

From: RE-wrenches 
<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 on behalf of Howie Michaelson via RE-wrenches 
<mailto:re-wrenches@lists.re-wrenches.org>
Sent: Friday, October 21, 2022 6:29:31 PM
To: RE-wrenches 
<mailto:re-wrenches@lists.re-wrenches.org>
Cc: Howie Michaelson 
<mailto:howie.michael...@gmail.com>
Subject: Re: [RE-wrenches] "Qualified solar electric property"?

Kris,
I found your query in the archives and Marcos follow-up question, but not the 
reply, apparently from George McClellan. I just called Sol-Ark and the sales 
person I talked with knew nothing about such a letter.  Fortress didn't have 
anything on their website and didn;'t answer their phone.
Do you still have the email response from George?
Thanks,
Howie
Howie Michaelson
Sun Catcher
NABCEP Certified Solar PV Installer™
[https://drive.google.com/uc?id=1MQF8aTcFNnBR59ia5JAm1DsPHCxzNkPx=download]
Solar Electric Systems Sales & Service
802-272-0004


On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Search the archives, Howie.  I posted the same question this year and got a 
good response.  The documents should be available from the manufacturer.

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Hi folks,
I have a client that I'm doing a larger inverter and battery upgrade. We're are 
putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units. The client is 
wanting manufacturer certification that the equipment is "qualified solar 
electric property". I don't know that I've ever run across this type of request 
before or that I've seen manufacturers supply such documentation. Is this 
something that anyone is familiar with? Did I miss something here?
Thanks,
Howie
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




___
List sponsored by Redwood Alliance

Pay optional member dues here: h

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-26 Thread Kristopher Schmid via RE-wrenches
Yes, but I believe an accountant wants to know how they prove and document
that it is "solar electric property".

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Wed, Oct 26, 2022, 2:55 PM Christopher Warfel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I agree with Lloyd. It is qualified if listed I would have to believe.
> Chris
> On 10/21/2022 6:36 PM, Lloyd Hoffstatter via RE-wrenches wrote:
>
> Howie,
> I think he is referring to the tax language
> https://www.irs.gov/newsroom/energy-incentives-for-individuals-residential-property-updated-questions-and-answers
> Best regards,
> Lloyd
> Lloyd Hoffstatter
> Sunstruck Consulting
> Get Outlook for iOS <https://aka.ms/o0ukef>
> --
> *From:* RE-wrenches 
>  on behalf of Howie Michaelson
> via RE-wrenches 
> 
> *Sent:* Friday, October 21, 2022 6:29:31 PM
> *To:* RE-wrenches 
> 
> *Cc:* Howie Michaelson 
> 
> *Subject:* Re: [RE-wrenches] "Qualified solar electric property"?
>
> Kris,
> I found your query in the archives and Marcos follow-up question, but not
> the reply, apparently from George McClellan. I just called Sol-Ark and the
> sales person I talked with knew nothing about such a letter.  Fortress
> didn't have anything on their website and didn;'t answer their phone.
> Do you still have the email response from George?
> Thanks,
> Howie
>
> *Howie Michaelson **Sun Catcher*
>
> *NABCEP Certified Solar PV Installer™ *
>
> *Solar Electric Systems Sales & Service 802-272-0004*
>
>
> On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Search the archives, Howie.  I posted the same question this year and got
> a good response.  The documents should be available from the manufacturer.
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
> On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
> Hi folks,
> I have a client that I'm doing a larger inverter and battery upgrade.
> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
> The client is wanting manufacturer certification that the equipment is
> "qualified solar electric property". I don't know that I've ever run across
> this type of request before or that I've seen manufacturers supply such
> documentation. Is this something that anyone is familiar with? Did I miss
> something here?
> Thanks,
> Howie
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-26 Thread Christopher Warfel via RE-wrenches

I agree with Lloyd. It is qualified if listed I would have to believe. Chris

On 10/21/2022 6:36 PM, Lloyd Hoffstatter via RE-wrenches wrote:

