Ray:

I believe either a MPPT or PWM charge controller will work.
I say I believe because IndOp is new and we actually designed it to work with 
MPPT inverters.
It should work with PWM as well but I have only tried it with one PWM charge 
controller (Morningstar) and that worked fine.
Until we get some experience out there I don't want to over promise but in 
theory it should be fine.

Another option is to use IndOp connected directly to the battery and a separate 
diversion regulator.
Since failure of a diversion regulator can create serious problems some backup 
is highly recommended (also required by NEC).

Best Regards,

John Berdner
General Manager, North America

[cid:image001.jpg@01CDFAC6.C81684C0]

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters
Sent: Thursday, January 24, 2013 2:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 24V Module Query

Hi John;

Would we not need an MPPT controller, just a regular PWM type, then?  That 
might be a solution for these democracy arrays.

Ray

On 1/24/2013 3:16 PM, John Berdner wrote:
Alan:

You can also use one of our Optimizers with IndOp.
This will buck of boost the module voltage to match the battery voltage.
Still would need some form of charge control to protect the battery but this 
would provide an easy way to add new 60 cell modules to an existing 72 cell 
array.
Feel free to contact me if you have any questions.

Best Regards,

John Berdner
General Manager, North America

[cid:image001.jpg@01CDFAC6.C81684C0]

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: 
re-wrenches-boun...@lists.re-wrenches.orgmailto:re-wrenches-boun...@lists.re-wrenches.org
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Thursday, January 24, 2013 11:35 AM
To: RE-wrenches
Subject: [RE-wrenches] 24V Module Query

Wrenches,
We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
battery-based customers. Most of our systems are 24V or 48V nominal. Over the 
last few years, sources of conventionally-sized 72-cell modules have dried up - 
as cells have increased in size, most modules and most newer factory production 
lines have either gone to 60-cell (20V) modules, or 72 cells in 300+ watt 
ranges. It seems that the formerly common 72 cell, 24V modules in the 150-190 
watt range, which are well-suited to integrating into existing systems, are no 
longer available.

60-cell modules in the common 220-250 watt range can't be added to an existing 
system unless run through a dedicated MPPT charge controller that can convert 
voltage, such as an FM, XW60, Classic or TriStar; the added cost of any of 
these controllers cancels out the low prices of the modules.

Who continues to manufacture 72-cell modules? Which distributors carry them?
I am aware of three options - are there more?
- Sunpower makes one module in the 245 watt range that can be used negative 
ground, but it's very high efficiency (and with high Voc/Vmp as well) and very 
pricey;
- Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
pricey;
- Ameresco bought the rights to manufacture many former BP modules, and I 
think they make some. But we had to replace lots of failed BP modules in that 
size range, and are hesitant to use their technology, fearing that the problems 
may persist in the continued line.

Thank you for any discussion and recommendations.
Allan
--
Allan Sindelar
al...@positiveenergysolar.commailto:al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.comhttp://www.positiveenergysolar.com/


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P  Please think of the environment before printing this email




___

List sponsored by Home Power magazine



List Address: 
RE-wrenches@lists.re

[RE-wrenches] 24V Module Query

2013-01-24 Thread Allan Sindelar

  
  
Wrenches,
We have years of installing 36-cell (12V) and 72-cell (24V) modules
for battery-based customers. Most of our systems are 24V or 48V
nominal. Over the last few years, sources of conventionally-sized
72-cell modules have dried up - as cells have increased in size,
most modules and most newer factory production lines have either
gone to 60-cell (20V) modules, or 72 cells in 300+ watt ranges. It
seems that the formerly common 72 cell, 24V modules in the 150-190
watt range, which are well-suited to integrating into existing
systems, are no longer available.

60-cell modules in the common 220-250 watt range can't be added to
an existing system unless run through a dedicated MPPT charge
controller that can convert voltage, such as an FM, XW60, Classic or
TriStar; the added cost of any of these controllers cancels out the
low prices of the modules.

Who continues to manufacture 72-cell modules? Which distributors
carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be
used negative ground, but it's very high efficiency (and with high
Voc/Vmp as well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite
premium and pricey;
 - Ameresco bought the rights to manufacture many former BP
modules, and I think they make some. But we had to replace lots of
failed BP modules in that size range, and are hesitant to use their
technology, fearing that the problems may persist in the continued
line.

Thank you for any discussion and recommendations.
Allan
-- 
  
  
  Allan Sindelar
  al...@positiveenergysolar.com
NABCEP Certified Photovoltaic
  Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc.
  3209 Richards Lane (note new address)
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com
  
  
  
   
  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Ray Walters

Hi Allan;

I've been in the same conundrum lately.  I found that AEE and others 
have 12 v modules (Solartech), but the price per watt is double or 
triple.  My take is that somewhere around 200 to 400 watts, its more 
cost effective to go to the GT modules with an MPPT controller.  Blue 
Sky makes the 1524, and 3024 that can take up to 57 Voc, so those would 
work at still fairly low cost. Unfortunately many of the other low cost 
MPPT controllers won't work with the 60 cell modules.  At some point, it 
may actually be cost effective to just use 60 cell modules with non MPPT 
controllers, and just forget about the extra 24 cells.  (I know that 
sounds crazy, but PV less than $1/ watt is crazy too)


I'm trying to add modules to an existing array of 8 Siemens 12 v 
modules, and it just doesn't work out, except with separate controllers.
Also, its amazing how much PV you can throw at an off grid project these 
days for $10k.

It almost makes messing around with the old modules a waste of time.
Perhaps the solution might be to remove old arrays for customers wanting 
to really up size, and then reuse the old modules for small systems?


Ray

On 1/24/2013 12:35 PM, Allan Sindelar wrote:

Wrenches,
We have years of installing 36-cell (12V) and 72-cell (24V) modules 
for battery-based customers. Most of our systems are 24V or 48V 
nominal. Over the last few years, sources of conventionally-sized 
72-cell modules have dried up - as cells have increased in size, most 
modules and most newer factory production lines have either gone to 
60-cell (20V) modules, or 72 cells in 300+ watt ranges. It seems that 
the formerly common 72 cell, 24V modules in the 150-190 watt range, 
which are well-suited to integrating into existing systems, are no 
longer available.


