Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp

2011-01-28 Thread Dave Click

John,
240.4(B) allows the ampacity of a wire to drop below the OCPD rating so 
you could argue that wouldn't be a safety issue. It's always irritated 
me that these NEC derating factors have two decimal places so that you 
feel your calculations are extremely exact... and then your 
carefully-derated-to-126.39A wire has no problem at all on a 150A 
breaker. But that's the way it is.


It takes a lot of heating to exceed the 90C rating of a wire, but yes 
theoretically that would damage the insulation and cause a fault. As for 
voltage drop of your wires, I don't think that's as big an issue as you 
think. Heating from 40C to 80C, a wire is going to see its resistance 
increase by about 15%, so your voltage drop may go from 1.5% to 1.73%. 
Your module voltage drop is going to be the more pressing concern.


If on your drawings you state something like conduits to be minimum 3.5 
inches above the roof (or for residential, put the run in the attic) 
then that puts you at a 17C adder which is pretty manageable for most 
areas of the US (worst case, you're in the 61-70C temp derate range). 
And again, in some cases where you have a very hot section of conduit, 
the 10'/10% rule may let you ignore that localized heating. Since you're 
the one stamping these drawings, you have to stay within your comfort 
zone- add another 10C if you're worried about it and add some extra 
expansion joints. Or you can specify that your contractors shade all 
rooftop conduit, but I imagine that would limit your repeat business.


Dave

John Wadley wrote:

Dave,
Thanks for responding in Mr. Brooks place. Since ASHREA 2% is not the
very worst case, it seems like it might be possible for the ampacity of
the wire chosen to dip below the rating of the OCPD protecting it, if
there is not much margin. I've been trying to rationalize whether this
would become a safety issue. I don't think it would since the OCPD
protects the wire from a current source increasing beyond the expected
design output. I don't think there is much chance of that for a PV
module (unless there was a short between two strings). I think the
increased heating would more likely increase wire resistance/voltage
drop and lower production. With enough voltage drop, the inverter might
shut off.
I guess my new concern is in the most severe case where there is solar
concentration on a short section of conduit. Here, the heating effect of
both the elevated ambient temp and reduced wire resistance might lead to
premature failure of the wire insulation. If the combined heating
effects exceed the 90C rating of the wire, does the insulation embrittle
or melt? In either case, I foresee a grounding fault, and if the GFCI
failed, it could spark a fire.
I know the best solution is to keep conduit shaded and avoid these worst
case solar concentrating conditions. Sometimes. when I design a system
for a new contractor, I don't always know exactly where they plan to run
conduit on a roof (nor can I control it) and I start what-if'ing
whether my design numbers will be conservative enough to prevent a
system failure or a fire.

Thanks and regards,
John Wadley, PE
NABCEP Certified Solar PV Installer (TM)
Wadley Engineering

  Date: Tue, 25 Jan 2011 15:37:20 -0500
  From: Dave Click davecl...@fsec.ucf.edu
  To: re-wrenches@lists.re-wrenches.org
  Subject: Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp
  Message-ID: 4d3f3480.9030...@fsec.ucf.edu
  Content-Type: text/plain; charset=UTF-8; format=flowed
 
  John,
 
  The 2% ambient temperature from ASHRAE is the appropriate starting
  point to use for these calculations. For some additional background I'll
  quote Bill:
 
  **
  ASHRAE bases its ?warm?season temperature conditions? for each city on
  annual percentiles of 0.4%, 1.0% and 2.0%. As an example, the June 2.0%
  dry?bulb design temperature for Atlanta is 91.7?F. Therefore, based on a
  30?day month (i.e. 720 hours), the actual temperatures can be expected
  to exceed 91.7?F a total of 14 hours a month. The corresponding 1.0%
  design temperature (93.1?F) can be expected to be exceeded for 7 hours a
  month; while the 0.4% design temperature (94.6?F) can be expected to be
  exceeded for 3 hours a month (column 2).
  **
 
  In Jim Dunlop's example it sounds like he's starting with the summer
  ambient high (likely around 90F / 32C) and adding the 310.15(B)(2)(c)
  33C figure to reach the 61-70C range.
 
