Re: [RE-wrenches] 690.47(D)

2017-02-01 Thread Mac Lewis
Hi Mark,

Here in Colorado, we've been on the 2014 code for about 3 years. There have
been various AHJ interpretations.  Unfortunately for us, its kind of ended
up that on all arrays, the inspectors expect a dedicated ground rod
directly adjacent to the array.  This includes arrays mounted on the same
building as the service entrance equipment.  I've had to beg to be able to
run it down the north roof to keep it out of view.  If it happens that the
roof you are mounting to is right near the service entrance, you can use
the existing ground rod.

I think its a very strange requirement and no one quite understands why
this makes these installations safer.

Good luck

On Jan 30, 2017 2:01 PM, "Jason Szumlanski"  wrote:

> Further to August’s reply, here it is:
>
> http://iaeimagazine.org/magazine/2015/06/23/bonding-and-
> grounding-pv-systems/
>
> ​Jason​
>
>
> On Mon, Jan 30, 2017 at 1:47 PM, August Goers  wrote:
>
>> Hi Mark,
>>
>> The current issue of IAEI magazine has an article writing by Bill Brooks
>> called "Hot Topics for PV System Installations." In the article, he
>> directly addresses 2014 NEC 690.47(D).
>>
>> Unfortunately I don't see this article posted online, but you might want
>> to check it out if you can find it.
>>
>> My understanding is that the intent of 690.47(D) is to require an
>> additional electrode when PV is installed on structures that don't already
>> have and electrode system such as a separate building, garage, etc.
>>
>> August
>>
>> -Original Message-
>> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
>> Behalf Of ma...@berkeleysolar.com
>> Sent: Monday, January 30, 2017 10:24 AM
>> To: re-wrenches@lists.re-wrenches.org
>> Subject: [RE-wrenches] 690.47(D)
>>
>> Folks,
>>
>> NEC 2014 is in effect in California. I just pulled a permit for a
>> residential system and it had a little stamp that had 690.47(D) circled as
>> a requirement.
>>
>> Anyone worked with AHJ's in California who are now requiring this? I am
>> planning to not install the electrode, siting Exception 2 and trying to
>> say that the existing electrode next to the build is "next to the array"?
>>
>> Mark
>>
>>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or
> g/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 690.47(D)

2017-01-31 Thread Mike Kocsmiersky
You may also want to cite the 2017 code which does not require the GEC for 
ungrounded inverters, or rather non transformer isolated inverters.  

 

From: Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com] 
Sent: Monday, January 30, 2017 2:55 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] 690.47(D)

 

I don’t think that was the intention necessarily, but I have argued the same 
thing with varying degrees of success. Fortunately (?) we are still on 2011 
here, but 2014 is coming and hopefully AHJs will remain permissive of no 
additional electrode if the home already has one within 6 feet of the service 
entrance (which it almost always does).

 

Jason Szumlanski




 

 

On Mon, Jan 30, 2017 at 1:57 PM, William Miller  wrote:

Mark:

For micro-inverter systems I have successfully argued the application of
Exception No. 1. in that the load is the micro-inverter.

William


Lic 773985
millersolar.com
805-438-5600

-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of ma...@berkeleysolar.com
Sent: Monday, January 30, 2017 10:24 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] 690.47(D)

Folks,

NEC 2014 is in effect in California. I just pulled a permit for a
residential system and it had a little stamp that had 690.47(D) circled as
a requirement.

Anyone worked with AHJ's in California who are now requiring this? I am
planning to not install the electrode, siting Exception 2 and trying to
say that the existing electrode next to the build is "next to the array"?

Mark


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenchesorg> 

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenchesorg> 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

 

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 690.47(D)

2017-01-30 Thread Jason Szumlanski
I don’t think that was the intention necessarily, but I have argued the
same thing with varying degrees of success. Fortunately (?) we are still on
2011 here, but 2014 is coming and hopefully AHJs will remain permissive of
no additional electrode if the home already has one within 6 feet of the
service entrance (which it almost always does).

Jason Szumlanski



On Mon, Jan 30, 2017 at 1:57 PM, William Miller 
wrote:

> Mark:
>
> For micro-inverter systems I have successfully argued the application of
> Exception No. 1. in that the load is the micro-inverter.
>
> William
>
>
> Lic 773985
> millersolar.com
> 805-438-5600
>
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of ma...@berkeleysolar.com
> Sent: Monday, January 30, 2017 10:24 AM
> To: re-wrenches@lists.re-wrenches.org
> Subject: [RE-wrenches] 690.47(D)
>
> Folks,
>
> NEC 2014 is in effect in California. I just pulled a permit for a
> residential system and it had a little stamp that had 690.47(D) circled as
> a requirement.
>
> Anyone worked with AHJ's in California who are now requiring this? I am
> planning to not install the electrode, siting Exception 2 and trying to
> say that the existing electrode next to the build is "next to the array"?
>
> Mark
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
> l
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 690.47(D)

2017-01-30 Thread William Miller
Mark:

For micro-inverter systems I have successfully argued the application of
Exception No. 1. in that the load is the micro-inverter.

William


Lic 773985
millersolar.com
805-438-5600

-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of ma...@berkeleysolar.com
Sent: Monday, January 30, 2017 10:24 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] 690.47(D)

Folks,

NEC 2014 is in effect in California. I just pulled a permit for a
residential system and it had a little stamp that had 690.47(D) circled as
a requirement.

Anyone worked with AHJ's in California who are now requiring this? I am
planning to not install the electrode, siting Exception 2 and trying to
say that the existing electrode next to the build is "next to the array"?