60-cell modules in the common 220-250 watt range can't be added to an 
existing system unless run through a dedicated MPPT charge controller 
that can convert voltage, such as an FM, XW60, Classic or TriStar; the 
added cost of any of these controllers cancels out the low prices of 
the modules.


Who continues to manufacture 72-cell modules? Which distributors carry 
them?

I am aware of three options - are there more?
- Sunpower makes one module in the 245 watt range that can be used 
negative ground, but it's very high efficiency (and with high Voc/Vmp 
as well) and very pricey;
- Sanyo/Panasonic has 225-240 watt modules, but also quite premium 
and pricey;
- Ameresco bought the rights to manufacture many former BP 
modules, and I think they make some. But we had to replace lots of 
failed BP modules in that size range, and are hesitant to use their 
technology, fearing that the problems may persist in the continued line.


Thank you for any discussion and recommendations.
Allan
--
*Allan Sindelar*
_Allan@positiveenergysolar.com_ mailto:al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
_www.positiveenergysolar.com_ http://www.positiveenergysolar.com/

*
*




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Jay Peltz
Hi guys

I've buying the new 6 cell x 72 cell from Trina from a few suppliers. 
Big yea, but same 44voc  so it's an easy add to existing systems. 

A huge relief. 

Jay

Peltz power

Sent from my iPhone

On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com wrote:

 Hi Allan;
 
 I've been in the same conundrum lately.  I found that AEE and others have 12 
 v modules (Solartech), but the price per watt is double or triple.  My take 
 is that somewhere around 200 to 400 watts, its more cost effective to go to 
 the GT modules with an MPPT controller.  Blue Sky makes the 1524, and 3024 
 that can take up to 57 Voc, so those would work at still fairly low cost.  
 Unfortunately many of the other low cost MPPT controllers won't work with the 
 60 cell modules.  At some point, it may actually be cost effective to just 
 use 60 cell modules with non MPPT controllers, and just forget about the 
 extra 24 cells.  (I know that sounds crazy, but PV less than $1/ watt is 
 crazy too)
 
 I'm trying to add modules to an existing array of 8 Siemens 12 v modules, and 
 it just doesn't work out, except with separate controllers. 
 Also, its amazing how much PV you can throw at an off grid project these days 
 for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting to 
 really up size, and then reuse the old modules for small systems?
 
 Ray
 
 On 1/24/2013 12:35 PM, Allan Sindelar wrote:
 Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
 battery-based customers. Most of our systems are 24V or 48V nominal. Over 
 the last few years, sources of conventionally-sized 72-cell modules have 
 dried up - as cells have increased in size, most modules and most newer 
 factory production lines have either gone to 60-cell (20V) modules, or 72 
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V 
 modules in the 150-190 watt range, which are well-suited to integrating into 
 existing systems, are no longer available.
 
 60-cell modules in the common 220-250 watt range can't be added to an 
 existing system unless run through a dedicated MPPT charge controller that 
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added cost 
 of any of these controllers cancels out the low prices of the modules.
 
 Who continues to manufacture 72-cell modules? Which distributors carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used 
 negative ground, but it's very high efficiency (and with high Voc/Vmp as 
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
 pricey;
 - Ameresco bought the rights to manufacture many former BP modules, and 
 I think they make some. But we had to replace lots of failed BP modules in 
 that size range, and are hesitant to use their technology, fearing that the 
 problems may persist in the continued line.
 
 Thank you for any discussion and recommendations.
 Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Jason Szumlanski
I totally agree - old mods are usually not worth messing with at today's PV
prices. In some cases it might be best to downsize the system and then AC
couple some microinverters to cover the decrease in performance, or just
replace the entire array if there are enough problems. There is a used
market for smaller PV mods on Craigslist.

Back when I was installing Astropower 110W modules on single voltage
Xantrex C40's, I never thought we'd be using anything but 12V nominal PV
mods. Little did I know... Off-grid is really tough in these retrofit
situations, but this applies to failed/broken mods on grid-tie systems as
well. That's where I can make a good case for microinverters.

*Jason Szumlanski** *

* Fafco Solar
*


On Thu, Jan 24, 2013 at 3:11 PM, Ray Walters r...@solarray.com wrote:

  Hi Allan;

 I've been in the same conundrum lately.  I found that AEE and others have
 12 v modules (Solartech), but the price per watt is double or triple.  My
 take is that somewhere around 200 to 400 watts, its more cost effective to
 go to the GT modules with an MPPT controller.  Blue Sky makes the 1524, and
 3024 that can take up to 57 Voc, so those would work at still fairly low
 cost.  Unfortunately many of the other low cost MPPT controllers won't work
 with the 60 cell modules.  At some point, it may actually be cost effective
 to just use 60 cell modules with non MPPT controllers, and just forget
 about the extra 24 cells.  (I know that sounds crazy, but PV less than $1/
 watt is crazy too)

 I'm trying to add modules to an existing array of 8 Siemens 12 v modules,
 and it just doesn't work out, except with separate controllers.
 Also, its amazing how much PV you can throw at an off grid project these
 days for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting
 to really up size, and then reuse the old modules for small systems?

 Ray


 On 1/24/2013 12:35 PM, Allan Sindelar wrote:

 Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for
 battery-based customers. Most of our systems are 24V or 48V nominal. Over
 the last few years, sources of conventionally-sized 72-cell modules have
 dried up - as cells have increased in size, most modules and most newer
 factory production lines have either gone to 60-cell (20V) modules, or 72
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V
 modules in the 150-190 watt range, which are well-suited to integrating
 into existing systems, are no longer available.

 60-cell modules in the common 220-250 watt range can't be added to an
 existing system unless run through a dedicated MPPT charge controller that
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added
 cost of any of these controllers cancels out the low prices of the modules.

 Who continues to manufacture 72-cell modules? Which distributors carry
 them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used
 negative ground, but it's very high efficiency (and with high Voc/Vmp as
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and
 pricey;
 - Ameresco bought the rights to manufacture many former BP modules,
 and I think they make some. But we had to replace lots of failed BP modules
 in that size range, and are hesitant to use their technology, fearing that
 the problems may persist in the continued line.