  IMHO, ASHRAE 2% high temperature should be the standard practice for
  these conditions when calculating your base ambient temperature before
  additional adders. There are going to be site-specific conditions like
  your example where the conduits may heat up more than 310.15(B)(2)(c)
  requires; in that case I think you'd be on the right track to make your
  own field measurements to determine an appropriate temperature. In some
  cases the 10%/10ft rule may mean you can ignore short hot spots in the
  wire. If you had a situation where the conduit was in direct

Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp

2011-01-27 Thread David Brearley
John,

Bill has written an article for SolarPro that you may find relevant:

http://solarprofessional.com/article/?file=SP3_6_pg68_Brookssearch=

Here¹s an excerpt:

³...it is important for system designers to perform detailed low dc voltage
calculations for specific array configurations. Designers should use the
highest expected continuous ambient temperature for calculation purposes.
According to the Copper Development Association, the highest ASHRAE
temperature data that is likely to create a 3-hour continuous condition, per
the definition of continuous found in NEC Article 100, is the 2% Annual
Design Dry Bulb Temperature, which is also found in Appendix E of the
Expedited Permit Process for PV Systems. For designers who feel that the
ASHRAE 2% temperature is not high enough, the same table also includes
ASHRAE Extreme Annual Mean Maximum Design Dry Bulb Temperature data, which
can be used for even more conservative voltage or ampacity calculations.²

I realize you are talking about a different set of calculations, but the
rationale for which data to use may still apply.

David Brearley, Senior Technical Editor
SolarPro magazine 
NABCEP Certified PV Installer 
david.brear...@solarprofessional.com
Direct: 541.261.6545



On 1/27/11 1:20 AM, John Wadley wadle...@hotmail.com wrote:

 Dave,
  Thanks for responding in Mr. Brooks place.  Since ASHREA 2% is not the
 very worst case, it seems like it might be possible for the ampacity of the
 wire chosen to dip below the rating of the OCPD protecting it, if there is not
 much margin.  I've been trying to rationalize whether this would become a
 safety issue.  I don't think it would since the OCPD protects the wire from a
 current source increasing beyond the expected design output.  I don't think
 there is much chance of that for a PV module (unless there was a short between
 two strings).  I think the increased heating would more likely increase wire
 resistance/voltage drop and lower production.  With enough voltage drop, the
 inverter might shut off.
  I guess my new concern is in the most severe case where there is solar
 concentration on a short section of conduit.  Here, the heating effect of both
 the elevated ambient temp and reduced wire resistance might lead to premature
 failure of the wire insulation.  If the combined heating effects exceed the
 90C rating of the wire, does the insulation embrittle or melt?  In either
 case, I foresee a grounding fault, and if the GFCI failed, it could spark a
 fire.
  I know the best solution is to keep conduit shaded and avoid these worst
 case solar concentrating conditions.  Sometimes. when I design a system for a
 new contractor, I don't always know exactly where they plan to run conduit on
 a roof (nor can I control it) and I start what-if'ing whether my design
 numbers will be conservative enough to prevent a system failure or a fire.
 
 Thanks and regards,
 John Wadley, PE
 NABCEP Certified Solar PV Installer (TM)
 Wadley Engineering
 

___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp

2011-01-27 Thread John Wadley

David B.,
 Thanks for the reference to this excellent article by Mr. Brooks.  I'm a 
subscriber and fan of SolarPro and have adopted use of this article on several 
projects already.  In fact I'm butting heads with a customer now over this min 
string size check.  I've shown them the calculations, referenced this article 
directly and I'm sure they are aware of the weight behind Mr. Brooks expertise, 
but they are still willing to implement the shorter string size.  I plan to 
make sure they sign something in writing stating they have been informed of the 
potential consequences of their decision.
 
 If I see a situation where I think the contractor might install conduit 
that does not meet standard practices or may experience abnormally high ambient 
temps, I'll use the more conservative number (ASHRAE Extreme Annual Mean 
Maximum Design Dry Bulb Temperature ) to protect myself and the end customer.  
Otherwise, I'll have to force them to show conduit runs on a site layout 
drawing and say any change from that has to be approved through me.

