Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-16 Thread Darryl Thayer
If you have 120/208 you have WYE.  How much power do you have to put into the 
grid?  The question if you need back up power what is it for?  if it is simple 
plug loads or lighting you might serve the customer well with single phase 
backup. If you need 3-phase back-up I find it hard to accept that they need it 
in one box. The Xantrex is three seperate inverters on one board that looks 
like 1 box.  The three 120 volt units make 120/208 three phase.If you have 
120/240 three phase you have Delta, high leg.  Other combinations of three 
phase are possible, but more rare. 

I am old and I have never seen a problem of 3 phase imbalance if I stay within 
20% of the panel rating.  In fact I have seen single phase loads that will 
imbalance more than 20% not cause a problem.  The problem of imbalance is 
similar to what occurs with single phase and changed inverter rules to 
requireing a ground reference on 240 volt inverters.  This problem is that the 
neutral will get pushed off center voltage wise, I usually demonstrate this in 
my class.  YOu can not cause significat imbalance with three 120 volt 
inverters, but you could woty the old 208 no neutral inverters.  

Darryl   

--- On Tue, 2/16/10, All Solar Inc. Jeremy Rodriguez  
wrote:

> From: All Solar Inc. Jeremy Rodriguez 
> Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup
> To: "RE-wrenches" 
> Date: Tuesday, February 16, 2010, 9:27 AM
> 
> 
>  
> #yiv965209721 DIV {
> MARGIN:0px;}
> 
> 
>  
>  
> Yes, 
> No  Transformers,
> Single inverter. 
> 
> Another question, looking
> at the Fronius 10.1 and 
> 11.4-3, no battery backup of course, they both list
> 208v in the sizing 
> tool. I need to look at a manual, but I'm not sure
> if I would need 
> Delta, Wye, ..
>  
> Thanks
> everyone!
>  
>  
> 
>   - Original Message
> - 
>   From: 
>   Rebekah 
>   Hren 
>   To: al...@positiveenergysolar.com
> 
>   ; RE-wrenches
> 
>   Sent: Monday,
> February 15, 2010 5:34 
>   PM
>   Subject: Re:
> [RE-wrenches] 3 Phase Grid 
>   Tie with Battery Backup
>   
> 
>   
>   
>   Hi,
>   Does the utility mean by "match" that they
> don't want the inverter output 
>   transformed in any way? 
>   Could you not just use one 120V inverter? I've
> connected single 120 volt 
>   inverters (albeit not outback but I don't see why
> not) to a 120/208 wye 
>   without problems. You have to make sure the wires are
> sized correctly (solar 
>   pro had a recent article on unbalanced 3 phase wire
> sizing). This of course 
>   limits your backed up loads to 120V (w/out a
> transformer).
>   
> 
>   Rebekah Hren
>   North Carolina
>   
> 
> 
>   
> 
>   
> 
>   
>   
>   From: Allan
> Sindelar 
>   
> To: RE-wrenches 
>   
> Sent: Mon, February
> 15, 2010 6:51:12 
>   PM
> Subject: Re:
> [RE-wrenches] 
>   3 Phase Grid Tie with Battery Backup
> 
> Yes you would. I don't 
>   believe there is a single inverter that meets the
> utility's wishes. 
> 
> 
>   
>   
> 
> 
> 
>   
>   Allan Sindelar
> al...@positiveenergysolar.com
> NABCEP Certified 
>   Photovoltaic Installer
> EE98J Journeyman Electrician
> Positive Energy, 
>   Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 
>   424-1112
> www.positiveenergysolar.com
> 
> All 
>   Solar Inc. Jeremy Rodriguez wrote: 
>   Thanks Darryl, 
> Allen, would you have to use 3 
> Sunny Islands?  one for each phase? 
> The Utility wants a single 
> inverter. 
> 
> Jeremy 
> - Original Message - From: "Darryl 
> Thayer"  
> 
> To: "RE-wrenches"  
> 
> Sent: Monday, February 15, 2010 3:49 PM 
> Subject: Re: [RE-wrenches] 3 
> Phase Grid Tie with Battery Backup 
> 
> 
> I do not know what is going 
> on at Outback, but unless they reduced the product
> offering, they have the 
> capability.  I have such a system. 
> 
> Use 3 of their 120 volt 
> single phase inverters connected 3-phase WYE (120/208)
> 3 phase.  Each 
> inverter is only a single phase, and you connect each
> inverter to the 
> neutral and one phase, you program one to be the
> Master, and the others to 
> be slaves on phase B and Phase C.  When you lose
> the grid, the Master 
> inverter starts its sine wave and it generates the
> usual 60 Hz square wave 
> on the Outback Bus and the following slave units delays
> the start of their 
> sin waves by the appropriate 120 degrees to generate 3
> phases.  Each 
> inverter picks up and makes 60 hz 3 phas

Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-16 Thread All Solar Inc. Jeremy Rodriguez
Yes, 
No  Transformers, Single inverter. 
Another question, looking at the Fronius 10.1 and 11.4-3, no battery backup of 
course, they both list 208v in the sizing tool. I need to look at a manual, but 
I'm not sure if I would need Delta, Wye, ..

