Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Darryl Thayer
I found similar to Phil, but all the wire had thwn-2 on the spool label but not 
on the wire.  
Execpt for pink it did not have thwn-2 on the spool lable.  
 
Darryl 

--- On Fri, 7/23/10, Phil Undercuffler solarp...@gmail.com wrote:


From: Phil Undercuffler solarp...@gmail.com
Subject: Re: [RE-wrenches] #10 THWN-2
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Friday, July 23, 2010, 12:56 AM


Marco,


I found the same situation as what David mentions -- when we were doing a high 
profile job that was going to be inspected by a certain someone from Las 
Cruces, all the wire available from local suppliers was only physically marked 
as THHN / THWN, but when we dug a little deeper and found the actual spec 
sheets from the manufacturer we were able to determine that the wire actually 
was rated as THWN-2 (plus a whole alphabet soup worth of additional listings), 
although it wasn't marked as such.  Have the vendor pull up the spec sheet on 
the wire brands they typically carry, and keep a couple copies in your for the 
inspector file.


Phil Undercuffler





On Thu, Jul 22, 2010 at 7:33 PM, David Brearley 
david.brear...@solarprofessional.com wrote:


Marco,

The #10 THWN wire that your local suppliers carry may be cross-listed as 
THWN-2. My understanding is that it is not uncommon for smaller gauge wire to 
carry more listings than are printed on its insulation. (If that’s not true, 
we’ll find out shortly from someone on the list.) If your local supplier can’t 
confirm this cross-listing for you, I’d try tracing back to ask their supplier 
or the manufacturer.  

David Brearley, Senior Technical Editor
SolarPro magazine 




On 7/23/10 12:52 AM, Marco Mangelsdorf ma...@pvthawaii.com wrote:





Finding that wire in these here parts is pretty much impossible.
 
Can any of my CA. brethren/sistren provide me any leads on wholesalers in 
either northern or southern CA. that carry #10 THWN-2 wire?
 
Thanks,
marco
 






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




-Inline Attachment Follows-


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] #10 THWN-2

2010-07-23 Thread Peter Parrish
We went through a similar problem with some beach communities here in SoCal.
Because of the high humidity (all winter and summer mornings) they wanted
THWN-2 for all conduit runs (as well as PVC instead of EMT). At first we
were charged a premium for THWN-2 compared to THHN. But then we found a
source at All Phase Electrical Supply Burbank CA (a part of CED) for THWN-2
#10 stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing is
printed on the insulation.
 
- Peter
 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Nick Soleil
I have specified THWN-2 for years, but occasionally will not be able to source 
it!

Sent from my iPhone

On Jul 23, 2010, at 11:37 AM, Peter Parrish peter.parr...@calsolareng.com 
wrote:

 We went through a similar problem with some beach communities here in SoCal. 
 Because of the high humidity (all winter and summer mornings) they wanted 
 THWN-2 for all conduit runs (as well as PVC instead of EMT). At first we were 
 charged a premium for THWN-2 compared to THHN. But then we found a source at 
 All Phase Electrical Supply Burbank CA (a part of CED) for THWN-2 #10 
 stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing is printed 
 on the insulation.
  
 - Peter
  
 Peter T. Parrish, Ph.D., President
 California Solar Engineering, Inc.
 820 Cynthia Ave., Los Angeles, CA 90065
 CA Lic. 854779, NABCEP Cert. 031806-26
 peter.parr...@calsolareng.com  
 Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

  
 
  
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Mick Abraham
I'm sorry to broadcast my ignorance, but:

Could someone explain to me the significance of the -2 marking? Reply
off-list if you wish to save bandwidth...but other List members may also be
wondering...

Thanks,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675


On Fri, Jul 23, 2010 at 10:48 AM, Nick Soleil nicksoleilso...@yahoo.comwrote:

 I have specified THWN-2 for years, but occasionally will not be able to
 source it!