Mark


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 690.47(D)

2017-01-30 Thread Glenn Burt
FYI, this has changed to more of a permissive rule in the 2017 NEC, than the 
mandatory one in 2014.

-Original Message-
From: "August Goers" 
Sent: ‎1/‎30/‎2017 13:47
To: "RE-wrenches" 
Subject: Re: [RE-wrenches] 690.47(D)

Hi Mark,

The current issue of IAEI magazine has an article writing by Bill Brooks
called "Hot Topics for PV System Installations." In the article, he
directly addresses 2014 NEC 690.47(D).

Unfortunately I don't see this article posted online, but you might want
to check it out if you can find it.

My understanding is that the intent of 690.47(D) is to require an
additional electrode when PV is installed on structures that don't already
have and electrode system such as a separate building, garage, etc.

August

-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of ma...@berkeleysolar.com
Sent: Monday, January 30, 2017 10:24 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] 690.47(D)

Folks,

NEC 2014 is in effect in California. I just pulled a permit for a
residential system and it had a little stamp that had 690.47(D) circled as
a requirement.

Anyone worked with AHJ's in California who are now requiring this? I am
planning to not install the electrode, siting Exception 2 and trying to
say that the existing electrode next to the build is "next to the array"?

Mark


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 690.47(D)

2017-01-30 Thread Jason Szumlanski
Further to August’s reply, here it is:

http://iaeimagazine.org/magazine/2015/06/23/bonding-and-grounding-pv-systems/

​Jason​


On Mon, Jan 30, 2017 at 1:47 PM, August Goers  wrote:

> Hi Mark,
>
> The current issue of IAEI magazine has an article writing by Bill Brooks
> called "Hot Topics for PV System Installations." In the article, he
> directly addresses 2014 NEC 690.47(D).
>
> Unfortunately I don't see this article posted online, but you might want
> to check it out if you can find it.
>
> My understanding is that the intent of 690.47(D) is to require an
> additional electrode when PV is installed on structures that don't already
> have and electrode system such as a separate building, garage, etc.
>
> August
>
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of ma...@berkeleysolar.com
> Sent: Monday, January 30, 2017 10:24 AM
> To: re-wrenches@lists.re-wrenches.org
> Subject: [RE-wrenches] 690.47(D)
>
> Folks,
>
> NEC 2014 is in effect in California. I just pulled a permit for a
> residential system and it had a little stamp that had 690.47(D) circled as
> a requirement.
>
> Anyone worked with AHJ's in California who are now requiring this? I am
> planning to not install the electrode, siting Exception 2 and trying to
> say that the existing electrode next to the build is "next to the array"?
>
> Mark
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 690.47(D)

2017-01-30 Thread markf
Thanks August,

I have seen the IAEI article from May-June 2015. It seemed to try the line
that if the exisitng electrode is within 6 feet of the building, then that
same electrode is within 6 feet of the "Array".

I guess my plan at this point is to not install the aux. electrode and use
the IAEI article as my justification and see what the inspector is
thinking.

Mark

> Hi Mark,
>
> The current issue of IAEI magazine has an article writing by Bill Brooks
> called "Hot Topics for PV System Installations." In the article, he
> directly addresses 2014 NEC 690.47(D).
>
> Unfortunately I don't see this article posted online, but you might want
> to check it out if you can find it.
>
> My understanding is that the intent of 690.47(D) is to require an
> additional electrode when PV is installed on structures that don't already
> have and electrode system such as a separate building, garage, etc.
>
> August
>
> -Original Message-
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of ma...@berkeleysolar.com
> Sent: Monday, January 30, 2017 10:24 AM
> To: re-wrenches@lists.re-wrenches.org
> Subject: [RE-wrenches] 690.47(D)
>
> Folks,
>
> NEC 2014 is in effect in California. I just pulled a permit for a
> residential system and it had a little stamp that had 690.47(D) circled as
> a requirement.
>
> Anyone worked with AHJ's in California who are now requiring this? I am
> planning to not install the electrode, siting Exception 2 and trying to
> say that the existing electrode next to the build is "next to the array"?
>
> Mark
>
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
> l
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] 690.47(D)

2017-01-30 Thread August Goers
Hi Mark,

The current issue of IAEI magazine has an article writing by Bill Brooks
called "Hot Topics for PV System Installations." In the article, he
directly addresses 2014 NEC 690.47(D).

Unfortunately I don't see this article posted online, but you might want
to check it out if you can find it.

My understanding is that the intent of 690.47(D) is to require an
additional electrode when PV is installed on structures that don't already
have and electrode system such as a separate building, garage, etc.

August

-Original Message-
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of ma...@berkeleysolar.com
Sent: Monday, January 30, 2017 10:24 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] 690.47(D)

Folks,

NEC 2014 is in effect in California. I just pulled a permit for a
residential system and it had a little stamp that had 690.47(D) circled as
a requirement.

Anyone worked with AHJ's in California who are now requiring this? I am
planning to not install the electrode, siting Exception 2 and trying to
say that the existing electrode next to the build is "next to the array"?

Mark


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm
l

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] 690.47(D)

2017-01-30 Thread markf
Folks,

NEC 2014 is in effect in California. I just pulled a permit for a
residential system and it had a little stamp that had 690.47(D) circled as
a requirement.

Anyone worked with AHJ's in California who are now requiring this? I am
planning to not install the electrode, siting Exception 2 and trying to
say that the existing electrode next to the build is "next to the array"?

Mark


___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org