 Thank you for any discussion and recommendations.
 Allan
 --
 *Allan Sindelar*
 *al...@positiveenergysolar.com* al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 *Positive Energy, Inc.*
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 *505 424-1112*
 *www.positiveenergysolar.com* http://www.positiveenergysolar.com/

 *
 *



___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Allan Sindelar

  
  
Jason,
  How do you AC couple some microinverters to cover the decrease in
  performance in an off grid system, especially with older
  equipment, such as an SW4024?
  Thanks, Allan
  
  


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



 
  On 1/24/2013 1:38 PM, Jason Szumlanski wrote:


  I totally agree - old mods are usually not worth
messing with at today's PV prices. In some cases it might be
best to downsize the system and then AC couple some
microinverters to cover the decrease in performance, or just
replace the entire array if there are enough problems. There is
a used market for smaller PV mods on Craigslist.

  

Back when I was installing Astropower 110W modules on
  single voltage Xantrex C40's, I never thought we'd be using
  anything but 12V nominal PV mods. Little did I know...
  Off-grid is really tough in these retrofit situations, but
  this applies to failed/broken mods on grid-tie systems as
  well. That's where I can make a good case for microinverters.
  


  

  Jason
Szumlanski
  
Fafco Solar
  
  

  


  
  On Thu, Jan 24, 2013 at 3:11 PM,
Ray Walters r...@solarray.com
wrote:

  
Hi Allan;
  
  I've been in the same conundrum lately. I found
  that AEE and others have 12 v modules (Solartech),
  but the price per watt is double or triple. My
  take is that somewhere around 200 to 400 watts,
  its more cost effective to go to the GT modules
  with an MPPT controller. Blue Sky makes the 1524,
  and 3024 that can take up to 57 Voc, so those
  would work at still fairly low cost.
  Unfortunately many of the other low cost MPPT
  controllers won't work with the 60 cell modules.
  At some point, it may actually be cost effective
  to just use 60 cell modules with non MPPT
  controllers, and just forget about the extra 24
  cells. (I know that sounds crazy, but PV less
  than $1/ watt is crazy too)
  
  I'm trying to add modules to an existing array of
  8 Siemens 12 v modules, and it just doesn't work
  out, except with separate controllers. 
  Also, its amazing how much PV you can throw at an
  off grid project these days for $10k.
  It almost makes messing around with the old
  modules a waste of time.
  Perhaps the solution might be to remove old arrays
  for customers wanting to really up size, and then
  reuse the old modules for small systems?
  
  Ray
  

  
  On 1/24/2013 12:35 PM, Allan Sindelar wrote:

  


  
 Wrenches,
  We have years of installing 36-cell (12V) and
  72-cell (24V) modules for battery-based
  customers. Most of our systems are 24V or 48V
  nominal. Over the last few years, sources of
  conventionally-sized 72-cell modules have
  dried up - as cells have increased in size,
  most modules and most newer factory production
  lines have either gone to 60-cell (20V)
  modules, or 72 cells in 300+ watt ranges. It
  seems that the formerly common 72 cell, 24V
  modules in the 150-190 watt range, which are
  well-suited to integrating into 

Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread All Solar, Inc.
Suntech 295's...  Biggin!
Thats about it!
We did get some 72 cell mods from  Oasis Montana (dealer)

We are in the same boat. 14 years of off grid installs!

Jeremy
All Solar
  - Original Message - 
  From: Allan Sindelar 
  To: RE-wrenches 
  Sent: Thursday, January 24, 2013 12:35 PM
  Subject: [RE-wrenches] 24V Module Query


  Wrenches,
  We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
battery-based customers. Most of our systems are 24V or 48V nominal. Over the 
last few years, sources of conventionally-sized 72-cell modules have dried up - 
as cells have increased in size, most modules and most newer factory production 
lines have either gone to 60-cell (20V) modules, or 72 cells in 300+ watt 
ranges. It seems that the formerly common 72 cell, 24V modules in the 150-190 
watt range, which are well-suited to integrating into existing systems, are no 
longer available.

  60-cell modules in the common 220-250 watt range can't be added to an 
existing system unless run through a dedicated MPPT charge controller that can 
convert voltage, such as an FM, XW60, Classic or TriStar; the added cost of any 
of these controllers cancels out the low prices of the modules.

  Who continues to manufacture 72-cell modules? Which distributors carry them?
  I am aware of three options - are there more?
  - Sunpower makes one module in the 245 watt range that can be used 
negative ground, but it's very high efficiency (and with high Voc/Vmp as well) 
and very pricey;
  - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
pricey;
  - Ameresco bought the rights to manufacture many former BP modules, and I 
think they make some. But we had to replace lots of failed BP modules in that 
size range, and are hesitant to use their technology, fearing that the problems 
may persist in the continued line.

  Thank you for any discussion and recommendations.
  Allan

  -- 
  Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic Installer
  NABCEP Certified Technical Sales Professional
  New Mexico EE98J Journeyman Electrician
  Founder and Chief Technology Officer
  Positive Energy, Inc.
  3209 Richards Lane (note new address)
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com 







--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options  settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules  etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Larry Crutcher, Starlight Solar Power Systems
Blue Sky Energy just came out with a MPPT controller for 60 cell modules called 
the 2512iX-HV. It can handle up to 270 Watts input/60 cells and 340 Watts input 
with 36 cell modules.

Larry Crutcher
Starlight Solar Power Systems




On Jan 24, 2013, at 1:15 PM, Jay Peltz wrote:

Hi guys

I've buying the new 6 cell x 72 cell from Trina from a few suppliers. 
Big yea, but same 44voc  so it's an easy add to existing systems. 

A huge relief. 

Jay

Peltz power

Sent from my iPhone

On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com wrote:

 Hi Allan;
 
 I've been in the same conundrum lately.  I found that AEE and others have 12 
 v modules (Solartech), but the price per watt is double or triple.  My take 
 is that somewhere around 200 to 400 watts, its more cost effective to go to 
 the GT modules with an MPPT controller.  Blue Sky makes the 1524, and 3024 
 that can take up to 57 Voc, so those would work at still fairly low cost.  
 Unfortunately many of the other low cost MPPT controllers won't work with the 
 60 cell modules.  At some point, it may actually be cost effective to just 
 use 60 cell modules with non MPPT controllers, and just forget about the 
 extra 24 cells.  (I know that sounds crazy, but PV less than $1/ watt is 
 crazy too)
 
 I'm trying to add modules to an existing array of 8 Siemens 12 v modules, and 
 it just doesn't work out, except with separate controllers. 
 Also, its amazing how much PV you can throw at an off grid project these days 
 for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting to 
 really up size, and then reuse the old modules for small systems?
 