 Sent from my iPhone

 On Jul 23, 2010, at 11:37 AM, Peter Parrish 
 peter.parr...@calsolareng.com wrote:

  We went through a similar problem with some beach communities here in
 SoCal. Because of the high humidity (all winter and summer mornings) they
 wanted THWN-2 for all conduit runs (as well as PVC instead of EMT). At first
 we were charged a premium for THWN-2 compared to THHN. But then we found a
 source at All Phase Electrical Supply Burbank CA (a part of CED) for THWN-2
 #10 stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing is
 printed on the insulation.



 - Peter



 Peter T. Parrish, Ph.D., President
 California Solar Engineering, Inc.
 820 Cynthia Ave., Los Angeles, CA 90065
 CA Lic. 854779, NABCEP Cert. 031806-26
  peter.parr...@calsolareng.competer.parr...@calsolareng.com
 Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885






 ___

 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org
 RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org


 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Mark Westbrock
-2 indicates that the insulation is rated for hot  wet; that is that 
it is rated for 90C and wet conditions.  See NEC  Table 310.13(A).


We also use Encore Wire.  The sticker on the spool has THHN in big 
print, but then in small print below it says Type MTW or THHN or 
THWN-2.  The insulation also says Type MTW or THHN or THWN-2.


Mark

Mark Westbrock
NABCEP Certified Solar PV Installer
NM ER-1J Journeyman Electrician
Positive Energy, Inc.
office: 575-524-2030
cell: 575-640-2432
westbr...@positiveenergysolar.com
www.positiveenergysolar.com



Mick Abraham wrote:

I'm sorry to broadcast my ignorance, but:

Could someone explain to me the significance of the -2 marking? Reply 
off-list if you wish to save bandwidth...but other List members may 
also be wondering... 

Thanks, 


Mick Abraham, Proprietor
www.abrahamsolar.com http://www.abrahamsolar.com

Voice: 970-731-4675


On Fri, Jul 23, 2010 at 10:48 AM, Nick Soleil 
nicksoleilso...@yahoo.com mailto:nicksoleilso...@yahoo.com wrote:


I have specified THWN-2 for years, but occasionally will not be
able to source it!

Sent from my iPhone

On Jul 23, 2010, at 11:37 AM, Peter Parrish
peter.parr...@calsolareng.com
mailto:peter.parr...@calsolareng.com wrote:


We went through a similar problem with some beach communities
here in SoCal. Because of the high humidity (all winter and
summer mornings) they wanted THWN-2 for all conduit runs (as well
as PVC instead of EMT). At first we were charged a premium for
THWN-2 compared to THHN. But then we found a source at All Phase
Electrical Supply Burbank CA (a part of CED) for THWN-2 #10
stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing
is printed on the insulation.

 


- Peter

 


Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com
mailto:peter.parr...@calsolareng.com 
Ph 323-258-8883, Mobile 323-839-6108, Fax
323-258-8885  


 

 


___

List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org
mailto:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm
http://www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org http://www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread David Brearley
Mick,

THWN-2 is 90°C rated per Table 310.16. This is key for conductors in conduit
on a roof. On a roof in full sun ambient temperatures are such that a 75°C
rated conductor will have a severely diminished allowable ampacity, if any
allowable ampacity.

Jollily,

David


On 7/23/10 11:52 AM, Mick Abraham m...@abrahamsolar.com wrote:

 I'm sorry to broadcast my ignorance, but:
 
 Could someone explain to me the significance of the -2 marking? Reply off-list
 if you wish to save bandwidth...but other List members may also be
 wondering... 
 
 Thanks, 
 
 Mick Abraham, Proprietor
 www.abrahamsolar.com http://www.abrahamsolar.com
 
 Voice: 970-731-4675
 
 
 On Fri, Jul 23, 2010 at 10:48 AM, Nick Soleil nicksoleilso...@yahoo.com
 wrote:
 I have specified THWN-2 for years, but occasionally will not be able to
 source it!
 