Howie,
I think he is referring to the tax language 
https://www.irs.gov/newsroom/energy-incentives-for-individuals-residential-property-updated-questions-and-answers

Best regards,
Lloyd
Lloyd Hoffstatter
Sunstruck Consulting
Get Outlook for iOS <https://aka.ms/o0ukef>

*From:* RE-wrenches  on 
behalf of Howie Michaelson via RE-wrenches 


*Sent:* Friday, October 21, 2022 6:29:31 PM
*To:* RE-wrenches 
*Cc:* Howie Michaelson 
*Subject:* Re: [RE-wrenches] "Qualified solar electric property"?
Kris,
I found your query in the archives and Marcos follow-up question, but 
not the reply, apparently from George McClellan. I just called Sol-Ark 
and the sales person I talked with knew nothing about such a letter.  
Fortress didn't have anything on their website and didn;'t answer 
their phone.

Do you still have the email response from George?
Thanks,
Howie
*Howie Michaelson
**Sun Catcher*
*/NABCEP Certified Solar PV Installer™
/**
**Solar Electric Systems Sales & Service
802-272-0004*


On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches 
 wrote:


Search the archives, Howie.  I posted the same question this year
and got a good response.  The documents should be available from
the manufacturer.

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com <http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches
 wrote:

Hi folks,
I have a client that I'm doing a larger inverter and battery
upgrade. We're are putting in 3Sol-Ark 15k inverters and 7
Fortress 18.5kwh units. The client is wanting manufacturer
certification that the equipment is "qualified solar electric
property". I don't know that I've ever run across this type of
request before or that I've seen manufacturers supply such
documentation. Is this something that anyone is familiar with?
Did I miss something here?
Thanks,
Howie
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't
work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work,
try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--
            Christopher Warfel
                 ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings

Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Lloyd Hoffstatter via RE-wrenches
Howie,
I think he is referring to the tax language 
https://www.irs.gov/newsroom/energy-incentives-for-individuals-residential-property-updated-questions-and-answers
Best regards,
Lloyd
Lloyd Hoffstatter
Sunstruck Consulting
Get Outlook for iOS<https://aka.ms/o0ukef>

From: RE-wrenches  on behalf of 
Howie Michaelson via RE-wrenches 
Sent: Friday, October 21, 2022 6:29:31 PM
To: RE-wrenches 
Cc: Howie Michaelson 
Subject: Re: [RE-wrenches] "Qualified solar electric property"?

Kris,
I found your query in the archives and Marcos follow-up question, but not the 
reply, apparently from George McClellan. I just called Sol-Ark and the sales 
person I talked with knew nothing about such a letter.  Fortress didn't have 
anything on their website and didn;'t answer their phone.
Do you still have the email response from George?
Thanks,
Howie
Howie Michaelson
Sun Catcher
NABCEP Certified Solar PV Installer™
[https://drive.google.com/uc?id=1MQF8aTcFNnBR59ia5JAm1DsPHCxzNkPx=download]
Solar Electric Systems Sales & Service
802-272-0004


On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Search the archives, Howie.  I posted the same question this year and got a 
good response.  The documents should be available from the manufacturer.

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com<http://www.legacysolar.com>
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Hi folks,
I have a client that I'm doing a larger inverter and battery upgrade. We're are 
putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units. The client is 
wanting manufacturer certification that the equipment is "qualified solar 
electric property". I don't know that I've ever run across this type of request 
before or that I've seen manufacturers supply such documentation. Is this 
something that anyone is familiar with? Did I miss something here?
Thanks,
Howie
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
Kris,
I found your query in the archives and Marcos follow-up question, but not
the reply, apparently from George McClellan. I just called Sol-Ark and the
sales person I talked with knew nothing about such a letter.  Fortress
didn't have anything on their website and didn;'t answer their phone.
Do you still have the email response from George?
Thanks,
Howie