 Ray
 
 On 1/24/2013 12:35 PM, Allan Sindelar wrote:
 Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
 battery-based customers. Most of our systems are 24V or 48V nominal. Over 
 the last few years, sources of conventionally-sized 72-cell modules have 
 dried up - as cells have increased in size, most modules and most newer 
 factory production lines have either gone to 60-cell (20V) modules, or 72 
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V 
 modules in the 150-190 watt range, which are well-suited to integrating into 
 existing systems, are no longer available.
 
 60-cell modules in the common 220-250 watt range can't be added to an 
 existing system unless run through a dedicated MPPT charge controller that 
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added cost 
 of any of these controllers cancels out the low prices of the modules.
 
 Who continues to manufacture 72-cell modules? Which distributors carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used 
 negative ground, but it's very high efficiency (and with high Voc/Vmp as 
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
 pricey;
 - Ameresco bought the rights to manufacture many former BP modules, and 
 I think they make some. But we had to replace lots of failed BP modules in 
 that size range, and are hesitant to use their technology, fearing that the 
 problems may persist in the continued line.
 
 Thank you for any discussion and recommendations.
 Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:

Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Jason Szumlanski
I'm not sure that AC coupling would work with the old SW inverters.
Assuming they are stacked for 240V, I don't see why it couldn't work. I
would actually like to know because I have dual SW5548's on my farm in the
Caribbean and I am considering adding more PV. Adding PV on the DC side
would be a bit difficult in this case. Since most of the load there is
during the day, I would rather avoid the losses through the batteries and
just add PV on the AC side of the off-grid inverter.

I was making more of a general statement. AC coupling would offset the
impact from reducing the DC PV rating if you lose modules and have to
reconfigure strings. It might not be the cheapest solution, but it might
make the best long-term sense. Every situation is going to be different...

*Jason Szumlanski*

*Fafco Solar*

On Thu, Jan 24, 2013 at 3:49 PM, Allan Sindelar 
al...@positiveenergysolar.com wrote:

  Jason,
 How do you AC couple some microinverters to cover the decrease in
 performance in an off grid system, especially with older equipment, such as
 an SW4024?
 Thanks, Allan


  *Allan Sindelar*
 *al...@positiveenergysolar.com* al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 *Positive Energy, Inc.*
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 *505 424-1112*
 *www.positiveenergysolar.com* http://www.positiveenergysolar.com/

 *
 *

  On 1/24/2013 1:38 PM, Jason Szumlanski wrote:

 I totally agree - old mods are usually not worth messing with at today's
 PV prices. In some cases it might be best to downsize the system and then
 AC couple some microinverters to cover the decrease in performance, or just
 replace the entire array if there are enough problems. There is a used
 market for smaller PV mods on Craigslist.

  Back when I was installing Astropower 110W modules on single voltage
 Xantrex C40's, I never thought we'd be using anything but 12V nominal PV
 mods. Little did I know... Off-grid is really tough in these retrofit
 situations, but this applies to failed/broken mods on grid-tie systems as
 well. That's where I can make a good case for microinverters.

   *Jason Szumlanski** *

 * Fafco Solar
 *


 On Thu, Jan 24, 2013 at 3:11 PM, Ray Walters r...@solarray.com wrote:

  Hi Allan;

 I've been in the same conundrum lately.  I found that AEE and others have
 12 v modules (Solartech), but the price per watt is double or triple.  My
 take is that somewhere around 200 to 400 watts, its more cost effective to
 go to the GT modules with an MPPT controller.  Blue Sky makes the 1524, and
 3024 that can take up to 57 Voc, so those would work at still fairly low
 cost.  Unfortunately many of the other low cost MPPT controllers won't work
 with the 60 cell modules.  At some point, it may actually be cost effective
 to just use 60 cell modules with non MPPT controllers, and just forget
 about the extra 24 cells.  (I know that sounds crazy, but PV less than $1/
 watt is crazy too)

 I'm trying to add modules to an existing array of 8 Siemens 12 v modules,
 and it just doesn't work out, except with separate controllers.
 Also, its amazing how much PV you can throw at an off grid project these
 days for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting
 to really up size, and then reuse the old modules for small systems?

 Ray


 On 1/24/2013 12:35 PM, Allan Sindelar wrote:

  Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for
 battery-based customers. Most of our systems are 24V or 48V nominal. Over
 the last few years, sources of conventionally-sized 72-cell modules have
 dried up - as cells have increased in size, most modules and most newer
 factory production lines have either gone to 60-cell (20V) modules, or 72
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V
 modules in the 150-190 watt range, which are well-suited to integrating
 into existing systems, are no longer available.

 60-cell modules in the common 220-250 watt range can't be added to an
 existing system unless run through a dedicated MPPT charge controller that
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added
 cost of any of these controllers cancels out the low prices of the modules.

 Who continues to manufacture 72-cell modules? Which distributors carry
 them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used
 negative ground, but it's very high efficiency (and with high Voc/Vmp as
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium
 and pricey;
 - Ameresco bought the rights to manufacture many former BP modules,
 and I think they make some. But we had to replace 

Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Larry Crutcher, Starlight Solar Power Systems
One other thingI have been selling 155 watt PV modules, mono with very low 
temp. coefficient of -0.23%/°C,  that are 17.5 Vmp and 21.6 Voc. These are very 
good performance modules and efficient too. 26.5 x 58.3 and Tyco connectors 
attached.

Larry Crutcher
Starlight Solar Power Systems






On Jan 24, 2013, at 1:15 PM, Jay Peltz wrote:

Hi guys

I've buying the new 6 cell x 72 cell from Trina from a few suppliers. 
Big yea, but same 44voc  so it's an easy add to existing systems. 

A huge relief. 