Best Regards,
John Wadley, PE
NABCEP Certified Solar PV Installer (TM)
Wadley Engineering

 Date: Thu, 27 Jan 2011 09:02:31 -0600
 From: David Brearley david.brear...@solarprofessional.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp
 Message-ID: c966e527.b6e2%david.brear...@solarprofessional.com
 Content-Type: text/plain; charset=iso-8859-1
 
 John,
 
 Bill has written an article for SolarPro that you may find relevant:
 
 http://solarprofessional.com/article/?file=SP3_6_pg68_Brookssearch=
 
 Here?s an excerpt:
 
 ?...it is important for system designers to perform detailed low dc voltage
 calculations for specific array configurations. Designers should use the
 highest expected continuous ambient temperature for calculation purposes.
 According to the Copper Development Association, the highest ASHRAE
 temperature data that is likely to create a 3-hour continuous condition, per
 the definition of continuous found in NEC Article 100, is the 2% Annual
 Design Dry Bulb Temperature, which is also found in Appendix E of the
 Expedited Permit Process for PV Systems. For designers who feel that the
 ASHRAE 2% temperature is not high enough, the same table also includes
 ASHRAE Extreme Annual Mean Maximum Design Dry Bulb Temperature data, which
 can be used for even more conservative voltage or ampacity calculations.?
 
 I realize you are talking about a different set of calculations, but the
 rationale for which data to use may still apply.
 
 David Brearley, Senior Technical Editor
 SolarPro magazine 
 NABCEP Certified PV Installer ?
 david.brear...@solarprofessional.com
 Direct: 541.261.6545
 
 
 
 On 1/27/11 1:20 AM, John Wadley wadle...@hotmail.com wrote:
 
  Dave,
  Thanks for responding in Mr. Brooks place. Since ASHREA 2% is not the
  very worst case, it seems like it might be possible for the ampacity of the
  wire chosen to dip below the rating of the OCPD protecting it, if there is 
  not
  much margin. I've been trying to rationalize whether this would become a
  safety issue. I don't think it would since the OCPD protects the wire from a
  current source increasing beyond the expected design output. I don't think
  there is much chance of that for a PV module (unless there was a short 
  between
  two strings). I think the increased heating would more likely increase wire
  resistance/voltage drop and lower production. With enough voltage drop, the
  inverter might shut off.
  I guess my new concern is in the most severe case where there is solar
  concentration on a short section of conduit. Here, the heating effect of 
  both
  the elevated ambient temp and reduced wire resistance might lead to 
  premature
  failure of the wire insulation. If the combined heating effects exceed the
  90C rating of the wire, does the insulation embrittle or melt? In either
  case, I foresee a grounding fault, and if the GFCI failed, it could spark a
  fire.
  I know the best solution is to keep conduit shaded and avoid these worst
  case solar concentrating conditions. Sometimes. when I design a system for a
  new contractor, I don't always know exactly where they plan to run conduit 
  on
  a roof (nor can I control it) and I start what-if'ing whether my design
  numbers will be conservative enough to prevent a system failure or a fire.
  
  Thanks and regards,
  John Wadley, PE
  NABCEP Certified Solar PV Installer (TM)
  Wadley Engineering
  
  ___
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options  settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules  etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re

Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp

2011-01-26 Thread John Wadley

Dave,
 Thanks for responding in Mr. Brooks place.  Since ASHREA 2% is not the 
very worst case, it seems like it might be possible for the ampacity of the 
wire chosen to dip below the rating of the OCPD protecting it, if there is not 
much margin.  I've been trying to rationalize whether this would become a 
safety issue.  I don't think it would since the OCPD protects the wire from a 
current source increasing beyond the expected design output.  I don't think 
there is much chance of that for a PV module (unless there was a short between 
two strings).  I think the increased heating would more likely increase wire 
resistance/voltage drop and lower production.  With enough voltage drop, the 
inverter might shut off.
 I guess my new concern is in the most severe case where there is solar 
concentration on a short section of conduit.  Here, the heating effect of both 
the elevated ambient temp and reduced wire resistance might lead to premature 
failure of the wire insulation.  If the combined heating effects exceed the 90C 
rating of the wire, does the insulation embrittle or melt?  In either case, I 
foresee a grounding fault, and if the GFCI failed, it could spark a fire.
 I know the best solution is to keep conduit shaded and avoid these worst 
case solar concentrating conditions.  Sometimes. when I design a system for a 
new contractor, I don't always know exactly where they plan to run conduit on a 
roof (nor can I control it) and I start what-if'ing whether my design numbers 
will be conservative enough to prevent a system failure or a fire.