*Howie Michaelson**Sun Catcher*

*NABCEP Certified Solar PV Installer™*

*Solar Electric Systems Sales & Service802-272-0004*


On Fri, Oct 21, 2022 at 2:32 PM Kristopher Schmid via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Search the archives, Howie.  I posted the same question this year and got
> a good response.  The documents should be available from the manufacturer.
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
> On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi folks,
>> I have a client that I'm doing a larger inverter and battery upgrade.
>> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
>> The client is wanting manufacturer certification that the equipment is
>> "qualified solar electric property". I don't know that I've ever run across
>> this type of request before or that I've seen manufacturers supply such
>> documentation. Is this something that anyone is familiar with? Did I miss
>> something here?
>> Thanks,
>> Howie
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
This is actually a corporate owned residence - a nice little tax
write-off...  Jerry, are you saying that from personal/professional
experience there is a limitation to the size  of the battery bank that a
residence can take a credit on?  I've never seen reference to anything like
that before.  Could you possibly elaborate?
Thanks,
Howie

*Howie Michaelson**Sun Catcher*

*NABCEP Certified Solar PV Installer™*

*Solar Electric Systems Sales & Service802-272-0004*


On Fri, Oct 21, 2022 at 2:46 PM Jerry Shafer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> On the system size of batteries We have had several issues with resi and
> 80kWhr limitations, I dont know if this is an issue for you or not just
> want to through it out there.
> Jerry
>
> On Fri, Oct 21, 2022 at 11:14 AM Howie Michaelson via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi folks,
>> I have a client that I'm doing a larger inverter and battery upgrade.
>> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
>> The client is wanting manufacturer certification that the equipment is
>> "qualified solar electric property". I don't know that I've ever run across
>> this type of request before or that I've seen manufacturers supply such
>> documentation. Is this something that anyone is familiar with? Did I miss
>> something here?
>> Thanks,
>> Howie
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Jerry Shafer via RE-wrenches
On the system size of batteries We have had several issues with resi and
80kWhr limitations, I dont know if this is an issue for you or not just
want to through it out there.
Jerry

On Fri, Oct 21, 2022 at 11:14 AM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi folks,
> I have a client that I'm doing a larger inverter and battery upgrade.
> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
> The client is wanting manufacturer certification that the equipment is
> "qualified solar electric property". I don't know that I've ever run across
> this type of request before or that I've seen manufacturers supply such
> documentation. Is this something that anyone is familiar with? Did I miss
> something here?
> Thanks,
> Howie
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Kristopher Schmid via RE-wrenches
Search the archives, Howie.  I posted the same question this year and got a
good response.  The documents should be available from the manufacturer.

Shine On!

Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE

On Fri, Oct 21, 2022, 1:14 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi folks,
> I have a client that I'm doing a larger inverter and battery upgrade.
> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
> The client is wanting manufacturer certification that the equipment is
> "qualified solar electric property". I don't know that I've ever run across
> this type of request before or that I've seen manufacturers supply such
> documentation. Is this something that anyone is familiar with? Did I miss
> something here?
> Thanks,
> Howie
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Brian Mehalic via RE-wrenches
I would hope that the UL certification documentation for the products
should suffice.

Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59
National Electrical Code® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Fri, Oct 21, 2022 at 12:13 PM Howie Michaelson via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi folks,
> I have a client that I'm doing a larger inverter and battery upgrade.
> We're are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units.
> The client is wanting manufacturer certification that the equipment is
> "qualified solar electric property". I don't know that I've ever run across
> this type of request before or that I've seen manufacturers supply such
> documentation. Is this something that anyone is familiar with? Did I miss
> something here?
> Thanks,
> Howie
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] "Qualified solar electric property"?

2022-10-21 Thread Howie Michaelson via RE-wrenches
Hi folks,
I have a client that I'm doing a larger inverter and battery upgrade. We're
are putting in 3Sol-Ark 15k inverters and 7 Fortress 18.5kwh units. The
client is wanting manufacturer certification that the equipment is
"qualified solar electric property". I don't know that I've ever run across
this type of request before or that I've seen manufacturers supply such
documentation. Is this something that anyone is familiar with? Did I miss
something here?
Thanks,
Howie
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org