Jay

Peltz power

Sent from my iPhone

On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com wrote:

 Hi Allan;
 
 I've been in the same conundrum lately.  I found that AEE and others have 12 
 v modules (Solartech), but the price per watt is double or triple.  My take 
 is that somewhere around 200 to 400 watts, its more cost effective to go to 
 the GT modules with an MPPT controller.  Blue Sky makes the 1524, and 3024 
 that can take up to 57 Voc, so those would work at still fairly low cost.  
 Unfortunately many of the other low cost MPPT controllers won't work with the 
 60 cell modules.  At some point, it may actually be cost effective to just 
 use 60 cell modules with non MPPT controllers, and just forget about the 
 extra 24 cells.  (I know that sounds crazy, but PV less than $1/ watt is 
 crazy too)
 
 I'm trying to add modules to an existing array of 8 Siemens 12 v modules, and 
 it just doesn't work out, except with separate controllers. 
 Also, its amazing how much PV you can throw at an off grid project these days 
 for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting to 
 really up size, and then reuse the old modules for small systems?
 
 Ray
 
 On 1/24/2013 12:35 PM, Allan Sindelar wrote:
 Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
 battery-based customers. Most of our systems are 24V or 48V nominal. Over 
 the last few years, sources of conventionally-sized 72-cell modules have 
 dried up - as cells have increased in size, most modules and most newer 
 factory production lines have either gone to 60-cell (20V) modules, or 72 
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V 
 modules in the 150-190 watt range, which are well-suited to integrating into 
 existing systems, are no longer available.
 
 60-cell modules in the common 220-250 watt range can't be added to an 
 existing system unless run through a dedicated MPPT charge controller that 
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added cost 
 of any of these controllers cancels out the low prices of the modules.
 
 Who continues to manufacture 72-cell modules? Which distributors carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used 
 negative ground, but it's very high efficiency (and with high Voc/Vmp as 
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
 pricey;
 - Ameresco bought the rights to manufacture many former BP modules, and 
 I think they make some. But we had to replace lots of failed BP modules in 
 that size range, and are hesitant to use their technology, fearing that the 
 problems may persist in the continued line.
 
 Thank you for any discussion and recommendations.
 Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 

[RE-wrenches] 24V Module Query

2013-01-24 Thread Larry Crutcher, Starlight Solar Power Systems

Blue Sky Energy just came out with a MPPT controller for 60 cell modules called 
the 2512iX-HV. It can handle up to 270 Watts input/60 cells and 340 Watts input 
with 36 cell modules.

Larry Crutcher
Starlight Solar Power Systems




On Jan 24, 2013, at 1:15 PM, Jay Peltz wrote:

Hi guys

I've buying the new 6 cell x 72 cell from Trina from a few suppliers. 
Big yea, but same 44voc  so it's an easy add to existing systems. 

A huge relief. 

Jay

Peltz power

Sent from my iPhone

On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com wrote:

 Hi Allan;
 
 I've been in the same conundrum lately.  I found that AEE and others have 12 
 v modules (Solartech), but the price per watt is double or triple.  My take 
 is that somewhere around 200 to 400 watts, its more cost effective to go to 
 the GT modules with an MPPT controller.  Blue Sky makes the 1524, and 3024 
 that can take up to 57 Voc, so those would work at still fairly low cost.  
 Unfortunately many of the other low cost MPPT controllers won't work with the 
 60 cell modules.  At some point, it may actually be cost effective to just 
 use 60 cell modules with non MPPT controllers, and just forget about the 
 extra 24 cells.  (I know that sounds crazy, but PV less than $1/ watt is 
 crazy too)
 
 I'm trying to add modules to an existing array of 8 Siemens 12 v modules, and 
 it just doesn't work out, except with separate controllers. 
 Also, its amazing how much PV you can throw at an off grid project these days 
 for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting to 
 really up size, and then reuse the old modules for small systems?
 
 Ray
 
 On 1/24/2013 12:35 PM, Allan Sindelar wrote:
 Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
 battery-based customers. Most of our systems are 24V or 48V nominal. Over 
 the last few years, sources of conventionally-sized 72-cell modules have 
 dried up - as cells have increased in size, most modules and most newer 
 factory production lines have either gone to 60-cell (20V) modules, or 72 
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V 
 modules in the 150-190 watt range, which are well-suited to integrating into 
 existing systems, are no longer available.
 
 60-cell modules in the common 220-250 watt range can't be added to an 
 existing system unless run through a dedicated MPPT charge controller that 
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added cost 
 of any of these controllers cancels out the low prices of the modules.
 
 Who continues to manufacture 72-cell modules? Which distributors carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used 
 negative ground, but it's very high efficiency (and with high Voc/Vmp as 
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
 pricey;
 - Ameresco bought the rights to manufacture many former BP modules, and 
 I think they make some. But we had to replace lots of failed BP modules in 
 that size range, and are hesitant to use their technology, fearing that the 
 problems may persist in the continued line.
 
 Thank you for any discussion and recommendations.
 Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112
 www.positiveenergysolar.com
 
 
 
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
 
 ___
 List sponsored by Home Power magazine
 
 List Address: RE-wrenches@lists.re-wrenches.org
 
 Options  settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
 List-Archive: 
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
 
 List rules  etiquette:
 www.re-wrenches.org/etiquette.htm
 
 Check out participant bios:
 www.members.re-wrenches.org
 
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:

Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread William Miller

Friends:

Again, welcome to the world of PV design.

I suggest one become accomplished at analyzing IV curves for various PV 
strings.  I created a spreadsheet that helps me analyze these values.  You 
can then see if you can mix and match modules to find workable solutions.


I recently was asked to upgrade a system with a bunch of Arco modules.  I 
found that if I mixed strings of I believe 3 or 4 Arco modules with strings 
of 1 or 2 Solar World modules (exact quantities escape me), I had a pretty 
good match.  We connected these to an MX60.  After install, we tested MPP 
parameters and charging rates of each string individually and the strings 
combined and we found the system worked pretty well.


Good luck,

William Miller

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Allan Sindelar

  
  
(off list) What brand and model are
  they, Larry?
  Allan
  
  


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



 
  On 1/24/2013 2:16 PM, Larry Crutcher, Starlight Solar Power
  Systems wrote:

Sorry, the 155 Watt modules have MC4's, not Tyco.
  