Thanks and regards,
John Wadley, PE
NABCEP Certified Solar PV Installer (TM)
Wadley Engineering

 Date: Tue, 25 Jan 2011 15:37:20 -0500
 From: Dave Click davecl...@fsec.ucf.edu
 To: re-wrenches@lists.re-wrenches.org
 Subject: Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp
 Message-ID: 4d3f3480.9030...@fsec.ucf.edu
 Content-Type: text/plain; charset=UTF-8; format=flowed
 
 John,
 
 The 2% ambient temperature from ASHRAE is the appropriate starting 
 point to use for these calculations. For some additional background I'll 
 quote Bill:
 
 **
 ASHRAE bases its ?warm?season temperature conditions? for each city on 
 annual percentiles of 0.4%, 1.0% and 2.0%. As an example, the June 2.0% 
 dry?bulb design temperature for Atlanta is 91.7?F. Therefore, based on a 
 30?day month (i.e. 720 hours), the actual temperatures can be expected 
 to exceed 91.7?F a total of 14 hours a month. The corresponding 1.0% 
 design temperature (93.1?F) can be expected to be exceeded for 7 hours a 
 month; while the 0.4% design temperature (94.6?F) can be expected to be 
 exceeded for 3 hours a month (column 2).
 **
 
 In Jim Dunlop's example it sounds like he's starting with the summer 
 ambient high (likely around 90F / 32C) and adding the 310.15(B)(2)(c) 
 33C figure to reach the 61-70C range.
 
 IMHO, ASHRAE 2% high temperature should be the standard practice for 
 these conditions when calculating your base ambient temperature before 
 additional adders. There are going to be site-specific conditions like 
 your example where the conduits may heat up more than 310.15(B)(2)(c) 
 requires; in that case I think you'd be on the right track to make your 
 own field measurements to determine an appropriate temperature. In some 
 cases the 10%/10ft rule may mean you can ignore short hot spots in the 
 wire. If you had a situation where the conduit was in direct sunlight, 
 plus light was being reflected off the roof and a light-colored wall 
 behind the conduit, I suppose that would yield more heating than what 
 the CDA study had found (http://www.iaei.org/magazine/?p=1743). I'm not 
 sure that shooting an IR thermometer is the best option here; if you 
 want to best replicate the study conditions, you may put a conduit 
 section up on the roof in the desired location, put a temperature sensor 
 in the conduit, and let it soak. Then compare that number with [ASHRAE 
 2% + 310.15(B)(2)(c)] and pick the higher number. Or just add an 
 additional 10C on top of ASHRAE+B2c and be done with it...
 
 I think your plan of trying to measure the temperature 4 off the roof 
 where the conduit sits, and then adding the additional 17C (or whatever) 
 from the Table, will be too conservative; your initial measurement will 
 be affected by some of the heating that's wrapped into the 
 310.15(B)(2)(c) factor and you'd be double-counting that effect.
 
 Hope that helps.
 Dave
 
  Original Message 
 Subject: [RE-wrenches] Cable Sizing - revisited, Ambient Temp
 From: John Wadley wadle...@hotmail.com
 To: RE-wrenches re-wrenches@lists.re-wrenches.org
 Date: 2011/1/22 02:40
 
  Mr. Brooks,
  You replied to Mr. Parrish back in 2009 with this example (below) on
  properly applying all the deratings to ampacity for wire sizing. I have
  a bit of confusion and a question about the definition of ambient
  temperature. You define it below as the ASHREA 2% high temp. My NEC

Re: [RE-wrenches] Cable Sizing - revisited, Ambient Temp

2011-01-25 Thread Dave Click

John,

The 2% ambient temperature from ASHRAE is the appropriate starting 
point to use for these calculations. For some additional background I'll 
quote Bill:


**
ASHRAE bases its ‘warm‐season temperature conditions’ for each city on 
annual percentiles of 0.4%, 1.0% and 2.0%. As an example, the June 2.0% 
dry‐bulb design temperature for Atlanta is 91.7°F. Therefore, based on a 
30‐day month (i.e. 720 hours), the actual temperatures can be expected 
to exceed 91.7°F a total of 14 hours a month. The corresponding 1.0% 
design temperature (93.1°F) can be expected to be exceeded for 7 hours a 
month; while the 0.4% design temperature (94.6°F) can be expected to be 
exceeded for 3 hours a month (column 2).

**

In Jim Dunlop's example it sounds like he's starting with the summer 
ambient high (likely around 90F / 32C) and adding the 310.15(B)(2)(c) 
33C figure to reach the 61-70C range.