Thanks everyone!


  - Original Message - 
  From: Rebekah Hren 
  To: al...@positiveenergysolar.com ; RE-wrenches 
  Sent: Monday, February 15, 2010 5:34 PM
  Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup


  Hi,
  Does the utility mean by "match" that they don't want the inverter output 
transformed in any way? 
  Could you not just use one 120V inverter? I've connected single 120 volt 
inverters (albeit not outback but I don't see why not) to a 120/208 wye without 
problems. You have to make sure the wires are sized correctly (solar pro had a 
recent article on unbalanced 3 phase wire sizing). This of course limits your 
backed up loads to 120V (w/out a transformer).


  Rebekah Hren
  North Carolina








--
  From: Allan Sindelar 
  To: RE-wrenches 
  Sent: Mon, February 15, 2010 6:51:12 PM
  Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

  Yes you would. I don't believe there is a single inverter that meets the 
utility's wishes. 


  Allan Sindelar
  al...@positiveenergysolar.com
  NABCEP Certified Photovoltaic Installer
  EE98J Journeyman Electrician
  Positive Energy, Inc.
  3201 Calle Marie
  Santa Fe, New Mexico 87507
  505 424-1112
  www.positiveenergysolar.com



  All Solar Inc. Jeremy Rodriguez wrote: 
Thanks Darryl, 
Allen, would you have to use 3 Sunny Islands?  one for each phase? 
The Utility wants a single inverter. 

Jeremy 
- Original Message - From: "Darryl Thayer"  
To: "RE-wrenches"  
    Sent: Monday, February 15, 2010 3:49 PM 
    Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup 


I do not know what is going on at Outback, but unless they reduced the 
product offering, they have the capability.  I have such a system. 

Use 3 of their 120 volt single phase inverters connected 3-phase WYE 
(120/208) 3 phase.  Each inverter is only a single phase, and you connect each 
inverter to the neutral and one phase, you program one to be the Master, and 
the others to be slaves on phase B and Phase C.  When you lose the grid, the 
Master inverter starts its sine wave and it generates the usual 60 Hz square 
wave on the Outback Bus and the following slave units delays the start of their 
sin waves by the appropriate 120 degrees to generate 3 phases.  Each inverter 
picks up and makes 60 hz 3 phase. 

One thing, besure to get a rotation meter and check that you are generating 
3-phase the same rotation as the grid. Else you will have big problems. (motors 
will reverse and you may fry the OB transfer relay) 

Next time you call outback ask a tech if you can slave the GVFX to make 3 
phase, 

--- On Mon, 2/15/10, All Solar Inc. Jeremy Rodriguez  
wrote: 


  From: All Solar Inc. Jeremy Rodriguez  
      Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup 
  To: starpowe...@juno.com, "RE-wrenches" 
 
  Date: Monday, February 15, 2010, 4:14 PM 
  Jeff, 
  That was my first choice, but I was told by Outback 
  that they do not offer 
  a 120/208 inverter(s). I have not set up a three 
  phase system yet, so bare 
  with me please. I was going to contact SMA next. 

  Jeremy 


  - Original Message - From: "Jeff Oldham"  
  To: ; 
   
  Sent: Monday, February 15, 2010 3:03 PM 
  Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery 
  Backup 


  > You can also do it w/Outback up to 10.8kW 
  > 
  >>From the Solar, Wind and Hydro powered office of 
  Jeff Oldham/Regenerative 
  >>SOLutions 








--


  ___
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread Rebekah Hren
Hi,
Does the utility mean by "match" that they don't want the inverter output 
transformed in any way? 
Could you not just use one 120V inverter? I've connected single 120 volt 
inverters (albeit not outback but I don't see why not) to a 120/208 wye without 
problems. You have to make sure the wires are sized correctly (solar pro had a 
recent article on unbalanced 3 phase wire sizing). This of course limits your 
backed up loads to 120V (w/out a transformer).

Rebekah Hren
North Carolina







From: Allan Sindelar 
To: RE-wrenches 
Sent: Mon, February 15, 2010 6:51:12 PM
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

Yes you would. I don't believe there is a single inverter that meets
the utility's wishes. 