  
  
  
  

  
  
  Larry

  





  
  
  
On Jan 24, 2013, at 12:35 PM, Allan Sindelar wrote:


 Wrenches,
  We have years of installing 36-cell (12V) and 72-cell (24V)
  modules for battery-based customers. Most of our systems are
  24V or 48V nominal. Over the last few years, sources of
  conventionally-sized 72-cell modules have dried up - as cells
  have increased in size, most modules and most newer factory
  production lines have either gone to 60-cell (20V) modules, or
  72 cells in 300+ watt ranges. It seems that the formerly
  common 72 cell, 24V modules in the 150-190 watt range, which
  are well-suited to integrating into existing systems, are no
  longer available.
  
  60-cell modules in the common 220-250 watt range can't be
  added to an existing system unless run through a dedicated
  MPPT charge controller that can convert voltage, such as an
  FM, XW60, Classic or TriStar; the added cost of any of these
  controllers cancels out the low prices of the modules.
  
  Who continues to manufacture 72-cell modules? Which
  distributors carry them?
   I am aware of three options - are there more?
   - Sunpower makes one module in the 245 watt range that can
  be used negative ground, but it's very high efficiency (and
  with high Voc/Vmp as well) and very pricey;
   - Sanyo/Panasonic has 225-240 watt modules, but also quite
  premium and pricey;
   - Ameresco bought the rights to manufacture many former BP
  modules, and I think they make some. But we had to replace
  lots of failed BP modules in that size range, and are hesitant
  to use their technology, fearing that the problems may persist
  in the continued line.
  
  Thank you for any discussion and recommendations.
  Allan
  -- 


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified
Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

  
  
  
  
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




  

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:

Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Allan Sindelar

  
  
Larry,
  Yes, but isn't it 12V-only output? When I called Rick Cullen to
  ask if he had anything to work with 60-cell modules, he told me
  only in 12V output, which we seldom encounter any more.
  Thanks,
  Allan
  
  


Allan Sindelar
al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic
Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



 
  On 1/24/2013 2:01 PM, Larry Crutcher, Starlight Solar Power
  Systems wrote:

Blue Sky Energy just came out with a MPPT controller
  for 60 cell modules called the 2512iX-HV. It can handle up to 270
  Watts input/60 cells and 340 Watts input with 36 cell modules.
  
  
  
  
  

  
Larry Crutcher
  Starlight Solar Power Systems

  


  




  

  
  
  
On Jan 24, 2013, at 1:15 PM, Jay Peltz wrote:



  Hi guys
  
  
  I've buying the new 6" cell x 72 cell from Trina from a
few suppliers.
  Big yea, but same 44voc so it's an easy add to existing
systems.
  
  
  A huge relief.
  
  
  Jay
  
  
  Peltz power
  
Sent from my iPhone
  
On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com
wrote:

  
  

  
  Hi Allan;

I've been in the same conundrum lately. I found that
AEE and others have 12 v modules (Solartech), but the
price per watt is double or triple. My take is that
somewhere around 200 to 400 watts, its more cost
effective to go to the GT modules with an MPPT
controller. Blue Sky makes the 1524, and 3024 that can
take up to 57 Voc, so those would work at still fairly
low cost. Unfortunately many of the other low cost MPPT
controllers won't work with the 60 cell modules. At
some point, it may actually be cost effective to just
use 60 cell modules with non MPPT controllers, and just
forget about the extra 24 cells. (I know that sounds
crazy, but PV less than $1/ watt is crazy too)

I'm trying to add modules to an existing array of 8
Siemens 12 v modules, and it just doesn't work out,
except with separate controllers. 
Also, its amazing how much PV you can throw at an off
grid project these days for $10k.
It almost makes messing around with the old modules a
waste of time.
Perhaps the solution might be to remove old arrays for
customers wanting to really up size, and then reuse the
old modules for small systems?

Ray

On 1/24/2013 12:35 PM, Allan Sindelar wrote:
  
  

Wrenches,
We have years of installing 36-cell (12V) and 72-cell
(24V) modules for battery-based customers. Most of our
systems are 24V or 48V nominal. Over the last few years,
sources of conventionally-sized 72-cell modules have
dried up - as cells have increased in size, most modules
and most newer factory production lines have either gone
to 60-cell (20V) modules, or 72 cells in 300+ watt
ranges. It seems that the formerly common 72 cell, 24V
modules in the 150-190 watt range, which are well-suited
to integrating into existing systems, are no longer
available.

60-cell modules in the common 220-250 watt range can't
be added to an existing system unless run through a
dedicated MPPT charge controller that can convert
voltage, such as an FM, XW60, 

Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread John Berdner
Alan:

You can also use one of our Optimizers with IndOp.
This will buck of boost the module voltage to match the battery voltage.
Still would need some form of charge control to protect the battery but this 
would provide an easy way to add new 60 cell modules to an existing 72 cell 
array.
Feel free to contact me if you have any questions.

Best Regards,

John Berdner
General Manager, North America

[cid:image001.jpg@01CDFA39.F671DEB0]

SolarEdge Technologies, Inc.
3347 Gateway Boulevard, Fremont CA 94538 USA  (*Please note of our new address.)
T: 510.498.3200, X 747
M: 530.277.4894

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Thursday, January 24, 2013 11:35 AM
To: RE-wrenches
Subject: [RE-wrenches] 24V Module Query

Wrenches,
We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
battery-based customers. Most of our systems are 24V or 48V nominal. Over the 
last few years, sources of conventionally-sized 72-cell modules have dried up - 
as cells have increased in size, most modules and most newer factory production 
lines have either gone to 60-cell (20V) modules, or 72 cells in 300+ watt 
ranges. It seems that the formerly common 72 cell, 24V modules in the 150-190 
watt range, which are well-suited to integrating into existing systems, are no 
longer available.

60-cell modules in the common 220-250 watt range can't be added to an existing 
system unless run through a dedicated MPPT charge controller that can convert 
voltage, such as an FM, XW60, Classic or TriStar; the added cost of any of 
these controllers cancels out the low prices of the modules.

Who continues to manufacture 72-cell modules? Which distributors carry them?
I am aware of three options - are there more?
- Sunpower makes one module in the 245 watt range that can be used negative 
ground, but it's very high efficiency (and with high Voc/Vmp as well) and very 
pricey;
- Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
pricey;
- Ameresco bought the rights to manufacture many former BP modules, and I 
think they make some. But we had to replace lots of failed BP modules in that 
size range, and are hesitant to use their technology, fearing that the problems 
may persist in the continued line.