 Sent from my iPhone
 
 On Jul 23, 2010, at 11:37 AM, Peter Parrish peter.parr...@calsolareng.com
 wrote:
 
 We went through a similar problem with some beach communities here in SoCal.
 Because of the high humidity (all winter and summer mornings) they wanted
 THWN-2 for all conduit runs (as well as PVC instead of EMT). At first we
 were charged a premium for THWN-2 compared to THHN. But then we found a
 source at All Phase Electrical Supply Burbank CA (a part of CED) for THWN-2
 #10 stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing is
 printed on the insulation.
  
 - Peter
  
 
 Peter T. Parrish, Ph.D., President
 California Solar Engineering, Inc.
 820 Cynthia Ave., Los Angeles, CA 90065
 CA Lic. 854779, NABCEP Cert. 031806-26
  mailto:peter.parr...@calsolareng.com peter.parr...@calsolareng.com 
 Ph 323-258-8883, Mobile 323-839-6108, Fax
 323-258-8885  
 
  
 
  
 ___
 
 List sponsored by Home Power magazine
 
 List Address:  mailto:RE-wrenches@lists.re-wrenches.org
 RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive:  
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm http://www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org http://www.members.re-wrenches.org
 
 
 ___

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Peter Parrish
The dash-two, as an appendage to THWN indicates that the wire, normally
rated for dry and wet locations and 75 deg C, is now rated dry/wet up to 90
deg C.

- Peter


Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mick Abraham
Sent: Friday, July 23, 2010 9:52 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] #10 THWN-2

I'm sorry to broadcast my ignorance, but:

Could someone explain to me the significance of the -2 marking? Reply
off-list if you wish to save bandwidth...but other List members may also be
wondering... 

Thanks, 

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675

On Fri, Jul 23, 2010 at 10:48 AM, Nick Soleil nicksoleilso...@yahoo.com
wrote:
I have specified THWN-2 for years, but occasionally will not be able to
source it!

Sent from my iPhone

On Jul 23, 2010, at 11:37 AM, Peter Parrish
peter.parr...@calsolareng.com wrote:
We went through a similar problem with some beach communities here in SoCal.
Because of the high humidity (all winter and summer mornings) they wanted
THWN-2 for all conduit runs (as well as PVC instead of EMT). At first we
were charged a premium for THWN-2 compared to THHN. But then we found a
source at All Phase Electrical Supply Burbank CA (a part of CED) for THWN-2
#10 stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing is
printed on the insulation.
 
- Peter
 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax
323-258-8885  

 
 
___

List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Allan Sindelar


  
  
Mick,
-2 means 90 degrees C rather than 75. THWN-2 thus means that it is
wet-rated at 90C. That is generally considered Code for arrays,
such as if it is run in NM flex conduit to a traditional module
j-box. The j-box area may be considered to be able to get hot enough
to require 90C rated wire. Nowadays with MC-type module leads,
combiner boxes aren't subject to the same high temperatures on the
THWN as when they terminate in module j-boxes, and the higher
temperature rating isn't generally necessary.

Much of what I'm saying here is older John Wiles stuff.
Allan


  
  
  
  
  
  
  
  
Allan Sindelar
Allan@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
  


On 7/23/2010 10:52 AM, Mick Abraham wrote:

I'm sorry to broadcast my ignorance, but:


Could someone explain to me the significance of the -2
  marking? Reply off-list if you wish to save bandwidth...but
  other List members may also be wondering...


Thanks,


  Mick Abraham, Proprietor
  www.abrahamsolar.com
  
  Voice: 970-731-4675
  
  
  On Fri, Jul 23, 2010 at 10:48 AM, Nick
Soleil nicksoleilso...@yahoo.com
wrote:

  
I have specified THWN-2 for years, but occasionally
  will not be able to source it!
  