 
AllanSindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com

All Solar Inc. Jeremy Rodriguez wrote: 
Thanks Darryl,
> 
>>Allen, would you have to use 3 Sunny Islands?  one for each phase?
> 
>>The Utility wants a single inverter.
> 
>
>>Jeremy
> 
>>- Original Message - From: "Darryl Thayer"
> 
>>To: "RE-wrenches"  
>>Sent: Monday, February 15, 2010 3:49 PM
> 
>>Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup
> 
>
>
>>I do not know what is going on at Outback, but unless they reduced the
>product offering, they have the capability.  I have such a system.
> 
>
>>Use 3 of their 120 volt single phase inverters connected 3-phase WYE
>(120/208) 3 phase.  Each inverter is only a single phase, and you
>connect each inverter to the neutral and one phase, you program one to
>be the Master, and the others to be slaves on phase B and Phase C. 
>When you lose the grid, the Master inverter starts its sine wave and it
>generates the usual 60 Hz square wave on the Outback Bus and the
>following slave units delays the start of their sin waves by the
>appropriate 120 degrees to generate 3 phases.  Each inverter picks up
>and makes 60 hz 3 phase.
> 
>
>>One thing, besure to get a rotation meter and check that you are
>generating 3-phase the same rotation as the grid. Else you will have
>big problems. (motors will reverse and you may fry the OB transfer
>relay)
> 
>
>>Next time you call outback ask a tech if you can slave the GVFX to make
>3 phase,
> 
>
>>--- On Mon, 2/15/10, All Solar Inc. Jeremy Rodriguez
> wrote:
> 
>
>
>From: All Solar Inc. Jeremy Rodriguez
>> 
>>>>Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup
>> 
>>>>To: starpowe...@juno.com, "RE-wrenches"
>> 
>>>>Date: Monday, February 15, 2010, 4:14 PM
>> 
>>>>Jeff,
>> 
>>>>That was my first choice, but I was told by Outback
>> 
>>>>that they do not offer
>> 
>>>>a 120/208 inverter(s). I have not set up a three
>> 
>>>>phase system yet, so bare
>> 
>>>>with me please. I was going to contact SMA next.
>> 
>>
>>>>Jeremy
>> 
>>
>>
>>>>- Original Message - From: "Jeff Oldham"
>> 
>>>>To: ;
>> 
>> 
>>>>Sent: Monday, February 15, 2010 3:03 PM
>> 
>>>>Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery
>> 
>>>>Backup
>> 
>>
>>
>>>>> You can also do it w/Outback up to 10.8kW
>> 
>>>>>
>> 
>>>>>>From the Solar, Wind and Hydro powered office of
>> 
>>>>Jeff Oldham/Regenerative
>> 
>>>>>>SOLutions
>> 
>>
>>
>


  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread Allan Sindelar




Yes you would. I don't believe there is a single inverter that meets
the utility's wishes. 








 
 

Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread All Solar Inc. Jeremy Rodriguez

Thanks Darryl,
Allen, would you have to use 3 Sunny Islands?  one for each phase?
The Utility wants a single inverter.

Jeremy
- Original Message - 
From: "Darryl Thayer" 

To: "RE-wrenches" 
Sent: Monday, February 15, 2010 3:49 PM
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup


I do not know what is going on at Outback, but unless they reduced the 
product offering, they have the capability.  I have such a system.


Use 3 of their 120 volt single phase inverters connected 3-phase WYE 
(120/208) 3 phase.  Each inverter is only a single phase, and you connect 
each inverter to the neutral and one phase, you program one to be the 
Master, and the others to be slaves on phase B and Phase C.  When you lose 
the grid, the Master inverter starts its sine wave and it generates the 
usual 60 Hz square wave on the Outback Bus and the following slave units 
delays the start of their sin waves by the appropriate 120 degrees to 
generate 3 phases.  Each inverter picks up and makes 60 hz 3 phase.


One thing, besure to get a rotation meter and check that you are generating 
3-phase the same rotation as the grid. Else you will have big problems. 
(motors will reverse and you may fry the OB transfer relay)


Next time you call outback ask a tech if you can slave the GVFX to make 3 
phase,


--- On Mon, 2/15/10, All Solar Inc. Jeremy Rodriguez  
wrote:



From: All Solar Inc. Jeremy Rodriguez 
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup
To: starpowe...@juno.com, "RE-wrenches" 


Date: Monday, February 15, 2010, 4:14 PM
Jeff,
That was my first choice, but I was told by Outback
that they do not offer
a 120/208 inverter(s). I have not set up a three
phase system yet, so bare
with me please. I was going to contact SMA next.