IMHO, ASHRAE 2% high temperature should be the standard practice for 
these conditions when calculating your base ambient temperature before 
additional adders. There are going to be site-specific conditions like 
your example where the conduits may heat up more than 310.15(B)(2)(c) 
requires; in that case I think you'd be on the right track to make your 
own field measurements to determine an appropriate temperature. In some 
cases the 10%/10ft rule may mean you can ignore short hot spots in the 
wire. If you had a situation where the conduit was in direct sunlight, 
plus light was being reflected off the roof and a light-colored wall 
behind the conduit, I suppose that would yield more heating than what 
the CDA study had found (http://www.iaei.org/magazine/?p=1743). I'm not 
sure that shooting an IR thermometer is the best option here; if you 
want to best replicate the study conditions, you may put a conduit 
section up on the roof in the desired location, put a temperature sensor 
in the conduit, and let it soak. Then compare that number with [ASHRAE 
2% + 310.15(B)(2)(c)] and pick the higher number. Or just add an 
additional 10C on top of ASHRAE+B2c and be done with it...


I think your plan of trying to measure the temperature 4 off the roof 
where the conduit sits, and then adding the additional 17C (or whatever) 
from the Table, will be too conservative; your initial measurement will 
be affected by some of the heating that's wrapped into the 
310.15(B)(2)(c) factor and you'd be double-counting that effect.


Hope that helps.
Dave

 Original Message 
Subject: [RE-wrenches] Cable Sizing - revisited, Ambient Temp
From: John Wadley wadle...@hotmail.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: 2011/1/22 02:40


Mr. Brooks,
You replied to Mr. Parrish back in 2009 with this example (below) on
properly applying all the deratings to ampacity for wire sizing. I have
a bit of confusion and a question about the definition of ambient
temperature. You define it below as the ASHREA 2% high temp. My NEC
2008 (310.15 (2) Except No. 5 (3) (b) FPN) mentions it being an average
ASHREA number. The only definition for ambient temp in NEC I could
find was 310.10 FPN (1) which says it varies along the length of the
conductor by time and place. In the Photovoltaic Systems by Dunlop, p.
288, he cites a sizing example without saying where ambient comes from
but uses 61C-70C (142F-158F) derate factor (0.58) for a sunlit roof top
conduit. He does not say how he arrives at that tempature range, but I
suspect he started with the 90F rating of the USE-2 conductor in the
example and added a Table 310.15 (B) (2) (c) adder of 33C. Other
articles I've read talk about conditions like an unventilated attic or a
sunlit jbox on a roof where ambient temps could reach 150F. I can also
think of a situation where on a flat roof with a surrounding parapet
wall, the sunlight shining into a corner would act like a solar oven on
any conduit running close to the corner. So, given all these definitions
and possible exceptions to the definition of ambient temperature, does
your original definition (ASHREA 2% high temp) still stand as standard
practice for most conditions and are there situations where one should
use something other than that defined value? If one is unsure of an
exceptional situation, would it make sense to use an IR thermometer to
measure free air temp on a sunny, calm day and then the air temp exactly
where conduit might run and use the temp delta as an adder (like Table
310.15 (B) 2 (c)) to the ASHREA 2% high temp to arrive at a new,
situational ambient temp before applying the other factors cited?

Thanks in advance,
John Wadley, PE
Wadley Engineering
NABCEP Certified Solar PV Installer (TM)
Dallas, TX

Peter,

We cannot use load diversity to increase the number of conductors in a PV
conduit since there generally is little diversity among the conductors,
particularly on large arrays.

The more traditional conduit adjustment table to use is Table
310.15(B)(2)(a). The value from this table is multiplied