Thank you for any discussion and recommendations.
Allan
--
Allan Sindelar
al...@positiveenergysolar.commailto:al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.comhttp://www.positiveenergysolar.com/


CONFIDENTIALITY NOTICE: This e-mail and its attachments are intended only for 
the use of the individual or entity who is the intended recipient and may 
contain information that is privileged, confidential and exempt from disclosure 
or any type of use under applicable law. If the reader of this e-mail is not 
the intended recipient, or the employee, agent, or representative responsible 
for delivering the e-mail to the intended recipient, you are hereby notified 
that any dissemination, distribution, copying, or other use of this e-mail is 
strictly prohibited. If you have received this e-mail in error, please reply 
immediately to the sender.
P  Please think of the environment before printing this email
inline: image001.jpg___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Ray Walters
Blue Sky's 1524 and 3024 work with 60 cell mods, and have 12 or 24 v 
output.  I have a several 3048s that have been in service for over 12 
years, no problems.



Ray
On 1/24/2013 3:07 PM, Allan Sindelar wrote:

Larry,
Yes, but isn't it 12V-only output? When I called Rick Cullen to ask if 
he had anything to work with 60-cell modules, he told me only in 12V 
output, which we seldom encounter any more.

Thanks,
Allan

*Allan Sindelar*
_Allan@positiveenergysolar.com_ mailto:al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
_www.positiveenergysolar.com_ http://www.positiveenergysolar.com/

*
*


On 1/24/2013 2:01 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
Blue Sky Energy just came out with a MPPT controller for 60 cell 
modules called the 2512iX-HV. It can handle up to 270 Watts input/60 
cells and 340 Watts input with 36 cell modules.


Larry Crutcher
Starlight Solar Power Systems




On Jan 24, 2013, at 1:15 PM, Jay Peltz wrote:

Hi guys

I've buying the new 6 cell x 72 cell from Trina from a few suppliers.
Big yea, but same 44voc  so it's an easy add to existing systems.

A huge relief.

Jay

Peltz power

Sent from my iPhone

On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com 
mailto:r...@solarray.com wrote:



Hi Allan;

I've been in the same conundrum lately.  I found that AEE and others 
have 12 v modules (Solartech), but the price per watt is double or 
triple.  My take is that somewhere around 200 to 400 watts, its more 
cost effective to go to the GT modules with an MPPT controller.  
Blue Sky makes the 1524, and 3024 that can take up to 57 Voc, so 
those would work at still fairly low cost.  Unfortunately many of 
the other low cost MPPT controllers won't work with the 60 cell 
modules.  At some point, it may actually be cost effective to just 
use 60 cell modules with non MPPT controllers, and just forget about 
the extra 24 cells.  (I know that sounds crazy, but PV less than $1/ 
watt is crazy too)


I'm trying to add modules to an existing array of 8 Siemens 12 v 
modules, and it just doesn't work out, except with separate 
controllers.
Also, its amazing how much PV you can throw at an off grid project 
these days for $10k.

It almost makes messing around with the old modules a waste of time.
Perhaps the solution might be to remove old arrays for customers 
wanting to really up size, and then reuse the old modules for small 
systems?


Ray

On 1/24/2013 12:35 PM, Allan Sindelar wrote:

Wrenches,
We have years of installing 36-cell (12V) and 72-cell (24V) modules 
for battery-based customers. Most of our systems are 24V or 48V 
nominal. Over the last few years, sources of conventionally-sized 
72-cell modules have dried up - as cells have increased in size, 
most modules and most newer factory production lines have either 
gone to 60-cell (20V) modules, or 72 cells in 300+ watt ranges. It 
seems that the formerly common 72 cell, 24V modules in the 150-190 
watt range, which are well-suited to integrating into existing 
systems, are no longer available.


60-cell modules in the common 220-250 watt range can't be added to 
an existing system unless run through a dedicated MPPT charge 
controller that can convert voltage, such as an FM, XW60, Classic 
or TriStar; the added cost of any of these controllers cancels out 
the low prices of the modules.


Who continues to manufacture 72-cell modules? Which distributors 
carry them?

I am aware of three options - are there more?
- Sunpower makes one module in the 245 watt range that can be 
used negative ground, but it's very high efficiency (and with high 
Voc/Vmp as well) and very pricey;
- Sanyo/Panasonic has 225-240 watt modules, but also quite 
premium and pricey;
- Ameresco bought the rights to manufacture many former BP 
modules, and I think they make some. But we had to replace lots of 
failed BP modules in that size range, and are hesitant to use their 
technology, fearing that the problems may persist in the continued 
line.


Thank you for any discussion and recommendations.
Allan
--
*Allan Sindelar*
_Allan@positiveenergysolar.com_ mailto:al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
*Positive Energy, Inc.*
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
*505 424-1112*
_www.positiveenergysolar.com_ http://www.positiveenergysolar.com/

*
*




___
List sponsored by Home Power magazine

List Address:RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Ray Walters

  
  
Hi John;
  
  Would we not need an MPPT controller, just a regular PWM type,
  then? That might be a solution for these democracy arrays.
  
  Ray
  
  On 1/24/2013 3:16 PM, John Berdner wrote:


  
  
  
  
  
  

  Alan:
  
  You
  can also use one of our Optimizers with IndOp.
  This
  will buck of boost the module voltage to match the battery
  voltage.
  Still
  would need some form of charge control to protect the
  battery but this would provide an easy way to add new 60
  cell modules to an existing 72 cell array.
  Feel
  free to contact me if you have any questions.
  
  
Best
Regards,

John
Berdner
General
Manager, North America



SolarEdge
Technologies, Inc.
3347
Gateway Boulevard, Fremont CA 94538 USA (*Please
note of our new address.)
T: 510.498.3200, X 747
M:
530.277.4894 
  
  
  

  From:
  re-wrenches-boun...@lists.re-wrenches.org
  [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Allan Sindelar
  Sent: Thursday, January 24, 2013 11:35 AM
  To: RE-wrenches
  Subject: [RE-wrenches] 24V Module Query

  
  
  Wrenches,
We have years of installing 36-cell (12V) and 72-cell (24V)
modules for battery-based customers. Most of our systems are
24V or 48V nominal. Over the last few years, sources of
conventionally-sized 72-cell modules have dried up - as
cells have increased in size, most modules and most newer
factory production lines have either gone to 60-cell (20V)
modules, or 72 cells in 300+ watt ranges. It seems that the
formerly common 72 cell, 24V modules in the 150-190 watt
range, which are well-suited to integrating into existing
systems, are no longer available.