Jeremy


- Original Message - 
From: "Jeff Oldham" 

To: ;

Sent: Monday, February 15, 2010 3:03 PM
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery
Backup


> You can also do it w/Outback up to 10.8kW
>
>>From the Solar, Wind and Hydro powered office of
Jeff Oldham/Regenerative
>>SOLutions
>
>

> Nutrition
> Improve your career health. Click now to study
nutrition!
> 
http://thirdpartyoffers.juno.com/TGL2131/c?cp=cz_Q_kZ_GmgIujsbcDvK8wAAJz3wjMeYFQQEj9ak8QigdzdLAAYAAADNAAASQwA=
> ___
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org






___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread Darryl Thayer
I do not know what is going on at Outback, but unless they reduced the product 
offering, they have the capability.  I have such a system.  

Use 3 of their 120 volt single phase inverters connected 3-phase WYE (120/208) 
3 phase.  Each inverter is only a single phase, and you connect each inverter 
to the neutral and one phase, you program one to be the Master, and the others 
to be slaves on phase B and Phase C.  When you lose the grid, the Master 
inverter starts its sine wave and it generates the usual 60 Hz square wave on 
the Outback Bus and the following slave units delays the start of their sin 
waves by the appropriate 120 degrees to generate 3 phases.  Each inverter picks 
up and makes 60 hz 3 phase.  

One thing, besure to get a rotation meter and check that you are generating 
3-phase the same rotation as the grid. Else you will have big problems.  
(motors will reverse and you may fry the OB transfer relay) 

Next time you call outback ask a tech if you can slave the GVFX to make 3 
phase,

--- On Mon, 2/15/10, All Solar Inc. Jeremy Rodriguez  
wrote:

> From: All Solar Inc. Jeremy Rodriguez 
> Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup
> To: starpowe...@juno.com, "RE-wrenches" 
> Date: Monday, February 15, 2010, 4:14 PM
> Jeff,
> That was my first choice, but  I was told by Outback
> that they do not offer 
> a 120/208 inverter(s).  I have not set up a three
> phase system yet, so bare 
> with me please.  I was going to contact SMA next.
> 
> Jeremy
> 
> 
> - Original Message - 
> From: "Jeff Oldham" 
> To: ;
> 
> Sent: Monday, February 15, 2010 3:03 PM
> Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery
> Backup
> 
> 
> > You can also do it w/Outback up to 10.8kW
> >
> >>From the Solar, Wind and Hydro powered office of
> Jeff Oldham/Regenerative 
> >>SOLutions
> >
> >
> 
> > Nutrition
> > Improve your career health. Click now to study
> nutrition!
> > http://thirdpartyoffers.juno.com/TGL2131/c?cp=cz_Q_kZ_GmgIujsbcDvK8wAAJz3wjMeYFQQEj9ak8QigdzdLAAYAAADNAAASQwA=
> > ___
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: 
> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> > 
> 
> ___
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 


  
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread All Solar Inc. Jeremy Rodriguez

Jeff,
That was my first choice, but  I was told by Outback that they do not offer 
a 120/208 inverter(s).  I have not set up a three phase system yet, so bare 
with me please.  I was going to contact SMA next.


Jeremy


- Original Message - 
From: "Jeff Oldham" 

To: ; 
Sent: Monday, February 15, 2010 3:03 PM
Subject: Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup



You can also do it w/Outback up to 10.8kW

From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative 
SOLutions



Nutrition
Improve your career health. Click now to study nutrition!
http://thirdpartyoffers.juno.com/TGL2131/c?cp=cz_Q_kZ_GmgIujsbcDvK8wAAJz3wjMeYFQQEj9ak8QigdzdLAAYAAADNAAASQwA=
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread Jeff Oldham
You can also do it w/Outback up to 10.8kW

>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative 
>SOLutions


Nutrition
Improve your career health. Click now to study nutrition!
http://thirdpartyoffers.juno.com/TGL2131/c?cp=cz_Q_kZ_GmgIujsbcDvK8wAAJz3wjMeYFQQEj9ak8QigdzdLAAYAAADNAAASQwA=
___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread Allan Sindelar




Sunny Boy/Sunny Island will accomplish this.








 
 

[RE-wrenches] 3 Phase Grid Tie with Battery Backup

2010-02-15 Thread All Solar Inc. Jeremy Rodriguez
Anyone know of a system for Battery Backup that can also be grid tied for  3 
phase?
Our local Utilitly Co. wants system voltage to match service voltage.

Thanks in advance!

Jeremy___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org