[RE-wrenches] Cable Sizing - revisited, Ambient Temp

2011-01-21 Thread John Wadley

Mr. Brooks,
 You replied to Mr. Parrish back in 2009 with this example (below) on 
properly applying all the deratings to ampacity for wire sizing.  I have a bit 
of confusion and a question about the definition of ambient temperature.  You 
define it below as the ASHREA 2% high temp.  My NEC 2008 (310.15 (2) Except No. 
5 (3) (b) FPN) mentions it being an average ASHREA number.  The only 
definition for ambient temp in NEC I could find was 310.10 FPN (1) which says 
it varies along the length of the conductor by time and place.  In the 
Photovoltaic Systems by Dunlop, p. 288, he cites a sizing example without 
saying where ambient comes from but uses 61C-70C (142F-158F) derate factor 
(0.58) for a sunlit roof top conduit.  He does not say how he arrives at that 
tempature range, but I suspect he started with the 90F rating of the USE-2 
conductor in the example and added a Table 310.15 (B) (2) (c) adder of 33C.  
Other articles I've read talk about conditions like an unventilated attic or a 
sunlit jbox on a roof where ambient temps could reach 150F.  I can also think 
of a situation where on a flat roof with a surrounding parapet wall, the 
sunlight shining into a corner would act like a solar oven on any conduit 
running close to the corner.  So, given all these definitions and possible 
exceptions to the definition of ambient temperature, does your original 
definition (ASHREA 2% high temp) still stand as standard practice for most 
conditions and are there situations where one should use something other than 
that defined value?  If one is unsure of an exceptional situation, would it 
make sense to use an IR thermometer to measure free air temp on a sunny, calm 
day and then the air temp exactly where conduit might run and use the temp 
delta as an adder (like Table 310.15 (B) 2 (c)) to the ASHREA 2% high temp to 
arrive at a new, situational ambient temp before applying the other factors 
cited?
 
Thanks in advance,
John Wadley, PE
Wadley Engineering
NABCEP Certified Solar PV Installer (TM)
Dallas, TX
Peter,

We cannot use load diversity to increase the number of conductors in a PV
conduit since there generally is little diversity among the conductors,
particularly on large arrays.

The more traditional conduit adjustment table to use is Table
310.15(B)(2)(a). The value from this table is multiplied by the temperature
adjustment factor in Table 310.16. The key is what to use as the ambient
temperature in Table 310.16. We also have the third adjustment of Table
310.15(B)(2)(c) in the 2008 NEC for conduit close to rooftops. Even if you
are excused from using the 2008 NEC by a jurisdiction, the 2005 NEC has
310.10 FPN2 that generally recommends a 17C adder on ambient temperature.

The NEC has not had any explanation as to what ambient temperature to use
until the 2008 NEC in the FPN to Table 310.15(B)(2)(c) when it referenced
ASHRAE data in an incorrect way. To be consistent with the Copper
Development Industry, we have put a proposal into the 2011 NEC to use the
ASHRAE 2% design temperatures. These values can be downloaded at
www.copper.org.

Summarizing in an example:

Assume that 8 current carrying conductors, with and Imax of 10 amps [as
defined by 690.8(a)], are in a conduit in direct sun 4 off the roof deck in
Palm Springs, California. What must be the 30C ampacity of the conductor to
meet the requirement?

Answer:

I(30C) = 10A/(conduit fill adjustment)/(Temp adjustment--direct sunlit
conduit)

Conduit fill adjustment factor = 0.7 (70%)

Direct sunlit conduit temperature = +17C above ambient
2% Design Temp for Palm Springs = 44.1C (ASHRAE 2005 Fundamentals)
Design temp = 44.1 + 17 = 61.1C --corresponds to a 0.58 factor for 90C
conductors

I(30C) = 10A/0.7/0.58 = 24.63 amps -- minimum conductor size is 14 AWG
(barely)

Most inspectors will quickly cite the fact that the ampacity cannot be
greater than the 75C column, so we check to make sure (nearly always is just
fine). The 75C column says that 14 AWG wire can handle 20 amps (Imax is
10amps) at 30C but the asterisk limits our overcurrent protection to 15 amps
(since the module has a 15 amp max fuse rating, we are already using the
required 15 amp device).

The upshot is that even a 14 AWG 90C conductor works in almost the hottest
climate in the U.S. as long as only 8 conductors or less in conduit, conduit
is at least 4 above roof, and no more than 10 amps flowing through it. Most
contractors will use 10AWG for small systems and occasionally 12AWG. 10AWG
makes it simple since it meets all wiring options in today's smaller
systems. 12AWG works in many cases, and, as our example shows, even 14 AWG
works in some circumstances (we're talking ampacity, not voltage
drop--that's a different issue). In large systems, generally we specify the
minimum wire since it adds up after a few miles of conductor.

Now wasn't that fun--I can't believe anyone could be put to sleep by that
(maybe want to commit suicide, but no sleeping here). The short answer is