  Sent from my iPhone

  

  On Jul 23, 2010, at 11:37 AM, "Peter Parrish" peter.parr...@calsolareng.com
  wrote:
  


  

  We
went through a similar problem with
some beach communities here in SoCal.
Because of the high humidity (all winter
and summer mornings) they wanted THWN-2 for
all conduit runs (as well as PVC
instead of EMT). At first we were charged a
premium for THWN-2 compared to
THHN. But then we found a source at All
Phase Electrical Supply Burbank CA (a part
of CED) for THWN-2 #10 stranded @
$162.40/k-ft. Brand is En(m?)core
Wire. THWN-2 listing is printed on the
insulation.
  
  -
Peter
  
  
Peter T. Parrish,
  Ph.D., President
  California
  Solar Engineering, Inc.
  820 Cynthia Ave., Los Angeles, CA 90065
  CA Lic. 854779, NABCEP Cert. 031806-26
  peter.parr...@calsolareng.com
  
  Ph 323-258-8883, Mobile
  323-839-6108, Fax 323-258-8885
  

  
  

  

  


  ___

  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm
  
  Check out participant bios:
  www.members.re-wrenches.org
  

  

  
  
  ___
  List sponsored by Home Power magazine
  
  List Address: RE-wrenches@lists.re-wrenches.org
  
  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
  
  List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
  
  List rules  etiquette:
  

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Peter Parrish
Just a minor point: the dash-two appendage brings a wet-rated wire from 75
deg C to 90 deg C. 

If you are not in a locale that argues for wet-rated wire and your specific
application does not argue for wet-rated wire, IMHO it is perfectly
acceptable to use THHN wire (90 deg C rated for damp environments) for
outdoors, attics and other extreme temperature conditions. Of course you
have to use good 3R boxes and rain-tight EMT connectors.

For us, it is easier to purchase and inventory just one wire type for
conduit runs, and we usually get the same price for THWN-2 as we do for
THHN, or close enough. In fact we almost never use #12 either for the same
reason.
 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Friday, July 23, 2010 10:04 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] #10 THWN-2

Mick,
-2 means 90 degrees C rather than 75. THWN-2 thus means that it is wet-rated
at 90C.  That is generally considered Code for arrays, such as if it is run
in NM flex conduit to a traditional module j-box. The j-box area may be
considered to be able to get hot enough to require 90C rated wire. Nowadays
with MC-type module leads, combiner boxes aren't subject to the same high
temperatures on the THWN as when they terminate in module j-boxes, and the
higher temperature rating isn't generally necessary.

Much of what I'm saying here is older John Wiles stuff.
Allan
 
Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com

On 7/23/2010 10:52 AM, Mick Abraham wrote: 
I'm sorry to broadcast my ignorance, but:

Could someone explain to me the significance of the -2 marking? Reply
off-list if you wish to save bandwidth...but other List members may also be
wondering... 

Thanks, 

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675

On Fri, Jul 23, 2010 at 10:48 AM, Nick Soleil nicksoleilso...@yahoo.com
wrote:
I have specified THWN-2 for years, but occasionally will not be able to
source it!

Sent from my iPhone

On Jul 23, 2010, at 11:37 AM, Peter Parrish
peter.parr...@calsolareng.com wrote:
We went through a similar problem with some beach communities here in SoCal.
Because of the high humidity (all winter and summer mornings) they wanted
THWN-2 for all conduit runs (as well as PVC instead of EMT). At first we
were charged a premium for THWN-2 compared to THHN. But then we found a
source at All Phase Electrical Supply Burbank CA (a part of CED) for THWN-2
#10 stranded @ $162.40/k-ft. Brand is En(m?)core Wire. THWN-2 listing is
printed on the insulation.
 
- Peter
 
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parr...@calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax
323-258-8885  

 
 
___ 

List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org





___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re

Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Ryan Mayfield
Peter,

There was a change in the 2008 NEC (I know - CA is just getting to this Code
cycle) that won't allow THHN inside conduit when the conduit is installed in
wet locations, 300.9 (300.5 for underground):

300.9 Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the interior of
these raceways shall be considered to be a wet location. Insulated
conductors and cables installed in raceways in wet locations abovegrade
shall comply with 310.8(C).