60-cell modules in the common 220-250 watt range can't be
added to an existing system unless run through a dedicated
MPPT charge controller that can convert voltage, such as an
FM, XW60, Classic or TriStar; the added cost of any of these
controllers cancels out the low prices of the modules.

Who continues to manufacture 72-cell modules? Which
distributors carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that
can be used negative ground, but it's very high efficiency
(and with high Voc/Vmp as well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also
quite premium and pricey;
 - Ameresco bought the rights to manufacture many former
BP modules, and I think they make some. But we had to
replace lots of failed BP modules in that size range, and
are hesitant to use their technology, fearing that the
problems may persist in the continued line.

Thank you for any discussion and recommendations.
Allan
  
-- 
  Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified
Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com
  


  

  
  
CONFIDENTIALITY
  NOTICE: This e-mail and its attachments are intended only
  for the use of the individual or entity who is the
  intended recipient and may contain information that is
  privileged, confidential and exempt from disclosure or any
  type of use under applicable law. If the reader of this
  e-mail is not the intended recipient, or the employee,
  agent, or representative responsible for delivering the
  e-mail to the intended recipient, you are hereby notified
  that any dissemination, distribution, copying, or other
  use of this e-mail is strictly

Re: [RE-wrenches] 24V Module Query

2013-01-24 Thread Larry Crutcher, Starlight Solar Power Systems
True, the 2512iX-HV model is for 12 volt systems only. The 1524iX will operate 
with 12 or 24 volt and can handle up to 57Voc. However, in the manual it 
recommends no more than 45.6 Voc for 24 volt operation with 33 to 37 volt 
modules. I'm guessing the conversion efficiency suffers outside that range.

Larry Crutcher
Starlight Solar Power Systems



On Jan 24, 2013, at 3:07 PM, Allan Sindelar wrote:

Larry,
Yes, but isn't it 12V-only output? When I called Rick Cullen to ask if he had 
anything to work with 60-cell modules, he told me only in 12V output, which we 
seldom encounter any more.
Thanks,
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



On 1/24/2013 2:01 PM, Larry Crutcher, Starlight Solar Power Systems wrote:
 Blue Sky Energy just came out with a MPPT controller for 60 cell modules 
 called the 2512iX-HV. It can handle up to 270 Watts input/60 cells and 340 
 Watts input with 36 cell modules.
 
 Larry Crutcher
 Starlight Solar Power Systems
 
 
 
 
 On Jan 24, 2013, at 1:15 PM, Jay Peltz wrote:
 
 Hi guys
 
 I've buying the new 6 cell x 72 cell from Trina from a few suppliers. 
 Big yea, but same 44voc  so it's an easy add to existing systems. 
 
 A huge relief. 
 
 Jay
 
 Peltz power
 
 Sent from my iPhone
 
 On Jan 24, 2013, at 12:11 PM, Ray Walters r...@solarray.com wrote:
 
 Hi Allan;
 
 I've been in the same conundrum lately.  I found that AEE and others have 12 
 v modules (Solartech), but the price per watt is double or triple.  My take 
 is that somewhere around 200 to 400 watts, its more cost effective to go to 
 the GT modules with an MPPT controller.  Blue Sky makes the 1524, and 3024 
 that can take up to 57 Voc, so those would work at still fairly low cost.  
 Unfortunately many of the other low cost MPPT controllers won't work with 
 the 60 cell modules.  At some point, it may actually be cost effective to 
 just use 60 cell modules with non MPPT controllers, and just forget about 
 the extra 24 cells.  (I know that sounds crazy, but PV less than $1/ watt is 
 crazy too)
 
 I'm trying to add modules to an existing array of 8 Siemens 12 v modules, 
 and it just doesn't work out, except with separate controllers. 
 Also, its amazing how much PV you can throw at an off grid project these 
 days for $10k.
 It almost makes messing around with the old modules a waste of time.
 Perhaps the solution might be to remove old arrays for customers wanting to 
 really up size, and then reuse the old modules for small systems?
 
 Ray
 
 On 1/24/2013 12:35 PM, Allan Sindelar wrote:
 Wrenches,
 We have years of installing 36-cell (12V) and 72-cell (24V) modules for 
 battery-based customers. Most of our systems are 24V or 48V nominal. Over 
 the last few years, sources of conventionally-sized 72-cell modules have 
 dried up - as cells have increased in size, most modules and most newer 
 factory production lines have either gone to 60-cell (20V) modules, or 72 
 cells in 300+ watt ranges. It seems that the formerly common 72 cell, 24V 
 modules in the 150-190 watt range, which are well-suited to integrating 
 into existing systems, are no longer available.
 
 60-cell modules in the common 220-250 watt range can't be added to an 
 existing system unless run through a dedicated MPPT charge controller that 
 can convert voltage, such as an FM, XW60, Classic or TriStar; the added 
 cost of any of these controllers cancels out the low prices of the modules.
 
 Who continues to manufacture 72-cell modules? Which distributors carry them?
 I am aware of three options - are there more?
 - Sunpower makes one module in the 245 watt range that can be used 
 negative ground, but it's very high efficiency (and with high Voc/Vmp as 
 well) and very pricey;
 - Sanyo/Panasonic has 225-240 watt modules, but also quite premium and 
 pricey;
 - Ameresco bought the rights to manufacture many former BP modules, and 
 I think they make some. But we had to replace lots of failed BP modules in 
 that size range, and are hesitant to use their technology, fearing that the 
 problems may persist in the continued line.
 
 Thank you for any discussion and recommendations.
 Allan
 -- 
 Allan Sindelar
 al...@positiveenergysolar.com
 NABCEP Certified Photovoltaic Installer
 NABCEP Certified Technical Sales Professional
 New Mexico EE98J Journeyman Electrician
 Founder and Chief Technology Officer
 Positive Energy, Inc.
 3209 Richards Lane (note new address)
 Santa Fe, New Mexico 87507
 505 424-1112