And 310.8(C):

(C) Wet Locations. Insulated conductors and cables used in wet locations
shall comply with one of the following: 
(1) Be moisture-impervious metal-sheathed 
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2, THHW, THWN, THWN-2, XHHW,
XHHW-2, ZW 
(3) Be of a type listed for use in wet locations


So for an attic run, it wouldn't be considered a wet location but for the
outdoor runs it would be. And since so many runs will be exposed to both
types of locations, it only makes sense to me to keep it all THWN-2. I like
your position of only stocking one wire type to reduce the possibility of
confusion in the field.

Ryan




-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Peter
Parrish
Sent: Friday, July 23, 2010 11:28 AM
To: al...@positiveenergysolar.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] #10 THWN-2

Just a minor point: the dash-two appendage brings a wet-rated wire from 75
deg C to 90 deg C. 

If you are not in a locale that argues for wet-rated wire and your specific
application does not argue for wet-rated wire, IMHO it is perfectly
acceptable to use THHN wire (90 deg C rated for damp environments) for
outdoors, attics and other extreme temperature conditions. Of course you
have to use good 3R boxes and rain-tight EMT connectors.

For us, it is easier to purchase and inventory just one wire type for
conduit runs, and we usually get the same price for THWN-2 as we do for
THHN, or close enough. In fact we almost never use #12 either for the same
reason.
 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-23 Thread Kirk Herander, VSE
Dual rated thhn / thwn complies.  And every reel I've ever bought is dual
rated. I've never seen single-rated thhn.

Kirk Herander
Vermont Solar Engineering
802.863.1202
NABCEP(tm) Certified Solar Installer
NYSERDA-eligible Installer
VT Solar Incentive Program Partner

-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ryan
Mayfield
Sent: Friday, July 23, 2010 3:31 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] #10 THWN-2

Peter,

There was a change in the 2008 NEC (I know - CA is just getting to this Code
cycle) that won't allow THHN inside conduit when the conduit is installed in
wet locations, 300.9 (300.5 for underground):

300.9 Raceways in Wet Locations Above Grade.
Where raceways are installed in wet locations abovegrade, the interior of
these raceways shall be considered to be a wet location. Insulated
conductors and cables installed in raceways in wet locations abovegrade
shall comply with 310.8(C).

And 310.8(C):

(C) Wet Locations. Insulated conductors and cables used in wet locations
shall comply with one of the following: 
(1) Be moisture-impervious metal-sheathed 
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2, THHW, THWN, THWN-2, XHHW,
XHHW-2, ZW 
(3) Be of a type listed for use in wet locations


So for an attic run, it wouldn't be considered a wet location but for the
outdoor runs it would be. And since so many runs will be exposed to both
types of locations, it only makes sense to me to keep it all THWN-2. I like
your position of only stocking one wire type to reduce the possibility of
confusion in the field.

Ryan




-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Peter
Parrish
Sent: Friday, July 23, 2010 11:28 AM
To: al...@positiveenergysolar.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] #10 THWN-2

Just a minor point: the dash-two appendage brings a wet-rated wire from 75
deg C to 90 deg C. 

If you are not in a locale that argues for wet-rated wire and your specific
application does not argue for wet-rated wire, IMHO it is perfectly
acceptable to use THHN wire (90 deg C rated for damp environments) for
outdoors, attics and other extreme temperature conditions. Of course you
have to use good 3R boxes and rain-tight EMT connectors.

For us, it is easier to purchase and inventory just one wire type for
conduit runs, and we usually get the same price for THWN-2 as we do for
THHN, or close enough. In fact we almost never use #12 either for the same
reason.
 

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] #10 THWN-2

2010-07-23 Thread Marco Mangelsdorf
I've been looking hard to see what manufacturers produce this kinda elusive
#10 THHN/THWN-2 wire.

United Copper Industries (Texas) does.  I have a handy spec sheet from them
that I can email anyone who's interested.

marco


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



[RE-wrenches] #10 THWN-2

2010-07-22 Thread Marco Mangelsdorf
Finding that wire in these here parts is pretty much impossible.

 

Can any of my CA. brethren/sistren provide me any leads on wholesalers in
either northern or southern CA. that carry #10 THWN-2 wire?

 

Thanks,

marco

 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-22 Thread David Brearley
Marco,

The #10 THWN wire that your local suppliers carry may be cross-listed as
THWN-2. My understanding is that it is not uncommon for smaller gauge wire
to carry more listings than are printed on its insulation. (If that¹s not
true, we¹ll find out shortly from someone on the list.) If your local
supplier can¹t confirm this cross-listing for you, I¹d try tracing back to
ask their supplier or the manufacturer.

David Brearley, Senior Technical Editor
SolarPro magazine 

On 7/23/10 12:52 AM, Marco Mangelsdorf ma...@pvthawaii.com wrote:

 Finding that wire in these here parts is pretty much impossible.
  
 Can any of my CA. brethren/sistren provide me any leads on wholesalers in
 either northern or southern CA. that carry #10 THWN-2 wire?
  
 Thanks,
 marco
  
 
 



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-22 Thread Dave Click
THWN-2 smaller than #8 is hard to find but I hear 
http://www.encorewire.com/site_flash/index.html makes it and that 
Graybar sells it. When I asked Southwire about it about two years ago, I 
got a collective huh?


 Original Message 
Subject: Re: [RE-wrenches] #10 THWN-2
From: David Brearley david.brear...@solarprofessional.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: 2010/7/22 21:33


Marco,

The #10 THWN wire that your local suppliers carry may be cross-listed as
THWN-2. My understanding is that it is not uncommon for smaller gauge
wire to carry more listings than are printed on its insulation. (If
that’s not true, we’ll find out shortly from someone on the list.) If
your local supplier can’t confirm this cross-listing for you, I’d try
tracing back to ask their supplier or the manufacturer.

David Brearley, Senior Technical Editor
/SolarPro/ magazine

On 7/23/10 12:52 AM, Marco Mangelsdorf ma...@pvthawaii.com wrote:

Finding that wire in these here parts is pretty much impossible.

Can any of my CA. brethren/sistren provide me any leads on
wholesalers in either northern or southern CA. that carry #10 THWN-2
wire?

Thanks,
marco








___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] #10 THWN-2

2010-07-22 Thread Phil Undercuffler
Marco,

I found the same situation as what David mentions -- when we were doing a
high profile job that was going to be inspected by a certain someone from
Las Cruces, all the wire available from local suppliers was only physically
marked as THHN / THWN, but when we dug a little deeper and found the actual
spec sheets from the manufacturer we were able to determine that the wire
actually was rated as THWN-2 (plus a whole alphabet soup worth of additional
listings), although it wasn't marked as such.  Have the vendor pull up the
spec sheet on the wire brands they typically carry, and keep a couple copies
in your for the inspector file.

Phil Undercuffler



On Thu, Jul 22, 2010 at 7:33 PM, David Brearley 
david.brear...@solarprofessional.com wrote:

  Marco,

 The #10 THWN wire that your local suppliers carry may be cross-listed as
 THWN-2. My understanding is that it is not uncommon for smaller gauge wire
 to carry more listings than are printed on its insulation. (If that’s not
 true, we’ll find out shortly from someone on the list.) If your local
 supplier can’t confirm this cross-listing for you, I’d try tracing back to
 ask their supplier or the manufacturer.

 David Brearley, Senior Technical Editor
 *SolarPro* magazine

 On 7/23/10 12:52 AM, Marco Mangelsdorf ma...@pvthawaii.com wrote:

 Finding that wire in these here parts is pretty much impossible.

 Can any of my CA. brethren/sistren provide me any leads on wholesalers in
 either northern or southern CA. that carry #10 THWN-2 wire?

 Thanks,
 marco


 --




 ___
 List sponsored by Home Power magazine

 List Address: RE-wrenches@lists.re-wrenches.org

 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out participant bios:
 www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org